1

Könnyű

What is the base unit of mass in the International System of Units (SI)?


N
kg
t
lb (pound)

2

Közepes

What process takes place in the condenser of a refrigeration system?


The refrigerant rejects only the heat generated in the compressor
The refrigerant absorbs heat from the surroundings and evaporates
Hot vapour discharged by the compressor is desuperheated, condensed, and the resulting liquid is slightly subcooled
The secondary fluid (glycol, water) condenses while the refrigerant evaporates

3

Közepes

What mainly determines the condensing temperature of an air-cooled condenser?


The evaporating temperature
The ambient (inlet) air temperature
The compressor discharge temperature
The superheat

4

Közepes

Why does heat flow from the condenser to the surroundings?


Because the compressor pushes heat directly into the surroundings
Because the pressure in the condenser is lower than ambient
Because HFC refrigerants attract heat from the surroundings
Because the condensing temperature is higher than the ambient temperature, and heat flows spontaneously from a warmer to a colder body (second law of thermodynamics)

5

Közepes

What should you mainly pay attention to when operating a condenser?


That the outlet air temperature is higher than the condensing temperature
The colour of the condenser casing
Its general condition and the cleanliness of the heat-exchange surfaces
That the inlet air temperature is lower than the outlet air temperature

6

Közepes

What criteria should be considered when selecting a suitable condenser?


Fan noise, connection diameters and colour
Only own experience and the dimensions
The required capacity of the condenser and the technical specifications declared by the manufacturer
Only the size and number of fans

7

Közepes

How do contaminants (dust, particulates, deposits) affect the performance and efficiency of heat exchange surfaces in condensers?


Contaminants restrict heat transfer (reducing the heat transfer coefficient) and cause a reduction in condensing pressure.
Contaminants do not significantly affect the efficiency and effectiveness of the heat exchange surfaces in condensers.
Contaminants increase the heat transfer area and reduce the condensing pressure.
Contaminants restrict heat transfer (reducing the heat transfer coefficient) and cause an increase in condensing temperature and pressure, which in turn leads to a reduction in the condenser’s efficiency.

8

Közepes

How does the capacity of an air-cooled condenser change when it becomes dirty?


It increases
It increases because the fan speed rises
It decreases
It remains unchanged

9

Közepes

What is the main consequence of heavy frost on an air-cooling evaporator?


Reduced heat transfer and airflow, resulting in a drop in cooling capacity and evaporating temperature
A rise in the cooled-air temperature with no effect on capacity
An increase in condenser subcooling
A rise in evaporating pressure

10

Közepes

What happens when the evaporation temperature drops?


The discharge temperature decreases.
The compressor’s cooling capacity decreases.
The condenser fan speed increases.
The compressor’s cooling capacity increases.

11

Közepes

When is natural (off-cycle, air) defrosting possible?


Only in coolers fitted with speed-controlled fans
When the air passing through the cooler is above 0 °C
Never – electric heaters must be used in every air cooler
Only in freezer rooms below −18 °C

12

Közepes

When does frost form on the surface of an air-cooling evaporator?


Always, in every air cooler
Only when the room air temperature falls below 0 °C
Only when the system runs continuously
When the evaporator surface temperature is below 0 °C and below the dew point of the air

13

Közepes

In extensive pipework systems, flash gas (secondary evaporation) in the liquid line can be prevented by…


…additional subcooling of the liquid
…increasing the length of the liquid line
…using smaller-diameter pipes
…insulating the discharge line between the compressor and the condenser

14

Közepes

How does hot gas defrosting of the evaporator work?


Heated vapour (hot gas) from the compressor is directed into the evaporator piping.
We switch on the gas heater directed at the evaporator.
We swap the outlet and inlet sides of the evaporator.
This involves reversing the direction of rotation of the compressor.

15

Közepes

What is the function of the evaporator in a refrigeration system?


It cools the refrigerant.
It evaporates the water flowing through the evaporator.
It ensures that the refrigerant is superheated over the largest possible heat exchange surface area.
It transfers heat from the medium being cooled to the boiling refrigerant.

16

Közepes

What condition must electric heaters for evaporator defrosting meet?


They must be located beneath the evaporator
Heat from the heaters must be carried by the running fans
They must be in direct contact with the refrigerant
They must have good thermal contact with the heat-exchange surface (e.g. inserted in the fin block)

17

Közepes

Refrigerant distributor:


ensures an even distribution of the refrigerant to the individual sections of the evaporator.
acts as a buffer for the refrigerant in the event that the pressure upstream of the expansion valve is exceeded.
ensures even distribution of the refrigerant to the individual sections of the condenser.
ensures the even distribution of the refrigerant discharged by compressors connected in parallel.

18

Közepes

What defrosting methods are used for air coolers?


Natural only – other methods are ineffective and uneconomic
Only by switching off the fans with the compressor running
Electric only – other methods are not permitted in refrigeration
Electric, hot gas, water spray and natural (at positive temperatures)

19

Közepes

The boiling point of a liquid rises when the pressure above the liquid…


…falls
…rises
…varies depending on the ambient temperature
…remains constant

20

Közepes

MOP in thermostatic expansion valves stands for:


minimum flow opening.
self-cleaning of the valve in the event of moisture in the refrigerant freezing.
maximum operating pressure.
maximum pressure switch protection.

21

Közepes

The function of a thermostatic expansion valve (TEV) is:


to adjust the evaporating pressure in the condenser
to maintain a constant compressor suction pressure
to maintain a constant condensing pressure
to meter refrigerant into the evaporator according to the superheat of the vapour leaving the evaporator

22

Közepes

What type of compressor motor can be used with a capillary tube?


A low-speed motor
An electronically commutated motor
A high-starting-torque motor must be used
A low-starting-torque motor (pressures equalise during standstill)

23

Közepes

What does a thermostatic expansion valve control?


The temperature in the cold room
The condensing pressure
The mass flow of refrigerant fed into the evaporator
The discharge temperature

24

Könnyű

The refrigerant absorbs heat when…


…it condenses
…it is subcooled
…it evaporates
…it freezes

25

Közepes

What does the manufacturer state as the factory setting of a thermostatic expansion valve?


the degree to which the valve is filled with refrigerant liquid.
the static superheat of the valve.
the degree of refrigerant expansion.
the superheat value during valve operation.

26

Közepes

Where is a new or repaired system with an expansion valve and liquid receiver charged?


Through the capillary tube outlet during normal system operation
In the liquid phase on the high-pressure side, with the compressor stopped
Anywhere – the charging point does not matter
In the liquid phase into the compressor suction, with the compressor running

27

Közepes

What does a thermostatic or electronic expansion valve control?


Subcooling, by adjusting condensing pressure
The evaporating pressure – closing below the set point
The amount of refrigerant fed to the evaporator according to superheat
The compressor speed

28

Közepes

What does the MOP function of thermostatic expansion valves mean?


The valve prevents motor overheating by injecting liquid into the compressor
The valve limits subcooling
The valve limits the maximum evaporating (suction) pressure, protecting the compressor motor from overload, e.g. after defrost
The valve maintains a constant condensing pressure

29

Közepes

The lower the liquid temperature upstream of the expansion valve, (at the same mass flow)…


…the lower qo, with Qo unchanged
…the lower qo and the lower Qo
…the lower qo and the lower energy efficiency
…the higher the specific refrigerating effect qo [kJ/kg] and the higher the cooling capacity Qo

30

Közepes

How should the MOP point of an expansion valve be selected relative to the highest normal evaporating temperature?


