1

Stredne ťažká

Why is ammonia (R717) classed as a toxic refrigerant?


Because it does not react with water, making neutralisation difficult
Because it is colourless and odourless and therefore hard to detect
Because it is heavier than air and displaces oxygen
It severely irritates the respiratory tract, eyes and skin, and is poisonous when inhaled at higher concentrations

2

Ťažká

What is the main difference between a dry-expansion and a flooded evaporator?


A dry-expansion evaporator always has a lower pressure than a flooded one
In a dry-expansion evaporator the refrigerant completely evaporates and is superheated in the evaporator; in a flooded one part of the refrigerant remains liquid (incomplete evaporation, no superheat)
A dry-expansion evaporator needs no expansion valve, a flooded one does
A dry-expansion evaporator is filled with liquid, a flooded one with vapour

3

Ťažká

What is the typical pressure in the evaporator of an R717 deep-freeze system (below −40 °C)?


Positive pressure of 10–20 bar
Atmospheric pressure, approx. 1 bar abs
Below atmospheric (approx. 0.7 bar abs at −40 °C)
Positive pressure of 5–10 bar

4

Ľahká

What is the basic requirement when charging a system with R717 (NH₃)?


NH₃ can be charged together with air
Charging can be carried out without personal protective equipment
Charging should take place in a well-ventilated area using appropriate personal protective equipment
Charging must only take place at temperatures below 0°C

5

Ťažká

How is oil managed in R717 systems?


Oil collecting at the lowest points of vessels is regularly checked and drained, because it impairs heat transfer
Oil requires no monitoring
Oil has no effect on system operation
Oil can be mixed with any refrigerant

6

Ľahká

What is the correct procedure for recovering R717 from a system?


The gas can be released into the atmosphere
The refrigerant must be recovered into suitable, leak-proof tanks designed for NH₃
The refrigerant can be drained into the sewer system
Recovery is not required

7

Ľahká

How should R717 (NH₃) be stored?


In unmarked plastic containers
In any open containers
Near heat sources
In sealed, labelled containers, in a cool and well-ventilated place

8

Ťažká

What should be done with contaminated R717?


Continue to use it without restriction
Purify it or send it for disposal in accordance with regulations
Release it into the atmosphere
Dilute it with water and reuse it

9

Ľahká

What is the main hazard associated with an R717 leak during maintenance work?


No risk whatsoever
Toxic to humans and may cause chemical burns
Damage to electrical equipment only
Increased cooling efficiency

10

Ťažká

What should be done if an NH₃ leak is detected?


Evacuate people immediately and raise the alarm; stop the leak only if it is safe to do so and with suitable PPE (respiratory protection)
Increase the pressure in the system
Carry on working wearing a dust mask
Carry on working with the room door open

11

Ťažká

What role do scrubbers play in NH₃ systems?


Neutralise ammonia through absorption in a liquid (e.g. water)
They store the refrigerant
They increase the pressure in the system
They are used to measure temperature

12

Ťažká

How should the system be prepared before filling with R717?


Simply start it up
There is no need to check it
Check for leaks, remove air and moisture, and create a vacuum
The pressure must be increased above the standard level

13

Ťažká

What are the transport requirements for R717?


It must be carried in suitable, labelled packagings in accordance with ADR (UN 1005, class 2, code 2TC)
It can be carried in open containers
It can be carried without labelling
Transport is not regulated

14

Ľahká

What personal protective equipment is required when working with NH₃?


Workwear only
Only a safety helmet
Safety goggles, gloves and respiratory protective equipment
No requirements

15

Ťažká

Which statement best describes the behaviour of R717 and mineral compressor oil?


R717 does not mix with the oil; the oil, being heavier than liquid NH₃, collects beneath it at the lowest points (mainly on the low-pressure side)
An oil return line cannot be used in R717 systems because the oil is too hot
R717 does not mix with the oil; the oil collects on the high-pressure side above the R717
R717 mixes very well with the oil, which easily returns to the compressor

16

Ťažká

Which refrigerant can be detected with phenolphthalein paper?


R1270
R717
R744
R1234ze(E)

17

Ťažká

Which system may require manual oil recovery?


