1

Könnyű


2

Könnyű

What is the base unit of mass in the International System of Units (SI)?


t
N
kg
lb (pound)

3

Közepes

What process takes place in the condenser of a refrigeration system?


The refrigerant rejects only the heat generated in the compressor
Hot vapour discharged by the compressor is desuperheated, condensed, and the resulting liquid is slightly subcooled
The secondary fluid (glycol, water) condenses while the refrigerant evaporates
The refrigerant absorbs heat from the surroundings and evaporates

4

Közepes

What mainly determines the condensing temperature of an air-cooled condenser?


The superheat
The compressor discharge temperature
The evaporating temperature
The ambient (inlet) air temperature

5

Közepes

Why does heat flow from the condenser to the surroundings?


Because the condensing temperature is higher than the ambient temperature, and heat flows spontaneously from a warmer to a colder body (second law of thermodynamics)
Because the pressure in the condenser is lower than ambient
Because the compressor pushes heat directly into the surroundings
Because HFC refrigerants attract heat from the surroundings

6

Közepes

What should you mainly pay attention to when operating a condenser?


That the inlet air temperature is lower than the outlet air temperature
Its general condition and the cleanliness of the heat-exchange surfaces
The colour of the condenser casing
That the outlet air temperature is higher than the condensing temperature

7

Közepes

What criteria should be considered when selecting a suitable condenser?


Only own experience and the dimensions
The required capacity of the condenser and the technical specifications declared by the manufacturer
Only the size and number of fans
Fan noise, connection diameters and colour

8

Közepes

How do contaminants (dust, particulates, deposits) affect the performance and efficiency of heat exchange surfaces in condensers?


Contaminants do not significantly affect the efficiency and effectiveness of the heat exchange surfaces in condensers.
Contaminants restrict heat transfer (reducing the heat transfer coefficient) and cause a reduction in condensing pressure.
Contaminants increase the heat transfer area and reduce the condensing pressure.
Contaminants restrict heat transfer (reducing the heat transfer coefficient) and cause an increase in condensing temperature and pressure, which in turn leads to a reduction in the condenser’s efficiency.

9

Közepes

How does the capacity of an air-cooled condenser change when it becomes dirty?


It increases
It decreases
It increases because the fan speed rises
It remains unchanged

10

Közepes

What is the main consequence of heavy frost on an air-cooling evaporator?


A rise in the cooled-air temperature with no effect on capacity
An increase in condenser subcooling
Reduced heat transfer and airflow, resulting in a drop in cooling capacity and evaporating temperature
A rise in evaporating pressure

11

Közepes

What happens when the evaporation temperature drops?


The compressor’s cooling capacity decreases.
The condenser fan speed increases.
The discharge temperature decreases.
The compressor’s cooling capacity increases.

12

Közepes

When is natural (off-cycle, air) defrosting possible?


Only in freezer rooms below −18 °C
Never – electric heaters must be used in every air cooler
When the air passing through the cooler is above 0 °C
Only in coolers fitted with speed-controlled fans

13

Közepes

When does frost form on the surface of an air-cooling evaporator?


When the evaporator surface temperature is below 0 °C and below the dew point of the air
Always, in every air cooler
Only when the system runs continuously
Only when the room air temperature falls below 0 °C

14

Közepes

In extensive pipework systems, flash gas (secondary evaporation) in the liquid line can be prevented by…


…insulating the discharge line between the compressor and the condenser
…additional subcooling of the liquid
…increasing the length of the liquid line
…using smaller-diameter pipes

15

Közepes

How does hot gas defrosting of the evaporator work?


Heated vapour (hot gas) from the compressor is directed into the evaporator piping.
We switch on the gas heater directed at the evaporator.
This involves reversing the direction of rotation of the compressor.
We swap the outlet and inlet sides of the evaporator.

16

Közepes

What is the function of the evaporator in a refrigeration system?


It evaporates the water flowing through the evaporator.
It ensures that the refrigerant is superheated over the largest possible heat exchange surface area.
It cools the refrigerant.
It transfers heat from the medium being cooled to the boiling refrigerant.

17

Közepes

What condition must electric heaters for evaporator defrosting meet?


They must have good thermal contact with the heat-exchange surface (e.g. inserted in the fin block)
They must be in direct contact with the refrigerant
Heat from the heaters must be carried by the running fans
They must be located beneath the evaporator

18

Közepes

Refrigerant distributor:


ensures an even distribution of the refrigerant to the individual sections of the evaporator.
ensures the even distribution of the refrigerant discharged by compressors connected in parallel.
acts as a buffer for the refrigerant in the event that the pressure upstream of the expansion valve is exceeded.
ensures even distribution of the refrigerant to the individual sections of the condenser.

19

Közepes

What defrosting methods are used for air coolers?


Electric, hot gas, water spray and natural (at positive temperatures)
Electric only – other methods are not permitted in refrigeration
Only by switching off the fans with the compressor running
Natural only – other methods are ineffective and uneconomic

20

Közepes

The boiling point of a liquid rises when the pressure above the liquid…


…remains constant
…rises
…varies depending on the ambient temperature
…falls

21

Közepes

MOP in thermostatic expansion valves stands for:


self-cleaning of the valve in the event of moisture in the refrigerant freezing.
minimum flow opening.
maximum pressure switch protection.
maximum operating pressure.

22

Közepes

The function of a thermostatic expansion valve (TEV) is:


to adjust the evaporating pressure in the condenser
to maintain a constant compressor suction pressure
to maintain a constant condensing pressure
to meter refrigerant into the evaporator according to the superheat of the vapour leaving the evaporator

23

Közepes

What type of compressor motor can be used with a capillary tube?


An electronically commutated motor
A low-speed motor
A low-starting-torque motor (pressures equalise during standstill)
A high-starting-torque motor must be used

24

Közepes

What does a thermostatic expansion valve control?


The discharge temperature
The mass flow of refrigerant fed into the evaporator
The temperature in the cold room
The condensing pressure

25

Könnyű

The refrigerant absorbs heat when…


…it evaporates
…it is subcooled
…it freezes
…it condenses

26

Közepes

What does the manufacturer state as the factory setting of a thermostatic expansion valve?


the static superheat of the valve.
the degree of refrigerant expansion.
the degree to which the valve is filled with refrigerant liquid.
the superheat value during valve operation.

27

Közepes

Where is a new or repaired system with an expansion valve and liquid receiver charged?


In the liquid phase into the compressor suction, with the compressor running
Through the capillary tube outlet during normal system operation
Anywhere – the charging point does not matter
In the liquid phase on the high-pressure side, with the compressor stopped

28

Közepes

What does a thermostatic or electronic expansion valve control?


The compressor speed
The amount of refrigerant fed to the evaporator according to superheat
Subcooling, by adjusting condensing pressure
The evaporating pressure – closing below the set point

29

Közepes

What does the MOP function of thermostatic expansion valves mean?


The valve limits subcooling
The valve limits the maximum evaporating (suction) pressure, protecting the compressor motor from overload, e.g. after defrost
The valve prevents motor overheating by injecting liquid into the compressor
The valve maintains a constant condensing pressure

30

Közepes

The lower the liquid temperature upstream of the expansion valve, (at the same mass flow)…


…the lower qo and the lower energy efficiency
…the higher the specific refrigerating effect qo [kJ/kg] and the higher the cooling capacity Qo
…the lower qo and the lower Qo
…the lower qo, with Qo unchanged

31

Közepes

How should the MOP point of an expansion valve be selected relative to the highest normal evaporating temperature?


A few kelvin higher (approximately 7 K)
Freely – the MOP value is irrelevant
Higher by approx. 20 K
About 7 K lower than that temperature

32

Közepes

What is the function of the suction pressure regulator?


To maintain the suction pressure at the highest possible level.
It maintains the evaporation pressure at a constant level.
It limits the suction pressure and protects the compressor from excessively high suction pressure.
It prevents a drop in suction pressure and, if necessary, shuts down the refrigeration system.

33

Közepes

What is the function of the valve regulating water flow through the condenser?


To maintain the condensing pressure at the lowest possible level.
To maintain the water temperature at the highest level.
To maintain the condensing pressure at the highest possible level.
To maintain the condensing pressure at a constant level.

34

Közepes

The use of a refrigerant distributor requires a thermostatic expansion valve ...


... with an adsorption-type sensor filling.
... with external pressure equalisation.
... with a MOP function.
... with internal pressure equalisation.

35

Közepes

What properties should good insulation materials have?


The ability to absorb large amounts of moisture
An antistatic coating
High thermal conductivity
Low thermal conductivity (and low water absorption, vapour tightness)

36

Közepes

When is refrigerant vapour superheated?


When the compressor motor temperature rises excessively
When the pressure on the discharge side is higher than on the suction side
When its temperature is higher than the saturation temperature corresponding to its pressure
When the evaporating temperature is lower than the ambient temperature

37

Közepes

How can you check whether the liquid refrigerant is reaching the expansion valve without vapour bubbles?


We are unable to check this.
We check using a pressure gauge fitted on the discharge side of the compressor.
We check using a liquid pressure gauge.
We check this using a sight glass.

38

Közepes

Where does the liquid line run?


From the condenser (liquid receiver) to the expansion valve
Between the evaporator and the suction-line heat exchanger
Between the compressor and the condenser
Between the evaporator and the compressor

39

Közepes

What is the function of the liquid receiver in a refrigeration system?


To act as a reserve when the required charge is unknown
To collect liquid refrigerant and excess oil
To further subcool the condensed refrigerant
To store refrigerant and compensate for changes in the circulating charge as the heat load varies

40

Közepes

What is the purpose of the liquid receiver during service work?


It collects excess oil circulating in the system
It further subcools the refrigerant before the expansion valve
It allows pump-down and temporary storage of the refrigerant
It is a reserve when the installer does not know the required charge

41

Közepes

Where should the liquid receiver be installed?


It should be installed downstream of the condenser, upstream of the expansion valve.
It should be fitted just before the compressor.
It should be fitted between the compressor and the condenser.
It should be fitted after the evaporator.

42

Közepes

What is the function of the suction pressure regulator fitted to the suction pipe when the compressor starts up?


It closes when the suction pressure upstream of the compressor drops.
It opens when the suction pressure upstream of the compressor drops.
It regulates the evaporation pressure.
It regulates the condensing pressure.

43

Közepes

The use of microchannel heat exchangers, compared with conventional heat exchangers made of copper tubes and fins, results in:


A reduction in refrigerant charge and, typically, higher energy efficiency.
A reduction in the system’s energy efficiency.
An increase in the amount of refrigerant in the system and an increase in condensing pressure.
There is no effect whatsoever on either the amount of refrigerant or energy efficiency.

44

Közepes

Which refrigerants belong to the HFC group?


R134a, R404A, R507A, R410A.
R134a, R32, R22, R507A, R290.
R22, R401A.
R11, R12, R502.

45

Közepes

Which refrigerants belong to the HFO group?


R134a, R404A.
R1234yf, R1234ze(E).
R134a, R290.
R22, R12.

46

Közepes

What are the characteristics of R410A refrigerant compared to R407C refrigerant?


The saturation pressure of both refrigerants is roughly the same.
The saturation pressure of R407C refrigerant is much higher than that of R410A.
The saturation pressure of R407C is 150% higher than that of R410A.
The saturation pressure of R410A refrigerant is higher than that of R407C.

47

Közepes

What does the TEWI indicator define?


Total Equivalent Warming Impact: the sum of direct emissions (leakage and refrigerant losses at disposal) and indirect emissions (CO₂ from generating the energy consumed by the equipment) over its lifetime
The impact of a refrigerant on the ozone layer
The ability of the ozone layer to recover
The global warming potential of a gas relative to CO₂ over a 100-year horizon

48

Közepes

What are the characteristics of R452A compared with R404A?