A few kelvin higher (approximately 7 K)
Higher by approx. 20 K
Freely – the MOP value is irrelevant
About 7 K lower than that temperature

31

Közepes

What is the function of the suction pressure regulator?


To maintain the suction pressure at the highest possible level.
It limits the suction pressure and protects the compressor from excessively high suction pressure.
It maintains the evaporation pressure at a constant level.
It prevents a drop in suction pressure and, if necessary, shuts down the refrigeration system.

32

Közepes

What is the function of the valve regulating water flow through the condenser?


To maintain the condensing pressure at the highest possible level.
To maintain the condensing pressure at the lowest possible level.
To maintain the water temperature at the highest level.
To maintain the condensing pressure at a constant level.

33

Közepes

The use of a refrigerant distributor requires a thermostatic expansion valve ...


... with external pressure equalisation.
... with internal pressure equalisation.
... with a MOP function.
... with an adsorption-type sensor filling.

34

Közepes

What properties should good insulation materials have?


Low thermal conductivity (and low water absorption, vapour tightness)
An antistatic coating
High thermal conductivity
The ability to absorb large amounts of moisture

35

Közepes

When is refrigerant vapour superheated?


When the compressor motor temperature rises excessively
When the pressure on the discharge side is higher than on the suction side
When its temperature is higher than the saturation temperature corresponding to its pressure
When the evaporating temperature is lower than the ambient temperature

36

Közepes

How can you check whether the liquid refrigerant is reaching the expansion valve without vapour bubbles?


We check using a pressure gauge fitted on the discharge side of the compressor.
We check using a liquid pressure gauge.
We check this using a sight glass.
We are unable to check this.

37

Közepes

Where does the liquid line run?


Between the evaporator and the suction-line heat exchanger
Between the compressor and the condenser
Between the evaporator and the compressor
From the condenser (liquid receiver) to the expansion valve

38

Közepes

What is the function of the liquid receiver in a refrigeration system?


To act as a reserve when the required charge is unknown
To further subcool the condensed refrigerant
To store refrigerant and compensate for changes in the circulating charge as the heat load varies
To collect liquid refrigerant and excess oil

39

Közepes

What is the purpose of the liquid receiver during service work?


It further subcools the refrigerant before the expansion valve
It collects excess oil circulating in the system
It is a reserve when the installer does not know the required charge
It allows pump-down and temporary storage of the refrigerant

40

Közepes

Where should the liquid receiver be installed?


It should be installed downstream of the condenser, upstream of the expansion valve.
It should be fitted after the evaporator.
It should be fitted between the compressor and the condenser.
It should be fitted just before the compressor.

41

Közepes

What is the function of the suction pressure regulator fitted to the suction pipe when the compressor starts up?


It opens when the suction pressure upstream of the compressor drops.
It regulates the evaporation pressure.
It closes when the suction pressure upstream of the compressor drops.
It regulates the condensing pressure.

42

Közepes

The use of microchannel heat exchangers, compared with conventional heat exchangers made of copper tubes and fins, results in:


A reduction in refrigerant charge and, typically, higher energy efficiency.
A reduction in the system’s energy efficiency.
There is no effect whatsoever on either the amount of refrigerant or energy efficiency.
An increase in the amount of refrigerant in the system and an increase in condensing pressure.

43

Közepes

Which refrigerants belong to the HFC group?


R11, R12, R502.
R134a, R404A, R507A, R410A.
R134a, R32, R22, R507A, R290.
R22, R401A.

44

Közepes

Which refrigerants belong to the HFO group?


R134a, R404A.
R22, R12.
R134a, R290.
R1234yf, R1234ze(E).

45

Közepes

What are the characteristics of R410A refrigerant compared to R407C refrigerant?


The saturation pressure of R407C refrigerant is much higher than that of R410A.
The saturation pressure of R410A refrigerant is higher than that of R407C.
The saturation pressure of both refrigerants is roughly the same.
The saturation pressure of R407C is 150% higher than that of R410A.

46

Közepes

What does the TEWI indicator define?


The impact of a refrigerant on the ozone layer
Total Equivalent Warming Impact: the sum of direct emissions (leakage and refrigerant losses at disposal) and indirect emissions (CO₂ from generating the energy consumed by the equipment) over its lifetime
The ability of the ozone layer to recover
The global warming potential of a gas relative to CO₂ over a 100-year horizon

47

Közepes

What are the characteristics of R452A compared with R404A?


Both are azeotropic and have no temperature glide
It is a non-flammable (A1) HFC/HFO blend with properties similar to R404A and a GWP about 45% lower
The temperature glide of R452A is half that of R404A
It is a flammable and toxic single-component HFC

48

Közepes

What distinguishes R1234yf from R134a?


A higher normal boiling point
It is mildly flammable (class A2L), whereas R134a is non-flammable (A1)
A higher critical temperature
Higher toxicity

49

Közepes

How does CO₂ (R744) compare with R134a?


Unlike R134a, it is an azeotropic mixture
Its temperature glide is 7 K greater than that of R134a
It has identical properties and is a drop-in replacement for R134a
It has a lower critical temperature, much higher operating pressures and a much higher volumetric cooling capacity (smaller compressors and pipes)

50

Közepes

Which of the following is NOT a fluorinated greenhouse gas?


Sulphur hexafluoride (SF6).
Hydrofluorocarbons (HFCs).
Perfluorocarbons (PFCs).
Carbon dioxide (CO₂).

51

Közepes

What is the greenhouse effect?


Chlorine compounds destroy stratospheric ozone, increasing UV radiation at the surface
Greenhouse gases absorb and re-emit the Earth's infrared radiation, warming the lower atmosphere
Dust in the atmosphere reflects sunlight, lowering the average surface temperature
Clouds reflect ultraviolet radiation, which makes the air near the surface warmer

52

Könnyű

What does the GWP indicator mean?


The annual rise in mean air temperature caused by the emission of 1 kg of the gas
Ozone depletion potential
The ability of a substance to restore the ozone layer
Global Warming Potential: the climate warming impact of 1 kg of a gas compared with 1 kg of CO₂ (GWP = 1) over a defined time horizon, usually 100 years

53

Közepes

How do refrigeration systems contribute to the greenhouse effect?


Indirectly (through energy consumption) and directly (through emissions of refrigerant into the atmosphere)
Only through the heat rejected by the condenser
Only through CO₂ given off by the compressor motor
Through oil emitted into the atmosphere from the condenser and filter

54

Közepes

What is the greenhouse effect?


The absorption of solar radiation by the Earth's surface
The formation of a layer that traps only heat from fuel combustion in aircraft
The filtering of solar radiation by the atmosphere
The trapping of heat in the Earth's atmosphere, which hinders the radiation of heat into space

55

Közepes

Which EU regulation is currently the primary piece of legislation governing the use of fluorinated greenhouse gases (F-gases) in the European Union?


Directive 2009/125/EC
Regulation (EU) 2024/573
Regulation (EU) No 517/2014
Regulation (EU) 2015/1188

56

Közepes

What is the main objective of Regulation (EU) 2024/573?


