F-Gas English Low GWP

Všetky otázky
HFC | Flammable | CO₂ | NH₃
Ľahké otázky | Stredne ťažké otázky | Ťažké otázky

1

Ľahká


2

Ľahká

What is the base unit of mass in the International System of Units (SI)?


kg
N
lb (pound)
t

3

Stredne ťažká

What process takes place in the condenser of a refrigeration system?


The refrigerant absorbs heat from the surroundings and evaporates
Hot vapour discharged by the compressor is desuperheated, condensed, and the resulting liquid is slightly subcooled
The refrigerant rejects only the heat generated in the compressor
The secondary fluid (glycol, water) condenses while the refrigerant evaporates

4

Stredne ťažká

What mainly determines the condensing temperature of an air-cooled condenser?


The ambient (inlet) air temperature
The evaporating temperature
The compressor discharge temperature
The superheat

5

Stredne ťažká

Why does heat flow from the condenser to the surroundings?


Because the compressor pushes heat directly into the surroundings
Because the condensing temperature is higher than the ambient temperature, and heat flows spontaneously from a warmer to a colder body (second law of thermodynamics)
Because HFC refrigerants attract heat from the surroundings
Because the pressure in the condenser is lower than ambient

6

Stredne ťažká

What should you mainly pay attention to when operating a condenser?


That the inlet air temperature is lower than the outlet air temperature
The colour of the condenser casing
That the outlet air temperature is higher than the condensing temperature
Its general condition and the cleanliness of the heat-exchange surfaces

7

Stredne ťažká

What criteria should be considered when selecting a suitable condenser?


Only own experience and the dimensions
The required capacity of the condenser and the technical specifications declared by the manufacturer
Only the size and number of fans
Fan noise, connection diameters and colour

8

Stredne ťažká

How do contaminants (dust, particulates, deposits) affect the performance and efficiency of heat exchange surfaces in condensers?


Contaminants increase the heat transfer area and reduce the condensing pressure.
Contaminants do not significantly affect the efficiency and effectiveness of the heat exchange surfaces in condensers.
Contaminants restrict heat transfer (reducing the heat transfer coefficient) and cause an increase in condensing temperature and pressure, which in turn leads to a reduction in the condenser’s efficiency.
Contaminants restrict heat transfer (reducing the heat transfer coefficient) and cause a reduction in condensing pressure.

9

Stredne ťažká

How does the capacity of an air-cooled condenser change when it becomes dirty?


It remains unchanged
It increases
It decreases
It increases because the fan speed rises

10

Stredne ťažká

What is the main consequence of heavy frost on an air-cooling evaporator?


Reduced heat transfer and airflow, resulting in a drop in cooling capacity and evaporating temperature
A rise in evaporating pressure
A rise in the cooled-air temperature with no effect on capacity
An increase in condenser subcooling

11

Stredne ťažká

What happens when the evaporation temperature drops?


The compressor’s cooling capacity decreases.
The compressor’s cooling capacity increases.
The condenser fan speed increases.
The discharge temperature decreases.

12

Stredne ťažká

When is natural (off-cycle, air) defrosting possible?


Never – electric heaters must be used in every air cooler
When the air passing through the cooler is above 0 °C
Only in freezer rooms below −18 °C
Only in coolers fitted with speed-controlled fans

13

Stredne ťažká

When does frost form on the surface of an air-cooling evaporator?


When the evaporator surface temperature is below 0 °C and below the dew point of the air
Always, in every air cooler
Only when the room air temperature falls below 0 °C
Only when the system runs continuously

14

Stredne ťažká

In extensive pipework systems, flash gas (secondary evaporation) in the liquid line can be prevented by…


…using smaller-diameter pipes
…insulating the discharge line between the compressor and the condenser
…increasing the length of the liquid line
…additional subcooling of the liquid

15

Stredne ťažká

How does hot gas defrosting of the evaporator work?


Heated vapour (hot gas) from the compressor is directed into the evaporator piping.
This involves reversing the direction of rotation of the compressor.
We switch on the gas heater directed at the evaporator.
We swap the outlet and inlet sides of the evaporator.

16

Stredne ťažká

What is the function of the evaporator in a refrigeration system?


It ensures that the refrigerant is superheated over the largest possible heat exchange surface area.
It transfers heat from the medium being cooled to the boiling refrigerant.
It cools the refrigerant.
It evaporates the water flowing through the evaporator.

17

Stredne ťažká

What condition must electric heaters for evaporator defrosting meet?


They must have good thermal contact with the heat-exchange surface (e.g. inserted in the fin block)
Heat from the heaters must be carried by the running fans
They must be in direct contact with the refrigerant
They must be located beneath the evaporator

18

Stredne ťažká

Refrigerant distributor:


ensures the even distribution of the refrigerant discharged by compressors connected in parallel.
acts as a buffer for the refrigerant in the event that the pressure upstream of the expansion valve is exceeded.
ensures an even distribution of the refrigerant to the individual sections of the evaporator.
ensures even distribution of the refrigerant to the individual sections of the condenser.

19

Stredne ťažká

What defrosting methods are used for air coolers?


Only by switching off the fans with the compressor running
Electric only – other methods are not permitted in refrigeration
Natural only – other methods are ineffective and uneconomic
Electric, hot gas, water spray and natural (at positive temperatures)

20

Stredne ťažká

The boiling point of a liquid rises when the pressure above the liquid…


…varies depending on the ambient temperature
…falls
…remains constant
…rises

21

Stredne ťažká

MOP in thermostatic expansion valves stands for:


self-cleaning of the valve in the event of moisture in the refrigerant freezing.
maximum operating pressure.
maximum pressure switch protection.
minimum flow opening.

22

Stredne ťažká

The function of a thermostatic expansion valve (TEV) is:


to adjust the evaporating pressure in the condenser
to maintain a constant compressor suction pressure
to maintain a constant condensing pressure
to meter refrigerant into the evaporator according to the superheat of the vapour leaving the evaporator

23

Stredne ťažká

What type of compressor motor can be used with a capillary tube?


An electronically commutated motor
A high-starting-torque motor must be used
A low-starting-torque motor (pressures equalise during standstill)
A low-speed motor

24

Stredne ťažká

What does a thermostatic expansion valve control?


The condensing pressure
The temperature in the cold room
The discharge temperature
The mass flow of refrigerant fed into the evaporator

25

Ľahká

The refrigerant absorbs heat when…


…it is subcooled
…it evaporates
…it condenses
…it freezes

26

Stredne ťažká

What does the manufacturer state as the factory setting of a thermostatic expansion valve?


the superheat value during valve operation.
the static superheat of the valve.
the degree of refrigerant expansion.
the degree to which the valve is filled with refrigerant liquid.

27

Stredne ťažká

Where is a new or repaired system with an expansion valve and liquid receiver charged?


In the liquid phase into the compressor suction, with the compressor running
Anywhere – the charging point does not matter
In the liquid phase on the high-pressure side, with the compressor stopped
Through the capillary tube outlet during normal system operation

28

Stredne ťažká

What does a thermostatic or electronic expansion valve control?


The amount of refrigerant fed to the evaporator according to superheat
Subcooling, by adjusting condensing pressure
The evaporating pressure – closing below the set point
The compressor speed

29

Stredne ťažká

What does the MOP function of thermostatic expansion valves mean?


The valve limits the maximum evaporating (suction) pressure, protecting the compressor motor from overload, e.g. after defrost
The valve limits subcooling
The valve prevents motor overheating by injecting liquid into the compressor
The valve maintains a constant condensing pressure

30

Stredne ťažká

The lower the liquid temperature upstream of the expansion valve, (at the same mass flow)…


…the lower qo and the lower Qo
…the higher the specific refrigerating effect qo [kJ/kg] and the higher the cooling capacity Qo
…the lower qo and the lower energy efficiency
…the lower qo, with Qo unchanged

31

Stredne ťažká

How should the MOP point of an expansion valve be selected relative to the highest normal evaporating temperature?


Higher by approx. 20 K
A few kelvin higher (approximately 7 K)
Freely – the MOP value is irrelevant
About 7 K lower than that temperature

32

Stredne ťažká

What is the function of the suction pressure regulator?


It prevents a drop in suction pressure and, if necessary, shuts down the refrigeration system.
It limits the suction pressure and protects the compressor from excessively high suction pressure.
To maintain the suction pressure at the highest possible level.
It maintains the evaporation pressure at a constant level.

33

Stredne ťažká

What is the function of the valve regulating water flow through the condenser?


To maintain the condensing pressure at the highest possible level.
To maintain the condensing pressure at a constant level.
To maintain the water temperature at the highest level.
To maintain the condensing pressure at the lowest possible level.

34

Stredne ťažká

The use of a refrigerant distributor requires a thermostatic expansion valve ...


... with a MOP function.
... with an adsorption-type sensor filling.
... with external pressure equalisation.
... with internal pressure equalisation.

35

Stredne ťažká

What properties should good insulation materials have?


An antistatic coating
High thermal conductivity
The ability to absorb large amounts of moisture
Low thermal conductivity (and low water absorption, vapour tightness)

36

Stredne ťažká

When is refrigerant vapour superheated?


When its temperature is higher than the saturation temperature corresponding to its pressure
When the pressure on the discharge side is higher than on the suction side
When the evaporating temperature is lower than the ambient temperature
When the compressor motor temperature rises excessively

37

Stredne ťažká

How can you check whether the liquid refrigerant is reaching the expansion valve without vapour bubbles?


We check using a pressure gauge fitted on the discharge side of the compressor.
We check using a liquid pressure gauge.
We check this using a sight glass.
We are unable to check this.

38

Stredne ťažká

Where does the liquid line run?


Between the evaporator and the compressor
From the condenser (liquid receiver) to the expansion valve
Between the compressor and the condenser
Between the evaporator and the suction-line heat exchanger

39

Stredne ťažká

What is the function of the liquid receiver in a refrigeration system?


To store refrigerant and compensate for changes in the circulating charge as the heat load varies
To further subcool the condensed refrigerant
To act as a reserve when the required charge is unknown
To collect liquid refrigerant and excess oil

40

Stredne ťažká

What is the purpose of the liquid receiver during service work?


It allows pump-down and temporary storage of the refrigerant
It collects excess oil circulating in the system
It further subcools the refrigerant before the expansion valve
It is a reserve when the installer does not know the required charge

41

Stredne ťažká

Where should the liquid receiver be installed?


It should be fitted between the compressor and the condenser.
It should be fitted just before the compressor.
It should be installed downstream of the condenser, upstream of the expansion valve.
It should be fitted after the evaporator.

42

Stredne ťažká

What is the function of the suction pressure regulator fitted to the suction pipe when the compressor starts up?


It closes when the suction pressure upstream of the compressor drops.
It regulates the evaporation pressure.
It opens when the suction pressure upstream of the compressor drops.
It regulates the condensing pressure.

43

Stredne ťažká

The use of microchannel heat exchangers, compared with conventional heat exchangers made of copper tubes and fins, results in:


A reduction in refrigerant charge and, typically, higher energy efficiency.
An increase in the amount of refrigerant in the system and an increase in condensing pressure.
There is no effect whatsoever on either the amount of refrigerant or energy efficiency.
A reduction in the system’s energy efficiency.

44

Stredne ťažká

Which refrigerants belong to the HFC group?


R11, R12, R502.
R134a, R404A, R507A, R410A.
R134a, R32, R22, R507A, R290.
R22, R401A.

45

Stredne ťažká

Which refrigerants belong to the HFO group?


R134a, R290.
R134a, R404A.
R1234yf, R1234ze(E).
R22, R12.

46

Stredne ťažká

What are the characteristics of R410A refrigerant compared to R407C refrigerant?


The saturation pressure of R410A refrigerant is higher than that of R407C.
The saturation pressure of R407C is 150% higher than that of R410A.
The saturation pressure of both refrigerants is roughly the same.
The saturation pressure of R407C refrigerant is much higher than that of R410A.