It is a flammable and toxic single-component HFC
It is a non-flammable (A1) HFC/HFO blend with properties similar to R404A and a GWP about 45% lower
The temperature glide of R452A is half that of R404A
Both are azeotropic and have no temperature glide

49

Közepes

What distinguishes R1234yf from R134a?


A higher normal boiling point
Higher toxicity
It is mildly flammable (class A2L), whereas R134a is non-flammable (A1)
A higher critical temperature

50

Közepes

How does CO₂ (R744) compare with R134a?


Unlike R134a, it is an azeotropic mixture
It has a lower critical temperature, much higher operating pressures and a much higher volumetric cooling capacity (smaller compressors and pipes)
It has identical properties and is a drop-in replacement for R134a
Its temperature glide is 7 K greater than that of R134a

51

Közepes

Which of the following is NOT a fluorinated greenhouse gas?


Perfluorocarbons (PFCs).
Carbon dioxide (CO₂).
Hydrofluorocarbons (HFCs).
Sulphur hexafluoride (SF6).

52

Nehéz

What additional protective equipment will you use when brazing systems containing HC refrigerants?


A high-visibility vest
A flammable gas detector
Latex gloves
Ear defenders

53

Nehéz

Why can’t a sealed high-pressure switch be replaced with a standard mechanical one in a system containing a flammable refrigerant?


Dust and moisture may enter
There is a risk of refrigerant leakage
The pressure switch setting will not be correct
It is a potential source of ignition

54

Nehéz

What is the minimum (recommended) distance from a work area with HC refrigerants within which there must be no sources of ignition?


0.5 m
2 m
3 m
1 m

55

Nehéz

What is the maximum safe R32 fill of a recovery cylinder approved for flammable gas that holds 20 kg of R410A (the liquid density of R32 is about 8-10% lower)?


9 kg
33 kg
20 kg
18 kg

56

Nehéz

What is the maximum charge of an A3 refrigerant for a hermetic display cabinet with an integral condenser located in the ground-floor sales area of a supermarket?


10 kg
0,494 kg
2.5 kg
1.0 kg

57

Nehéz

How can a vacuum pump be used safely to evacuate a system containing a flammable refrigerant?


Position the pump at least 3 m above floor level
Place the pump directly on the floor, as low as possible
Ignition-source-free pump, good ventilation, exhaust to a safe place
Such systems need not be evacuated before charging

58

Közepes

What is the greenhouse effect?


Chlorine compounds destroy stratospheric ozone, increasing UV radiation at the surface
Dust in the atmosphere reflects sunlight, lowering the average surface temperature
Clouds reflect ultraviolet radiation, which makes the air near the surface warmer
Greenhouse gases absorb and re-emit the Earth's infrared radiation, warming the lower atmosphere

59

Nehéz

What safety measure must you carry in your vehicle when transporting flammable refrigerant cylinders?


A fire blanket
Thick gloves
Tinted safety goggles
A fire extinguisher

60

Nehéz

How would you prepare a 10 kg R32 water chiller located outdoors for debrazing its joints?


Vent the R32 outdoors, then fill and vent the system with nitrogen three times
Recover the R32 to a vacuum and start desoldering immediately
Recover the R32 to a vacuum, then fill the system with nitrogen to a slight positive pressure (approx. 0.1 bar g)
Vent the R32 outdoors and purge the system

61

Közepes

What is R1270?


Isobutane
Propene (propylene)
n-Butane
Propane

62

Nehéz

Which of the following leak detection methods should NOT be used to locate an HC refrigerant leak?


Electronic HFC leak detector
Leak detection foam
Soapy water solution
Electronic leak detector for flammable refrigerants

63

Nehéz

What is the most important difference between a flammable refrigerant recovery unit and a standard one?


A flammable refrigerant recovery unit has no ignition sources
Different connection sizes
A different colour for the station
Different low-pressure switch setting

64

Nehéz

Which of the following is a source of ignition?


A sealed NTC temperature sensor
An Ex-certified fan motor
An 'n'-type (non-sparking) thermostat
A contactor (sparking contacts)

65

Nehéz

What particularly hazardous substance is formed when R32 burns?


Phosgene
Hydrogen chloride (HCl)
Sulphur dioxide (SO₂)
Hydrogen fluoride (HF)

66

Nehéz

What type of refrigerant is R1234ze(E)?


HFO (hydrofluoroolefin)
CFC (chlorofluorocarbon)
HC (hydrocarbon)
HCFC (hydrochlorofluorocarbon)

67

Nehéz

What hazards does a safety group A3 refrigerant pose?


Lower toxicity, moderate flammability
Higher toxicity, moderate flammability
Lower toxicity, higher flammability
Higher toxicity, higher flammability

68

Nehéz

According to EN 378, what is the maximum R290 charge in a cold room measuring 5 m × 3 m × 2.5 m (LFL of R290 = 0.038 kg/m³, access category a, location class I, no additional measures))?


4.93 kg
1.0 kg
0.285 kg
1.5 kg

69

Könnyű

What does the GWP indicator mean?


Global Warming Potential: the climate warming impact of 1 kg of a gas compared with 1 kg of CO₂ (GWP = 1) over a defined time horizon, usually 100 years
The annual rise in mean air temperature caused by the emission of 1 kg of the gas
The ability of a substance to restore the ozone layer
Ozone depletion potential

70

Nehéz

What is the approximate ratio of the volumetric cooling capacity of R32 to that of R410A (same compressor and conditions)?


approx. 0.6
approx. 1.05–1.1
approx. 0.75
approx. 1.3

71

Nehéz

Why are Ex-certified evaporator fan motors used in some systems with flammable refrigerants?


Because they are more reliable
To avoid a source of ignition in the event of a flammable refrigerant leak
Because they must be kept running continuously to disperse the leaking refrigerant
Because they are more energy-efficient

72

Nehéz

Why is the density difference between HC and HFC refrigerants important?


Because HCs operate at much higher pressures
Because HCs must be charged much more slowly than HFCs
Because it determines the system's energy efficiency
An HC charge in kg is roughly half that of an HFC

73

Nehéz

What is the GWP of R290 according to Annex VI to Regulation (EU) 2024/573?


7
675
150
0.02

74

Nehéz

Which of the following is NOT a source of ignition?


An electrical switch
An unsealed mechanical pressure switch
An Ex-certified fan motor
A light switch

75

Nehéz

What is R290?


Isobutane
Propene (Propylene)
Propane
Butane

76

Nehéz

What is the maximum A2L charge for a hermetic display cabinet with integral condenser in the ground-floor sales area of a supermarket?


150 g
2.5 kg
1.5 kg
1.2 kg

77

Nehéz

Why can’t a standard relay be fitted when retrofitting a compressor’s electrical system for flammable refrigerants?


A relay is never required for compressors using flammable refrigerants
Current consumption differs for compressors using flammable refrigerants compared to those using HFCs
It could be a source of ignition
The method of starting the compressor motor differs from that used with HFCs

78

Nehéz

What is the minimum (recommended) distance from a work area with HC refrigerants within which there must be no ignition sources?


5 m
3 m
10 m
1 m

79

Nehéz

A recovery cylinder holds 10 kg of R404A (filling ratio 0.82 kg/l). What is the maximum R290 charge for this cylinder (propane filling ratio 0.43 kg/l per ADR P200)?


20 kg
approx. 8 kg
approx. 17 kg
approx. 5.2 kg

80

Közepes

How do refrigeration systems contribute to the greenhouse effect?


Only through CO₂ given off by the compressor motor
Indirectly (through energy consumption) and directly (through emissions of refrigerant into the atmosphere)
Through oil emitted into the atmosphere from the condenser and filter
Only through the heat rejected by the condenser

81

Nehéz

How can a vacuum pump be used safely to evacuate a system containing R290?


R290 systems need not be evacuated before charging
Place the pump directly on the floor, as low as possible
Ignition-source-free pump, good ventilation, exhaust to a safe place
Position the pump at least 3 m above floor level

82

Nehéz

Under ADR, what equipment must you carry in your vehicle when transporting flammable refrigerant cylinders (under the 1.1.3.6 exemption)?


A fire extinguisher (at least 2 kg dry powder)
Tinted safety goggles
Thick gloves
A fire blanket

83

Nehéz

How do you make sure it is safe to light the torch for desoldering joints in a system from which a flammable refrigerant has been removed?


Such joints must never be desoldered; they must be cut with a pipe cutter
Working outdoors is sufficient
Purge the system with compressed air
Ensure good ventilation and check the work area with a flammable gas detector

84

Nehéz

How would you prepare a system containing 100 g of R1270 for debrazing, if local regulations allow controlled venting of small HC quantities?


Recover the R1270 to a vacuum and start brazing immediately without a nitrogen purge
Vent the R1270 into the room and open a window
Vent the R1270 outdoors and start brazing immediately
Vent the R1270 to a safe outdoor location, then purge with OFN three times (pressurise and vent), and braze with OFN flowing

85

Nehéz

Which method should NOT be used to locate an R290 leak?


An electronic detector for flammable refrigerants
An electronic leak detector designed for HFCs
Fluorescent dye and UV lamp (if approved by the manufacturer)
Leak detection foam

86

Nehéz

Why can’t recovery stations designed for HFCs be used with R600a?


The low-pressure switch setting will not be suitable for R600a due to its lower operating pressure
The recovery unit cannot withstand the working pressure of R600a
The oil in the recovery unit is not soluble in R600a
They contain ignition sources

87

Nehéz

According to EN 378, what is the maximum R1234ze(E) charge in a cold room measuring 5 m × 3 m × 2.5 m (LFL = 0.303 kg/m³, access category a, location class I, no additional measures)?


227 kg
618 kg
6.18 kg
2.27 kg

88

Nehéz

What type of refrigerant is R32?


Hydrofluorocarbon
Hydrofluoroolefin
Hydrocarbon
Carbon dioxide

89

Nehéz

What hazards do A2L refrigerants pose?


Lower toxicity, lower flammability (burning velocity ≤ 10 cm/s)
Lower toxicity, higher flammability
Higher toxicity, higher flammability
Higher toxicity, lower flammability

90

Nehéz

What hazard is associated with the combustion of HFO or HFC refrigerants?


Phosgene is formed
Hydrogen fluoride (HF) is formed
Nitrous oxide is formed
Ozone is formed

91

Közepes

What is the greenhouse effect?


The formation of a layer that traps only heat from fuel combustion in aircraft
The filtering of solar radiation by the atmosphere
The trapping of heat in the Earth's atmosphere, which hinders the radiation of heat into space
The absorption of solar radiation by the Earth's surface

92

Nehéz

Approximately what compressor displacement is required for R600a compared with R134a for the same cooling capacity?


The same
About half
About seven times as large
About twice as large

93

Nehéz

What is the GWP value for R32 according to Regulation (EU) 2024/573?


675
0
3
7

94

Nehéz

Why is charge accuracy more important in critically charged R290 systems than in HFC systems?


Because R290 is only used in systems below 150 g
The charge mass is much smaller than in an HFC system, because the liquid density of R290 is much lower
Because such systems never have liquid receivers
Because of lower operating pressures

95

Nehéz

Why does the condenser fan run continuously in some systems using R1270?


To ensure that the discharge pressure never becomes excessive
To reduce energy consumption
To dilute the refrigerant in the event of a leak
To prevent the build-up of contaminants in the condenser

96

Közepes

Which EU regulation is currently the primary piece of legislation governing the use of fluorinated greenhouse gases (F-gases) in the European Union?