Prevention of F-gas emissions and the achievement of the EU’s climate targets
To facilitate the import of electrical appliances
To reduce taxes on refrigeration equipment
Standardising metal recycling standards

57

Közepes

What are the ecodesign obligations of manufacturers of refrigerating appliances?


Only using energy labels under Regulation (EU) 2024/573
Only declaring F-gas quantities under Regulation (EU) No 517/2014
Meeting implementing regulations (e.g. 2019/2019, 2015/1095): efficiency, spare parts, reparability
Only implementing an ISO 9001 quality management system

58

Közepes

What is the main objective of EU ecodesign legislation (Directive 2009/125/EC, now Regulation (EU) 2024/1781 – ESPR)?


To standardise the appearance of products in the EU
To increase sales of electrical appliances in the EU
To facilitate imports from outside the EU
To reduce the negative environmental impact of products by improving energy efficiency, durability and recyclability

59

Közepes

What is the function of a ball valve in a refrigeration system?


It regulates the temperature of the refrigerant
It measures the moisture content of the refrigerant
Enables the refrigerant flow to be completely shut off
It prevents excessive pressure build-up in the system

60

Könnyű

What is the main function of a safety valve?


Discharges refrigerant when the set pressure is exceeded
It controls the oil level in the compressor
Prevents the evaporator from freezing
It monitors the moisture content of the refrigerant

61

Közepes

How do certain gases contribute to the greenhouse effect?


They limit UV radiation reaching the Earth's surface, changing the heat balance
They trap thermal radiation that the Earth would otherwise emit into space
They deplete the ozone layer, so more solar radiation reaches the surface
They heat the air through chemical reactions with atmospheric oxygen and nitrogen

62

Közepes

What is the purpose of a sight glass (with moisture indicator)?


Regulating compressor pressure
Visual assessment of the refrigerant condition in the liquid line (bubbles) and of system moisture
Emergency shut-off of flow
Measuring condenser temperature

63

Közepes

What is the function of the temperature regulator in a refrigeration system?


Controls the operation of the compressor and valves to maintain the set temperature
To maintain a constant pressure in the compressor
It drains excess refrigerant into the receiver
It restricts oil flow

64

Nehéz

What is the role of a suction liquid separator (also in systems with flammable or toxic refrigerants)?


It prevents liquid refrigerant from entering the compressor
It separates liquid from oil
It heats the refrigerant before the evaporator
It is used only to measure moisture

65

Nehéz

What is the function of an oil separator in systems using flammable or toxic refrigerants?


They are used solely to measure the moisture content of the refrigerant
Separates oil from the refrigerant and facilitates the return of oil to the compressor
It prevents liquid from entering the compressor
Heats the refrigerant before it enters the evaporator

66

Közepes

What is the purpose of oil level regulators in a refrigeration system?


They control the evaporator temperature
They drain off excess refrigerant
They control the pressure in the condenser
Maintains the correct oil level in the compressor

67

Közepes

What is the function of the liquid receiver in relation to system tightness?


It controls the evaporating temperature by varying the circulating charge
It stores refrigerant; checking its liquid level helps detect charge loss
It keeps the whole system at constant pressure regardless of load
It regulates the oil returning to the compressor

68

Közepes

What is the role of a gauge manifold with thermometers (temperature probes)?


It controls oil level
It monitors refrigerant moisture content
It measures pressures and temperatures to determine superheat and subcooling and thus assess the system charge (indirect leak check)
It relieves pressure if it is exceeded

69

Közepes

What is the role of defrost controls?


They protect the evaporator from icing and damage that could lead to leaks
They control compressor discharge pressure during defrost
They monitor the moisture content of the refrigerant
They drain excess oil from the evaporator to the receiver

70

Könnyű

What is the unit of pressure in the International System of Units (SI)?


bar (gauge)
atm (standard atmosphere)
psi (pound per square inch)
Pa (pascal)

71

Közepes

Where can the lists of fluorinated greenhouse gases be found?


In a regulation of the Minister of Economy on the list of fluorinated greenhouse gases
In Annexes I–III to Regulation (EU) 2024/573 of the European Parliament and of the Council
In the national Act on ozone-depleting substances and certain fluorinated greenhouse gases
In the Vienna Convention for the Protection of the Ozone Layer

72

Közepes

Where can the lists of ozone-depleting substances be found?


In the Vienna Convention for the Protection of the Ozone Layer
In Annexes I and II to Regulation (EU) 2024/590 of the European Parliament and of the Council
In a regulation of the Minister of the Environment on the list of controlled substances
In the national Act on ozone-depleting substances and certain fluorinated greenhouse gases

73

Nehéz

Why are PFAS formed by the decomposition of certain F-gases (e.g. TFA from HFOs) problematic?


They are very persistent, accumulate in the environment (e.g. water) and may be toxic
They are readily biodegradable
They are climate- and environment-neutral
They cause rapid cooling of the atmosphere

74

Közepes

Where and by when must entities obliged under the Polish Act of 15 May 2015 submit annual reports on ODS and F-gases?


By the end of the calendar year, on a form at a regional office of the Office of Technical Inspection (UDT)
By 28 February of the following year, electronically via the Reports Database (BDS) run at the Institute of Industrial Chemistry (ICHP)
By 31 March, electronically to the Ministry of Climate and Environment
By 31 January, in the Central Register of Operators (CRO)

75

Közepes

Which installation measure has a major impact on compressor energy efficiency?


Charging extra refrigerant 'as a reserve' above the nameplate value
Omitting the filter-drier to reduce flow resistance
Proper evacuation and dehydration of the system (removing air and moisture)
Installing a suction line smaller than recommended

76

Közepes

How does regular oil-level monitoring affect compressor operation?


It ensures proper lubrication and limits wear and energy losses
It increases cooling capacity above nominal
It allows any type of oil to be topped up
It allows the crankcase heater to be omitted

77

Könnyű

How do system leaks affect compressor energy efficiency?


Refrigerant loss reduces capacity and increases energy use (longer run times, higher superheat)
They improve efficiency because condensing pressure drops
They affect only safety, not energy use
No effect as long as the system still cools

78

Közepes

Regulation (EU) 2024/590 relates to:


Ozone-depleting substances
Conditions for F-gas certification of companies recovering and reclaiming refrigerants
Health and safety during refrigerant recovery
Alternative refrigerants replacing fluorinated greenhouse gases

79

Közepes

What is the significance of proper suction and discharge pressure control?


Pressures do not affect energy use
It keeps the compressor at optimal conditions (suction pressure as high and condensing pressure as low as permissible)
The highest possible condensing pressure is best
The lowest possible suction pressure is best

80

Közepes

Which maintenance measure reduces compressor energy consumption?


Permanently disabling the crankcase heater
Replacing the filter-drier when the pressure drop or moisture indicator shows it is necessary
Topping up refrigerant at every service visit
Raising the high-pressure switch setting

81

Közepes

How does air (non-condensable gas) in the system affect operation?


It improves condenser heat transfer
It only affects the sight-glass indication
It raises the condensing pressure and reduces efficiency
It lowers the condensing pressure

82

Közepes

What role do controls play in compressor efficiency?


They enable optimised operation and lower energy use (e.g. floating head pressure, capacity matching)
They matter only in NH₃ systems
They increase the circulating refrigerant charge
They provide safety only, with no energy effect

83

Közepes

How does suction superheat at the compressor affect efficiency?