47

Stredne ťažká

What does the TEWI indicator define?


The global warming potential of a gas relative to CO₂ over a 100-year horizon
Total Equivalent Warming Impact: the sum of direct emissions (leakage and refrigerant losses at disposal) and indirect emissions (CO₂ from generating the energy consumed by the equipment) over its lifetime
The impact of a refrigerant on the ozone layer
The ability of the ozone layer to recover

48

Stredne ťažká

What are the characteristics of R452A compared with R404A?


Both are azeotropic and have no temperature glide
It is a non-flammable (A1) HFC/HFO blend with properties similar to R404A and a GWP about 45% lower
It is a flammable and toxic single-component HFC
The temperature glide of R452A is half that of R404A

49

Stredne ťažká

What distinguishes R1234yf from R134a?


A higher critical temperature
It is mildly flammable (class A2L), whereas R134a is non-flammable (A1)
Higher toxicity
A higher normal boiling point

50

Stredne ťažká

How does CO₂ (R744) compare with R134a?


It has identical properties and is a drop-in replacement for R134a
Its temperature glide is 7 K greater than that of R134a
It has a lower critical temperature, much higher operating pressures and a much higher volumetric cooling capacity (smaller compressors and pipes)
Unlike R134a, it is an azeotropic mixture

51

Stredne ťažká

Which of the following is NOT a fluorinated greenhouse gas?


Hydrofluorocarbons (HFCs).
Sulphur hexafluoride (SF6).
Perfluorocarbons (PFCs).
Carbon dioxide (CO₂).

52

Ťažká

What additional protective equipment will you use when brazing systems containing HC refrigerants?


Latex gloves
Ear defenders
A flammable gas detector
A high-visibility vest

53

Ťažká

Why can’t a sealed high-pressure switch be replaced with a standard mechanical one in a system containing a flammable refrigerant?


It is a potential source of ignition
Dust and moisture may enter
There is a risk of refrigerant leakage
The pressure switch setting will not be correct

54

Ťažká

What is the minimum (recommended) distance from a work area with HC refrigerants within which there must be no sources of ignition?


2 m
1 m
0.5 m
3 m

55

Ťažká

What is the maximum safe R32 fill of a recovery cylinder approved for flammable gas that holds 20 kg of R410A (the liquid density of R32 is about 8-10% lower)?


18 kg
33 kg
9 kg
20 kg

56

Ťažká

What is the maximum charge of an A3 refrigerant for a hermetic display cabinet with an integral condenser located in the ground-floor sales area of a supermarket?


0,494 kg
1.0 kg
10 kg
2.5 kg

57

Ťažká

How can a vacuum pump be used safely to evacuate a system containing a flammable refrigerant?


Ignition-source-free pump, good ventilation, exhaust to a safe place
Position the pump at least 3 m above floor level
Place the pump directly on the floor, as low as possible
Such systems need not be evacuated before charging

58

Stredne ťažká

What is the greenhouse effect?


Chlorine compounds destroy stratospheric ozone, increasing UV radiation at the surface
Greenhouse gases absorb and re-emit the Earth's infrared radiation, warming the lower atmosphere
Clouds reflect ultraviolet radiation, which makes the air near the surface warmer
Dust in the atmosphere reflects sunlight, lowering the average surface temperature

59

Ťažká

What safety measure must you carry in your vehicle when transporting flammable refrigerant cylinders?


A fire extinguisher
Tinted safety goggles
A fire blanket
Thick gloves

60

Ťažká

How would you prepare a 10 kg R32 water chiller located outdoors for debrazing its joints?


Vent the R32 outdoors, then fill and vent the system with nitrogen three times
Recover the R32 to a vacuum, then fill the system with nitrogen to a slight positive pressure (approx. 0.1 bar g)
Recover the R32 to a vacuum and start desoldering immediately
Vent the R32 outdoors and purge the system

61

Stredne ťažká

What is R1270?


Propane
Propene (propylene)
Isobutane
n-Butane

62

Ťažká

Which of the following leak detection methods should NOT be used to locate an HC refrigerant leak?


Soapy water solution
Electronic leak detector for flammable refrigerants
Leak detection foam
Electronic HFC leak detector

63

Ťažká

What is the most important difference between a flammable refrigerant recovery unit and a standard one?


A different colour for the station
Different low-pressure switch setting
A flammable refrigerant recovery unit has no ignition sources
Different connection sizes

64

Ťažká

Which of the following is a source of ignition?


A sealed NTC temperature sensor
An Ex-certified fan motor
An 'n'-type (non-sparking) thermostat
A contactor (sparking contacts)

65

Ťažká

What particularly hazardous substance is formed when R32 burns?


Sulphur dioxide (SO₂)
Phosgene
Hydrogen chloride (HCl)
Hydrogen fluoride (HF)

66

Ťažká

What type of refrigerant is R1234ze(E)?


HFO (hydrofluoroolefin)
CFC (chlorofluorocarbon)
HC (hydrocarbon)
HCFC (hydrochlorofluorocarbon)

67

Ťažká

What hazards does a safety group A3 refrigerant pose?


Lower toxicity, higher flammability
Higher toxicity, moderate flammability
Lower toxicity, moderate flammability
Higher toxicity, higher flammability

68

Ťažká

According to EN 378, what is the maximum R290 charge in a cold room measuring 5 m × 3 m × 2.5 m (LFL of R290 = 0.038 kg/m³, access category a, location class I, no additional measures))?


1.5 kg
0.285 kg
4.93 kg
1.0 kg

69

Ľahká

What does the GWP indicator mean?


The ability of a substance to restore the ozone layer
The annual rise in mean air temperature caused by the emission of 1 kg of the gas
Ozone depletion potential
Global Warming Potential: the climate warming impact of 1 kg of a gas compared with 1 kg of CO₂ (GWP = 1) over a defined time horizon, usually 100 years

70

Ťažká

What is the approximate ratio of the volumetric cooling capacity of R32 to that of R410A (same compressor and conditions)?


approx. 0.75
approx. 1.05–1.1
approx. 1.3
approx. 0.6

71

Ťažká

Why are Ex-certified evaporator fan motors used in some systems with flammable refrigerants?


Because they are more energy-efficient
Because they are more reliable
Because they must be kept running continuously to disperse the leaking refrigerant
To avoid a source of ignition in the event of a flammable refrigerant leak

72

Ťažká

Why is the density difference between HC and HFC refrigerants important?


Because it determines the system's energy efficiency
An HC charge in kg is roughly half that of an HFC
Because HCs operate at much higher pressures
Because HCs must be charged much more slowly than HFCs

73

Ťažká

What is the GWP of R290 according to Annex VI to Regulation (EU) 2024/573?


0.02
7
150
675

74

Ťažká

Which of the following is NOT a source of ignition?


A light switch
An Ex-certified fan motor
An unsealed mechanical pressure switch
An electrical switch

75

Ťažká

What is R290?


Propene (Propylene)
Isobutane
Propane
Butane

76

Ťažká

What is the maximum A2L charge for a hermetic display cabinet with integral condenser in the ground-floor sales area of a supermarket?


1.5 kg
1.2 kg
2.5 kg
150 g

77

Ťažká

Why can’t a standard relay be fitted when retrofitting a compressor’s electrical system for flammable refrigerants?


Current consumption differs for compressors using flammable refrigerants compared to those using HFCs
A relay is never required for compressors using flammable refrigerants
It could be a source of ignition
The method of starting the compressor motor differs from that used with HFCs

78

Ťažká

What is the minimum (recommended) distance from a work area with HC refrigerants within which there must be no ignition sources?


3 m
1 m
5 m
10 m

79

Ťažká

A recovery cylinder holds 10 kg of R404A (filling ratio 0.82 kg/l). What is the maximum R290 charge for this cylinder (propane filling ratio 0.43 kg/l per ADR P200)?


20 kg
approx. 8 kg
approx. 17 kg
approx. 5.2 kg

80

Stredne ťažká

How do refrigeration systems contribute to the greenhouse effect?


Only through the heat rejected by the condenser
Only through CO₂ given off by the compressor motor
Indirectly (through energy consumption) and directly (through emissions of refrigerant into the atmosphere)
Through oil emitted into the atmosphere from the condenser and filter

81

Ťažká

How can a vacuum pump be used safely to evacuate a system containing R290?


Position the pump at least 3 m above floor level
R290 systems need not be evacuated before charging
Ignition-source-free pump, good ventilation, exhaust to a safe place
Place the pump directly on the floor, as low as possible

82

Ťažká

Under ADR, what equipment must you carry in your vehicle when transporting flammable refrigerant cylinders (under the 1.1.3.6 exemption)?


A fire extinguisher (at least 2 kg dry powder)
Thick gloves
Tinted safety goggles
A fire blanket

83

Ťažká

How do you make sure it is safe to light the torch for desoldering joints in a system from which a flammable refrigerant has been removed?


Working outdoors is sufficient
Ensure good ventilation and check the work area with a flammable gas detector
Such joints must never be desoldered; they must be cut with a pipe cutter
Purge the system with compressed air

84

Ťažká

How would you prepare a system containing 100 g of R1270 for debrazing, if local regulations allow controlled venting of small HC quantities?


Vent the R1270 outdoors and start brazing immediately
Vent the R1270 to a safe outdoor location, then purge with OFN three times (pressurise and vent), and braze with OFN flowing
Recover the R1270 to a vacuum and start brazing immediately without a nitrogen purge
Vent the R1270 into the room and open a window

85

Ťažká

Which method should NOT be used to locate an R290 leak?


Leak detection foam
An electronic detector for flammable refrigerants
An electronic leak detector designed for HFCs
Fluorescent dye and UV lamp (if approved by the manufacturer)

86

Ťažká

Why can’t recovery stations designed for HFCs be used with R600a?


They contain ignition sources
The recovery unit cannot withstand the working pressure of R600a
The low-pressure switch setting will not be suitable for R600a due to its lower operating pressure
The oil in the recovery unit is not soluble in R600a

87

Ťažká

According to EN 378, what is the maximum R1234ze(E) charge in a cold room measuring 5 m × 3 m × 2.5 m (LFL = 0.303 kg/m³, access category a, location class I, no additional measures)?


618 kg
227 kg
6.18 kg
2.27 kg

88

Ťažká

What type of refrigerant is R32?


Hydrocarbon
Hydrofluorocarbon
Hydrofluoroolefin
Carbon dioxide

89

Ťažká

What hazards do A2L refrigerants pose?


Lower toxicity, lower flammability (burning velocity ≤ 10 cm/s)
Lower toxicity, higher flammability
Higher toxicity, lower flammability
Higher toxicity, higher flammability

90

Ťažká

What hazard is associated with the combustion of HFO or HFC refrigerants?


Hydrogen fluoride (HF) is formed
Nitrous oxide is formed
Ozone is formed
Phosgene is formed

91

Stredne ťažká

What is the greenhouse effect?


The trapping of heat in the Earth's atmosphere, which hinders the radiation of heat into space
The filtering of solar radiation by the atmosphere
The formation of a layer that traps only heat from fuel combustion in aircraft
The absorption of solar radiation by the Earth's surface

92

Ťažká

Approximately what compressor displacement is required for R600a compared with R134a for the same cooling capacity?


About half
About seven times as large
The same
About twice as large

93

Ťažká

What is the GWP value for R32 according to Regulation (EU) 2024/573?


3
0
675
7

94

Ťažká

Why is charge accuracy more important in critically charged R290 systems than in HFC systems?


Because of lower operating pressures
Because such systems never have liquid receivers
Because R290 is only used in systems below 150 g
The charge mass is much smaller than in an HFC system, because the liquid density of R290 is much lower

95

Ťažká

Why does the condenser fan run continuously in some systems using R1270?