Regulation (EU) 2024/573
Regulation (EU) 2015/1188
Regulation (EU) No 517/2014
Directive 2009/125/EC

97

Közepes

What is the main objective of Regulation (EU) 2024/573?


Prevention of F-gas emissions and the achievement of the EU’s climate targets
To reduce taxes on refrigeration equipment
To facilitate the import of electrical appliances
Standardising metal recycling standards

98

Közepes

What are the ecodesign obligations of manufacturers of refrigerating appliances?


Only using energy labels under Regulation (EU) 2024/573
Only declaring F-gas quantities under Regulation (EU) No 517/2014
Meeting implementing regulations (e.g. 2019/2019, 2015/1095): efficiency, spare parts, reparability
Only implementing an ISO 9001 quality management system

99

Közepes

What is the main objective of EU ecodesign legislation (Directive 2009/125/EC, now Regulation (EU) 2024/1781 – ESPR)?


To increase sales of electrical appliances in the EU
To reduce the negative environmental impact of products by improving energy efficiency, durability and recyclability
To facilitate imports from outside the EU
To standardise the appearance of products in the EU

100

Közepes

What is the function of a ball valve in a refrigeration system?


It prevents excessive pressure build-up in the system
It regulates the temperature of the refrigerant
Enables the refrigerant flow to be completely shut off
It measures the moisture content of the refrigerant

101

Könnyű

What is the main function of a safety valve?


Discharges refrigerant when the set pressure is exceeded
It monitors the moisture content of the refrigerant
It controls the oil level in the compressor
Prevents the evaporator from freezing

102

Közepes

How do certain gases contribute to the greenhouse effect?


They deplete the ozone layer, so more solar radiation reaches the surface
They trap thermal radiation that the Earth would otherwise emit into space
They heat the air through chemical reactions with atmospheric oxygen and nitrogen
They limit UV radiation reaching the Earth's surface, changing the heat balance

103

Közepes

What is the purpose of a sight glass (with moisture indicator)?


Visual assessment of the refrigerant condition in the liquid line (bubbles) and of system moisture
Emergency shut-off of flow
Measuring condenser temperature
Regulating compressor pressure

104

Közepes

What is the function of the temperature regulator in a refrigeration system?


To maintain a constant pressure in the compressor
It drains excess refrigerant into the receiver
It restricts oil flow
Controls the operation of the compressor and valves to maintain the set temperature

105

Nehéz

What is the role of a suction liquid separator (also in systems with flammable or toxic refrigerants)?


It heats the refrigerant before the evaporator
It prevents liquid refrigerant from entering the compressor
It separates liquid from oil
It is used only to measure moisture

106

Nehéz

What is the function of an oil separator in systems using flammable or toxic refrigerants?


It prevents liquid from entering the compressor
They are used solely to measure the moisture content of the refrigerant
Separates oil from the refrigerant and facilitates the return of oil to the compressor
Heats the refrigerant before it enters the evaporator

107

Közepes

What is the purpose of oil level regulators in a refrigeration system?


They control the pressure in the condenser
Maintains the correct oil level in the compressor
They control the evaporator temperature
They drain off excess refrigerant

108

Közepes

What is the function of the liquid receiver in relation to system tightness?


It stores refrigerant; checking its liquid level helps detect charge loss
It keeps the whole system at constant pressure regardless of load
It regulates the oil returning to the compressor
It controls the evaporating temperature by varying the circulating charge

109

Közepes

What is the role of a gauge manifold with thermometers (temperature probes)?


It controls oil level
It measures pressures and temperatures to determine superheat and subcooling and thus assess the system charge (indirect leak check)
It relieves pressure if it is exceeded
It monitors refrigerant moisture content

110

Közepes

What is the role of defrost controls?


They control compressor discharge pressure during defrost
They protect the evaporator from icing and damage that could lead to leaks
They monitor the moisture content of the refrigerant
They drain excess oil from the evaporator to the receiver

111

Nehéz

Why do liquid and oil separators in CO₂ systems require particular attention?


Because CO₂ needs no lubrication, so oil separators are unnecessary
Because of very high pressures – adequate PS and protection devices are required
Because CO₂ is flammable and separators must not be used
Because sight glasses and level indicators must not be used in CO₂ systems

112

Nehéz

What is the critical pressure of CO₂ (R744)?


Approx. 120 bar
Approx. 10 bar
Approx. 74 bar (abs)
Approx. 31 bar

113

Könnyű

What is the unit of pressure in the International System of Units (SI)?


Pa (pascal)
atm (standard atmosphere)
psi (pound per square inch)
bar (gauge)

114

Közepes

Where can the lists of fluorinated greenhouse gases be found?


In the national Act on ozone-depleting substances and certain fluorinated greenhouse gases
In the Vienna Convention for the Protection of the Ozone Layer
In Annexes I–III to Regulation (EU) 2024/573 of the European Parliament and of the Council
In a regulation of the Minister of Economy on the list of fluorinated greenhouse gases

115

Nehéz

What characterises the transcritical process in CO₂ systems?


It is irrelevant to system operation
It occurs only at low temperatures
Conventional condensation occurs
Heat rejection takes place above the critical point – the refrigerant does not condense in the conventional way (gas cooler instead of condenser)

116

Nehéz

What characterises the subcritical CO₂ process?


The absence of condensation
The absence of evaporation
Operation above the critical point
The conventional condensation process below the critical point

117

Könnyű

What is the log(p)-h diagram for CO₂ used for?


To detect leaks
For analysing thermodynamic processes in a refrigeration system
To regulate pressure
To measure temperature

118

Könnyű

What can be read from the log(p)-h graph?


Only the temperature
Pressure, enthalpy, temperature and state of the refrigerant
Only the amount of refrigerant
Only the humidity

119

Könnyű

What are CO₂ saturation tables used for?


To measure humidity
To regulate the compressor
To determine the relationship between temperature and pressure at saturation
To determine the oil quantity

120

Könnyű

What does the CO₂ saturation state mean?


A state of high pressure
Equilibrium between the liquid and vapour phases
Dry ice state
A state in which the refrigerant is only a gas

121

Nehéz

When can dry ice (solid CO₂) form?


At high temperature
During normal operation of the system
At high pressure
When the pressure drops suddenly below the triple point (approx. 5.2 bar abs, −56.6 °C), e.g. when venting liquid CO₂ or charging liquid into an evacuated system

122

Nehéz

What risks are associated with dry ice forming in a CO₂ system?


Improved efficiency
No risk
Blocked pipes and valves and system damage (and a sharp pressure rise when it thaws)
Pressure reduction

123

Nehéz

How does CO₂ saturation pressure change as temperature increases?


It first decreases, then increases
It decreases
It increases rapidly
It remains the same

124

Könnyű

Why is understanding the log(p)-h graph particularly important for CO₂?


It only applies to NH₃
As CO₂ systems operate in different modes (sub- and transcritical) and require detailed analysis
It doesn’t matter
It is only used for design purposes

125

Közepes

Where can the lists of ozone-depleting substances be found?


In Annexes I and II to Regulation (EU) 2024/590 of the European Parliament and of the Council
In the national Act on ozone-depleting substances and certain fluorinated greenhouse gases
In a regulation of the Minister of the Environment on the list of controlled substances
In the Vienna Convention for the Protection of the Ozone Layer

126

Nehéz

What happens to CO₂ above the critical point?


It turns into a liquid
It transitions to a supercritical state (no distinction between liquid and gas)
It turns into a solid
It ceases to conduct heat

127

Könnyű

Why do CO₂ systems require precise pressure control?


Due to significant pressure changes with temperature fluctuations
They do not require control
Because there are no valves
Due to low pressures

128

Közepes

Why is ammonia (R717) classed as a toxic refrigerant?


Because it is heavier than air and displaces oxygen
Because it is colourless and odourless and therefore hard to detect
It severely irritates the respiratory tract, eyes and skin, and is poisonous when inhaled at higher concentrations
Because it does not react with water, making neutralisation difficult

129

Nehéz

What is the main difference between a dry-expansion and a flooded evaporator?


A dry-expansion evaporator always has a lower pressure than a flooded one
In a dry-expansion evaporator the refrigerant completely evaporates and is superheated in the evaporator; in a flooded one part of the refrigerant remains liquid (incomplete evaporation, no superheat)
A dry-expansion evaporator needs no expansion valve, a flooded one does
A dry-expansion evaporator is filled with liquid, a flooded one with vapour

130

Nehéz

What is the typical pressure in the evaporator of an R717 deep-freeze system (below −40 °C)?


Positive pressure of 5–10 bar
Atmospheric pressure, approx. 1 bar abs
Below atmospheric (approx. 0.7 bar abs at −40 °C)
Positive pressure of 10–20 bar

131

Nehéz

Why are PFAS formed by the decomposition of certain F-gases (e.g. TFA from HFOs) problematic?


They are climate- and environment-neutral
They are readily biodegradable
They are very persistent, accumulate in the environment (e.g. water) and may be toxic
They cause rapid cooling of the atmosphere

132

Könnyű

What is the basic requirement when charging a system with R717 (NH₃)?


Charging should take place in a well-ventilated area using appropriate personal protective equipment
Charging must only take place at temperatures below 0°C
Charging can be carried out without personal protective equipment
NH₃ can be charged together with air

133

Nehéz

How is oil managed in R717 systems?


Oil collecting at the lowest points of vessels is regularly checked and drained, because it impairs heat transfer
Oil requires no monitoring
Oil can be mixed with any refrigerant
Oil has no effect on system operation

134

Könnyű

What is the correct procedure for recovering R717 from a system?


Recovery is not required
The gas can be released into the atmosphere
The refrigerant can be drained into the sewer system
The refrigerant must be recovered into suitable, leak-proof tanks designed for NH₃

135

Könnyű

How should R717 (NH₃) be stored?


Near heat sources
In sealed, labelled containers, in a cool and well-ventilated place
In unmarked plastic containers
In any open containers

136

Közepes

Where and by when must entities obliged under the Polish Act of 15 May 2015 submit annual reports on ODS and F-gases?


By 28 February of the following year, electronically via the Reports Database (BDS) run at the Institute of Industrial Chemistry (ICHP)
By the end of the calendar year, on a form at a regional office of the Office of Technical Inspection (UDT)
By 31 January, in the Central Register of Operators (CRO)
By 31 March, electronically to the Ministry of Climate and Environment

137

Nehéz

What should be done with contaminated R717?


Dilute it with water and reuse it
Release it into the atmosphere
Purify it or send it for disposal in accordance with regulations
Continue to use it without restriction

138

Könnyű

What is the main hazard associated with an R717 leak during maintenance work?


No risk whatsoever
Increased cooling efficiency
Toxic to humans and may cause chemical burns
Damage to electrical equipment only

139

Nehéz

What should be done if an NH₃ leak is detected?


Evacuate people immediately and raise the alarm; stop the leak only if it is safe to do so and with suitable PPE (respiratory protection)
Carry on working with the room door open
Carry on working wearing a dust mask
Increase the pressure in the system

140

Nehéz

What role do scrubbers play in NH₃ systems?


They are used to measure temperature
They increase the pressure in the system
Neutralise ammonia through absorption in a liquid (e.g. water)
They store the refrigerant

141

Nehéz

How should the system be prepared before filling with R717?


Check for leaks, remove air and moisture, and create a vacuum
Simply start it up
There is no need to check it
The pressure must be increased above the standard level

142

Nehéz

What are the transport requirements for R717?


Transport is not regulated
It can be carried without labelling
It can be carried in open containers
It must be carried in suitable, labelled packagings in accordance with ADR (UN 1005, class 2, code 2TC)

143

Könnyű

What personal protective equipment is required when working with NH₃?