Zero suction superheat is optimal
Excessive superheat reduces efficiency and raises the discharge temperature
Superheat has no effect
The higher the superheat, the higher the efficiency

84

Közepes

How does correct system layout affect efficiency?


It affects only appearance
It doesn't matter
It shortens pipe runs and limits pressure drops and energy losses
Longer pipes improve subcooling and always increase efficiency

85

Közepes

How important is suction pipe insulation?


It increases energy consumption
It has no effect
It is needed only for appearance
It limits heat gain and excessive superheat, improving efficiency

86

Közepes

Which measure most improves condenser energy efficiency?


Raising the condensing pressure set point
Increasing the refrigerant charge
Regular cleaning of heat-exchange surfaces
Reducing fan speed to the minimum

87

Könnyű

How does a dirty condenser affect the operation of the refrigeration system?


It lowers the condensing pressure
Causes an increase in pressure and energy consumption by the compressor
It has no effect
It improves efficiency

88

Könnyű

Why is adequate airflow through an air-cooled condenser important?


The lower the airflow, the lower the condensing pressure
It doesn't matter
It ensures effective heat rejection and low condensing pressure
It affects only noise

89

Közepes

Which refrigerants damage the ozone layer?


All refrigerants containing chlorine or bromine in their molecules
All refrigerants containing fluorine and hydrogen in their molecules
All natural refrigerants
All refrigerants containing carbon in their molecules

90

Könnyű

How does the presence of limescale in a water-cooled condenser affect performance?


Impairs heat exchange and increases energy consumption
It has no effect
It improves heat transfer
It lowers the condensation temperature

91

Közepes

How does correct condensing pressure control affect efficiency?


It always increases energy use
It has no effect
It keeps the lowest pressure that still ensures proper expansion-valve feed, reducing energy use
It is best to keep a constant high condensing pressure all year

92

Könnyű

How do condenser leaks affect energy efficiency?


Have no effect
Causes refrigerant loss and a drop in efficiency
They improve efficiency
They lower the temperature

93

Könnyű

How important is the correct positioning of an air-cooled condenser?


It should be housed in a small room
It should be close to heat sources
It should be installed in a well-ventilated area with unobstructed airflow
It doesn’t matter

94

Könnyű

How does hot air recirculation affect the condenser?


It reduces the pressure
It has no effect
Impairs cooling and increases energy consumption
It improves efficiency

95

Közepes

How does insulation of heating and DHW pipework affect the efficiency of a heat pump system?


It reduces energy losses and improves overall system efficiency
It increases pressure
It impairs cooling
It doesn't matter

96

Közepes

Which measure most improves the energy efficiency of an air-cooling evaporator?


Raising the condensing temperature by a few kelvin
Restricting the airflow through the evaporator
Increasing the refrigerant charge above nominal
Defrosting at the right time and keeping the fins clean

97

Könnyű

How does evaporator icing affect the system’s operation?


It improves cooling performance
Impairs heat exchange and increases energy consumption
It has no effect
It lowers the condensation temperature

98

Könnyű

How does dirt on the evaporator surface affect its performance?


It improves efficiency
It has no effect
It reduces the pressure
Impairs heat exchange and increases energy consumption

99

Könnyű

What maintenance task is crucial for the evaporator?


Increasing the refrigerant charge
Reduced airflow
Lack of maintenance
Regular cleaning and defrosting

100

Közepes

What does a Certificate A2 for natural persons (Implementing Regulation (EU) 2024/2215) authorise?


Only recovery of F-gases from equipment containing less than 3 kg (or 6 kg in hermetically sealed systems)
Only leak checks that do not entail breaking into the refrigerant circuit
All activities involving equipment using CO₂ (R744)
All activities (leak checks, installation, repair, maintenance, servicing, decommissioning, recovery) involving F-gases and hydrocarbons in equipment containing less than 3 kg, or less than 6 kg in labelled hermetically sealed systems

101

Könnyű

How does superheat at the evaporator outlet affect efficiency?


It always improves performance
It only causes a temperature drop
It has no effect
Excessive superheat reduces energy efficiency

102

Könnyű

How do leaks in the evaporator affect efficiency?


Have no effect
Increase capacity
Improves performance
These cause refrigerant loss and a drop in efficiency

103

Könnyű

How important is correct expansion valve adjustment?


It doesn’t matter
It increases energy consumption
Ensures optimal evaporator charge and improves efficiency
Causes leaks

104

Könnyű

How does inadequate insulation of suction (or secondary-coolant) pipes affect evaporator performance?


It lowers the condensing temperature
It has no effect
It causes cooling losses and increased energy use
It improves efficiency

105

Könnyű

How does correct TEV adjustment affect system energy efficiency?


It causes leaks
It has no effect
It increases energy use
It ensures optimal superheat and improves efficiency

106

Könnyű

What happens if the superheat set by the TEV is too high?


It has no effect
Efficiency will drop because the evaporator is not being fully utilised
Cooling efficiency will improve
The refrigerant charge will increase

107

Közepes

How does too low superheat setting on the TEV affect performance?


It increases operational safety
It may lead to improved efficiency, but it increases the risk of the compressor becoming flooded with liquid
It reduces refrigerant flow
It has no effect

108

Könnyű

How do contaminants in the system affect the operation of the TEV?


They lower the temperature
They improve its performance
Have no effect
They can cause it to become blocked and reduce efficiency

109

Könnyű

What role does the filter-drier play in terms of system efficiency?


It increases the amount of refrigerant
It doesn’t matter
Removes moisture and contaminants, improving the system’s efficiency
It lowers the temperature

110

Könnyű

How does proper insulation of components (e.g. pipes near the TEV) affect the system?


It doesn’t matter
It increases energy consumption
It causes leaks
Prevents unwanted heat gains and improves efficiency

111

Közepes

What is the scope of Regulation (EU) 2024/573?


Health and safety requirements for brazing and welding on refrigeration installations
Design requirements and conformity assessment for pressure equipment
Limiting emissions, use and marketing of F-gases, HFC phase-down, certification and reporting
Only requirements for periodic leak checks of refrigeration equipment

112

Könnyű

How important is it to check the operation of the condensing pressure control valve in the system?


It increases energy consumption
Ensures operation within the optimum pressure range and reduces energy losses
It causes a significant rise in temperature
It has no effect

113

Könnyű

How does the correct selection of a TEV affect energy efficiency?


Ensures the system is matched to its capacity and operates optimally
It doesn’t matter
It increases the amount of refrigerant
It lowers the temperature

114

Közepes

How can you tell that the system has been overcharged with refrigerant?


It cannot be checked, because the sight glass is not intended for this
Even under a very small heat load, frost forms on the suction line
Under normal operating conditions the condensing pressure and subcooling rise markedly because excess liquid floods the condenser and reduces its active surface
The compressor runs at a lower load and the suction pressure drops

115

Közepes

Before charging the unit with refrigerant, it is essential to…


…check the compressor suction and discharge connections
…fill in the unit's data sheet
…carry out a trial start-up
…carry out a tightness test (and evacuate the system)

116

Közepes

What information must appear on the label of equipment containing F-gases?