To reduce energy consumption
To prevent the build-up of contaminants in the condenser
To ensure that the discharge pressure never becomes excessive
To dilute the refrigerant in the event of a leak

96

Stredne ťažká

Which EU regulation is currently the primary piece of legislation governing the use of fluorinated greenhouse gases (F-gases) in the European Union?


Regulation (EU) No 517/2014
Regulation (EU) 2015/1188
Regulation (EU) 2024/573
Directive 2009/125/EC

97

Stredne ťažká

What is the main objective of Regulation (EU) 2024/573?


Standardising metal recycling standards
To facilitate the import of electrical appliances
To reduce taxes on refrigeration equipment
Prevention of F-gas emissions and the achievement of the EU’s climate targets

98

Stredne ťažká

What are the ecodesign obligations of manufacturers of refrigerating appliances?


Only using energy labels under Regulation (EU) 2024/573
Only implementing an ISO 9001 quality management system
Only declaring F-gas quantities under Regulation (EU) No 517/2014
Meeting implementing regulations (e.g. 2019/2019, 2015/1095): efficiency, spare parts, reparability

99

Stredne ťažká

What is the main objective of EU ecodesign legislation (Directive 2009/125/EC, now Regulation (EU) 2024/1781 – ESPR)?


To reduce the negative environmental impact of products by improving energy efficiency, durability and recyclability
To standardise the appearance of products in the EU
To increase sales of electrical appliances in the EU
To facilitate imports from outside the EU

100

Stredne ťažká

What is the function of a ball valve in a refrigeration system?


It regulates the temperature of the refrigerant
It prevents excessive pressure build-up in the system
It measures the moisture content of the refrigerant
Enables the refrigerant flow to be completely shut off

101

Ľahká

What is the main function of a safety valve?


It controls the oil level in the compressor
Discharges refrigerant when the set pressure is exceeded
Prevents the evaporator from freezing
It monitors the moisture content of the refrigerant

102

Stredne ťažká

How do certain gases contribute to the greenhouse effect?


They heat the air through chemical reactions with atmospheric oxygen and nitrogen
They deplete the ozone layer, so more solar radiation reaches the surface
They trap thermal radiation that the Earth would otherwise emit into space
They limit UV radiation reaching the Earth's surface, changing the heat balance

103

Stredne ťažká

What is the purpose of a sight glass (with moisture indicator)?


Measuring condenser temperature
Regulating compressor pressure
Emergency shut-off of flow
Visual assessment of the refrigerant condition in the liquid line (bubbles) and of system moisture

104

Stredne ťažká

What is the function of the temperature regulator in a refrigeration system?


Controls the operation of the compressor and valves to maintain the set temperature
It drains excess refrigerant into the receiver
It restricts oil flow
To maintain a constant pressure in the compressor

105

Ťažká

What is the role of a suction liquid separator (also in systems with flammable or toxic refrigerants)?


It separates liquid from oil
It is used only to measure moisture
It prevents liquid refrigerant from entering the compressor
It heats the refrigerant before the evaporator

106

Ťažká

What is the function of an oil separator in systems using flammable or toxic refrigerants?


Separates oil from the refrigerant and facilitates the return of oil to the compressor
They are used solely to measure the moisture content of the refrigerant
It prevents liquid from entering the compressor
Heats the refrigerant before it enters the evaporator

107

Stredne ťažká

What is the purpose of oil level regulators in a refrigeration system?


They control the pressure in the condenser
Maintains the correct oil level in the compressor
They control the evaporator temperature
They drain off excess refrigerant

108

Stredne ťažká

What is the function of the liquid receiver in relation to system tightness?


It keeps the whole system at constant pressure regardless of load
It regulates the oil returning to the compressor
It controls the evaporating temperature by varying the circulating charge
It stores refrigerant; checking its liquid level helps detect charge loss

109

Stredne ťažká

What is the role of a gauge manifold with thermometers (temperature probes)?


It monitors refrigerant moisture content
It measures pressures and temperatures to determine superheat and subcooling and thus assess the system charge (indirect leak check)
It controls oil level
It relieves pressure if it is exceeded

110

Stredne ťažká

What is the role of defrost controls?


They protect the evaporator from icing and damage that could lead to leaks
They monitor the moisture content of the refrigerant
They control compressor discharge pressure during defrost
They drain excess oil from the evaporator to the receiver

111

Ťažká

Why do liquid and oil separators in CO₂ systems require particular attention?


Because sight glasses and level indicators must not be used in CO₂ systems
Because CO₂ needs no lubrication, so oil separators are unnecessary
Because CO₂ is flammable and separators must not be used
Because of very high pressures – adequate PS and protection devices are required

112

Ťažká

What is the critical pressure of CO₂ (R744)?


Approx. 74 bar (abs)
Approx. 120 bar
Approx. 31 bar
Approx. 10 bar

113

Ľahká

What is the unit of pressure in the International System of Units (SI)?


atm (standard atmosphere)
psi (pound per square inch)
Pa (pascal)
bar (gauge)

114

Stredne ťažká

Where can the lists of fluorinated greenhouse gases be found?


In the national Act on ozone-depleting substances and certain fluorinated greenhouse gases
In a regulation of the Minister of Economy on the list of fluorinated greenhouse gases
In the Vienna Convention for the Protection of the Ozone Layer
In Annexes I–III to Regulation (EU) 2024/573 of the European Parliament and of the Council

115

Ťažká

What characterises the transcritical process in CO₂ systems?


It occurs only at low temperatures
Heat rejection takes place above the critical point – the refrigerant does not condense in the conventional way (gas cooler instead of condenser)
It is irrelevant to system operation
Conventional condensation occurs

116

Ťažká

What characterises the subcritical CO₂ process?


Operation above the critical point
The absence of condensation
The absence of evaporation
The conventional condensation process below the critical point

117

Ľahká

What is the log(p)-h diagram for CO₂ used for?


To measure temperature
To regulate pressure
For analysing thermodynamic processes in a refrigeration system
To detect leaks

118

Ľahká

What can be read from the log(p)-h graph?


Only the amount of refrigerant
Only the humidity
Pressure, enthalpy, temperature and state of the refrigerant
Only the temperature

119

Ľahká

What are CO₂ saturation tables used for?


To regulate the compressor
To determine the oil quantity
To measure humidity
To determine the relationship between temperature and pressure at saturation

120

Ľahká

What does the CO₂ saturation state mean?


Equilibrium between the liquid and vapour phases
A state of high pressure
Dry ice state
A state in which the refrigerant is only a gas

121

Ťažká

When can dry ice (solid CO₂) form?


At high temperature
At high pressure
When the pressure drops suddenly below the triple point (approx. 5.2 bar abs, −56.6 °C), e.g. when venting liquid CO₂ or charging liquid into an evacuated system
During normal operation of the system

122

Ťažká

What risks are associated with dry ice forming in a CO₂ system?


Pressure reduction
Blocked pipes and valves and system damage (and a sharp pressure rise when it thaws)
Improved efficiency
No risk

123

Ťažká

How does CO₂ saturation pressure change as temperature increases?


It increases rapidly
It first decreases, then increases
It decreases
It remains the same

124

Ľahká

Why is understanding the log(p)-h graph particularly important for CO₂?


It is only used for design purposes
As CO₂ systems operate in different modes (sub- and transcritical) and require detailed analysis
It only applies to NH₃
It doesn’t matter

125

Stredne ťažká

Where can the lists of ozone-depleting substances be found?


In Annexes I and II to Regulation (EU) 2024/590 of the European Parliament and of the Council
In a regulation of the Minister of the Environment on the list of controlled substances
In the Vienna Convention for the Protection of the Ozone Layer
In the national Act on ozone-depleting substances and certain fluorinated greenhouse gases

126

Ťažká

What happens to CO₂ above the critical point?


It ceases to conduct heat
It turns into a solid
It turns into a liquid
It transitions to a supercritical state (no distinction between liquid and gas)

127

Ľahká

Why do CO₂ systems require precise pressure control?


Due to low pressures
Because there are no valves
Due to significant pressure changes with temperature fluctuations
They do not require control

128

Stredne ťažká

Why is ammonia (R717) classed as a toxic refrigerant?


Because it is colourless and odourless and therefore hard to detect
Because it does not react with water, making neutralisation difficult
It severely irritates the respiratory tract, eyes and skin, and is poisonous when inhaled at higher concentrations
Because it is heavier than air and displaces oxygen

129

Ťažká

What is the main difference between a dry-expansion and a flooded evaporator?


A dry-expansion evaporator needs no expansion valve, a flooded one does
A dry-expansion evaporator always has a lower pressure than a flooded one
In a dry-expansion evaporator the refrigerant completely evaporates and is superheated in the evaporator; in a flooded one part of the refrigerant remains liquid (incomplete evaporation, no superheat)
A dry-expansion evaporator is filled with liquid, a flooded one with vapour

130

Ťažká

What is the typical pressure in the evaporator of an R717 deep-freeze system (below −40 °C)?


Positive pressure of 10–20 bar
Atmospheric pressure, approx. 1 bar abs
Below atmospheric (approx. 0.7 bar abs at −40 °C)
Positive pressure of 5–10 bar

131

Ťažká

Why are PFAS formed by the decomposition of certain F-gases (e.g. TFA from HFOs) problematic?


They cause rapid cooling of the atmosphere
They are very persistent, accumulate in the environment (e.g. water) and may be toxic
They are readily biodegradable
They are climate- and environment-neutral

132

Ľahká

What is the basic requirement when charging a system with R717 (NH₃)?


Charging should take place in a well-ventilated area using appropriate personal protective equipment
NH₃ can be charged together with air
Charging must only take place at temperatures below 0°C
Charging can be carried out without personal protective equipment

133

Ťažká

How is oil managed in R717 systems?


Oil has no effect on system operation
Oil can be mixed with any refrigerant
Oil collecting at the lowest points of vessels is regularly checked and drained, because it impairs heat transfer
Oil requires no monitoring

134

Ľahká

What is the correct procedure for recovering R717 from a system?


The refrigerant can be drained into the sewer system
The gas can be released into the atmosphere
Recovery is not required
The refrigerant must be recovered into suitable, leak-proof tanks designed for NH₃

135

Ľahká

How should R717 (NH₃) be stored?


In unmarked plastic containers
In any open containers
Near heat sources
In sealed, labelled containers, in a cool and well-ventilated place

136

Stredne ťažká

Where and by when must entities obliged under the Polish Act of 15 May 2015 submit annual reports on ODS and F-gases?


By 31 March, electronically to the Ministry of Climate and Environment
By 28 February of the following year, electronically via the Reports Database (BDS) run at the Institute of Industrial Chemistry (ICHP)
By the end of the calendar year, on a form at a regional office of the Office of Technical Inspection (UDT)
By 31 January, in the Central Register of Operators (CRO)

137

Ťažká

What should be done with contaminated R717?


Purify it or send it for disposal in accordance with regulations
Dilute it with water and reuse it
Release it into the atmosphere
Continue to use it without restriction

138

Ľahká

What is the main hazard associated with an R717 leak during maintenance work?


Increased cooling efficiency
Damage to electrical equipment only
Toxic to humans and may cause chemical burns
No risk whatsoever

139

Ťažká

What should be done if an NH₃ leak is detected?


Evacuate people immediately and raise the alarm; stop the leak only if it is safe to do so and with suitable PPE (respiratory protection)
Increase the pressure in the system
Carry on working with the room door open
Carry on working wearing a dust mask

140

Ťažká

What role do scrubbers play in NH₃ systems?


They increase the pressure in the system
Neutralise ammonia through absorption in a liquid (e.g. water)
They are used to measure temperature
They store the refrigerant

141

Ťažká

How should the system be prepared before filling with R717?


Check for leaks, remove air and moisture, and create a vacuum
Simply start it up
There is no need to check it
The pressure must be increased above the standard level

142

Ťažká

What are the transport requirements for R717?