Only a safety helmet
Workwear only
No requirements
Safety goggles, gloves and respiratory protective equipment

144

Közepes

Which installation measure has a major impact on compressor energy efficiency?


Installing a suction line smaller than recommended
Proper evacuation and dehydration of the system (removing air and moisture)
Omitting the filter-drier to reduce flow resistance
Charging extra refrigerant 'as a reserve' above the nameplate value

145

Közepes

How does regular oil-level monitoring affect compressor operation?


It increases cooling capacity above nominal
It ensures proper lubrication and limits wear and energy losses
It allows the crankcase heater to be omitted
It allows any type of oil to be topped up

146

Könnyű

How do system leaks affect compressor energy efficiency?


They improve efficiency because condensing pressure drops
They affect only safety, not energy use
Refrigerant loss reduces capacity and increases energy use (longer run times, higher superheat)
No effect as long as the system still cools

147

Közepes

Regulation (EU) 2024/590 relates to:


Alternative refrigerants replacing fluorinated greenhouse gases
Health and safety during refrigerant recovery
Conditions for F-gas certification of companies recovering and reclaiming refrigerants
Ozone-depleting substances

148

Közepes

What is the significance of proper suction and discharge pressure control?


It keeps the compressor at optimal conditions (suction pressure as high and condensing pressure as low as permissible)
The lowest possible suction pressure is best
The highest possible condensing pressure is best
Pressures do not affect energy use

149

Közepes

Which maintenance measure reduces compressor energy consumption?


Topping up refrigerant at every service visit
Permanently disabling the crankcase heater
Raising the high-pressure switch setting
Replacing the filter-drier when the pressure drop or moisture indicator shows it is necessary

150

Közepes

How does air (non-condensable gas) in the system affect operation?


It lowers the condensing pressure
It only affects the sight-glass indication
It improves condenser heat transfer
It raises the condensing pressure and reduces efficiency

151

Közepes

What role do controls play in compressor efficiency?


They provide safety only, with no energy effect
They increase the circulating refrigerant charge
They enable optimised operation and lower energy use (e.g. floating head pressure, capacity matching)
They matter only in NH₃ systems

152

Közepes

How does suction superheat at the compressor affect efficiency?


Superheat has no effect
The higher the superheat, the higher the efficiency
Excessive superheat reduces efficiency and raises the discharge temperature
Zero suction superheat is optimal

153

Közepes

How does correct system layout affect efficiency?


It shortens pipe runs and limits pressure drops and energy losses
It affects only appearance
It doesn't matter
Longer pipes improve subcooling and always increase efficiency

154

Közepes

How important is suction pipe insulation?


It limits heat gain and excessive superheat, improving efficiency
It is needed only for appearance
It increases energy consumption
It has no effect

155

Közepes

Which measure most improves condenser energy efficiency?


Regular cleaning of heat-exchange surfaces
Increasing the refrigerant charge
Raising the condensing pressure set point
Reducing fan speed to the minimum

156

Könnyű

How does a dirty condenser affect the operation of the refrigeration system?


It lowers the condensing pressure
It improves efficiency
It has no effect
Causes an increase in pressure and energy consumption by the compressor

157

Könnyű

Why is adequate airflow through an air-cooled condenser important?


It ensures effective heat rejection and low condensing pressure
The lower the airflow, the lower the condensing pressure
It doesn't matter
It affects only noise

158

Közepes

Which refrigerants damage the ozone layer?


All refrigerants containing chlorine or bromine in their molecules
All natural refrigerants
All refrigerants containing fluorine and hydrogen in their molecules
All refrigerants containing carbon in their molecules

159

Könnyű

How does the presence of limescale in a water-cooled condenser affect performance?


It improves heat transfer
Impairs heat exchange and increases energy consumption
It lowers the condensation temperature
It has no effect

160

Közepes

How does correct condensing pressure control affect efficiency?


It has no effect
It always increases energy use
It is best to keep a constant high condensing pressure all year
It keeps the lowest pressure that still ensures proper expansion-valve feed, reducing energy use

161

Könnyű

How do condenser leaks affect energy efficiency?


They improve efficiency
They lower the temperature
Causes refrigerant loss and a drop in efficiency
Have no effect

162

Könnyű

How important is the correct positioning of an air-cooled condenser?


It should be installed in a well-ventilated area with unobstructed airflow
It should be housed in a small room
It doesn’t matter
It should be close to heat sources

163

Könnyű

How does hot air recirculation affect the condenser?


It improves efficiency
It has no effect
It reduces the pressure
Impairs cooling and increases energy consumption

164

Közepes

How does insulation of heating and DHW pipework affect the efficiency of a heat pump system?


It increases pressure
It reduces energy losses and improves overall system efficiency
It doesn't matter
It impairs cooling

165

Közepes

Which measure most improves the energy efficiency of an air-cooling evaporator?


Raising the condensing temperature by a few kelvin
Increasing the refrigerant charge above nominal
Defrosting at the right time and keeping the fins clean
Restricting the airflow through the evaporator

166

Könnyű

How does evaporator icing affect the system’s operation?


Impairs heat exchange and increases energy consumption
It improves cooling performance
It lowers the condensation temperature
It has no effect

167

Könnyű

How does dirt on the evaporator surface affect its performance?


It improves efficiency
It reduces the pressure
Impairs heat exchange and increases energy consumption
It has no effect

168

Könnyű

What maintenance task is crucial for the evaporator?


Reduced airflow
Increasing the refrigerant charge
Lack of maintenance
Regular cleaning and defrosting

169

Közepes

What does a Certificate A2 for natural persons (Implementing Regulation (EU) 2024/2215) authorise?


All activities involving equipment using CO₂ (R744)
Only recovery of F-gases from equipment containing less than 3 kg (or 6 kg in hermetically sealed systems)
All activities (leak checks, installation, repair, maintenance, servicing, decommissioning, recovery) involving F-gases and hydrocarbons in equipment containing less than 3 kg, or less than 6 kg in labelled hermetically sealed systems
Only leak checks that do not entail breaking into the refrigerant circuit

170

Könnyű

How does superheat at the evaporator outlet affect efficiency?


It has no effect
It only causes a temperature drop
Excessive superheat reduces energy efficiency
It always improves performance

171

Könnyű

How do leaks in the evaporator affect efficiency?


Have no effect
Improves performance
These cause refrigerant loss and a drop in efficiency
Increase capacity

172

Könnyű

How important is correct expansion valve adjustment?


Causes leaks
It increases energy consumption
Ensures optimal evaporator charge and improves efficiency
It doesn’t matter

173

Könnyű

How does inadequate insulation of suction (or secondary-coolant) pipes affect evaporator performance?


It causes cooling losses and increased energy use
It has no effect
It lowers the condensing temperature
It improves efficiency

174

Könnyű

How does correct TEV adjustment affect system energy efficiency?


It causes leaks
It increases energy use
It ensures optimal superheat and improves efficiency
It has no effect

175

Könnyű

What happens if the superheat set by the TEV is too high?


Cooling efficiency will improve
It has no effect
Efficiency will drop because the evaporator is not being fully utilised
The refrigerant charge will increase

176

Közepes

How does too low superheat setting on the TEV affect performance?


It has no effect
It may lead to improved efficiency, but it increases the risk of the compressor becoming flooded with liquid
It reduces refrigerant flow
It increases operational safety

177

Könnyű

How do contaminants in the system affect the operation of the TEV?


Have no effect
They lower the temperature
They can cause it to become blocked and reduce efficiency
They improve its performance

178

Könnyű

What role does the filter-drier play in terms of system efficiency?


It lowers the temperature
Removes moisture and contaminants, improving the system’s efficiency
It increases the amount of refrigerant
It doesn’t matter

179

Könnyű

How does proper insulation of components (e.g. pipes near the TEV) affect the system?


It causes leaks
Prevents unwanted heat gains and improves efficiency
It doesn’t matter
It increases energy consumption

180

Közepes

What is the scope of Regulation (EU) 2024/573?


Only requirements for periodic leak checks of refrigeration equipment
Design requirements and conformity assessment for pressure equipment
Health and safety requirements for brazing and welding on refrigeration installations
Limiting emissions, use and marketing of F-gases, HFC phase-down, certification and reporting

181

Könnyű

How important is it to check the operation of the condensing pressure control valve in the system?


It causes a significant rise in temperature
It increases energy consumption
Ensures operation within the optimum pressure range and reduces energy losses
It has no effect

182

Könnyű

How does the correct selection of a TEV affect energy efficiency?


It doesn’t matter
Ensures the system is matched to its capacity and operates optimally
It increases the amount of refrigerant
It lowers the temperature

183

Közepes

What is the main design difference in hydrocarbon refrigeration systems?


No need for safety measures
Lower energy efficiency
The need to eliminate ignition sources and limit the charge because of the refrigerant's flammability
Higher operating pressures

184

Közepes

How do compressors used in hydrocarbon systems differ?


There is no difference
They must operate at higher pressures than HFC compressors
They must be approved by the manufacturer for the specific flammable refrigerant (e.g. electrical components that are not ignition sources, suitable oil)
They need no lubrication

185

Nehéz

What is the main characteristic of R744 (CO₂) refrigeration systems?


Very high operating pressures
No need for control
Low energy efficiency under all conditions
Low operating pressures

186

Nehéz

What are the requirements for piping materials in CO₂ systems?


Any material may be used
Only plastics
It doesn't matter
They must withstand high pressures (e.g. stainless steel, high-strength copper-alloy tubes such as K65)

187

Nehéz

How does a booster system work in CO₂ installations?


It reduces the refrigerant quantity
Low-temperature (LT) compressors discharge into the suction of medium-temperature (MT) compressors – two-stage compression in a single circuit
It reduces evaporator pressure
It is used to store refrigerant

188

Könnyű

What is the function of high-pressure control valves in CO₂ systems?


They are used to store the refrigerant
They control the pressure on the high-pressure side and optimise system operation
They lower the evaporator temperature
They regulate oil flow

189

Nehéz

Why is pressure optimisation in CO₂ systems crucial?


It reduces the ambient temperature
It doesn’t matter
It enables the system to achieve maximum energy efficiency in transcritical mode
It reduces the amount of refrigerant

190

Nehéz

What role does parallel compression play in CO₂ systems?


It lowers the ambient temperature
It increases energy consumption
It compresses flash gas from the intermediate receiver directly to high pressure, improving efficiency
It has no significance

191

Közepes

How can you tell that the system has been overcharged with refrigerant?


It cannot be checked, because the sight glass is not intended for this
The compressor runs at a lower load and the suction pressure drops
Even under a very small heat load, frost forms on the suction line
Under normal operating conditions the condensing pressure and subcooling rise markedly because excess liquid floods the condenser and reduces its active surface

192

Nehéz

How does an ejector work in a CO₂ system?


It uses the energy of the higher-pressure refrigerant to raise the pressure of the refrigerant from the lower stage, which improves efficiency
It increases the amount of refrigerant
It lowers the evaporator temperature
Stores the refrigerant

193

Nehéz

What is the function of liquid ejectors in CO₂ systems?


They reduce atmospheric pressure
They increase the amount of oil
They raise the refrigerant temperature
They return liquid from the separator and allow partially flooded evaporator operation (better evaporator feed)

194

Nehéz

What are the characteristics of partially flooded systems in CO₂ systems?


Lack of regulation
The absence of liquid in the evaporator
The presence of liquid in the evaporator, which improves heat transfer and efficiency
Low operating pressure

195

Nehéz

What is the main risk associated with standstill pressure in CO₂ systems?