The weight and capacity of the pipework and the colour code of the casing paint
The manufacturer's logo, the unit weight and year of manufacture from the rating plate
That it contains an F-gas, its designation, quantity in kg and t CO₂ eq, and GWP
Only the trade name of the refrigerant and the unit's serial number

117

Könnyű

What is the base unit of temperature according to the International System of Units (Système International d’Unités)?


°R
°C
°F
K

118

Közepes

Which set of information best reflects the content of the equipment records required by Regulation (EU) 2024/573?


Only the date of installation and the installer's name
Operator details, equipment details, type and quantity of refrigerant, and information on servicing and repairs
The owner, installer and service technician of the unit
The make and model of the unit

119

Nehéz

Which statement about installing Schrader valves is correct?


When brazing the valve body, the core must be removed, then refitted and tightened to the correct torque
All Schrader cores are suitable for all refrigerants
Schrader valves must not be used in R744 systems
Hydrocarbons leak through Schrader valves

120

Nehéz

How does an undercharge affect the high-pressure side (without discharge pressure control)?


Discharge (condensing) pressure and subcooling will both be lower
Discharge pressure higher, subcooling higher
Discharge pressure lower, subcooling higher
Discharge pressure higher, subcooling lower

121

Nehéz

What is the benefit of adding helium as a tracer gas to nitrogen in a pressure test?


Its small atoms pass easily through leaks and are detected
It has a distinctive odour that helps locate the leak
It reacts with refrigerant residues, producing a visible colour change
It has a higher pressure than pure nitrogen in the same cylinder

122

Közepes

Who is responsible for keeping the equipment records?


The equipment maintenance technician.
The operator of the unit or system.
There is no such obligation.
The person responsible for risk assessment.

123

Nehéz

What can be the effect of a relief valve lifting repeatedly?


The set pressure increases
The valve no longer opens
The valve may not reseat tightly and its set (opening) pressure may decrease
The valve stays fully open permanently

124

Közepes

Where are oil traps installed on the suction line?


At the bottom of vertical suction risers with upward flow
Immediately before the compressor suction connection
At the inlet to every component of the refrigeration system
Before the safety valve on the suction side

125

Nehéz

What is the relationship between the pressure (p) and temperature (T) of nitrogen at the start (1) and end (2) of a tightness test (p absolute, T in kelvin)?


p₂ = T₂/(p₁ × T₁)
p₂ = (p₁ × T₁)/T₂
p₂ = (p₁ × T₂)/T₁
p₂ = T₁/(p₁ × T₂)

126

Közepes

Which symptoms with the compressor running indicate a refrigerant leak (undercharge)?


Rising liquid level in the receiver and increasing subcooling
Rising condensing and suction pressures with no superheat
Sight glass full of liquid and rising oil level in the crankcase
Low suction pressure, high superheat and negligible subcooling

127

Közepes

Which components of a refrigeration system are potential leak points subject to leak checks?


Joints, valves (including stems), seals (including those on replaceable filters and driers), parts subject to vibration and connections to safety and measuring devices
Only high-pressure-side components
Hermetic compressors, liquid receivers and liquid separators
Only suction-side components

128

Közepes

What pressure is used for the pressure tightness test of an installation?


Always 30 bar
A pressure equal to the maximum pressure measured during operation
A pressure chosen by the technician based on experience
The pressure specified in EN 378-2 or by the manufacturer, not exceeding the maximum allowable pressure of the system (PS)

129

Közepes

At which points of the unit must the leak check be carried out?


Only on discharge-side components
Only on compressor shut-off valves, solenoid valves and filters
Only at connections of measuring instruments
At all points where there is a potential risk of refrigerant leakage

130

Közepes

When can a unit be considered tight after a pressure test?


When the pressure remains constant during the test (allowing for temperature-related changes); any unexplained pressure drop requires the leak to be located
When gas bubbles appear after immersion in water
When the pressure drop does not exceed 0.1 bar regardless of the test duration
When it has been checked with a fixed electronic detector

131

Közepes

Which legal act currently sets out the obligation to check stationary refrigeration equipment containing F-gases for leaks, and how often this must be done?


Regulation (EU) No 517/2014
Commission Regulation (EC) No 1516/2007
Regulation (EU) 2024/573
Implementing Regulation (EU) 2024/2215

132

Nehéz

Which parts of a refrigeration system should be given particular attention during a leak check?


Joints, valves incl. stems, seals, parts subject to vibration, connections to safety devices
Compressor and receiver connections, because the pressure is highest there
Only condenser connections, because the refrigerant is liquid there
Only compressor connections, because they are the only parts subject to vibration

133

Könnyű

What is the superheat of refrigerant vapour?


The difference between the saturation temperature and the actual liquid temperature in the liquid line
The amount of heat required to evaporate a liquid
The difference between the condensing temperature and the ambient temperature
The difference between the actual vapour temperature and the saturation temperature corresponding to its pressure (expressed in K)

134

Nehéz

Leak checks can be carried out using various methods. Which pair is correct?


Direct and indirect methods
Material quality control methods and electronic methods
Physical and chemical methods
Methods with and without quality control of supplies

135

Nehéz

To whom can leak checks of stationary refrigeration equipment containing F-gases be entrusted?


An employee appointed by the owner of the installation
A person who has carried out such checks before
A natural person holding a certificate covering leak checks (A1, A2 within its charge limit, or E)
Any leak-testing specialist

136

Nehéz

What conditions must be met to use UV dye for leak checking?


It is sufficient to have a UV lamp, dye and safety goggles
A UDT authorisation for pressure testing is required
It is sufficient that introducing dye into the circuit is technically feasible
Manufacturer approval of the method and a certificate covering breaking into the circuit

137

Nehéz

Which leak-checking methods are considered direct methods?


Nitrogen with tracer gas and pressure measurement
1. gas detection devices (portable or fixed leak detection system), 2. UV detection fluid or dye, 3. bubble/foam solutions
Pressure-change measurement and immersion in water
Vacuum test and foam solution

138

Nehéz

What do indirect leak-checking methods involve?


Leak detection with an electronic detector
Ultrasonic measurement
A visual and manual check and analysis of parameters: pressure, temperature, compressor current, liquid levels and recharge volume
Leak detection with UV dye

139

Közepes

How should the pressure be increased during a pressure tightness test?


Gradually, in stages, checking for leaks at each level until the test pressure is reached
In any way
As quickly as possible
In one step, by fully opening the nitrogen cylinder valve

140

Közepes

What electronic equipment should be used for leak checking?


Only detectors with an infrared sensor
Only devices with an 'ion pump' sensor
Only hot-cathode devices
Detectors suited to the refrigerant in the system, with appropriate sensitivity, checked periodically

141

Közepes

What documentation should be checked before starting a leak check?


Only the installation invoice and the first start-up report
The equipment records – especially recurring problems and previous leaks
Attendance sheets of the plant-room staff for the year
The operator's fixed-asset inventory ledger

142

Közepes

What information must be recorded in the leak check report?


Only the number of leaks found and the date of the check
The method used, the time spent on site and the cost of repair
The date, a general note about the leak and the operator's signature
Date, number and location of leaks, how they were repaired, technician details and signature

143

Közepes

What pressure should be used for the pressure tightness test?


Always 10–12 bar
A pressure not exceeding the maximum allowable pressure of the system (PS)
Any pressure, at the technician's discretion
Always 2–3 bar

144

Közepes

What is the temperature glide of a refrigerant?