Transport is not regulated
It can be carried without labelling
It can be carried in open containers
It must be carried in suitable, labelled packagings in accordance with ADR (UN 1005, class 2, code 2TC)

143

Ľahká

What personal protective equipment is required when working with NH₃?


Workwear only
Only a safety helmet
No requirements
Safety goggles, gloves and respiratory protective equipment

144

Stredne ťažká

Which installation measure has a major impact on compressor energy efficiency?


Omitting the filter-drier to reduce flow resistance
Proper evacuation and dehydration of the system (removing air and moisture)
Installing a suction line smaller than recommended
Charging extra refrigerant 'as a reserve' above the nameplate value

145

Stredne ťažká

How does regular oil-level monitoring affect compressor operation?


It ensures proper lubrication and limits wear and energy losses
It increases cooling capacity above nominal
It allows any type of oil to be topped up
It allows the crankcase heater to be omitted

146

Ľahká

How do system leaks affect compressor energy efficiency?


Refrigerant loss reduces capacity and increases energy use (longer run times, higher superheat)
They improve efficiency because condensing pressure drops
They affect only safety, not energy use
No effect as long as the system still cools

147

Stredne ťažká

Regulation (EU) 2024/590 relates to:


Alternative refrigerants replacing fluorinated greenhouse gases
Conditions for F-gas certification of companies recovering and reclaiming refrigerants
Health and safety during refrigerant recovery
Ozone-depleting substances

148

Stredne ťažká

What is the significance of proper suction and discharge pressure control?


It keeps the compressor at optimal conditions (suction pressure as high and condensing pressure as low as permissible)
The highest possible condensing pressure is best
Pressures do not affect energy use
The lowest possible suction pressure is best

149

Stredne ťažká

Which maintenance measure reduces compressor energy consumption?


Permanently disabling the crankcase heater
Replacing the filter-drier when the pressure drop or moisture indicator shows it is necessary
Raising the high-pressure switch setting
Topping up refrigerant at every service visit

150

Stredne ťažká

How does air (non-condensable gas) in the system affect operation?


It raises the condensing pressure and reduces efficiency
It only affects the sight-glass indication
It improves condenser heat transfer
It lowers the condensing pressure

151

Stredne ťažká

What role do controls play in compressor efficiency?


They provide safety only, with no energy effect
They matter only in NH₃ systems
They enable optimised operation and lower energy use (e.g. floating head pressure, capacity matching)
They increase the circulating refrigerant charge

152

Stredne ťažká

How does suction superheat at the compressor affect efficiency?


The higher the superheat, the higher the efficiency
Excessive superheat reduces efficiency and raises the discharge temperature
Zero suction superheat is optimal
Superheat has no effect

153

Stredne ťažká

How does correct system layout affect efficiency?


Longer pipes improve subcooling and always increase efficiency
It affects only appearance
It shortens pipe runs and limits pressure drops and energy losses
It doesn't matter

154

Stredne ťažká

How important is suction pipe insulation?


It is needed only for appearance
It increases energy consumption
It has no effect
It limits heat gain and excessive superheat, improving efficiency

155

Stredne ťažká

Which measure most improves condenser energy efficiency?


Reducing fan speed to the minimum
Regular cleaning of heat-exchange surfaces
Raising the condensing pressure set point
Increasing the refrigerant charge

156

Ľahká

How does a dirty condenser affect the operation of the refrigeration system?


It lowers the condensing pressure
Causes an increase in pressure and energy consumption by the compressor
It improves efficiency
It has no effect

157

Ľahká

Why is adequate airflow through an air-cooled condenser important?


The lower the airflow, the lower the condensing pressure
It affects only noise
It doesn't matter
It ensures effective heat rejection and low condensing pressure

158

Stredne ťažká

Which refrigerants damage the ozone layer?


All natural refrigerants
All refrigerants containing fluorine and hydrogen in their molecules
All refrigerants containing carbon in their molecules
All refrigerants containing chlorine or bromine in their molecules

159

Ľahká

How does the presence of limescale in a water-cooled condenser affect performance?


It lowers the condensation temperature
It has no effect
Impairs heat exchange and increases energy consumption
It improves heat transfer

160

Stredne ťažká

How does correct condensing pressure control affect efficiency?


It has no effect
It always increases energy use
It keeps the lowest pressure that still ensures proper expansion-valve feed, reducing energy use
It is best to keep a constant high condensing pressure all year

161

Ľahká

How do condenser leaks affect energy efficiency?


They improve efficiency
Have no effect
They lower the temperature
Causes refrigerant loss and a drop in efficiency

162

Ľahká

How important is the correct positioning of an air-cooled condenser?


It should be close to heat sources
It should be installed in a well-ventilated area with unobstructed airflow
It should be housed in a small room
It doesn’t matter

163

Ľahká

How does hot air recirculation affect the condenser?


It has no effect
It improves efficiency
Impairs cooling and increases energy consumption
It reduces the pressure

164

Stredne ťažká

How does insulation of heating and DHW pipework affect the efficiency of a heat pump system?


It reduces energy losses and improves overall system efficiency
It impairs cooling
It doesn't matter
It increases pressure

165

Stredne ťažká

Which measure most improves the energy efficiency of an air-cooling evaporator?


Raising the condensing temperature by a few kelvin
Defrosting at the right time and keeping the fins clean
Restricting the airflow through the evaporator
Increasing the refrigerant charge above nominal

166

Ľahká

How does evaporator icing affect the system’s operation?


It improves cooling performance
It has no effect
Impairs heat exchange and increases energy consumption
It lowers the condensation temperature

167

Ľahká

How does dirt on the evaporator surface affect its performance?


It has no effect
It improves efficiency
It reduces the pressure
Impairs heat exchange and increases energy consumption

168

Ľahká

What maintenance task is crucial for the evaporator?


Regular cleaning and defrosting
Increasing the refrigerant charge
Reduced airflow
Lack of maintenance

169

Stredne ťažká

What does a Certificate A2 for natural persons (Implementing Regulation (EU) 2024/2215) authorise?


All activities (leak checks, installation, repair, maintenance, servicing, decommissioning, recovery) involving F-gases and hydrocarbons in equipment containing less than 3 kg, or less than 6 kg in labelled hermetically sealed systems
Only leak checks that do not entail breaking into the refrigerant circuit
Only recovery of F-gases from equipment containing less than 3 kg (or 6 kg in hermetically sealed systems)
All activities involving equipment using CO₂ (R744)

170

Ľahká

How does superheat at the evaporator outlet affect efficiency?


It only causes a temperature drop
It always improves performance
It has no effect
Excessive superheat reduces energy efficiency

171

Ľahká

How do leaks in the evaporator affect efficiency?


These cause refrigerant loss and a drop in efficiency
Have no effect
Improves performance
Increase capacity

172

Ľahká

How important is correct expansion valve adjustment?


Causes leaks
It increases energy consumption
Ensures optimal evaporator charge and improves efficiency
It doesn’t matter

173

Ľahká

How does inadequate insulation of suction (or secondary-coolant) pipes affect evaporator performance?


It has no effect
It improves efficiency
It lowers the condensing temperature
It causes cooling losses and increased energy use

174

Ľahká

How does correct TEV adjustment affect system energy efficiency?


It causes leaks
It has no effect
It ensures optimal superheat and improves efficiency
It increases energy use

175

Ľahká

What happens if the superheat set by the TEV is too high?


It has no effect
Efficiency will drop because the evaporator is not being fully utilised
The refrigerant charge will increase
Cooling efficiency will improve

176

Stredne ťažká

How does too low superheat setting on the TEV affect performance?


It has no effect
It increases operational safety
It reduces refrigerant flow
It may lead to improved efficiency, but it increases the risk of the compressor becoming flooded with liquid

177

Ľahká

How do contaminants in the system affect the operation of the TEV?


They can cause it to become blocked and reduce efficiency
They lower the temperature
They improve its performance
Have no effect

178

Ľahká

What role does the filter-drier play in terms of system efficiency?


It lowers the temperature
It increases the amount of refrigerant
It doesn’t matter
Removes moisture and contaminants, improving the system’s efficiency

179

Ľahká

How does proper insulation of components (e.g. pipes near the TEV) affect the system?


Prevents unwanted heat gains and improves efficiency
It increases energy consumption
It causes leaks
It doesn’t matter

180

Stredne ťažká

What is the scope of Regulation (EU) 2024/573?


Design requirements and conformity assessment for pressure equipment
Health and safety requirements for brazing and welding on refrigeration installations
Only requirements for periodic leak checks of refrigeration equipment
Limiting emissions, use and marketing of F-gases, HFC phase-down, certification and reporting

181

Ľahká

How important is it to check the operation of the condensing pressure control valve in the system?


It increases energy consumption
It causes a significant rise in temperature
Ensures operation within the optimum pressure range and reduces energy losses
It has no effect

182

Ľahká

How does the correct selection of a TEV affect energy efficiency?


It lowers the temperature
It increases the amount of refrigerant
It doesn’t matter
Ensures the system is matched to its capacity and operates optimally

183

Stredne ťažká

What is the main design difference in hydrocarbon refrigeration systems?


Higher operating pressures
Lower energy efficiency
The need to eliminate ignition sources and limit the charge because of the refrigerant's flammability
No need for safety measures

184

Stredne ťažká

How do compressors used in hydrocarbon systems differ?


They must operate at higher pressures than HFC compressors
There is no difference
They must be approved by the manufacturer for the specific flammable refrigerant (e.g. electrical components that are not ignition sources, suitable oil)
They need no lubrication

185

Ťažká

What is the main characteristic of R744 (CO₂) refrigeration systems?


Low energy efficiency under all conditions
Low operating pressures
Very high operating pressures
No need for control

186

Ťažká

What are the requirements for piping materials in CO₂ systems?


Any material may be used
They must withstand high pressures (e.g. stainless steel, high-strength copper-alloy tubes such as K65)
It doesn't matter
Only plastics

187

Ťažká

How does a booster system work in CO₂ installations?


It is used to store refrigerant
Low-temperature (LT) compressors discharge into the suction of medium-temperature (MT) compressors – two-stage compression in a single circuit
It reduces evaporator pressure
It reduces the refrigerant quantity

188

Ľahká

What is the function of high-pressure control valves in CO₂ systems?


They lower the evaporator temperature
They regulate oil flow
They control the pressure on the high-pressure side and optimise system operation
They are used to store the refrigerant

189

Ťažká

Why is pressure optimisation in CO₂ systems crucial?


It reduces the ambient temperature
It reduces the amount of refrigerant
It doesn’t matter
It enables the system to achieve maximum energy efficiency in transcritical mode

190

Ťažká

What role does parallel compression play in CO₂ systems?


It lowers the ambient temperature
It has no significance
It compresses flash gas from the intermediate receiver directly to high pressure, improving efficiency
It increases energy consumption

191

Stredne ťažká

How can you tell that the system has been overcharged with refrigerant?


Even under a very small heat load, frost forms on the suction line
Under normal operating conditions the condensing pressure and subcooling rise markedly because excess liquid floods the condenser and reduces its active surface
The compressor runs at a lower load and the suction pressure drops
It cannot be checked, because the sight glass is not intended for this

192

Ťažká

How does an ejector work in a CO₂ system?


It uses the energy of the higher-pressure refrigerant to raise the pressure of the refrigerant from the lower stage, which improves efficiency
It increases the amount of refrigerant
Stores the refrigerant
It lowers the evaporator temperature

193

Ťažká

What is the function of liquid ejectors in CO₂ systems?


They increase the amount of oil
They raise the refrigerant temperature
They reduce atmospheric pressure
They return liquid from the separator and allow partially flooded evaporator operation (better evaporator feed)

194

Ťažká

What are the characteristics of partially flooded systems in CO₂ systems?


The absence of liquid in the evaporator
Low operating pressure
The presence of liquid in the evaporator, which improves heat transfer and efficiency
Lack of regulation

195

Ťažká

What is the main risk associated with standstill pressure in CO₂ systems?


