1

Közepes

Why is ammonia (R717) classed as a toxic refrigerant?


Because it is colourless and odourless and therefore hard to detect
Because it is heavier than air and displaces oxygen
It severely irritates the respiratory tract, eyes and skin, and is poisonous when inhaled at higher concentrations
Because it does not react with water, making neutralisation difficult

2

Nehéz

What is the main difference between a dry-expansion and a flooded evaporator?


A dry-expansion evaporator always has a lower pressure than a flooded one
A dry-expansion evaporator needs no expansion valve, a flooded one does
In a dry-expansion evaporator the refrigerant completely evaporates and is superheated in the evaporator; in a flooded one part of the refrigerant remains liquid (incomplete evaporation, no superheat)
A dry-expansion evaporator is filled with liquid, a flooded one with vapour

3

Nehéz

What is the typical pressure in the evaporator of an R717 deep-freeze system (below −40 °C)?


Positive pressure of 10–20 bar
Atmospheric pressure, approx. 1 bar abs
Below atmospheric (approx. 0.7 bar abs at −40 °C)
Positive pressure of 5–10 bar

4

Könnyű

What is the basic requirement when charging a system with R717 (NH₃)?


NH₃ can be charged together with air
Charging should take place in a well-ventilated area using appropriate personal protective equipment
Charging must only take place at temperatures below 0°C
Charging can be carried out without personal protective equipment

5

Nehéz

How is oil managed in R717 systems?


Oil can be mixed with any refrigerant
Oil requires no monitoring
Oil has no effect on system operation
Oil collecting at the lowest points of vessels is regularly checked and drained, because it impairs heat transfer

6

Könnyű

What is the correct procedure for recovering R717 from a system?


The refrigerant must be recovered into suitable, leak-proof tanks designed for NH₃
The gas can be released into the atmosphere
Recovery is not required
The refrigerant can be drained into the sewer system

7

Könnyű

How should R717 (NH₃) be stored?


In sealed, labelled containers, in a cool and well-ventilated place
In any open containers
In unmarked plastic containers
Near heat sources

8

Nehéz

What should be done with contaminated R717?


Release it into the atmosphere
Dilute it with water and reuse it
Continue to use it without restriction
Purify it or send it for disposal in accordance with regulations

9

Könnyű

What is the main hazard associated with an R717 leak during maintenance work?


Damage to electrical equipment only
Toxic to humans and may cause chemical burns
No risk whatsoever
Increased cooling efficiency

10

Nehéz

What should be done if an NH₃ leak is detected?


Carry on working wearing a dust mask
Increase the pressure in the system
Evacuate people immediately and raise the alarm; stop the leak only if it is safe to do so and with suitable PPE (respiratory protection)
Carry on working with the room door open

11

Nehéz

What role do scrubbers play in NH₃ systems?


They are used to measure temperature
They store the refrigerant
Neutralise ammonia through absorption in a liquid (e.g. water)
They increase the pressure in the system

12

Nehéz

How should the system be prepared before filling with R717?


There is no need to check it
The pressure must be increased above the standard level
Simply start it up
Check for leaks, remove air and moisture, and create a vacuum

13

Nehéz

What are the transport requirements for R717?


It must be carried in suitable, labelled packagings in accordance with ADR (UN 1005, class 2, code 2TC)
It can be carried in open containers
It can be carried without labelling
Transport is not regulated

14

Könnyű

What personal protective equipment is required when working with NH₃?


Safety goggles, gloves and respiratory protective equipment
Only a safety helmet
Workwear only
No requirements

15

Nehéz

Which statement best describes the behaviour of R717 and mineral compressor oil?


R717 does not mix with the oil; the oil collects on the high-pressure side above the R717
R717 mixes very well with the oil, which easily returns to the compressor
R717 does not mix with the oil; the oil, being heavier than liquid NH₃, collects beneath it at the lowest points (mainly on the low-pressure side)
An oil return line cannot be used in R717 systems because the oil is too hot

16

Nehéz

Which refrigerant can be detected with phenolphthalein paper?


R1270
R1234ze(E)
R717
R744

17

Nehéz

Which system may require manual oil recovery?