A property of single-component refrigerants, for which one saturation temperature corresponds to a given pressure
In zeotropic mixtures, the difference between the temperatures at the start and end of a phase change (boiling or condensation) at constant pressure
The temperature rise of the vapour in the compressor
The temperature drop of the refrigerant across the expansion valve

145

Nehéz

What does a vacuum (decay) test involve?


The pump runs continuously to hold the required vacuum for the test
The pump is restarted every time the system pressure rises
After isolating the pump, you check whether the system pressure rises
With the pump running, you watch the vacuum gauge reading

146

Nehéz

How often should leak tests be carried out on equipment containing 1.5 kg of R404A refrigerant (5.9 tonnes of CO₂ equivalent)?


Once every six months.
Only when servicing the unit.
At least once every 12 months.
On initial commissioning.

147

Nehéz

How often should leak tests be carried out on equipment containing 7 kg of R404A refrigerant (27.45 tonnes of CO₂ equivalent)?


On initial commissioning.
Once every six months.
At least once every 12 months.
Only when servicing the unit.

148

Közepes

In which equipment is a leakage detection system required?


Equipment with 30 kg or more of F-gases, regardless of their GWP
Equipment with 50 t CO₂ eq or more of F-gases, regardless of equipment type
Equipment with 5 t CO₂ eq or more of F-gases, regardless of equipment type
Equipment with ≥ 500 t CO₂ eq of Annex I F-gases (or ≥ 100 kg of Annex II Section 1 gases)

149

Nehéz

Under Regulation (EU) 2024/573, a leakage detection system is mandatory when:


the charge is 100 kg or more of ozone-depleting substances
the equipment operates in an enclosed space
the equipment contains a flammable refrigerant in any quantity
the F-gas charge of the refrigeration equipment is 500 t CO₂ eq or more

150

Nehéz

Which leak-checking method may NOT be used by a holder of a Category E certificate?


Checking with a foaming solution
Leak checking with a fluorescent dye introduced into the circuit
Visual inspection
Measurement with a handheld electronic detector

151

Közepes

What should you check before using a portable electronic leak detector?


That it suits the refrigerant and has been checked as the manufacturer requires
That it has been zeroed close to the suspected leak point
That it holds a valid UDT inspection certificate
That it has an infrared sensor, as only this type is permitted

152

Közepes

Which certificate types (A1, A2, B, C, D, E) authorise leak checks of equipment containing F-gases?


Only A1 and A2
A1, A2 and E
Only E
All except D

153

Nehéz

Within what timeframe must a leak test be carried out on a stationary refrigeration system after a leak has been repaired, in accordance with EU Regulation 2024/573 on F-gases?


At any time.
Between 24 hours and 1 month after the repair.
Immediately after the repair.
At the next periodic inspection.

154

Nehéz

How often must refrigeration equipment containing ≥500 t CO₂ eq of F-gases be checked if (contrary to Article 6) no leakage detection system is installed?


Every 12 months
Every 6 months
Every 3 months
Every month

155

Közepes

Why is it advisable to subcool the liquid refrigerant?


To allow a smaller expansion valve to be used
To ensure that liquid free of vapour bubbles enters the expansion valve
To lower the evaporating temperature in the evaporator
To allow a condenser with a smaller heat-exchange surface to be used

156

Közepes

What must be done after repairing a leak in the refrigeration unit of a refrigerated trailer?


Issue the invoice and leave the leak check to the next periodic service
Charge an alternative refrigerant, start up and measure the parameters
Visually inspect only the bolted and brazed joints near the repair
Update the equipment records and carry out a leak check (it may be done directly after repair)

157

Közepes

Recovery of fluorinated greenhouse gases means:


The reprocessing of fluorinated greenhouse gases to achieve their specified standard properties.
The reuse of fluorinated greenhouse gases following a basic purification process.
The final decommissioning and withdrawal from service or use of a product or piece of equipment containing fluorinated greenhouse gases.
The collection and storage of fluorinated greenhouse gases from containers, products and equipment during maintenance or servicing or prior to their disposal.

158

Közepes

Who is authorised to recover refrigerant from stationary refrigeration equipment containing F-gases?


A natural person holding a certificate of the relevant type (A1; A2. or D within their charge limit)
The operator
The owner of the installation
The administrator of the operator's account in the register

159

Közepes

How must recovered refrigerants be stored?


In any used refrigerant cylinder, provided it is leak-tight
In a labelled recovery cylinder with a dual valve and a valid inspection
In any pressure vessel that has some form of approval
In a disposable (non-refillable) cylinder that held the same refrigerant

160

Közepes

When should the recovery of fluorinated greenhouse gases be carried out:


Before each leak test of the equipment.
Before the final disposal of equipment and, where applicable, during its servicing and maintenance.
Always during servicing and maintenance of equipment.
Only prior to the final disposal of equipment.

161

Közepes

What should be done if recovered refrigerant is contaminated (e.g. with acid, air or moisture)?


Add a special contaminant neutraliser
Hand it over to a specialised, authorised company for reclamation or destruction
Clean the mixture yourself using a filter-drier
Pass it through a particle filter and reuse it

162

Közepes

What should be done if different refrigerants have been mixed in a storage cylinder?


Pass it through a filter-drier and reuse it
Separate the mixture into its components yourself
Add a special refrigerant to the mixture
Hand the mixture over to an authorised company – as a rule for destruction

163

Közepes

How does push-pull refrigerant recovery work?


Nitrogen is injected into the system, pushing the refrigerant into the atmosphere
The recovery unit draws vapour from the system and condenses it in the cylinder
The recovery unit draws vapour from the recovery cylinder and pushes it into the system; the pressure difference forces liquid refrigerant out of the system into the cylinder
Refrigerant is drawn alternately from the suction and discharge sides of the compressor

164

Közepes

What are the options for managing waste refrigerant?


Recovery, disposal
Disposal, storage
Reclamation, recovery
Recycling, reclamation, destruction

165

Közepes

Which management option restores recovered refrigerant to a quality equivalent to virgin product, so that it can be used by any undertaking?


Storage
Reclamation
Destruction
Recycling

166

Közepes

The lower the evaporating temperature, …


…the greater the density of the suction vapour and the lower the refrigerant mass flow rate
…the lower the density of the suction vapour and the lower the refrigerant mass flow rate
…the lower the density of the suction vapour and the greater the cooling capacity of the compressor
…the greater the density of the suction vapour and the greater the refrigerant mass flow rate

167

Közepes

How must transportable pressure vessels (e.g. refrigerant cylinders) be marked?


Among other things: the number of the design and testing standard, marks of the approving country and the inspection body, the date of the initial inspection, and the manufacturer's and operational marks
With the manufacturer's logo and date of manufacture
The marking is optional
Only with weight and capacity marks

168

Közepes

The recovery of refrigerants does not require the use of:


Hoses with shut-off valves.
An electronic leak detector.
A refrigerant recovery station.
Scales with a measurement range suitable for the size of the cylinder being filled.

169

Közepes

What functions does the compressor perform in a refrigeration system?


The compressor compresses ambient air and increases the pressure of the refrigerant.
The compressor draws in refrigerant vapour from the evaporator, compresses it, and then forces it into the condenser, raising the pressure to the required condensing pressure.
The compressor creates a vacuum on the suction side of the system
The compressor condenses the refrigerant.