A pressure rise as the refrigerant warms up during standstill (possibly exceeding PS and lifting the relief valves)
A drop in temperature
Increased efficiency
A decrease in refrigerant quantity

196

Ťažká

How is standstill pressure limited in CO₂ systems?


By using an auxiliary standstill (stagnation) cooling unit, e.g. cooling the receiver, with back-up power, and by selecting an adequate PS and relief valves
By increasing the refrigerant charge
By completely shutting down the system and power supply
By raising the plant-room temperature

197

Ťažká

What does standstill (stagnation) of a CO₂ system mean, and why is it important?


Normal system operation
A state with no compressor operation or refrigerant flow – pressure rises with ambient temperature and may exceed PS
Improved efficiency
A drop in system temperature

198

Ľahká

Why do CO₂ systems require more advanced automation than traditional systems?


Due to the need for precise control of pressure and temperature
Because there are no valves
They do not require automation
Due to low pressures

199

Ťažká

What must the label of a flammable refrigerant cylinder include?


The refrigerant name, the UN number, the hazard label (e.g. 2.1 – flammable gas) and basic safety information
Only the refrigerant name
Information about the cylinder owner
Only the net weight

200

Ťažká

Why is the absence of a 'flammable refrigerant' label on equipment a serious hazard?


It may lead to the wrong oil being selected
It reduces system efficiency
It may lead to the use of tools that are ignition sources
It has no significant effect on safety

201

Ťažká

Which set of information on the label of a flammable refrigerant cylinder is crucial from a safety perspective?


Manufacturer’s name and country of origin
Name of the substance, hazard label (ADR) / GHS pictogram (CLP), UN number
Cylinder colour and date of manufacture
Gross weight and batch number

202

Stredne ťažká

Before charging the unit with refrigerant, it is essential to…


…fill in the unit's data sheet
…carry out a trial start-up
…carry out a tightness test (and evacuate the system)
…check the compressor suction and discharge connections

203

Ľahká

What is the requirement regarding the labelling of an installation containing a flammable substance?


Labelling is required only in technical rooms
The labelling must indicate the type of substance and the flammability hazard
Colour-coding of pipes is sufficient
Labelling is not required for hermetically sealed systems

204

Ľahká

What are the potential consequences of using unsuitable connections in a system containing a flammable substance?


No impact on safety
Risk of leakage and the formation of an explosive mixture
Merely installation difficulties
Merely a reduction in efficiency

205

Ťažká

What is the purpose of gas detectors in a room with a refrigeration system?


Measuring refrigerant temperature
Controlling compressor capacity
Early leak detection and triggering of measures preventing health risks and explosive atmospheres (alarm, ventilation, shut-off)
Monitoring pipe pressure

206

Ťažká

How often should gas detection sensors in a machinery room be checked?


According to the manufacturer's instructions and regulations – at least every 12 months
Once every 5 years
Only after a leak has occurred
Before every start-up of the unit

207

Ťažká

Where should a gas detector be located according to EN 378?


Where the refrigerant would accumulate: low (near the floor) for refrigerants heavier than air, high (near the ceiling) for lighter ones such as NH₃
Only at the room entrance
Near the control panel
Anywhere in the room

208

Ľahká

How should an employee respond when a gas alarm is triggered?


Carry on working until they see a leak
Reduce the pressure in the system
Leave the room immediately and notify their supervisor
Switch off the system and wait for the alarm to stop

209

Ťažká

What safety checks should be carried out when installing a new refrigeration system with a flammable refrigerant?


Only that the air filter is new
The presence of health and safety signage, adequate ventilation and gas detectors
Only the compressor power
The colour of pipes and hoses

210

Ľahká

Gas detectors should be installed in rooms where:


The room is less than 5 m²
The amount of refrigerant exceeds a specified permissible threshold
Ventilation is natural
Any refrigerant is present, regardless of the quantity

211

Ťažká

What are the requirements for emergency exits from a refrigeration machinery room?


Outward-opening doors and signed escape routes (number of exits per the standard)
At least two exits are required and signage is optional
In small machinery rooms emergency exits need not be signed
One exit with a sign stating the refrigerant type is sufficient

212

Ťažká

Which installation measure for a flammable-refrigerant system improves its energy efficiency?


Omitting the filter-drier
A thorough tightness test and evacuation (dehydration) of the system
Charging above the nameplate quantity
Restricting room ventilation

213

Stredne ťažká

What information must appear on the label of equipment containing F-gases?


That it contains an F-gas, its designation, quantity in kg and t CO₂ eq, and GWP
The manufacturer's logo, the unit weight and year of manufacture from the rating plate
The weight and capacity of the pipework and the colour code of the casing paint
Only the trade name of the refrigerant and the unit's serial number

214

Ľahká

How do leaks affect systems using flammable refrigerants?


They lower the temperature
Have no effect
They improve efficiency
They cause refrigerant loss, reduced efficiency and a fire hazard

215

Ťažká

Why is it important to limit the refrigerant charge in HC systems?


It limits the possibility of reaching a flammable concentration (≥ LFL) in a leak, increasing safety
It doesn't matter
It lowers the temperature
It increases capacity

216

Ľahká

Why is the cleanliness of heat exchangers in HC systems important?


It improves heat transfer and reduces energy consumption
It increases the pressure
It doesn’t matter
Causes leaks

217

Ľahká

What maintenance measures improve the efficiency of a system using a flammable refrigerant?


Disabling safety devices
Regular checks for leaks and operating parameters
Increasing the refrigerant charge
Lack of servicing

218

Ľahká

How does the correct selection of components affect a system using a flammable refrigerant?


It ensures safe and optimal operation and minimises energy losses
It lowers the temperature
It doesn’t matter
It increases the amount of refrigerant

219

Ľahká

Why is it important to use the correct service tools in HC systems?


It ensures operational safety and reduces refrigerant losses
Causes leaks
It doesn’t matter
It increases energy consumption

220

Ľahká

How does pipe insulation affect the efficiency of systems containing HC?


It doesn’t matter
Causes leaks
It increases the pressure
It reduces energy losses and improves efficiency

221

Ťažká

Which safety class applies to R744?


A3
A2.
A1
B2L

222

Ťažká

In a simple single-stage R744 system without an intermediate receiver (refrigerant flows from the gas cooler directly to the expansion valve), operating transcritically at 90 bar with a gas-cooler outlet temperature of 35 °C, the refrigerant upstream of the expansion valve is…


…saturated vapour at intermediate pressure
…a subcooled liquid
…a two-phase mixture at intermediate pressure
…a supercritical fluid

223

Ťažká

In R744 transcritical systems, the gas cooler outlet valve controls:


The gas cooler fans
The inlet temperature to the gas cooler
The pressure in the gas cooler
The outlet temperature of the gas cooler

224

Ľahká

What is the base unit of temperature according to the International System of Units (Système International d’Unités)?


°C
K
°F
°R

225

Stredne ťažká

Which set of information best reflects the content of the equipment records required by Regulation (EU) 2024/573?


The make and model of the unit
Only the date of installation and the installer's name
Operator details, equipment details, type and quantity of refrigerant, and information on servicing and repairs
The owner, installer and service technician of the unit

226

Ťažká

Which statement best describes the behaviour of R717 and mineral compressor oil?


R717 does not mix with the oil; the oil collects on the high-pressure side above the R717
R717 mixes very well with the oil, which easily returns to the compressor
R717 does not mix with the oil; the oil, being heavier than liquid NH₃, collects beneath it at the lowest points (mainly on the low-pressure side)
An oil return line cannot be used in R717 systems because the oil is too hot

227

Ťažká

What is the main reason for using K65 copper tubing in some R744 systems?


They come in a wider range of diameters
They can withstand higher pressures
They bend easily
They have good low-temperature performance

228

Ťažká

Which statement about installing Schrader valves is correct?


When brazing the valve body, the core must be removed, then refitted and tightened to the correct torque
Hydrocarbons leak through Schrader valves
Schrader valves must not be used in R744 systems
All Schrader cores are suitable for all refrigerants

229

Ťažká

Which refrigerant can be detected with phenolphthalein paper?


R717
R1270
R1234ze(E)
R744

230

Ťažká

How does an undercharge affect the high-pressure side (without discharge pressure control)?


Discharge pressure higher, subcooling higher
Discharge pressure higher, subcooling lower
Discharge pressure lower, subcooling higher
Discharge (condensing) pressure and subcooling will both be lower

231

Ťažká

What is the benefit of adding helium as a tracer gas to nitrogen in a pressure test?


Its small atoms pass easily through leaks and are detected
It has a distinctive odour that helps locate the leak
It has a higher pressure than pure nitrogen in the same cylinder
It reacts with refrigerant residues, producing a visible colour change

232

Ťažká

Why should an evacuated R744 system initially be charged with refrigerant in the vapour phase?


To avoid damaging the compressor with liquid CO₂
To prevent dry ice forming (until approx. 5.2 bar abs is exceeded)
To prevent the drain valve on the receiver from opening
To charge R744 more slowly and measure it more accurately

233

Ťažká

If moisture remains in an R744 system because it was not properly evacuated (dehydrated), what is the likely consequence?


Reduced cooling capacity
Formation of hydrogen fluoride and hydrofluoric acid
Excessive discharge pressure
Formation of carbonic acid, which damages the system

234

Ťažká

Which system may require manual oil recovery?


An R717 system
Supercritical ‘booster’ system using R744
R744 cascade system
Secondary system using R744

235

Ťažká

The pressure of R744 at a saturation temperature of 20 °C is approx.


90 bar g
14 bar g
56 bar g
25 bar g

236

Stredne ťažká

Who is responsible for keeping the equipment records?


The person responsible for risk assessment.
The equipment maintenance technician.
The operator of the unit or system.
There is no such obligation.

237

Ťažká

Which refrigerant is lighter than air?


R744
R1270
R1234ze(E)
R717

238

Ťažká

What hazards are associated with a safety group A3 refrigerant?


Lower flammability, lower toxicity
Lower toxicity, no flame propagation
Higher toxicity, no flame propagation
Higher flammability, lower toxicity

239

Ťažká

What is the GWP of R32 (per AR4, as used in Regulation (EU) 2024/573)?


3922
675
6
0

240

Ťažká

What factors are taken into account when determining the maximum charge for comfort air-conditioning/heating applications?


Practical limit, height of the indoor unit, floor area
Lower flammability limit, height of the indoor unit, floor area
Practical limit, room volume
Lower flammability limit, room volume

241

Ťažká

What compressor displacement is required for R1270 compared with an R404A compressor in the medium-temperature range (cold room)?


About 6 times larger
About 1.5 times larger
Similar
About half

242

Ťažká

At an ambient temperature of 25 °C, the standstill pressure in the low-pressure stage of an R744 cascade (without standstill cooling) will typically be…


…higher than the maximum allowable pressure (PS) of the low-pressure stage
…approx. 27.5 bar g
…the same as the high-pressure switch setting
…the same as the relief valve set pressure

243

Ťažká

What is the correct definition of critical temperature?


The temperature at which, for certain substances, electrical resistance is zero
The temperature at which the vapour pressure of a liquid is equal to the ambient pressure surrounding the liquid
The temperature at which a substance changes from a gaseous to a solid state
The temperature above which there are no distinct liquid and gaseous phases

244

Ťažká

In the gas cooler of a transcritical system, the supercritical working fluid…


…rejects heat during a phase change
…rejects heat as its temperature falls
…rejects heat as its pressure falls
…rejects heat at constant temperature and pressure

245

Ťažká

R717 is highly corrosive to:


aluminium
stainless steel
titanium
copper (and its alloys)

246

Ťažká

What can be the effect of a relief valve lifting repeatedly?