A decrease in refrigerant quantity
A pressure rise as the refrigerant warms up during standstill (possibly exceeding PS and lifting the relief valves)
Increased efficiency
A drop in temperature

196

Nehéz

How is standstill pressure limited in CO₂ systems?


By raising the plant-room temperature
By increasing the refrigerant charge
By using an auxiliary standstill (stagnation) cooling unit, e.g. cooling the receiver, with back-up power, and by selecting an adequate PS and relief valves
By completely shutting down the system and power supply

197

Nehéz

What does standstill (stagnation) of a CO₂ system mean, and why is it important?


Improved efficiency
A state with no compressor operation or refrigerant flow – pressure rises with ambient temperature and may exceed PS
Normal system operation
A drop in system temperature

198

Könnyű

Why do CO₂ systems require more advanced automation than traditional systems?


Due to the need for precise control of pressure and temperature
Because there are no valves
They do not require automation
Due to low pressures

199

Nehéz

What must the label of a flammable refrigerant cylinder include?


Information about the cylinder owner
Only the refrigerant name
Only the net weight
The refrigerant name, the UN number, the hazard label (e.g. 2.1 – flammable gas) and basic safety information

200

Nehéz

Why is the absence of a 'flammable refrigerant' label on equipment a serious hazard?


It reduces system efficiency
It may lead to the wrong oil being selected
It may lead to the use of tools that are ignition sources
It has no significant effect on safety

201

Nehéz

Which set of information on the label of a flammable refrigerant cylinder is crucial from a safety perspective?


Gross weight and batch number
Manufacturer’s name and country of origin
Cylinder colour and date of manufacture
Name of the substance, hazard label (ADR) / GHS pictogram (CLP), UN number

202

Közepes

Before charging the unit with refrigerant, it is essential to…


…check the compressor suction and discharge connections
…fill in the unit's data sheet
…carry out a tightness test (and evacuate the system)
…carry out a trial start-up

203

Könnyű

What is the requirement regarding the labelling of an installation containing a flammable substance?


Labelling is required only in technical rooms
Labelling is not required for hermetically sealed systems
Colour-coding of pipes is sufficient
The labelling must indicate the type of substance and the flammability hazard

204

Könnyű

What are the potential consequences of using unsuitable connections in a system containing a flammable substance?


Risk of leakage and the formation of an explosive mixture
Merely a reduction in efficiency
No impact on safety
Merely installation difficulties

205

Nehéz

What is the purpose of gas detectors in a room with a refrigeration system?


Measuring refrigerant temperature
Early leak detection and triggering of measures preventing health risks and explosive atmospheres (alarm, ventilation, shut-off)
Monitoring pipe pressure
Controlling compressor capacity

206

Nehéz

How often should gas detection sensors in a machinery room be checked?


According to the manufacturer's instructions and regulations – at least every 12 months
Only after a leak has occurred
Before every start-up of the unit
Once every 5 years

207

Nehéz

Where should a gas detector be located according to EN 378?


Where the refrigerant would accumulate: low (near the floor) for refrigerants heavier than air, high (near the ceiling) for lighter ones such as NH₃
Only at the room entrance
Near the control panel
Anywhere in the room

208

Könnyű

How should an employee respond when a gas alarm is triggered?


Carry on working until they see a leak
Switch off the system and wait for the alarm to stop
Leave the room immediately and notify their supervisor
Reduce the pressure in the system

209

Nehéz

What safety checks should be carried out when installing a new refrigeration system with a flammable refrigerant?


The presence of health and safety signage, adequate ventilation and gas detectors
Only the compressor power
Only that the air filter is new
The colour of pipes and hoses

210

Könnyű

Gas detectors should be installed in rooms where:


The amount of refrigerant exceeds a specified permissible threshold
Ventilation is natural
Any refrigerant is present, regardless of the quantity
The room is less than 5 m²

211

Nehéz

What are the requirements for emergency exits from a refrigeration machinery room?


At least two exits are required and signage is optional
In small machinery rooms emergency exits need not be signed
One exit with a sign stating the refrigerant type is sufficient
Outward-opening doors and signed escape routes (number of exits per the standard)

212

Nehéz

Which installation measure for a flammable-refrigerant system improves its energy efficiency?


Charging above the nameplate quantity
Restricting room ventilation
Omitting the filter-drier
A thorough tightness test and evacuation (dehydration) of the system

213

Közepes

What information must appear on the label of equipment containing F-gases?


The manufacturer's logo, the unit weight and year of manufacture from the rating plate
Only the trade name of the refrigerant and the unit's serial number
That it contains an F-gas, its designation, quantity in kg and t CO₂ eq, and GWP
The weight and capacity of the pipework and the colour code of the casing paint

214

Könnyű

How do leaks affect systems using flammable refrigerants?


They improve efficiency
They lower the temperature
Have no effect
They cause refrigerant loss, reduced efficiency and a fire hazard

215

Nehéz

Why is it important to limit the refrigerant charge in HC systems?


It increases capacity
It limits the possibility of reaching a flammable concentration (≥ LFL) in a leak, increasing safety
It doesn't matter
It lowers the temperature

216

Könnyű

Why is the cleanliness of heat exchangers in HC systems important?


It increases the pressure
It improves heat transfer and reduces energy consumption
It doesn’t matter
Causes leaks

217

Könnyű

What maintenance measures improve the efficiency of a system using a flammable refrigerant?


Regular checks for leaks and operating parameters
Lack of servicing
Increasing the refrigerant charge
Disabling safety devices

218

Könnyű

How does the correct selection of components affect a system using a flammable refrigerant?


It lowers the temperature
It increases the amount of refrigerant
It ensures safe and optimal operation and minimises energy losses
It doesn’t matter

219

Könnyű

Why is it important to use the correct service tools in HC systems?


It increases energy consumption
Causes leaks
It doesn’t matter
It ensures operational safety and reduces refrigerant losses

220

Könnyű

How does pipe insulation affect the efficiency of systems containing HC?


It doesn’t matter
It reduces energy losses and improves efficiency
It increases the pressure
Causes leaks

221

Nehéz

Which safety class applies to R744?


A3
A1
B2L
A2.

222

Nehéz

In a simple single-stage R744 system without an intermediate receiver (refrigerant flows from the gas cooler directly to the expansion valve), operating transcritically at 90 bar with a gas-cooler outlet temperature of 35 °C, the refrigerant upstream of the expansion valve is…


…a two-phase mixture at intermediate pressure
…saturated vapour at intermediate pressure
…a subcooled liquid
…a supercritical fluid

223

Nehéz

In R744 transcritical systems, the gas cooler outlet valve controls:


The pressure in the gas cooler
The gas cooler fans
The inlet temperature to the gas cooler
The outlet temperature of the gas cooler

224

Könnyű

What is the base unit of temperature according to the International System of Units (Système International d’Unités)?


K
°F
°R
°C

225

Közepes

Which set of information best reflects the content of the equipment records required by Regulation (EU) 2024/573?


Only the date of installation and the installer's name
Operator details, equipment details, type and quantity of refrigerant, and information on servicing and repairs
The owner, installer and service technician of the unit
The make and model of the unit

226

Nehéz

Which statement best describes the behaviour of R717 and mineral compressor oil?


R717 mixes very well with the oil, which easily returns to the compressor
R717 does not mix with the oil; the oil, being heavier than liquid NH₃, collects beneath it at the lowest points (mainly on the low-pressure side)
An oil return line cannot be used in R717 systems because the oil is too hot
R717 does not mix with the oil; the oil collects on the high-pressure side above the R717

227

Nehéz

What is the main reason for using K65 copper tubing in some R744 systems?


They can withstand higher pressures
They have good low-temperature performance
They bend easily
They come in a wider range of diameters

228

Nehéz

Which statement about installing Schrader valves is correct?


Schrader valves must not be used in R744 systems
Hydrocarbons leak through Schrader valves
All Schrader cores are suitable for all refrigerants
When brazing the valve body, the core must be removed, then refitted and tightened to the correct torque

229

Nehéz

Which refrigerant can be detected with phenolphthalein paper?


R1270
R717
R1234ze(E)
R744

230

Nehéz

How does an undercharge affect the high-pressure side (without discharge pressure control)?


Discharge pressure higher, subcooling higher
Discharge pressure lower, subcooling higher
Discharge pressure higher, subcooling lower
Discharge (condensing) pressure and subcooling will both be lower

231

Nehéz

What is the benefit of adding helium as a tracer gas to nitrogen in a pressure test?


Its small atoms pass easily through leaks and are detected
It has a distinctive odour that helps locate the leak
It reacts with refrigerant residues, producing a visible colour change
It has a higher pressure than pure nitrogen in the same cylinder

232

Nehéz

Why should an evacuated R744 system initially be charged with refrigerant in the vapour phase?


To charge R744 more slowly and measure it more accurately
To prevent dry ice forming (until approx. 5.2 bar abs is exceeded)
To avoid damaging the compressor with liquid CO₂
To prevent the drain valve on the receiver from opening

233

Nehéz

If moisture remains in an R744 system because it was not properly evacuated (dehydrated), what is the likely consequence?


Formation of hydrogen fluoride and hydrofluoric acid
Excessive discharge pressure
Formation of carbonic acid, which damages the system
Reduced cooling capacity

234

Nehéz

Which system may require manual oil recovery?


R744 cascade system
An R717 system
Secondary system using R744
Supercritical ‘booster’ system using R744

235

Nehéz

The pressure of R744 at a saturation temperature of 20 °C is approx.


90 bar g
25 bar g
56 bar g
14 bar g

236

Közepes

Who is responsible for keeping the equipment records?


The equipment maintenance technician.
There is no such obligation.
The operator of the unit or system.
The person responsible for risk assessment.

237

Nehéz

Which refrigerant is lighter than air?


R1234ze(E)
R717
R744
R1270

238

Nehéz

What hazards are associated with a safety group A3 refrigerant?


Higher flammability, lower toxicity
Lower flammability, lower toxicity
Lower toxicity, no flame propagation
Higher toxicity, no flame propagation

239

Nehéz

What is the GWP of R32 (per AR4, as used in Regulation (EU) 2024/573)?


675
3922
0
6

240

Nehéz

What factors are taken into account when determining the maximum charge for comfort air-conditioning/heating applications?


Practical limit, height of the indoor unit, floor area
Lower flammability limit, height of the indoor unit, floor area
Lower flammability limit, room volume
Practical limit, room volume

241

Nehéz

What compressor displacement is required for R1270 compared with an R404A compressor in the medium-temperature range (cold room)?


About 6 times larger
About half
About 1.5 times larger
Similar

242

Nehéz

At an ambient temperature of 25 °C, the standstill pressure in the low-pressure stage of an R744 cascade (without standstill cooling) will typically be…


…the same as the high-pressure switch setting
…higher than the maximum allowable pressure (PS) of the low-pressure stage
…the same as the relief valve set pressure
…approx. 27.5 bar g

243

Nehéz

What is the correct definition of critical temperature?


The temperature at which the vapour pressure of a liquid is equal to the ambient pressure surrounding the liquid
The temperature above which there are no distinct liquid and gaseous phases
The temperature at which a substance changes from a gaseous to a solid state
The temperature at which, for certain substances, electrical resistance is zero

244

Nehéz

In the gas cooler of a transcritical system, the supercritical working fluid…


…rejects heat at constant temperature and pressure
…rejects heat as its pressure falls
…rejects heat during a phase change
…rejects heat as its temperature falls

245

Nehéz

R717 is highly corrosive to:


aluminium
stainless steel
copper (and its alloys)
titanium

246

Nehéz

What can be the effect of a relief valve lifting repeatedly?