170

Könnyű

What is the compression ratio of a compressor?


The ratio of suction pressure to discharge pressure (po/pc)
The amount of refrigerant compressed per cycle relative to heat capacity
The ratio of discharge pressure to the effective capacity of the compressor (p/Vk)
The ratio of absolute discharge pressure to absolute suction pressure (pc/po)

171

Közepes

What is compressor flooding (liquid slugging)?


Excess oil in the condenser
A large amount of liquid refrigerant in a flooded evaporator, which is a normal operating condition
Liquid refrigerant or oil entering the compression chamber
Flooding of the compressor by rainwater

172

Közepes

Within what range is the compressor motor speed typically controlled using a frequency inverter?


By a maximum of 10%
From approximately 10% to 90% of nominal capacity
Approximately 30 to 75 Hz, corresponding to about 60–150% of nominal capacity (depending on the compressor manufacturer)
Speed control does not change the cooling capacity

173

Könnyű

What is the theoretical displacement (swept volume flow) of a compressor?


The volume of vapour drawn in per unit of time, determined by the compressor's geometry and speed (stated by the manufacturer, e.g. in m³/h)
A value expressed by the coefficient of performance (COP)
The volume of a single cylinder in cm³
The volume of refrigerant flowing in one piston cycle under actual operating conditions

174

Közepes

Why is it essential to observe the correct phase sequence for scroll compressors and screw compressors?


Because changing the phase sequence would reverse the direction of rotation of the compressor rotors, which could result in damage to the compressors.
Because these types of compressors are sensitive to voltage drops.
Because the motor speed would decrease, and consequently the compressor’s capacity.
Because this type of compressor has difficulty starting up if the phase sequence is changed.

175

Közepes

What compression ratio should each stage of a two-stage vapour-compression system have (rule of thumb)?


Equal to 1
Less than approximately 8
Greater than 10
Greater than 18

176

Közepes

Why is a shaft seal necessary in open-type compressors?


To prevent air from entering and refrigerant from leaking out of the compressor
To protect the crankshaft bearing
Only to prevent oil leakage
To ensure the bearing remains lubricated

177

Közepes

How can you check whether the liquid refrigerant is sufficiently subcooled?


Check whether the liquid distributor upstream of the evaporator feels warm
Check by touch whether the condenser outlet is noticeably colder than ambient
Compare the liquid-line temperature with the saturation temperature at the measured condensing pressure
Check whether the whole evaporator surface is covered with an even layer of frost

178

Közepes

Why is the compressor crankcase heated?


To dehydrate the oil
To keep the lubricating oil liquid
To increase dissolution of refrigerant in the oil and improve its viscosity
To limit refrigerant migration into, and dissolution in, the oil during standstill

179

Könnyű

What is the clearance (dead) volume of a reciprocating compressor?


The space between the side of the piston and the cylinder
The space between the underside of the piston and the crankcase cover
The volume between the valve plate and the piston at bottom dead centre
The volume between the valve plate and the piston crown at top dead centre

180

Közepes

What are compressor packs (racks)?


Several air-cooled condensers
Sets of compressors connected in any configuration
Units with two-stage compressors
Several compressors connected in parallel on a common frame with common suction and discharge headers

181

Közepes

What is the main advantage of multi-compressor packs?


A smaller refrigerant charge than a single-compressor system
No need for compressor controls and safety devices
Low purchase cost and easy installation without special controls
Stepwise capacity matching to demand, plus redundancy

182

Közepes

What is meant by the operating envelope (application range) of a compressor?


The capacity, refrigerant type and dimensions of the compressor
A range determined by the evaporating temperature at a given ambient temperature
The permissible range of evaporating and condensing temperatures (to, tk), or the corresponding pressures, within which the compressor may operate
A range determined only by the evaporating temperature

183

Közepes

What are the basic functions of oil in a compressor?


Increasing the cooling capacity of the refrigerant
Sealing leaks that develop in the installation
Lubricating bearings and sliding surfaces, removing heat, and sealing clearances (e.g. between piston and cylinder, or rotors)
Absorbing moisture from the refrigerant

184

Közepes

What are the most effective ways of controlling compressor cooling capacity?


Changing the displacement: varying the rotational speed or unloading cylinders
An expansion valve
Partially covering the evaporator
Pressure control valves

185

Közepes

What does hot-gas bypass capacity control involve?


High-pressure liquid is injected into the suction to increase capacity
Part of the hot discharge gas is passed through a bypass valve to the suction side (or evaporator inlet), reducing the effective capacity
Bypass is not used for capacity control
The compressor speed is varied

186

Közepes

What is the fundamental difference between hermetic and semi-hermetic compressors?


The semi-hermetic compressor has no motor inside the casing
Both can be dismantled; they differ only in cooling capacity
The semi-hermetic casing is bolted (can be opened); the hermetic one is welded
Semi-hermetic compressors run more quietly as a complete unit

187

Közepes

How does a scroll compressor work?


A scroll compressor is also known as a turbo compressor.
It is a positive-displacement compressor in which compression results from the interaction of a fixed and an orbiting scroll.
It is a type of piston-type device.
It uses two screws to compress the refrigerant.

188

Közepes

What physical process takes place in the evaporator?


The secondary fluid (glycol, water) evaporates while the refrigerant condenses
The refrigerant condenses
The refrigerant is subcooled as a liquid
The liquid refrigerant evaporates, absorbing heat, and the vapour is slightly superheated at the outlet

189

Közepes

What is the purpose of compressor capacity control?


To match the cooling capacity to the current demand
To ensure compressor lubrication
To match capacity to the condensing temperature
To increase the condensing pressure

190

Közepes

Why is inverter speed control advantageous for refrigeration compressors?


Reducing the speed improves oil return to the compressor
It enables continuous, smooth control of cooling capacity
It increases compressor capacity above nominal at any frequency
It can be used with any compressor to ensure lubrication

191

Közepes

Does the suction gas temperature affect the cooling capacity of the compressor?


Yes – higher temperature lowers vapour density, mass flow and capacity
Yes, but only in reciprocating compressors, not scroll
No – capacity depends only on the compressor displacement
Yes, but only if the suction gas is deeply cooled

192

Közepes

In the case of compressor units fitted with an oil level control system, is it necessary to install the compressors at the same height?


No.
Yes.
Only screw compressors.
Only scroll compressors.

193

Közepes

What functions does a compressor powered by the vehicle’s engine perform in a transport refrigeration system?


This compressor condenses the refrigerant whilst the vehicle is in motion.
This compressor draws in refrigerant vapour from the evaporator, compresses it and then forces it into the condenser whilst the vehicle’s engine is running.
The compressor compresses ambient air and increases the pressure of the refrigerant.
This compressor creates a vacuum on the suction side of the system whilst the vehicle’s engine is switched off.

194

Közepes

Which media most commonly absorb heat from the refrigerant in the condenser?


Air and CO₂
Only a water–glycol mixture
Air or water
Ammonia

195

Közepes

What is the function of the condenser in refrigeration systems?


Releasing to the environment the heat absorbed in the evaporator and the heat added during compression
Absorption of heat rejected in the regenerative heat exchanger
Releasing only the heat from the compressor into the surroundings
Releasing only the heat absorbed in the evaporator into the surroundings

196

Közepes

If the refrigerant temperature on the high-pressure side is above its critical temperature, condensation…


…always occurs regardless of temperature
…occurs provided a special condenser is used
…does not occur
…does not depend on temperature

197

Közepes

How is liquid subcooling usually achieved in a refrigeration system?