The valve no longer opens
The set pressure increases
The valve may not reseat tightly and its set (opening) pressure may decrease
The valve stays fully open permanently

247

Stredne ťažká

Where are oil traps installed on the suction line?


At the inlet to every component of the refrigeration system
Before the safety valve on the suction side
At the bottom of vertical suction risers with upward flow
Immediately before the compressor suction connection

248

Ťažká

What is the relationship between the pressure (p) and temperature (T) of nitrogen at the start (1) and end (2) of a tightness test (p absolute, T in kelvin)?


p₂ = T₂/(p₁ × T₁)
p₂ = (p₁ × T₁)/T₂
p₂ = T₁/(p₁ × T₂)
p₂ = (p₁ × T₂)/T₁

249

Ťažká

What is the recommended pre-alarm level for fixed leak detection systems for R717?


5,000 ppm
500,000 ppm
500 ppm
50,000 ppm

250

Ťažká

Why are compressors with a separate motor (open type) mostly used in R717 systems?


To increase the refrigerant charge
Because they are cheaper
To lower the condensing pressure
Because NH₃ attacks copper motor windings, so hermetic compressors with conventional windings are not used

251

Ťažká

Which type of compressor is most commonly used in large ammonia systems?


Diaphragm compressor
Rotary vane compressor
A reciprocating or screw compressor
Hermetic scroll

252

Ťažká

How is the capacity of a piston compressor regulated in NH₃ systems?


By unloading the cylinders or changing the rotational speed
Solely by adjusting the oil volume
By increasing the condensing pressure
By reducing the refrigerant charge

253

Ťažká

How is the capacity of a screw compressor most commonly controlled?


By changing the type of oil
By using a slide valve
By adjusting the oil level
By closing the suction valve

254

Ťažká

When is two-stage compression used in NH₃ systems?


At small temperature differences
At low evaporating temperatures (pressures) and high pressure ratios
Only in small systems
Only with water-cooled condensers

255

Ťažká

What is the advantage of two-stage compression over single-stage compression?


Higher energy consumption
No need for a separator
Higher efficiency and lower discharge temperature
Lower efficiency

256

Ťažká

How does an evaporative condenser used in NH₃ systems work?


It utilises the evaporation of water to increase cooling efficiency
It does not require a water supply
Operates without a fan
It transfers heat only to the air

257

Ťažká

What is the function of the liquid separator in an NH₃ system?


Regulates the condensing pressure
Increases the discharge temperature
It separates oil from the refrigerant
It prevents liquid from entering the compressor

258

Stredne ťažká

Which symptoms with the compressor running indicate a refrigerant leak (undercharge)?


Rising condensing and suction pressures with no superheat
Sight glass full of liquid and rising oil level in the crankcase
Low suction pressure, high superheat and negligible subcooling
Rising liquid level in the receiver and increasing subcooling

259

Ťažká

What is the purpose of monitoring the liquid level in the separator?


To increase the oil volume
To maintain the correct refrigerant level and prevent the compressor from flooding
To control the condenser fan
To reduce the condensing temperature

260

Ťažká

What is the role of the float switch in NH₃ systems?


It is used to detect leaks
It monitors the liquid level in the tank or separator
It regulates the condensation temperature
It controls the fan’s operation

261

Ťažká

What is a thermosyphon in NH₃ systems?


A type of safety valve
A defrosting device
A system with gravity-driven (natural) circulation of liquid refrigerant caused by density differences, used e.g. for screw compressor oil cooling
An oil circulation pump

262

Ťažká

Why are oils that are immiscible with the refrigerant used in NH₃ systems?


To reduce the pressure
To increase the amount of refrigerant
Because NH₃ does not mix with most compressor oils
Because the oil mixes only with water

263

Ťažká

What is the main function of an oil separator in NH₃ systems?


To separate the oil from the refrigerant and return the oil to the compressor
To increase fan efficiency
To lower the condensation temperature
Removing moisture from the system

264

Ťažká

In which NH₃ system does the refrigerant evaporate completely with superheat in the evaporator, fed by an expansion valve?


A glycol system
An indirect system
A direct-expansion (DX) system
A pumped liquid-recirculation system

265

Ťažká

What is the characteristic feature of a flooded evaporator system?


No separator is used
The evaporator is filled exclusively with vapour
No level control is required
The evaporator contains a large amount of liquid, which improves heat transfer

266

Ťažká

What is the main difference between a direct and an indirect system?


In an indirect system, no compressor is used
In a direct system, there is no evaporator
In an indirect system, NH₃ flows directly into the space being cooled
In an indirect system, NH₃ cools an intermediate medium (e.g. glycol), which in turn cools the load

267

Stredne ťažká

Which components of a refrigeration system are potential leak points subject to leak checks?


Hermetic compressors, liquid receivers and liquid separators
Only high-pressure-side components
Joints, valves (including stems), seals (including those on replaceable filters and driers), parts subject to vibration and connections to safety and measuring devices
Only suction-side components

268

Stredne ťažká

What pressure is used for the pressure tightness test of an installation?


Always 30 bar
The pressure specified in EN 378-2 or by the manufacturer, not exceeding the maximum allowable pressure of the system (PS)
A pressure equal to the maximum pressure measured during operation
A pressure chosen by the technician based on experience

269

Stredne ťažká

At which points of the unit must the leak check be carried out?


Only on compressor shut-off valves, solenoid valves and filters
At all points where there is a potential risk of refrigerant leakage
Only on discharge-side components
Only at connections of measuring instruments

270

Stredne ťažká

When can a unit be considered tight after a pressure test?


When the pressure remains constant during the test (allowing for temperature-related changes); any unexplained pressure drop requires the leak to be located
When it has been checked with a fixed electronic detector
When the pressure drop does not exceed 0.1 bar regardless of the test duration
When gas bubbles appear after immersion in water

271

Stredne ťažká

Which legal act currently sets out the obligation to check stationary refrigeration equipment containing F-gases for leaks, and how often this must be done?


Regulation (EU) 2024/573
Regulation (EU) No 517/2014
Implementing Regulation (EU) 2024/2215
Commission Regulation (EC) No 1516/2007

272

Ťažká

Which parts of a refrigeration system should be given particular attention during a leak check?


Only compressor connections, because they are the only parts subject to vibration
Joints, valves incl. stems, seals, parts subject to vibration, connections to safety devices
Compressor and receiver connections, because the pressure is highest there
Only condenser connections, because the refrigerant is liquid there

273

Ľahká

What is the superheat of refrigerant vapour?


The amount of heat required to evaporate a liquid
The difference between the actual vapour temperature and the saturation temperature corresponding to its pressure (expressed in K)
The difference between the condensing temperature and the ambient temperature
The difference between the saturation temperature and the actual liquid temperature in the liquid line

274

Ťažká

Leak checks can be carried out using various methods. Which pair is correct?


Methods with and without quality control of supplies
Material quality control methods and electronic methods
Direct and indirect methods
Physical and chemical methods

275

Ťažká

To whom can leak checks of stationary refrigeration equipment containing F-gases be entrusted?


Any leak-testing specialist
A natural person holding a certificate covering leak checks (A1, A2 within its charge limit, or E)
A person who has carried out such checks before
An employee appointed by the owner of the installation

276

Ťažká

What conditions must be met to use UV dye for leak checking?


A UDT authorisation for pressure testing is required
It is sufficient that introducing dye into the circuit is technically feasible
It is sufficient to have a UV lamp, dye and safety goggles
Manufacturer approval of the method and a certificate covering breaking into the circuit

277

Ťažká

Which leak-checking methods are considered direct methods?


Vacuum test and foam solution
Pressure-change measurement and immersion in water
Nitrogen with tracer gas and pressure measurement
1. gas detection devices (portable or fixed leak detection system), 2. UV detection fluid or dye, 3. bubble/foam solutions

278

Ťažká

What do indirect leak-checking methods involve?


Ultrasonic measurement
A visual and manual check and analysis of parameters: pressure, temperature, compressor current, liquid levels and recharge volume
Leak detection with UV dye
Leak detection with an electronic detector

279

Stredne ťažká

How should the pressure be increased during a pressure tightness test?


In one step, by fully opening the nitrogen cylinder valve
In any way
As quickly as possible
Gradually, in stages, checking for leaks at each level until the test pressure is reached

280

Stredne ťažká

What electronic equipment should be used for leak checking?


Only devices with an 'ion pump' sensor
Only hot-cathode devices
Only detectors with an infrared sensor
Detectors suited to the refrigerant in the system, with appropriate sensitivity, checked periodically

281

Stredne ťažká

What documentation should be checked before starting a leak check?


The operator's fixed-asset inventory ledger
Only the installation invoice and the first start-up report
The equipment records – especially recurring problems and previous leaks
Attendance sheets of the plant-room staff for the year

282

Stredne ťažká

What information must be recorded in the leak check report?


Date, number and location of leaks, how they were repaired, technician details and signature
The method used, the time spent on site and the cost of repair
The date, a general note about the leak and the operator's signature
Only the number of leaks found and the date of the check

283

Stredne ťažká

What pressure should be used for the pressure tightness test?


Always 2–3 bar
Always 10–12 bar
A pressure not exceeding the maximum allowable pressure of the system (PS)
Any pressure, at the technician's discretion

284

Stredne ťažká

What is the temperature glide of a refrigerant?


The temperature drop of the refrigerant across the expansion valve
A property of single-component refrigerants, for which one saturation temperature corresponds to a given pressure
In zeotropic mixtures, the difference between the temperatures at the start and end of a phase change (boiling or condensation) at constant pressure
The temperature rise of the vapour in the compressor

285

Ťažká

What does a vacuum (decay) test involve?


The pump runs continuously to hold the required vacuum for the test
The pump is restarted every time the system pressure rises
With the pump running, you watch the vacuum gauge reading
After isolating the pump, you check whether the system pressure rises

286

Ťažká

How often should leak tests be carried out on equipment containing 1.5 kg of R404A refrigerant (5.9 tonnes of CO₂ equivalent)?


At least once every 12 months.
Once every six months.
On initial commissioning.
Only when servicing the unit.

287

Ťažká

How often should leak tests be carried out on equipment containing 7 kg of R404A refrigerant (27.45 tonnes of CO₂ equivalent)?


At least once every 12 months.
On initial commissioning.
Only when servicing the unit.
Once every six months.

288

Stredne ťažká

In which equipment is a leakage detection system required?


Equipment with 5 t CO₂ eq or more of F-gases, regardless of equipment type
Equipment with 30 kg or more of F-gases, regardless of their GWP
Equipment with 50 t CO₂ eq or more of F-gases, regardless of equipment type
Equipment with ≥ 500 t CO₂ eq of Annex I F-gases (or ≥ 100 kg of Annex II Section 1 gases)

289

Ťažká

Under Regulation (EU) 2024/573, a leakage detection system is mandatory when:


the equipment operates in an enclosed space
the F-gas charge of the refrigeration equipment is 500 t CO₂ eq or more
the charge is 100 kg or more of ozone-depleting substances
the equipment contains a flammable refrigerant in any quantity

290

Ťažká

Which leak-checking method may NOT be used by a holder of a Category E certificate?


Checking with a foaming solution
Measurement with a handheld electronic detector
Leak checking with a fluorescent dye introduced into the circuit
Visual inspection

291

Stredne ťažká

What should you check before using a portable electronic leak detector?


That it has been zeroed close to the suspected leak point
That it holds a valid UDT inspection certificate
That it has an infrared sensor, as only this type is permitted
That it suits the refrigerant and has been checked as the manufacturer requires

292

Stredne ťažká

Which certificate types (A1, A2, B, C, D, E) authorise leak checks of equipment containing F-gases?


All except D
Only A1 and A2
A1, A2 and E
Only E

293

Ťažká

Within what timeframe must a leak test be carried out on a stationary refrigeration system after a leak has been repaired, in accordance with EU Regulation 2024/573 on F-gases?