The valve stays fully open permanently
The set pressure increases
The valve may not reseat tightly and its set (opening) pressure may decrease
The valve no longer opens

247

Közepes

Where are oil traps installed on the suction line?


Before the safety valve on the suction side
At the inlet to every component of the refrigeration system
Immediately before the compressor suction connection
At the bottom of vertical suction risers with upward flow

248

Nehéz

What is the relationship between the pressure (p) and temperature (T) of nitrogen at the start (1) and end (2) of a tightness test (p absolute, T in kelvin)?


p₂ = (p₁ × T₂)/T₁
p₂ = (p₁ × T₁)/T₂
p₂ = T₂/(p₁ × T₁)
p₂ = T₁/(p₁ × T₂)

249

Nehéz

What is the recommended pre-alarm level for fixed leak detection systems for R717?


50,000 ppm
500 ppm
500,000 ppm
5,000 ppm

250

Nehéz

Why are compressors with a separate motor (open type) mostly used in R717 systems?


To increase the refrigerant charge
Because they are cheaper
Because NH₃ attacks copper motor windings, so hermetic compressors with conventional windings are not used
To lower the condensing pressure

251

Nehéz

Which type of compressor is most commonly used in large ammonia systems?


A reciprocating or screw compressor
Hermetic scroll
Diaphragm compressor
Rotary vane compressor

252

Nehéz

How is the capacity of a piston compressor regulated in NH₃ systems?


Solely by adjusting the oil volume
By increasing the condensing pressure
By unloading the cylinders or changing the rotational speed
By reducing the refrigerant charge

253

Nehéz

How is the capacity of a screw compressor most commonly controlled?


By adjusting the oil level
By using a slide valve
By closing the suction valve
By changing the type of oil

254

Nehéz

When is two-stage compression used in NH₃ systems?


At small temperature differences
Only with water-cooled condensers
Only in small systems
At low evaporating temperatures (pressures) and high pressure ratios

255

Nehéz

What is the advantage of two-stage compression over single-stage compression?


Higher efficiency and lower discharge temperature
Lower efficiency
Higher energy consumption
No need for a separator

256

Nehéz

How does an evaporative condenser used in NH₃ systems work?


Operates without a fan
It does not require a water supply
It utilises the evaporation of water to increase cooling efficiency
It transfers heat only to the air

257

Nehéz

What is the function of the liquid separator in an NH₃ system?


It separates oil from the refrigerant
It prevents liquid from entering the compressor
Regulates the condensing pressure
Increases the discharge temperature

258

Közepes

Which symptoms with the compressor running indicate a refrigerant leak (undercharge)?


Rising liquid level in the receiver and increasing subcooling
Low suction pressure, high superheat and negligible subcooling
Sight glass full of liquid and rising oil level in the crankcase
Rising condensing and suction pressures with no superheat

259

Nehéz

What is the purpose of monitoring the liquid level in the separator?


To reduce the condensing temperature
To maintain the correct refrigerant level and prevent the compressor from flooding
To control the condenser fan
To increase the oil volume

260

Nehéz

What is the role of the float switch in NH₃ systems?


It monitors the liquid level in the tank or separator
It controls the fan’s operation
It regulates the condensation temperature
It is used to detect leaks

261

Nehéz

What is a thermosyphon in NH₃ systems?


A defrosting device
A system with gravity-driven (natural) circulation of liquid refrigerant caused by density differences, used e.g. for screw compressor oil cooling
An oil circulation pump
A type of safety valve

262

Nehéz

Why are oils that are immiscible with the refrigerant used in NH₃ systems?


To reduce the pressure
To increase the amount of refrigerant
Because the oil mixes only with water
Because NH₃ does not mix with most compressor oils

263

Nehéz

What is the main function of an oil separator in NH₃ systems?


Removing moisture from the system
To lower the condensation temperature
To separate the oil from the refrigerant and return the oil to the compressor
To increase fan efficiency

264

Nehéz

In which NH₃ system does the refrigerant evaporate completely with superheat in the evaporator, fed by an expansion valve?


A direct-expansion (DX) system
A pumped liquid-recirculation system
An indirect system
A glycol system

265

Nehéz

What is the characteristic feature of a flooded evaporator system?


The evaporator contains a large amount of liquid, which improves heat transfer
The evaporator is filled exclusively with vapour
No separator is used
No level control is required

266

Nehéz

What is the main difference between a direct and an indirect system?


In an indirect system, NH₃ flows directly into the space being cooled
In an indirect system, no compressor is used
In a direct system, there is no evaporator
In an indirect system, NH₃ cools an intermediate medium (e.g. glycol), which in turn cools the load

267

Közepes

Which components of a refrigeration system are potential leak points subject to leak checks?


Only high-pressure-side components
Only suction-side components
Joints, valves (including stems), seals (including those on replaceable filters and driers), parts subject to vibration and connections to safety and measuring devices
Hermetic compressors, liquid receivers and liquid separators

268

Közepes

What pressure is used for the pressure tightness test of an installation?


The pressure specified in EN 378-2 or by the manufacturer, not exceeding the maximum allowable pressure of the system (PS)
A pressure equal to the maximum pressure measured during operation
Always 30 bar
A pressure chosen by the technician based on experience

269

Közepes

At which points of the unit must the leak check be carried out?


Only on compressor shut-off valves, solenoid valves and filters
Only at connections of measuring instruments
Only on discharge-side components
At all points where there is a potential risk of refrigerant leakage

270

Közepes

When can a unit be considered tight after a pressure test?


When the pressure drop does not exceed 0.1 bar regardless of the test duration
When it has been checked with a fixed electronic detector
When gas bubbles appear after immersion in water
When the pressure remains constant during the test (allowing for temperature-related changes); any unexplained pressure drop requires the leak to be located

271

Közepes

Which legal act currently sets out the obligation to check stationary refrigeration equipment containing F-gases for leaks, and how often this must be done?


Regulation (EU) No 517/2014
Commission Regulation (EC) No 1516/2007
Regulation (EU) 2024/573
Implementing Regulation (EU) 2024/2215

272

Nehéz

Which parts of a refrigeration system should be given particular attention during a leak check?


Joints, valves incl. stems, seals, parts subject to vibration, connections to safety devices
Only compressor connections, because they are the only parts subject to vibration
Compressor and receiver connections, because the pressure is highest there
Only condenser connections, because the refrigerant is liquid there

273

Könnyű

What is the superheat of refrigerant vapour?


The amount of heat required to evaporate a liquid
The difference between the saturation temperature and the actual liquid temperature in the liquid line
The difference between the actual vapour temperature and the saturation temperature corresponding to its pressure (expressed in K)
The difference between the condensing temperature and the ambient temperature

274

Nehéz

Leak checks can be carried out using various methods. Which pair is correct?


Physical and chemical methods
Methods with and without quality control of supplies
Material quality control methods and electronic methods
Direct and indirect methods

275

Nehéz

To whom can leak checks of stationary refrigeration equipment containing F-gases be entrusted?


Any leak-testing specialist
An employee appointed by the owner of the installation
A person who has carried out such checks before
A natural person holding a certificate covering leak checks (A1, A2 within its charge limit, or E)

276

Nehéz

What conditions must be met to use UV dye for leak checking?


A UDT authorisation for pressure testing is required
Manufacturer approval of the method and a certificate covering breaking into the circuit
It is sufficient that introducing dye into the circuit is technically feasible
It is sufficient to have a UV lamp, dye and safety goggles

277

Nehéz

Which leak-checking methods are considered direct methods?


Pressure-change measurement and immersion in water
1. gas detection devices (portable or fixed leak detection system), 2. UV detection fluid or dye, 3. bubble/foam solutions
Nitrogen with tracer gas and pressure measurement
Vacuum test and foam solution

278

Nehéz

What do indirect leak-checking methods involve?


Leak detection with an electronic detector
Leak detection with UV dye
A visual and manual check and analysis of parameters: pressure, temperature, compressor current, liquid levels and recharge volume
Ultrasonic measurement

279

Közepes

How should the pressure be increased during a pressure tightness test?


Gradually, in stages, checking for leaks at each level until the test pressure is reached
In any way
In one step, by fully opening the nitrogen cylinder valve
As quickly as possible

280

Közepes

What electronic equipment should be used for leak checking?


Detectors suited to the refrigerant in the system, with appropriate sensitivity, checked periodically
Only hot-cathode devices
Only devices with an 'ion pump' sensor
Only detectors with an infrared sensor

281

Közepes

What documentation should be checked before starting a leak check?


Only the installation invoice and the first start-up report
The operator's fixed-asset inventory ledger
Attendance sheets of the plant-room staff for the year
The equipment records – especially recurring problems and previous leaks

282

Közepes

What information must be recorded in the leak check report?


Only the number of leaks found and the date of the check
The method used, the time spent on site and the cost of repair
The date, a general note about the leak and the operator's signature
Date, number and location of leaks, how they were repaired, technician details and signature

283

Közepes

What pressure should be used for the pressure tightness test?


Always 2–3 bar
Always 10–12 bar
Any pressure, at the technician's discretion
A pressure not exceeding the maximum allowable pressure of the system (PS)

284

Közepes

What is the temperature glide of a refrigerant?


The temperature drop of the refrigerant across the expansion valve
The temperature rise of the vapour in the compressor
A property of single-component refrigerants, for which one saturation temperature corresponds to a given pressure
In zeotropic mixtures, the difference between the temperatures at the start and end of a phase change (boiling or condensation) at constant pressure

285

Nehéz

What does a vacuum (decay) test involve?


With the pump running, you watch the vacuum gauge reading
The pump runs continuously to hold the required vacuum for the test
After isolating the pump, you check whether the system pressure rises
The pump is restarted every time the system pressure rises

286

Nehéz

How often should leak tests be carried out on equipment containing 1.5 kg of R404A refrigerant (5.9 tonnes of CO₂ equivalent)?


At least once every 12 months.
Once every six months.
Only when servicing the unit.
On initial commissioning.

287

Nehéz

How often should leak tests be carried out on equipment containing 7 kg of R404A refrigerant (27.45 tonnes of CO₂ equivalent)?


Only when servicing the unit.
Once every six months.
On initial commissioning.
At least once every 12 months.

288

Közepes

In which equipment is a leakage detection system required?


Equipment with ≥ 500 t CO₂ eq of Annex I F-gases (or ≥ 100 kg of Annex II Section 1 gases)
Equipment with 30 kg or more of F-gases, regardless of their GWP
Equipment with 5 t CO₂ eq or more of F-gases, regardless of equipment type
Equipment with 50 t CO₂ eq or more of F-gases, regardless of equipment type

289

Nehéz

Under Regulation (EU) 2024/573, a leakage detection system is mandatory when:


the F-gas charge of the refrigeration equipment is 500 t CO₂ eq or more
the equipment operates in an enclosed space
the equipment contains a flammable refrigerant in any quantity
the charge is 100 kg or more of ozone-depleting substances

290

Nehéz

Which leak-checking method may NOT be used by a holder of a Category E certificate?


Visual inspection
Leak checking with a fluorescent dye introduced into the circuit
Measurement with a handheld electronic detector
Checking with a foaming solution

291

Közepes

What should you check before using a portable electronic leak detector?


That it suits the refrigerant and has been checked as the manufacturer requires
That it has an infrared sensor, as only this type is permitted
That it has been zeroed close to the suspected leak point
That it holds a valid UDT inspection certificate

292

Közepes

Which certificate types (A1, A2, B, C, D, E) authorise leak checks of equipment containing F-gases?