In the final section of the condenser (or in an additional subcooler)
With an additional heat exchanger using liquid nitrogen
By dissolving the refrigerant in oil
With hot high-pressure vapour

198

Közepes

What is the purpose of condenser fan speed control?


To reduce energy efficiency
Only to protect against exceeding the maximum condensing pressure
To disperse refrigerant in the event of a leak
To keep the condensing pressure at the correct level

199

Közepes

Which international agreement introduced the global phase-down of HFC production and consumption?


The Kyoto Protocol
The Vienna Convention for the Protection of the Ozone Layer
The Kigali Amendment to the Montreal Protocol
The Paris Agreement

200

Közepes

Which international treaty governs the phase-out of ozone-depleting substances (CFCs, HCFCs)?


The Paris Agreement
The Stockholm Convention
The UN Framework Convention on Climate Change (UNFCCC)
The Montreal Protocol

201

Nehéz

What is the basis of the GWP values in Regulation (EU) 2024/573?


For HFCs (Annex I) – mainly the IPCC Fourth Assessment Report (AR4); for HFOs and non-fluorinated substances (Annexes II and VI) – the Sixth Assessment Report (AR6)
Each Member State sets its own GWP values
AR6 for all substances
AR4 for all substances

202

Nehéz

An air conditioner (not hermetically sealed) contains 2.5 kg of R410A (GWP 2088). How often must it be checked for leaks?


Every 3 months
At least every 12 months (5.22 t CO₂ eq)
No checks required (below 3 kg)
Every 6 months

203

Nehéz

When is labelled hermetically sealed equipment containing HFCs (Annex I) exempt from leak checks?


Never – hermetically sealed equipment is always checked
When it contains less than 5 t CO₂ eq
Always, regardless of charge
When it contains less than 10 t CO₂ eq, and in residential buildings also when it contains less than 3 kg of F-gases

204

Nehéz

Is a chiller containing 50 kg of R1234ze(E) subject to leak checks under Regulation (EU) 2024/573?


Yes – every 12 months, because its GWP is low
No – HFOs are not subject to leak checks
No – the threshold is 5 t CO₂ eq and 50 kg of R1234ze is below 1 t CO₂ eq
Yes – at least every 6 months (every 12 months with a leakage detection system)

205

Nehéz

In 2026, may an existing refrigeration installation using R404A (GWP 3922) be topped up with virgin refrigerant?


Yes, if the equipment has a leakage detection system
Yes – bans apply only to new equipment
No – only reclaimed or recycled R404A is allowed (until 1 January 2030)
Yes – the ban applies only to equipment ≥40 t CO₂ eq

206

Nehéz

After 1 January 2026, may an R410A (GWP 2088) air conditioner be serviced using virgin R410A?


No – the ban covers all HFCs
Only with reclaimed refrigerant
Yes – the servicing ban for air conditioners and heat pumps covers F-gases with GWP ≥ 2500
No – the ban covers all refrigerants with GWP ≥ 750

207

Közepes

Can HFC refrigerant recovered during a repair be put straight back into the same equipment without any cleaning (filtering/drying)?


Yes, if the operator agrees
Yes, always
Yes, if less than 24 hours have passed
No – recovered F-gas may be used for filling only after it has been recycled or reclaimed

208

Közepes

Who may purchase HFCs for servicing refrigeration equipment?


Only the equipment operator
Only a person holding the relevant certificate or an undertaking employing such persons
Any business
Any adult

209

Közepes

Under what condition may non-hermetically sealed split air conditioning charged with F-gas be sold to an end user?


When the user signs a statement that they will install it themselves
Only if the unit contains less than 3 kg of refrigerant
When evidence is provided that installation will be carried out by a certified undertaking
Unconditionally

210

Közepes

By when must the holder of an F-gas certificate issued under Regulation (EU) No 517/2014 first complete refresher training or an evaluation process?


By 31 December 2030
By 12 March 2025
Never – the certificate is valid indefinitely
By 12 March 2029 (and then at least every 7 years)

211

Közepes

What must the holder of a Category I certificate (Regulation 2015/2067) do to continue using it?


Apply for an extension without training
Nothing – Category I automatically becomes A1
Update their knowledge to the level of Certificate E
Update their knowledge and skills to the level of Certificate A1 (Annex I to Regulation 2024/2215)

212

Közepes

What does Certificate C under Implementing Regulation (EU) 2024/2215 authorise?


All activities in Article 2(1) in relation to ammonia (NH₃)
All activities in relation to CO₂
Recovery of F-gases from equipment <3 kg
Leak checks without breaking into the circuit

213

Közepes

May a person enrolled in a certification training course carry out certified activities?


Yes – with no time limit, if employed by a certified company
Yes – independently, for 6 months
Yes – under the supervision of a certified person, for no more than 24 months in total
No, never

214

Közepes

How long must the operator keep the records of equipment subject to leak checks, if they are not kept in a national database?


At least 1 year
At least 5 years
Until the equipment is decommissioned
At least 2 years

215

Nehéz

Since 1 January 2025, may a new single-split air conditioner containing 1.5 kg of R410A be placed on the market?


Yes, if the unit is hermetically sealed
No – single splits <3 kg with F-gases of GWP ≥ 750 are banned
Yes – the ban applies from 2029
Yes – the ban applies only to units >12 kW

216

Nehéz

From when is it prohibited to place on the market split air-to-air systems up to 12 kW containing F-gases with GWP ≥150 (unless required for safety)?


From 1 January 2029
From 1 January 2027
From 1 January 2035
From 1 January 2025

217

Nehéz

Which persistent atmospheric degradation product of R1234yf is classed as a PFAS?


Ozone
Trifluoroacetic acid (TFA)
Carbonic acid
Carbon dioxide

218

Közepes

What is floating head pressure and what does it achieve?


It keeps a constant high condensing pressure all year
It lets the condensing pressure fall with ambient temperature, reducing compressor work and raising COP (requires an expansion valve that works at a small pressure difference)
It increases subcooling by flooding the condenser
It means switching condenser fans off periodically

219

Közepes

How do SEER/SCOP differ from EER/COP?


SEER/SCOP are seasonal indicators accounting for part load and climate (EN 14825); EER/COP refer to a single operating point (EN 14511)
SEER/SCOP apply only to natural-refrigerant equipment
EER/COP are always higher than SEER/SCOP
There is no difference – they are synonyms

220

Közepes

Which design approach can significantly reduce the F-gas charge of a large refrigeration installation?


Adding a second liquid receiver
An indirect (secondary-coolant) system or a cascade with a natural refrigerant in the low stage, plus heat exchangers with small internal volume
Omitting pipe insulation
Larger liquid-line diameters

221

Közepes

Which information must be entered in the equipment records after a leak check?


Only the operator's signature
The date and result of the check and the identity of the undertaking and person who performed it (with certificate number)
Only the equipment's energy consumption
Only the date of the check

222

Közepes

What must be done when an indirect method (e.g. parameter analysis) indicates a possible leak?


Record it and check at the next periodic inspection
Top up the refrigerant and end the check
Nothing – indirect methods are sufficient
Carry out a direct-method examination to locate the leak