At the next periodic inspection.
At any time.
Between 24 hours and 1 month after the repair.
Immediately after the repair.

294

Ťažká

How often must refrigeration equipment containing ≥500 t CO₂ eq of F-gases be checked if (contrary to Article 6) no leakage detection system is installed?


Every 3 months
Every 6 months
Every month
Every 12 months

295

Stredne ťažká

Why is it advisable to subcool the liquid refrigerant?


To allow a smaller expansion valve to be used
To ensure that liquid free of vapour bubbles enters the expansion valve
To allow a condenser with a smaller heat-exchange surface to be used
To lower the evaporating temperature in the evaporator

296

Stredne ťažká

What must be done after repairing a leak in the refrigeration unit of a refrigerated trailer?


Charge an alternative refrigerant, start up and measure the parameters
Visually inspect only the bolted and brazed joints near the repair
Update the equipment records and carry out a leak check (it may be done directly after repair)
Issue the invoice and leave the leak check to the next periodic service

297

Stredne ťažká

Recovery of fluorinated greenhouse gases means:


The final decommissioning and withdrawal from service or use of a product or piece of equipment containing fluorinated greenhouse gases.
The reprocessing of fluorinated greenhouse gases to achieve their specified standard properties.
The collection and storage of fluorinated greenhouse gases from containers, products and equipment during maintenance or servicing or prior to their disposal.
The reuse of fluorinated greenhouse gases following a basic purification process.

298

Stredne ťažká

Who is authorised to recover refrigerant from stationary refrigeration equipment containing F-gases?


The administrator of the operator's account in the register
A natural person holding a certificate of the relevant type (A1; A2. or D within their charge limit)
The operator
The owner of the installation

299

Stredne ťažká

How must recovered refrigerants be stored?


In any used refrigerant cylinder, provided it is leak-tight
In any pressure vessel that has some form of approval
In a labelled recovery cylinder with a dual valve and a valid inspection
In a disposable (non-refillable) cylinder that held the same refrigerant

300

Stredne ťažká

When should the recovery of fluorinated greenhouse gases be carried out:


Before the final disposal of equipment and, where applicable, during its servicing and maintenance.
Only prior to the final disposal of equipment.
Always during servicing and maintenance of equipment.
Before each leak test of the equipment.

301

Stredne ťažká

What should be done if recovered refrigerant is contaminated (e.g. with acid, air or moisture)?


Add a special contaminant neutraliser
Pass it through a particle filter and reuse it
Hand it over to a specialised, authorised company for reclamation or destruction
Clean the mixture yourself using a filter-drier

302

Stredne ťažká

What should be done if different refrigerants have been mixed in a storage cylinder?


Add a special refrigerant to the mixture
Pass it through a filter-drier and reuse it
Hand the mixture over to an authorised company – as a rule for destruction
Separate the mixture into its components yourself

303

Stredne ťažká

How does push-pull refrigerant recovery work?


The recovery unit draws vapour from the recovery cylinder and pushes it into the system; the pressure difference forces liquid refrigerant out of the system into the cylinder
Nitrogen is injected into the system, pushing the refrigerant into the atmosphere
Refrigerant is drawn alternately from the suction and discharge sides of the compressor
The recovery unit draws vapour from the system and condenses it in the cylinder

304

Stredne ťažká

What are the options for managing waste refrigerant?


Disposal, storage
Reclamation, recovery
Recovery, disposal
Recycling, reclamation, destruction

305

Stredne ťažká

Which management option restores recovered refrigerant to a quality equivalent to virgin product, so that it can be used by any undertaking?


Storage
Reclamation
Destruction
Recycling

306

Stredne ťažká

The lower the evaporating temperature, …


…the greater the density of the suction vapour and the greater the refrigerant mass flow rate
…the lower the density of the suction vapour and the greater the cooling capacity of the compressor
…the lower the density of the suction vapour and the lower the refrigerant mass flow rate
…the greater the density of the suction vapour and the lower the refrigerant mass flow rate

307

Stredne ťažká

How must transportable pressure vessels (e.g. refrigerant cylinders) be marked?


With the manufacturer's logo and date of manufacture
Among other things: the number of the design and testing standard, marks of the approving country and the inspection body, the date of the initial inspection, and the manufacturer's and operational marks
Only with weight and capacity marks
The marking is optional

308

Stredne ťažká

The recovery of refrigerants does not require the use of:


An electronic leak detector.
Scales with a measurement range suitable for the size of the cylinder being filled.
Hoses with shut-off valves.
A refrigerant recovery station.

309

Stredne ťažká

What functions does the compressor perform in a refrigeration system?


The compressor creates a vacuum on the suction side of the system
The compressor condenses the refrigerant.
The compressor draws in refrigerant vapour from the evaporator, compresses it, and then forces it into the condenser, raising the pressure to the required condensing pressure.
The compressor compresses ambient air and increases the pressure of the refrigerant.

310

Ľahká

What is the compression ratio of a compressor?


The ratio of absolute discharge pressure to absolute suction pressure (pc/po)
The amount of refrigerant compressed per cycle relative to heat capacity
The ratio of suction pressure to discharge pressure (po/pc)
The ratio of discharge pressure to the effective capacity of the compressor (p/Vk)

311

Stredne ťažká

What is compressor flooding (liquid slugging)?


A large amount of liquid refrigerant in a flooded evaporator, which is a normal operating condition
Flooding of the compressor by rainwater
Excess oil in the condenser
Liquid refrigerant or oil entering the compression chamber

312

Stredne ťažká

Within what range is the compressor motor speed typically controlled using a frequency inverter?


Approximately 30 to 75 Hz, corresponding to about 60–150% of nominal capacity (depending on the compressor manufacturer)
By a maximum of 10%
From approximately 10% to 90% of nominal capacity
Speed control does not change the cooling capacity

313

Ľahká

What is the theoretical displacement (swept volume flow) of a compressor?


The volume of refrigerant flowing in one piston cycle under actual operating conditions
A value expressed by the coefficient of performance (COP)
The volume of a single cylinder in cm³
The volume of vapour drawn in per unit of time, determined by the compressor's geometry and speed (stated by the manufacturer, e.g. in m³/h)

314

Stredne ťažká

Why is it essential to observe the correct phase sequence for scroll compressors and screw compressors?


Because these types of compressors are sensitive to voltage drops.
Because changing the phase sequence would reverse the direction of rotation of the compressor rotors, which could result in damage to the compressors.
Because the motor speed would decrease, and consequently the compressor’s capacity.
Because this type of compressor has difficulty starting up if the phase sequence is changed.

315

Stredne ťažká

What compression ratio should each stage of a two-stage vapour-compression system have (rule of thumb)?


Greater than 10
Equal to 1
Less than approximately 8
Greater than 18

316

Stredne ťažká

Why is a shaft seal necessary in open-type compressors?


To protect the crankshaft bearing
To ensure the bearing remains lubricated
Only to prevent oil leakage
To prevent air from entering and refrigerant from leaking out of the compressor

317

Stredne ťažká

How can you check whether the liquid refrigerant is sufficiently subcooled?


Check whether the liquid distributor upstream of the evaporator feels warm
Compare the liquid-line temperature with the saturation temperature at the measured condensing pressure
Check by touch whether the condenser outlet is noticeably colder than ambient
Check whether the whole evaporator surface is covered with an even layer of frost

318

Stredne ťažká

Why is the compressor crankcase heated?


To limit refrigerant migration into, and dissolution in, the oil during standstill
To keep the lubricating oil liquid
To dehydrate the oil
To increase dissolution of refrigerant in the oil and improve its viscosity

319

Ľahká

What is the clearance (dead) volume of a reciprocating compressor?


The volume between the valve plate and the piston at bottom dead centre
The space between the underside of the piston and the crankcase cover
The volume between the valve plate and the piston crown at top dead centre
The space between the side of the piston and the cylinder

320

Stredne ťažká

What are compressor packs (racks)?


Several compressors connected in parallel on a common frame with common suction and discharge headers
Several air-cooled condensers
Sets of compressors connected in any configuration
Units with two-stage compressors

321

Stredne ťažká

What is the main advantage of multi-compressor packs?


A smaller refrigerant charge than a single-compressor system
Stepwise capacity matching to demand, plus redundancy
No need for compressor controls and safety devices
Low purchase cost and easy installation without special controls

322

Stredne ťažká

What is meant by the operating envelope (application range) of a compressor?


The capacity, refrigerant type and dimensions of the compressor
The permissible range of evaporating and condensing temperatures (to, tk), or the corresponding pressures, within which the compressor may operate
A range determined by the evaporating temperature at a given ambient temperature
A range determined only by the evaporating temperature

323

Stredne ťažká

What are the basic functions of oil in a compressor?


Increasing the cooling capacity of the refrigerant
Lubricating bearings and sliding surfaces, removing heat, and sealing clearances (e.g. between piston and cylinder, or rotors)
Absorbing moisture from the refrigerant
Sealing leaks that develop in the installation

324

Stredne ťažká

What are the most effective ways of controlling compressor cooling capacity?


An expansion valve
Pressure control valves
Partially covering the evaporator
Changing the displacement: varying the rotational speed or unloading cylinders

325

Stredne ťažká

What does hot-gas bypass capacity control involve?


Part of the hot discharge gas is passed through a bypass valve to the suction side (or evaporator inlet), reducing the effective capacity
High-pressure liquid is injected into the suction to increase capacity
Bypass is not used for capacity control
The compressor speed is varied

326

Stredne ťažká

What is the fundamental difference between hermetic and semi-hermetic compressors?


The semi-hermetic casing is bolted (can be opened); the hermetic one is welded
Semi-hermetic compressors run more quietly as a complete unit
Both can be dismantled; they differ only in cooling capacity
The semi-hermetic compressor has no motor inside the casing

327

Stredne ťažká

How does a scroll compressor work?


A scroll compressor is also known as a turbo compressor.
It uses two screws to compress the refrigerant.
It is a positive-displacement compressor in which compression results from the interaction of a fixed and an orbiting scroll.
It is a type of piston-type device.

328

Stredne ťažká

What physical process takes place in the evaporator?


The secondary fluid (glycol, water) evaporates while the refrigerant condenses
The refrigerant condenses
The refrigerant is subcooled as a liquid
The liquid refrigerant evaporates, absorbing heat, and the vapour is slightly superheated at the outlet

329

Stredne ťažká

What is the purpose of compressor capacity control?


To ensure compressor lubrication
To increase the condensing pressure
To match capacity to the condensing temperature
To match the cooling capacity to the current demand

330

Stredne ťažká

Why is inverter speed control advantageous for refrigeration compressors?


Reducing the speed improves oil return to the compressor
It enables continuous, smooth control of cooling capacity
It increases compressor capacity above nominal at any frequency
It can be used with any compressor to ensure lubrication

331

Stredne ťažká

Does the suction gas temperature affect the cooling capacity of the compressor?


No – capacity depends only on the compressor displacement
Yes – higher temperature lowers vapour density, mass flow and capacity
Yes, but only in reciprocating compressors, not scroll
Yes, but only if the suction gas is deeply cooled

332

Stredne ťažká

In the case of compressor units fitted with an oil level control system, is it necessary to install the compressors at the same height?


Only scroll compressors.
Yes.
Only screw compressors.
No.

333

Stredne ťažká

What functions does a compressor powered by the vehicle’s engine perform in a transport refrigeration system?


This compressor draws in refrigerant vapour from the evaporator, compresses it and then forces it into the condenser whilst the vehicle’s engine is running.
The compressor compresses ambient air and increases the pressure of the refrigerant.
This compressor creates a vacuum on the suction side of the system whilst the vehicle’s engine is switched off.
This compressor condenses the refrigerant whilst the vehicle is in motion.

334

Stredne ťažká

Which media most commonly absorb heat from the refrigerant in the condenser?


Ammonia
Air and CO₂
Air or water
Only a water–glycol mixture

335

Stredne ťažká

What is the function of the condenser in refrigeration systems?


