1

Közepes

Why is ammonia (R717) classed as a toxic refrigerant?


Because it is heavier than air and displaces oxygen
Because it does not react with water, making neutralisation difficult
It severely irritates the respiratory tract, eyes and skin, and is poisonous when inhaled at higher concentrations
Because it is colourless and odourless and therefore hard to detect

2

Nehéz

What is the main difference between a dry-expansion and a flooded evaporator?


A dry-expansion evaporator always has a lower pressure than a flooded one
A dry-expansion evaporator needs no expansion valve, a flooded one does
A dry-expansion evaporator is filled with liquid, a flooded one with vapour
In a dry-expansion evaporator the refrigerant completely evaporates and is superheated in the evaporator; in a flooded one part of the refrigerant remains liquid (incomplete evaporation, no superheat)

3

Nehéz

What is the typical pressure in the evaporator of an R717 deep-freeze system (below −40 °C)?


Atmospheric pressure, approx. 1 bar abs
Positive pressure of 10–20 bar
Positive pressure of 5–10 bar
Below atmospheric (approx. 0.7 bar abs at −40 °C)

4

Könnyű

What is the basic requirement when charging a system with R717 (NH₃)?


Charging must only take place at temperatures below 0°C
NH₃ can be charged together with air
Charging can be carried out without personal protective equipment
Charging should take place in a well-ventilated area using appropriate personal protective equipment

5

Nehéz

How is oil managed in R717 systems?


Oil collecting at the lowest points of vessels is regularly checked and drained, because it impairs heat transfer
Oil can be mixed with any refrigerant
Oil has no effect on system operation
Oil requires no monitoring

6

Könnyű

What is the correct procedure for recovering R717 from a system?


The gas can be released into the atmosphere
Recovery is not required
The refrigerant can be drained into the sewer system
The refrigerant must be recovered into suitable, leak-proof tanks designed for NH₃

7

Könnyű

How should R717 (NH₃) be stored?


In unmarked plastic containers
In sealed, labelled containers, in a cool and well-ventilated place
Near heat sources
In any open containers

8

Nehéz

What should be done with contaminated R717?


Purify it or send it for disposal in accordance with regulations
Dilute it with water and reuse it
Release it into the atmosphere
Continue to use it without restriction

9

Könnyű

What is the main hazard associated with an R717 leak during maintenance work?


Increased cooling efficiency
Toxic to humans and may cause chemical burns
Damage to electrical equipment only
No risk whatsoever

10

Nehéz

What should be done if an NH₃ leak is detected?


Carry on working wearing a dust mask
Increase the pressure in the system
Carry on working with the room door open
Evacuate people immediately and raise the alarm; stop the leak only if it is safe to do so and with suitable PPE (respiratory protection)

11

Nehéz

What role do scrubbers play in NH₃ systems?


They are used to measure temperature
They increase the pressure in the system
They store the refrigerant
Neutralise ammonia through absorption in a liquid (e.g. water)

12

Nehéz

How should the system be prepared before filling with R717?


Check for leaks, remove air and moisture, and create a vacuum
The pressure must be increased above the standard level
There is no need to check it
Simply start it up

13

Nehéz

What are the transport requirements for R717?


It can be carried in open containers
It can be carried without labelling
It must be carried in suitable, labelled packagings in accordance with ADR (UN 1005, class 2, code 2TC)
Transport is not regulated

14

Könnyű

What personal protective equipment is required when working with NH₃?


No requirements
Workwear only
Only a safety helmet
Safety goggles, gloves and respiratory protective equipment

15

Nehéz

Which statement best describes the behaviour of R717 and mineral compressor oil?


An oil return line cannot be used in R717 systems because the oil is too hot
R717 does not mix with the oil; the oil collects on the high-pressure side above the R717
R717 does not mix with the oil; the oil, being heavier than liquid NH₃, collects beneath it at the lowest points (mainly on the low-pressure side)
R717 mixes very well with the oil, which easily returns to the compressor

16

Nehéz

Which refrigerant can be detected with phenolphthalein paper?


R1270
R744
R1234ze(E)
R717

17

Nehéz

Which system may require manual oil recovery?