R744 cascade system
Supercritical ‘booster’ system using R744
Secondary system using R744
An R717 system

18

Ťažká

Which refrigerant is lighter than air?


R717
R1270
R1234ze(E)
R744

19

Ťažká

R717 is highly corrosive to:


stainless steel
copper (and its alloys)
aluminium
titanium

20

Ťažká

What is the recommended pre-alarm level for fixed leak detection systems for R717?


500 ppm
500,000 ppm
5,000 ppm
50,000 ppm

21

Ťažká

Why are compressors with a separate motor (open type) mostly used in R717 systems?


Because they are cheaper
Because NH₃ attacks copper motor windings, so hermetic compressors with conventional windings are not used
To increase the refrigerant charge
To lower the condensing pressure

22

Ťažká

Which type of compressor is most commonly used in large ammonia systems?


Diaphragm compressor
Hermetic scroll
Rotary vane compressor
A reciprocating or screw compressor

23

Ťažká

How is the capacity of a piston compressor regulated in NH₃ systems?


Solely by adjusting the oil volume
By increasing the condensing pressure
By unloading the cylinders or changing the rotational speed
By reducing the refrigerant charge

24

Ťažká

How is the capacity of a screw compressor most commonly controlled?


By using a slide valve
By adjusting the oil level
By closing the suction valve
By changing the type of oil

25

Ťažká

When is two-stage compression used in NH₃ systems?


Only in small systems
Only with water-cooled condensers
At low evaporating temperatures (pressures) and high pressure ratios
At small temperature differences

26

Ťažká

What is the advantage of two-stage compression over single-stage compression?


Higher energy consumption
Lower efficiency
No need for a separator
Higher efficiency and lower discharge temperature

27

Ťažká

How does an evaporative condenser used in NH₃ systems work?


It transfers heat only to the air
Operates without a fan
It does not require a water supply
It utilises the evaporation of water to increase cooling efficiency

28

Ťažká

What is the function of the liquid separator in an NH₃ system?


It separates oil from the refrigerant
Increases the discharge temperature
Regulates the condensing pressure
It prevents liquid from entering the compressor

29

Ťažká

What is the purpose of monitoring the liquid level in the separator?


To maintain the correct refrigerant level and prevent the compressor from flooding
To control the condenser fan
To increase the oil volume
To reduce the condensing temperature

30

Ťažká

What is the role of the float switch in NH₃ systems?


It regulates the condensation temperature
It is used to detect leaks
It monitors the liquid level in the tank or separator
It controls the fan’s operation

31

Ťažká

What is a thermosyphon in NH₃ systems?


An oil circulation pump
A defrosting device
A type of safety valve
A system with gravity-driven (natural) circulation of liquid refrigerant caused by density differences, used e.g. for screw compressor oil cooling

32

Ťažká

Why are oils that are immiscible with the refrigerant used in NH₃ systems?


To reduce the pressure
Because NH₃ does not mix with most compressor oils
Because the oil mixes only with water
To increase the amount of refrigerant

33

Ťažká

What is the main function of an oil separator in NH₃ systems?


To lower the condensation temperature
Removing moisture from the system
To separate the oil from the refrigerant and return the oil to the compressor
To increase fan efficiency

34

Ťažká

In which NH₃ system does the refrigerant evaporate completely with superheat in the evaporator, fed by an expansion valve?


An indirect system
A direct-expansion (DX) system
A glycol system
A pumped liquid-recirculation system

35

Ťažká

What is the characteristic feature of a flooded evaporator system?


The evaporator contains a large amount of liquid, which improves heat transfer
The evaporator is filled exclusively with vapour
No separator is used
No level control is required

36

Ťažká

What is the main difference between a direct and an indirect system?


In an indirect system, no compressor is used
In an indirect system, NH₃ cools an intermediate medium (e.g. glycol), which in turn cools the load
In a direct system, there is no evaporator
In an indirect system, NH₃ flows directly into the space being cooled

37

Stredne ťažká

Which property of ammonia helps people detect a leak early?


It is denser than air
It is odourless
It is yellow in air
A very low odour threshold (a few ppm)