Releasing only the heat absorbed in the evaporator into the surroundings
Releasing to the environment the heat absorbed in the evaporator and the heat added during compression
Absorption of heat rejected in the regenerative heat exchanger
Releasing only the heat from the compressor into the surroundings

336

Stredne ťažká

If the refrigerant temperature on the high-pressure side is above its critical temperature, condensation…


…always occurs regardless of temperature
…occurs provided a special condenser is used
…does not depend on temperature
…does not occur

337

Stredne ťažká

How is liquid subcooling usually achieved in a refrigeration system?


In the final section of the condenser (or in an additional subcooler)
With an additional heat exchanger using liquid nitrogen
By dissolving the refrigerant in oil
With hot high-pressure vapour

338

Stredne ťažká

What is the purpose of condenser fan speed control?


Only to protect against exceeding the maximum condensing pressure
To keep the condensing pressure at the correct level
To disperse refrigerant in the event of a leak
To reduce energy efficiency

339

Stredne ťažká

Which international agreement introduced the global phase-down of HFC production and consumption?


The Paris Agreement
The Kigali Amendment to the Montreal Protocol
The Vienna Convention for the Protection of the Ozone Layer
The Kyoto Protocol

340

Stredne ťažká

Which international treaty governs the phase-out of ozone-depleting substances (CFCs, HCFCs)?


The Stockholm Convention
The Paris Agreement
The UN Framework Convention on Climate Change (UNFCCC)
The Montreal Protocol

341

Ťažká

What is the basis of the GWP values in Regulation (EU) 2024/573?


Each Member State sets its own GWP values
For HFCs (Annex I) – mainly the IPCC Fourth Assessment Report (AR4); for HFOs and non-fluorinated substances (Annexes II and VI) – the Sixth Assessment Report (AR6)
AR4 for all substances
AR6 for all substances

342

Ťažká

An air conditioner (not hermetically sealed) contains 2.5 kg of R410A (GWP 2088). How often must it be checked for leaks?


No checks required (below 3 kg)
Every 6 months
At least every 12 months (5.22 t CO₂ eq)
Every 3 months

343

Ťažká

When is labelled hermetically sealed equipment containing HFCs (Annex I) exempt from leak checks?


Never – hermetically sealed equipment is always checked
When it contains less than 10 t CO₂ eq, and in residential buildings also when it contains less than 3 kg of F-gases
Always, regardless of charge
When it contains less than 5 t CO₂ eq

344

Ťažká

Is a chiller containing 50 kg of R1234ze(E) subject to leak checks under Regulation (EU) 2024/573?


Yes – at least every 6 months (every 12 months with a leakage detection system)
No – HFOs are not subject to leak checks
Yes – every 12 months, because its GWP is low
No – the threshold is 5 t CO₂ eq and 50 kg of R1234ze is below 1 t CO₂ eq

345

Ťažká

In 2026, may an existing refrigeration installation using R404A (GWP 3922) be topped up with virgin refrigerant?


No – only reclaimed or recycled R404A is allowed (until 1 January 2030)
Yes, if the equipment has a leakage detection system
Yes – the ban applies only to equipment ≥40 t CO₂ eq
Yes – bans apply only to new equipment

346

Ťažká

After 1 January 2026, may an R410A (GWP 2088) air conditioner be serviced using virgin R410A?


No – the ban covers all HFCs
No – the ban covers all refrigerants with GWP ≥ 750
Yes – the servicing ban for air conditioners and heat pumps covers F-gases with GWP ≥ 2500
Only with reclaimed refrigerant

347

Stredne ťažká

Can HFC refrigerant recovered during a repair be put straight back into the same equipment without any cleaning (filtering/drying)?


Yes, if less than 24 hours have passed
No – recovered F-gas may be used for filling only after it has been recycled or reclaimed
Yes, if the operator agrees
Yes, always

348

Stredne ťažká

Who may purchase HFCs for servicing refrigeration equipment?


Any adult
Only a person holding the relevant certificate or an undertaking employing such persons
Any business
Only the equipment operator

349

Stredne ťažká

Under what condition may non-hermetically sealed split air conditioning charged with F-gas be sold to an end user?


When the user signs a statement that they will install it themselves
When evidence is provided that installation will be carried out by a certified undertaking
Unconditionally
Only if the unit contains less than 3 kg of refrigerant

350

Stredne ťažká

By when must the holder of an F-gas certificate issued under Regulation (EU) No 517/2014 first complete refresher training or an evaluation process?


Never – the certificate is valid indefinitely
By 31 December 2030
By 12 March 2029 (and then at least every 7 years)
By 12 March 2025

351

Stredne ťažká

What must the holder of a Category I certificate (Regulation 2015/2067) do to continue using it?


Nothing – Category I automatically becomes A1
Update their knowledge and skills to the level of Certificate A1 (Annex I to Regulation 2024/2215)
Update their knowledge to the level of Certificate E
Apply for an extension without training

352

Stredne ťažká

What does Certificate C under Implementing Regulation (EU) 2024/2215 authorise?


Recovery of F-gases from equipment <3 kg
Leak checks without breaking into the circuit
All activities in Article 2(1) in relation to ammonia (NH₃)
All activities in relation to CO₂

353

Stredne ťažká

May a person enrolled in a certification training course carry out certified activities?


No, never
Yes – with no time limit, if employed by a certified company
Yes – independently, for 6 months
Yes – under the supervision of a certified person, for no more than 24 months in total

354

Stredne ťažká

How long must the operator keep the records of equipment subject to leak checks, if they are not kept in a national database?


At least 5 years
At least 2 years
At least 1 year
Until the equipment is decommissioned

355

Ťažká

Since 1 January 2025, may a new single-split air conditioner containing 1.5 kg of R410A be placed on the market?


Yes – the ban applies only to units >12 kW
No – single splits <3 kg with F-gases of GWP ≥ 750 are banned
Yes, if the unit is hermetically sealed
Yes – the ban applies from 2029

356

Ťažká

From when is it prohibited to place on the market split air-to-air systems up to 12 kW containing F-gases with GWP ≥150 (unless required for safety)?


From 1 January 2029
From 1 January 2035
From 1 January 2025
From 1 January 2027

357

Ťažká

Which persistent atmospheric degradation product of R1234yf is classed as a PFAS?


Trifluoroacetic acid (TFA)
Carbonic acid
Carbon dioxide
Ozone

358

Stredne ťažká

What distinguishes class 2L refrigerants from class 2?


A maximum burning velocity of no more than 10 cm/s
Higher toxicity
Heat of combustion above 19 MJ/kg
No lower flammability limit

359

Stredne ťažká

What is the lower flammability limit (LFL) of propane R290?


Approx. 0.307 kg/m³
Approx. 0.038 kg/m³ (approx. 2.1% by volume)
Approx. 1.8 kg/m³
Approx. 0.38 kg/m³

360

Ťažká

What is the maximum R290 charge per circuit of a commercial refrigerating appliance (e.g. a cabinet) according to EN IEC 60335-2-89:2022?


1.5 kg
1.2 kg
13 × LFL ≈ 494 g
150 g

361

Ťažká

Calculate the maximum R32 charge (LFL = 0.307 kg/m³) for a wall-mounted air conditioner (h₀ = 1.8 m) in a 20 m² room using m_max = 2.5 × LFL^1.25 × h₀ × A^0.5.


approx. 13.8 kg
approx. 0.46 kg
approx. 1.5 kg
approx. 4.6 kg

362

Stredne ťažká

Equipment marked 'Ex II 3G' may be used in zone:


1
20 (dusts)
2 (explosive gas atmosphere unlikely and short-lived)
0

363

Stredne ťažká

How is explosion hazard zone 2 defined?


An explosive atmosphere is likely to occur in normal operation
An area where flammable refrigerants are never used
An explosive atmosphere is not likely in normal operation and, if it occurs, persists only for a short period
An explosive atmosphere is present continuously or for long periods

364

Stredne ťažká

Under which UN number is propane (R290) carried under ADR?


UN 1005
UN 1978
UN 3337
UN 3252

365

Ťažká

What is the maximum quantity of R290 (class 2, group F) that may be carried per transport unit under the ADR 1.1.3.6 exemption?


1000 kg
Unlimited
20 kg
333 kg

366

Stredne ťažká

At what concentration should a portable flammable gas detector used for R290 work raise an alarm at the latest?


No higher than 25% of LFL
At 5% propane by volume
At 100% of LFL
At 150% of LFL

367

Stredne ťažká

How should a recovery cylinder be prepared before filling it with a hydrocarbon refrigerant?


Evacuate it (no air) and label it for the specific flammable refrigerant
Purge it with compressed air
Partly fill it with nitrogen to 5 bar
No preparation is needed

368

Stredne ťažká

What is the correct approach in a risk analysis before work on an HC system?


First eliminate hazard sources (e.g. ignition sources); where this is not possible, identify them and apply mitigating measures (ventilation, detection, PPE)
The risk analysis is done after the work is finished
Having a fire extinguisher is sufficient
First select PPE, then possibly remove ignition sources

369

Ťažká

What is the charge limit m₃ = 130 m³ × LFL for R290 (LFL = 0.038 kg/m³) according to IEC 60335-2-40?


approx. 0.15 kg
approx. 13 kg
approx. 4.94 kg
approx. 0.99 kg

370

Stredne ťažká

Which property of ammonia helps people detect a leak early?


It is yellow in air
A very low odour threshold (a few ppm)
It is odourless
It is denser than air

371

Stredne ťažká

What hazard does a large CO₂ leak in an enclosed room pose to people?


Explosion of the mixture with air
CO₂ is completely safe
Accumulation near the floor and asphyxiating/toxic effects at high concentrations
Formation of hydrogen fluoride

372

Ťažká

Why does the efficiency of transcritical CO₂ systems fall in warm climates, and how is this mitigated?


Gas cooler pressure drops – extra charge is added
Efficiency does not depend on climate
At high ambient temperatures the system operates transcritically with large throttling losses – parallel compression and ejectors are used, among others
CO₂ freezes in the gas cooler – heaters are used

373

Stredne ťažká

What is floating head pressure and what does it achieve?


It keeps a constant high condensing pressure all year
It increases subcooling by flooding the condenser
It lets the condensing pressure fall with ambient temperature, reducing compressor work and raising COP (requires an expansion valve that works at a small pressure difference)
It means switching condenser fans off periodically

374

Stredne ťažká

How do SEER/SCOP differ from EER/COP?


There is no difference – they are synonyms
EER/COP are always higher than SEER/SCOP
SEER/SCOP apply only to natural-refrigerant equipment
SEER/SCOP are seasonal indicators accounting for part load and climate (EN 14825); EER/COP refer to a single operating point (EN 14511)

375

Stredne ťažká

Which design approach can significantly reduce the F-gas charge of a large refrigeration installation?


Larger liquid-line diameters
Omitting pipe insulation
Adding a second liquid receiver
An indirect (secondary-coolant) system or a cascade with a natural refrigerant in the low stage, plus heat exchangers with small internal volume

376

Stredne ťažká

Why must the charge of small, critically charged R290 systems be weighed to within a few grams during service?


Because extra R290 improves efficiency
Small charge deviations significantly change superheat/subcooling and efficiency, and overcharge increases the risk in a leak
Because scales are not needed – charging is done by sight glass
Because R290 is more expensive than HFCs

377

Stredne ťažká

Which information must be entered in the equipment records after a leak check?


Only the date of the check
The date and result of the check and the identity of the undertaking and person who performed it (with certificate number)
Only the operator's signature
Only the equipment's energy consumption

378

Stredne ťažká

What must be done when an indirect method (e.g. parameter analysis) indicates a possible leak?


Record it and check at the next periodic inspection
Top up the refrigerant and end the check
Nothing – indirect methods are sufficient
Carry out a direct-method examination to locate the leak