Supercritical ‘booster’ system using R744
R744 cascade system
An R717 system
Secondary system using R744

18

Nehéz

Which refrigerant is lighter than air?


R744
R1234ze(E)
R717
R1270

19

Nehéz

R717 is highly corrosive to:


titanium
copper (and its alloys)
stainless steel
aluminium

20

Nehéz

What is the recommended pre-alarm level for fixed leak detection systems for R717?


500,000 ppm
5,000 ppm
50,000 ppm
500 ppm

21

Nehéz

Why are compressors with a separate motor (open type) mostly used in R717 systems?


To increase the refrigerant charge
Because NH₃ attacks copper motor windings, so hermetic compressors with conventional windings are not used
To lower the condensing pressure
Because they are cheaper

22

Nehéz

Which type of compressor is most commonly used in large ammonia systems?


Hermetic scroll
Diaphragm compressor
A reciprocating or screw compressor
Rotary vane compressor

23

Nehéz

How is the capacity of a piston compressor regulated in NH₃ systems?


By increasing the condensing pressure
Solely by adjusting the oil volume
By reducing the refrigerant charge
By unloading the cylinders or changing the rotational speed

24

Nehéz

How is the capacity of a screw compressor most commonly controlled?


By adjusting the oil level
By closing the suction valve
By using a slide valve
By changing the type of oil

25

Nehéz

When is two-stage compression used in NH₃ systems?


Only with water-cooled condensers
Only in small systems
At low evaporating temperatures (pressures) and high pressure ratios
At small temperature differences

26

Nehéz

What is the advantage of two-stage compression over single-stage compression?


Lower efficiency
Higher efficiency and lower discharge temperature
Higher energy consumption
No need for a separator

27

Nehéz

How does an evaporative condenser used in NH₃ systems work?


It utilises the evaporation of water to increase cooling efficiency
It transfers heat only to the air
It does not require a water supply
Operates without a fan

28

Nehéz

What is the function of the liquid separator in an NH₃ system?


It separates oil from the refrigerant
It prevents liquid from entering the compressor
Increases the discharge temperature
Regulates the condensing pressure

29

Nehéz

What is the purpose of monitoring the liquid level in the separator?


To increase the oil volume
To maintain the correct refrigerant level and prevent the compressor from flooding
To control the condenser fan
To reduce the condensing temperature

30

Nehéz

What is the role of the float switch in NH₃ systems?


It regulates the condensation temperature
It controls the fan’s operation
It monitors the liquid level in the tank or separator
It is used to detect leaks

31

Nehéz

What is a thermosyphon in NH₃ systems?


A defrosting device
A type of safety valve
An oil circulation pump
A system with gravity-driven (natural) circulation of liquid refrigerant caused by density differences, used e.g. for screw compressor oil cooling

32

Nehéz

Why are oils that are immiscible with the refrigerant used in NH₃ systems?


To reduce the pressure
Because the oil mixes only with water
To increase the amount of refrigerant
Because NH₃ does not mix with most compressor oils

33

Nehéz

What is the main function of an oil separator in NH₃ systems?


Removing moisture from the system
To lower the condensation temperature
To increase fan efficiency
To separate the oil from the refrigerant and return the oil to the compressor

34

Nehéz

In which NH₃ system does the refrigerant evaporate completely with superheat in the evaporator, fed by an expansion valve?


A direct-expansion (DX) system
A pumped liquid-recirculation system
A glycol system
An indirect system

35

Nehéz

What is the characteristic feature of a flooded evaporator system?


The evaporator is filled exclusively with vapour
No level control is required
The evaporator contains a large amount of liquid, which improves heat transfer
No separator is used

36

Nehéz

What is the main difference between a direct and an indirect system?


In an indirect system, NH₃ flows directly into the space being cooled
In a direct system, there is no evaporator
In an indirect system, NH₃ cools an intermediate medium (e.g. glycol), which in turn cools the load
In an indirect system, no compressor is used

37

Közepes

Which property of ammonia helps people detect a leak early?


A very low odour threshold (a few ppm)
It is odourless
It is denser than air
It is yellow in air