An R717 system
Supercritical ‘booster’ system using R744
Secondary system using R744
R744 cascade system

18

Nehéz

Which refrigerant is lighter than air?


R1234ze(E)
R1270
R744
R717

19

Nehéz

R717 is highly corrosive to:


aluminium
titanium
stainless steel
copper (and its alloys)

20

Nehéz

What is the recommended pre-alarm level for fixed leak detection systems for R717?


500,000 ppm
500 ppm
5,000 ppm
50,000 ppm

21

Nehéz

Why are compressors with a separate motor (open type) mostly used in R717 systems?


Because they are cheaper
Because NH₃ attacks copper motor windings, so hermetic compressors with conventional windings are not used
To increase the refrigerant charge
To lower the condensing pressure

22

Nehéz

Which type of compressor is most commonly used in large ammonia systems?


Hermetic scroll
Rotary vane compressor
Diaphragm compressor
A reciprocating or screw compressor

23

Nehéz

How is the capacity of a piston compressor regulated in NH₃ systems?


By reducing the refrigerant charge
By unloading the cylinders or changing the rotational speed
Solely by adjusting the oil volume
By increasing the condensing pressure

24

Nehéz

How is the capacity of a screw compressor most commonly controlled?


By using a slide valve
By changing the type of oil
By closing the suction valve
By adjusting the oil level

25

Nehéz

When is two-stage compression used in NH₃ systems?


At low evaporating temperatures (pressures) and high pressure ratios
At small temperature differences
Only with water-cooled condensers
Only in small systems

26

Nehéz

What is the advantage of two-stage compression over single-stage compression?


No need for a separator
Lower efficiency
Higher efficiency and lower discharge temperature
Higher energy consumption

27

Nehéz

How does an evaporative condenser used in NH₃ systems work?


It utilises the evaporation of water to increase cooling efficiency
It transfers heat only to the air
Operates without a fan
It does not require a water supply

28

Nehéz

What is the function of the liquid separator in an NH₃ system?


It prevents liquid from entering the compressor
Increases the discharge temperature
Regulates the condensing pressure
It separates oil from the refrigerant

29

Nehéz

What is the purpose of monitoring the liquid level in the separator?


To control the condenser fan
To reduce the condensing temperature
To increase the oil volume
To maintain the correct refrigerant level and prevent the compressor from flooding

30

Nehéz

What is the role of the float switch in NH₃ systems?


It regulates the condensation temperature
It controls the fan’s operation
It monitors the liquid level in the tank or separator
It is used to detect leaks

31

Nehéz

What is a thermosyphon in NH₃ systems?


A defrosting device
A type of safety valve
An oil circulation pump
A system with gravity-driven (natural) circulation of liquid refrigerant caused by density differences, used e.g. for screw compressor oil cooling

32

Nehéz

Why are oils that are immiscible with the refrigerant used in NH₃ systems?


To increase the amount of refrigerant
Because NH₃ does not mix with most compressor oils
Because the oil mixes only with water
To reduce the pressure

33

Nehéz

What is the main function of an oil separator in NH₃ systems?


To lower the condensation temperature
Removing moisture from the system
To separate the oil from the refrigerant and return the oil to the compressor
To increase fan efficiency

34

Nehéz

In which NH₃ system does the refrigerant evaporate completely with superheat in the evaporator, fed by an expansion valve?


A direct-expansion (DX) system
An indirect system
A glycol system
A pumped liquid-recirculation system

35

Nehéz

What is the characteristic feature of a flooded evaporator system?


No level control is required
No separator is used
The evaporator contains a large amount of liquid, which improves heat transfer
The evaporator is filled exclusively with vapour

36

Nehéz

What is the main difference between a direct and an indirect system?


In a direct system, there is no evaporator
In an indirect system, no compressor is used
In an indirect system, NH₃ flows directly into the space being cooled
In an indirect system, NH₃ cools an intermediate medium (e.g. glycol), which in turn cools the load

37

Közepes

Which property of ammonia helps people detect a leak early?


It is denser than air
A very low odour threshold (a few ppm)
It is yellow in air
It is odourless