All except D
A1, A2 and E
Only E
Only A1 and A2

293

Nehéz

Within what timeframe must a leak test be carried out on a stationary refrigeration system after a leak has been repaired, in accordance with EU Regulation 2024/573 on F-gases?


At any time.
Between 24 hours and 1 month after the repair.
At the next periodic inspection.
Immediately after the repair.

294

Nehéz

How often must refrigeration equipment containing ≥500 t CO₂ eq of F-gases be checked if (contrary to Article 6) no leakage detection system is installed?


Every month
Every 3 months
Every 12 months
Every 6 months

295

Közepes

Why is it advisable to subcool the liquid refrigerant?


To ensure that liquid free of vapour bubbles enters the expansion valve
To allow a condenser with a smaller heat-exchange surface to be used
To allow a smaller expansion valve to be used
To lower the evaporating temperature in the evaporator

296

Közepes

What must be done after repairing a leak in the refrigeration unit of a refrigerated trailer?


Charge an alternative refrigerant, start up and measure the parameters
Issue the invoice and leave the leak check to the next periodic service
Update the equipment records and carry out a leak check (it may be done directly after repair)
Visually inspect only the bolted and brazed joints near the repair

297

Közepes

Recovery of fluorinated greenhouse gases means:


The collection and storage of fluorinated greenhouse gases from containers, products and equipment during maintenance or servicing or prior to their disposal.
The final decommissioning and withdrawal from service or use of a product or piece of equipment containing fluorinated greenhouse gases.
The reuse of fluorinated greenhouse gases following a basic purification process.
The reprocessing of fluorinated greenhouse gases to achieve their specified standard properties.

298

Közepes

Who is authorised to recover refrigerant from stationary refrigeration equipment containing F-gases?


The administrator of the operator's account in the register
A natural person holding a certificate of the relevant type (A1; A2. or D within their charge limit)
The operator
The owner of the installation

299

Közepes

How must recovered refrigerants be stored?


In a labelled recovery cylinder with a dual valve and a valid inspection
In a disposable (non-refillable) cylinder that held the same refrigerant
In any pressure vessel that has some form of approval
In any used refrigerant cylinder, provided it is leak-tight

300

Közepes

When should the recovery of fluorinated greenhouse gases be carried out:


Before the final disposal of equipment and, where applicable, during its servicing and maintenance.
Always during servicing and maintenance of equipment.
Before each leak test of the equipment.
Only prior to the final disposal of equipment.

301

Közepes

What should be done if recovered refrigerant is contaminated (e.g. with acid, air or moisture)?


Clean the mixture yourself using a filter-drier
Pass it through a particle filter and reuse it
Add a special contaminant neutraliser
Hand it over to a specialised, authorised company for reclamation or destruction

302

Közepes

What should be done if different refrigerants have been mixed in a storage cylinder?


Separate the mixture into its components yourself
Hand the mixture over to an authorised company – as a rule for destruction
Pass it through a filter-drier and reuse it
Add a special refrigerant to the mixture

303

Közepes

How does push-pull refrigerant recovery work?


Nitrogen is injected into the system, pushing the refrigerant into the atmosphere
The recovery unit draws vapour from the recovery cylinder and pushes it into the system; the pressure difference forces liquid refrigerant out of the system into the cylinder
Refrigerant is drawn alternately from the suction and discharge sides of the compressor
The recovery unit draws vapour from the system and condenses it in the cylinder

304

Közepes

What are the options for managing waste refrigerant?


Reclamation, recovery
Recycling, reclamation, destruction
Recovery, disposal
Disposal, storage

305

Közepes

Which management option restores recovered refrigerant to a quality equivalent to virgin product, so that it can be used by any undertaking?


Recycling
Reclamation
Destruction
Storage

306

Közepes

The lower the evaporating temperature, …


…the lower the density of the suction vapour and the greater the cooling capacity of the compressor
…the greater the density of the suction vapour and the lower the refrigerant mass flow rate
…the lower the density of the suction vapour and the lower the refrigerant mass flow rate
…the greater the density of the suction vapour and the greater the refrigerant mass flow rate

307

Közepes

How must transportable pressure vessels (e.g. refrigerant cylinders) be marked?


Only with weight and capacity marks
Among other things: the number of the design and testing standard, marks of the approving country and the inspection body, the date of the initial inspection, and the manufacturer's and operational marks
The marking is optional
With the manufacturer's logo and date of manufacture

308

Közepes

The recovery of refrigerants does not require the use of:


Scales with a measurement range suitable for the size of the cylinder being filled.
An electronic leak detector.
A refrigerant recovery station.
Hoses with shut-off valves.

309

Közepes

What functions does the compressor perform in a refrigeration system?


The compressor compresses ambient air and increases the pressure of the refrigerant.
The compressor draws in refrigerant vapour from the evaporator, compresses it, and then forces it into the condenser, raising the pressure to the required condensing pressure.
The compressor creates a vacuum on the suction side of the system
The compressor condenses the refrigerant.

310

Könnyű

What is the compression ratio of a compressor?


The ratio of suction pressure to discharge pressure (po/pc)
The ratio of discharge pressure to the effective capacity of the compressor (p/Vk)
The amount of refrigerant compressed per cycle relative to heat capacity
The ratio of absolute discharge pressure to absolute suction pressure (pc/po)

311

Közepes

What is compressor flooding (liquid slugging)?


Liquid refrigerant or oil entering the compression chamber
A large amount of liquid refrigerant in a flooded evaporator, which is a normal operating condition
Flooding of the compressor by rainwater
Excess oil in the condenser

312

Közepes

Within what range is the compressor motor speed typically controlled using a frequency inverter?


Speed control does not change the cooling capacity
Approximately 30 to 75 Hz, corresponding to about 60–150% of nominal capacity (depending on the compressor manufacturer)
From approximately 10% to 90% of nominal capacity
By a maximum of 10%

313

Könnyű

What is the theoretical displacement (swept volume flow) of a compressor?


A value expressed by the coefficient of performance (COP)
The volume of vapour drawn in per unit of time, determined by the compressor's geometry and speed (stated by the manufacturer, e.g. in m³/h)
The volume of refrigerant flowing in one piston cycle under actual operating conditions
The volume of a single cylinder in cm³

314

Közepes

Why is it essential to observe the correct phase sequence for scroll compressors and screw compressors?


Because changing the phase sequence would reverse the direction of rotation of the compressor rotors, which could result in damage to the compressors.
Because these types of compressors are sensitive to voltage drops.
Because this type of compressor has difficulty starting up if the phase sequence is changed.
Because the motor speed would decrease, and consequently the compressor’s capacity.

315

Közepes

What compression ratio should each stage of a two-stage vapour-compression system have (rule of thumb)?


Greater than 10
Less than approximately 8
Equal to 1
Greater than 18

316

Közepes

Why is a shaft seal necessary in open-type compressors?


To ensure the bearing remains lubricated
To prevent air from entering and refrigerant from leaking out of the compressor
To protect the crankshaft bearing
Only to prevent oil leakage

317

Közepes

How can you check whether the liquid refrigerant is sufficiently subcooled?


Check whether the whole evaporator surface is covered with an even layer of frost
Compare the liquid-line temperature with the saturation temperature at the measured condensing pressure
Check by touch whether the condenser outlet is noticeably colder than ambient
Check whether the liquid distributor upstream of the evaporator feels warm

318

Közepes

Why is the compressor crankcase heated?


To increase dissolution of refrigerant in the oil and improve its viscosity
To dehydrate the oil
To keep the lubricating oil liquid
To limit refrigerant migration into, and dissolution in, the oil during standstill

319

Könnyű

What is the clearance (dead) volume of a reciprocating compressor?


The space between the underside of the piston and the crankcase cover
The space between the side of the piston and the cylinder
The volume between the valve plate and the piston at bottom dead centre
The volume between the valve plate and the piston crown at top dead centre

320

Közepes

What are compressor packs (racks)?


Units with two-stage compressors
Several compressors connected in parallel on a common frame with common suction and discharge headers
Several air-cooled condensers
Sets of compressors connected in any configuration

321

Közepes

What is the main advantage of multi-compressor packs?


A smaller refrigerant charge than a single-compressor system
Stepwise capacity matching to demand, plus redundancy
No need for compressor controls and safety devices
Low purchase cost and easy installation without special controls

322

Közepes

What is meant by the operating envelope (application range) of a compressor?


A range determined by the evaporating temperature at a given ambient temperature
The capacity, refrigerant type and dimensions of the compressor
The permissible range of evaporating and condensing temperatures (to, tk), or the corresponding pressures, within which the compressor may operate
A range determined only by the evaporating temperature

323

Közepes

What are the basic functions of oil in a compressor?


Increasing the cooling capacity of the refrigerant
Sealing leaks that develop in the installation
Absorbing moisture from the refrigerant
Lubricating bearings and sliding surfaces, removing heat, and sealing clearances (e.g. between piston and cylinder, or rotors)

324

Közepes

What are the most effective ways of controlling compressor cooling capacity?


Partially covering the evaporator
An expansion valve
Changing the displacement: varying the rotational speed or unloading cylinders
Pressure control valves

325

Közepes

What does hot-gas bypass capacity control involve?


High-pressure liquid is injected into the suction to increase capacity
Bypass is not used for capacity control
Part of the hot discharge gas is passed through a bypass valve to the suction side (or evaporator inlet), reducing the effective capacity
The compressor speed is varied

326

Közepes

What is the fundamental difference between hermetic and semi-hermetic compressors?


Both can be dismantled; they differ only in cooling capacity
The semi-hermetic casing is bolted (can be opened); the hermetic one is welded
Semi-hermetic compressors run more quietly as a complete unit
The semi-hermetic compressor has no motor inside the casing

327

Közepes

How does a scroll compressor work?


It uses two screws to compress the refrigerant.
A scroll compressor is also known as a turbo compressor.
It is a type of piston-type device.
It is a positive-displacement compressor in which compression results from the interaction of a fixed and an orbiting scroll.

328

Közepes

What physical process takes place in the evaporator?


The refrigerant condenses
The secondary fluid (glycol, water) evaporates while the refrigerant condenses
The liquid refrigerant evaporates, absorbing heat, and the vapour is slightly superheated at the outlet
The refrigerant is subcooled as a liquid

329

Közepes

What is the purpose of compressor capacity control?


To increase the condensing pressure
To match the cooling capacity to the current demand
To ensure compressor lubrication
To match capacity to the condensing temperature

330

Közepes

Why is inverter speed control advantageous for refrigeration compressors?


It enables continuous, smooth control of cooling capacity
It can be used with any compressor to ensure lubrication
It increases compressor capacity above nominal at any frequency
Reducing the speed improves oil return to the compressor

331

Közepes

Does the suction gas temperature affect the cooling capacity of the compressor?


Yes, but only if the suction gas is deeply cooled
Yes – higher temperature lowers vapour density, mass flow and capacity
No – capacity depends only on the compressor displacement
Yes, but only in reciprocating compressors, not scroll

332

Közepes

In the case of compressor units fitted with an oil level control system, is it necessary to install the compressors at the same height?


Only scroll compressors.
Yes.
Only screw compressors.
No.

333

Közepes

What functions does a compressor powered by the vehicle’s engine perform in a transport refrigeration system?


The compressor compresses ambient air and increases the pressure of the refrigerant.
This compressor draws in refrigerant vapour from the evaporator, compresses it and then forces it into the condenser whilst the vehicle’s engine is running.
This compressor creates a vacuum on the suction side of the system whilst the vehicle’s engine is switched off.
This compressor condenses the refrigerant whilst the vehicle is in motion.

334

Közepes

Which media most commonly absorb heat from the refrigerant in the condenser?


Ammonia
Air and CO₂
Only a water–glycol mixture
Air or water

335

Közepes

What is the function of the condenser in refrigeration systems?


Absorption of heat rejected in the regenerative heat exchanger
Releasing only the heat from the compressor into the surroundings
Releasing only the heat absorbed in the evaporator into the surroundings
Releasing to the environment the heat absorbed in the evaporator and the heat added during compression

336

Közepes

If the refrigerant temperature on the high-pressure side is above its critical temperature, condensation…


…always occurs regardless of temperature
…occurs provided a special condenser is used
…does not occur
…does not depend on temperature

337

Közepes

How is liquid subcooling usually achieved in a refrigeration system?


With hot high-pressure vapour
With an additional heat exchanger using liquid nitrogen
By dissolving the refrigerant in oil
In the final section of the condenser (or in an additional subcooler)

338

Közepes

What is the purpose of condenser fan speed control?


To disperse refrigerant in the event of a leak
To keep the condensing pressure at the correct level
To reduce energy efficiency
Only to protect against exceeding the maximum condensing pressure

339

Közepes

Which international agreement introduced the global phase-down of HFC production and consumption?


The Vienna Convention for the Protection of the Ozone Layer
The Paris Agreement
The Kyoto Protocol
The Kigali Amendment to the Montreal Protocol

340

Közepes

Which international treaty governs the phase-out of ozone-depleting substances (CFCs, HCFCs)?


The Montreal Protocol
The UN Framework Convention on Climate Change (UNFCCC)
The Stockholm Convention
The Paris Agreement

341

Nehéz

What is the basis of the GWP values in Regulation (EU) 2024/573?


Each Member State sets its own GWP values
AR6 for all substances
AR4 for all substances
For HFCs (Annex I) – mainly the IPCC Fourth Assessment Report (AR4); for HFOs and non-fluorinated substances (Annexes II and VI) – the Sixth Assessment Report (AR6)

342

Nehéz

An air conditioner (not hermetically sealed) contains 2.5 kg of R410A (GWP 2088). How often must it be checked for leaks?


At least every 12 months (5.22 t CO₂ eq)
No checks required (below 3 kg)
Every 3 months
Every 6 months

343

Nehéz

When is labelled hermetically sealed equipment containing HFCs (Annex I) exempt from leak checks?


Never – hermetically sealed equipment is always checked
Always, regardless of charge
When it contains less than 5 t CO₂ eq
When it contains less than 10 t CO₂ eq, and in residential buildings also when it contains less than 3 kg of F-gases

344

Nehéz

Is a chiller containing 50 kg of R1234ze(E) subject to leak checks under Regulation (EU) 2024/573?


Yes – every 12 months, because its GWP is low
No – the threshold is 5 t CO₂ eq and 50 kg of R1234ze is below 1 t CO₂ eq
No – HFOs are not subject to leak checks
Yes – at least every 6 months (every 12 months with a leakage detection system)

345

Nehéz

In 2026, may an existing refrigeration installation using R404A (GWP 3922) be topped up with virgin refrigerant?


Yes, if the equipment has a leakage detection system
Yes – the ban applies only to equipment ≥40 t CO₂ eq
Yes – bans apply only to new equipment
No – only reclaimed or recycled R404A is allowed (until 1 January 2030)

346

Nehéz

After 1 January 2026, may an R410A (GWP 2088) air conditioner be serviced using virgin R410A?


Yes – the servicing ban for air conditioners and heat pumps covers F-gases with GWP ≥ 2500
Only with reclaimed refrigerant
No – the ban covers all HFCs
No – the ban covers all refrigerants with GWP ≥ 750

347

Közepes

Can HFC refrigerant recovered during a repair be put straight back into the same equipment without any cleaning (filtering/drying)?


Yes, always
No – recovered F-gas may be used for filling only after it has been recycled or reclaimed
Yes, if the operator agrees
Yes, if less than 24 hours have passed

348

Közepes

Who may purchase HFCs for servicing refrigeration equipment?


Only a person holding the relevant certificate or an undertaking employing such persons
Any adult
Only the equipment operator
Any business

349

Közepes

Under what condition may non-hermetically sealed split air conditioning charged with F-gas be sold to an end user?


When the user signs a statement that they will install it themselves
Unconditionally
When evidence is provided that installation will be carried out by a certified undertaking
Only if the unit contains less than 3 kg of refrigerant

350

Közepes

By when must the holder of an F-gas certificate issued under Regulation (EU) No 517/2014 first complete refresher training or an evaluation process?


By 31 December 2030
By 12 March 2025
By 12 March 2029 (and then at least every 7 years)
Never – the certificate is valid indefinitely

351

Közepes

What must the holder of a Category I certificate (Regulation 2015/2067) do to continue using it?


Update their knowledge and skills to the level of Certificate A1 (Annex I to Regulation 2024/2215)
Nothing – Category I automatically becomes A1
Apply for an extension without training
Update their knowledge to the level of Certificate E

352

Közepes

What does Certificate C under Implementing Regulation (EU) 2024/2215 authorise?


All activities in relation to CO₂
All activities in Article 2(1) in relation to ammonia (NH₃)
Recovery of F-gases from equipment <3 kg
Leak checks without breaking into the circuit

353

Közepes

May a person enrolled in a certification training course carry out certified activities?


Yes – independently, for 6 months
Yes – under the supervision of a certified person, for no more than 24 months in total
No, never
Yes – with no time limit, if employed by a certified company

354

Közepes

How long must the operator keep the records of equipment subject to leak checks, if they are not kept in a national database?


At least 5 years
At least 1 year
At least 2 years
Until the equipment is decommissioned

355

Nehéz

Since 1 January 2025, may a new single-split air conditioner containing 1.5 kg of R410A be placed on the market?


Yes – the ban applies from 2029
No – single splits <3 kg with F-gases of GWP ≥ 750 are banned
Yes – the ban applies only to units >12 kW
Yes, if the unit is hermetically sealed

356

Nehéz

From when is it prohibited to place on the market split air-to-air systems up to 12 kW containing F-gases with GWP ≥150 (unless required for safety)?


From 1 January 2035
From 1 January 2029
From 1 January 2025
From 1 January 2027

357

Nehéz

Which persistent atmospheric degradation product of R1234yf is classed as a PFAS?


Carbon dioxide
Ozone
Carbonic acid
Trifluoroacetic acid (TFA)

358

Közepes

What distinguishes class 2L refrigerants from class 2?


A maximum burning velocity of no more than 10 cm/s
No lower flammability limit
Heat of combustion above 19 MJ/kg
Higher toxicity

359

Közepes

What is the lower flammability limit (LFL) of propane R290?


Approx. 0.38 kg/m³
Approx. 0.038 kg/m³ (approx. 2.1% by volume)
Approx. 0.307 kg/m³
Approx. 1.8 kg/m³

360

Nehéz

What is the maximum R290 charge per circuit of a commercial refrigerating appliance (e.g. a cabinet) according to EN IEC 60335-2-89:2022?


1.2 kg
1.5 kg
150 g
13 × LFL ≈ 494 g

361

Nehéz

Calculate the maximum R32 charge (LFL = 0.307 kg/m³) for a wall-mounted air conditioner (h₀ = 1.8 m) in a 20 m² room using m_max = 2.5 × LFL^1.25 × h₀ × A^0.5.


approx. 4.6 kg
approx. 13.8 kg
approx. 1.5 kg
approx. 0.46 kg

362

Közepes

Equipment marked 'Ex II 3G' may be used in zone:


20 (dusts)
0
1
2 (explosive gas atmosphere unlikely and short-lived)

363

Közepes

How is explosion hazard zone 2 defined?


An explosive atmosphere is not likely in normal operation and, if it occurs, persists only for a short period
An area where flammable refrigerants are never used
An explosive atmosphere is likely to occur in normal operation
An explosive atmosphere is present continuously or for long periods

364

Közepes

Under which UN number is propane (R290) carried under ADR?


UN 1005
UN 1978
UN 3252
UN 3337

365

Nehéz

What is the maximum quantity of R290 (class 2, group F) that may be carried per transport unit under the ADR 1.1.3.6 exemption?


20 kg
333 kg
1000 kg
Unlimited

366

Közepes

At what concentration should a portable flammable gas detector used for R290 work raise an alarm at the latest?


At 150% of LFL
At 5% propane by volume
No higher than 25% of LFL
At 100% of LFL

367

Közepes

How should a recovery cylinder be prepared before filling it with a hydrocarbon refrigerant?


No preparation is needed
Purge it with compressed air
Evacuate it (no air) and label it for the specific flammable refrigerant
Partly fill it with nitrogen to 5 bar

368

Közepes

What is the correct approach in a risk analysis before work on an HC system?


First eliminate hazard sources (e.g. ignition sources); where this is not possible, identify them and apply mitigating measures (ventilation, detection, PPE)
Having a fire extinguisher is sufficient
The risk analysis is done after the work is finished
First select PPE, then possibly remove ignition sources

369

Nehéz

What is the charge limit m₃ = 130 m³ × LFL for R290 (LFL = 0.038 kg/m³) according to IEC 60335-2-40?


approx. 4.94 kg
approx. 0.15 kg
approx. 13 kg
approx. 0.99 kg

370

Közepes

Which property of ammonia helps people detect a leak early?


It is odourless
A very low odour threshold (a few ppm)
It is denser than air
It is yellow in air

371

Közepes

What hazard does a large CO₂ leak in an enclosed room pose to people?


Explosion of the mixture with air
Accumulation near the floor and asphyxiating/toxic effects at high concentrations
CO₂ is completely safe
Formation of hydrogen fluoride

372

Nehéz

Why does the efficiency of transcritical CO₂ systems fall in warm climates, and how is this mitigated?


CO₂ freezes in the gas cooler – heaters are used
Gas cooler pressure drops – extra charge is added
At high ambient temperatures the system operates transcritically with large throttling losses – parallel compression and ejectors are used, among others
Efficiency does not depend on climate

373

Közepes

What is floating head pressure and what does it achieve?


It means switching condenser fans off periodically
It lets the condensing pressure fall with ambient temperature, reducing compressor work and raising COP (requires an expansion valve that works at a small pressure difference)
It increases subcooling by flooding the condenser
It keeps a constant high condensing pressure all year

374

Közepes

How do SEER/SCOP differ from EER/COP?


SEER/SCOP apply only to natural-refrigerant equipment
There is no difference – they are synonyms
EER/COP are always higher than SEER/SCOP
SEER/SCOP are seasonal indicators accounting for part load and climate (EN 14825); EER/COP refer to a single operating point (EN 14511)

375

Közepes

Which design approach can significantly reduce the F-gas charge of a large refrigeration installation?


An indirect (secondary-coolant) system or a cascade with a natural refrigerant in the low stage, plus heat exchangers with small internal volume
Omitting pipe insulation
Larger liquid-line diameters
Adding a second liquid receiver

376

Közepes

Why must the charge of small, critically charged R290 systems be weighed to within a few grams during service?


Because extra R290 improves efficiency
Small charge deviations significantly change superheat/subcooling and efficiency, and overcharge increases the risk in a leak
Because scales are not needed – charging is done by sight glass
Because R290 is more expensive than HFCs

377

Közepes

Which information must be entered in the equipment records after a leak check?


Only the operator's signature
The date and result of the check and the identity of the undertaking and person who performed it (with certificate number)
Only the date of the check
Only the equipment's energy consumption

378

Közepes

What must be done when an indirect method (e.g. parameter analysis) indicates a possible leak?


Top up the refrigerant and end the check
Nothing – indirect methods are sufficient
Record it and check at the next periodic inspection
Carry out a direct-method examination to locate the leak