1

Könnyű

What is the base unit of mass in the International System of Units (SI)?


t
N
lb (pound)
kg

2

Közepes

What process takes place in the condenser of a refrigeration system?


The secondary fluid (glycol, water) condenses while the refrigerant evaporates
Hot vapour discharged by the compressor is desuperheated, condensed, and the resulting liquid is slightly subcooled
The refrigerant rejects only the heat generated in the compressor
The refrigerant absorbs heat from the surroundings and evaporates

3

Közepes

What mainly determines the condensing temperature of an air-cooled condenser?


The evaporating temperature
The compressor discharge temperature
The superheat
The ambient (inlet) air temperature

4

Közepes

Why does heat flow from the condenser to the surroundings?


Because HFC refrigerants attract heat from the surroundings
Because the pressure in the condenser is lower than ambient
Because the condensing temperature is higher than the ambient temperature, and heat flows spontaneously from a warmer to a colder body (second law of thermodynamics)
Because the compressor pushes heat directly into the surroundings

5

Közepes

What should you mainly pay attention to when operating a condenser?


That the outlet air temperature is higher than the condensing temperature
Its general condition and the cleanliness of the heat-exchange surfaces
The colour of the condenser casing
That the inlet air temperature is lower than the outlet air temperature

6

Közepes

What criteria should be considered when selecting a suitable condenser?


Fan noise, connection diameters and colour
Only the size and number of fans
The required capacity of the condenser and the technical specifications declared by the manufacturer
Only own experience and the dimensions

7

Közepes

How do contaminants (dust, particulates, deposits) affect the performance and efficiency of heat exchange surfaces in condensers?


Contaminants do not significantly affect the efficiency and effectiveness of the heat exchange surfaces in condensers.
Contaminants restrict heat transfer (reducing the heat transfer coefficient) and cause a reduction in condensing pressure.
Contaminants restrict heat transfer (reducing the heat transfer coefficient) and cause an increase in condensing temperature and pressure, which in turn leads to a reduction in the condenser’s efficiency.
Contaminants increase the heat transfer area and reduce the condensing pressure.

8

Közepes

How does the capacity of an air-cooled condenser change when it becomes dirty?


It increases because the fan speed rises
It decreases
It increases
It remains unchanged

9

Közepes

What is the main consequence of heavy frost on an air-cooling evaporator?


A rise in the cooled-air temperature with no effect on capacity
Reduced heat transfer and airflow, resulting in a drop in cooling capacity and evaporating temperature
A rise in evaporating pressure
An increase in condenser subcooling

10

Közepes

What happens when the evaporation temperature drops?


The discharge temperature decreases.
The compressor’s cooling capacity decreases.
The condenser fan speed increases.
The compressor’s cooling capacity increases.

11

Közepes

When is natural (off-cycle, air) defrosting possible?


Only in coolers fitted with speed-controlled fans
Never – electric heaters must be used in every air cooler
Only in freezer rooms below −18 °C
When the air passing through the cooler is above 0 °C

12

Közepes

When does frost form on the surface of an air-cooling evaporator?


Always, in every air cooler
When the evaporator surface temperature is below 0 °C and below the dew point of the air
Only when the system runs continuously
Only when the room air temperature falls below 0 °C

13

Közepes

In extensive pipework systems, flash gas (secondary evaporation) in the liquid line can be prevented by…


…using smaller-diameter pipes
…additional subcooling of the liquid
…increasing the length of the liquid line
…insulating the discharge line between the compressor and the condenser

14

Közepes

How does hot gas defrosting of the evaporator work?


We swap the outlet and inlet sides of the evaporator.
Heated vapour (hot gas) from the compressor is directed into the evaporator piping.
We switch on the gas heater directed at the evaporator.
This involves reversing the direction of rotation of the compressor.

15

Közepes

What is the function of the evaporator in a refrigeration system?


It evaporates the water flowing through the evaporator.
It ensures that the refrigerant is superheated over the largest possible heat exchange surface area.
It transfers heat from the medium being cooled to the boiling refrigerant.
It cools the refrigerant.

16

Közepes

What condition must electric heaters for evaporator defrosting meet?


They must have good thermal contact with the heat-exchange surface (e.g. inserted in the fin block)
They must be located beneath the evaporator
Heat from the heaters must be carried by the running fans
They must be in direct contact with the refrigerant

17

Közepes

Refrigerant distributor:


ensures an even distribution of the refrigerant to the individual sections of the evaporator.
acts as a buffer for the refrigerant in the event that the pressure upstream of the expansion valve is exceeded.
ensures the even distribution of the refrigerant discharged by compressors connected in parallel.
ensures even distribution of the refrigerant to the individual sections of the condenser.

18

Közepes

What defrosting methods are used for air coolers?


Electric only – other methods are not permitted in refrigeration
Natural only – other methods are ineffective and uneconomic
Electric, hot gas, water spray and natural (at positive temperatures)
Only by switching off the fans with the compressor running

19

Közepes

The boiling point of a liquid rises when the pressure above the liquid…


…varies depending on the ambient temperature
…rises
…remains constant
…falls

20

Közepes

MOP in thermostatic expansion valves stands for:


minimum flow opening.
maximum operating pressure.
self-cleaning of the valve in the event of moisture in the refrigerant freezing.
maximum pressure switch protection.

21

Közepes

The function of a thermostatic expansion valve (TEV) is:


to maintain a constant condensing pressure
to maintain a constant compressor suction pressure
to adjust the evaporating pressure in the condenser
to meter refrigerant into the evaporator according to the superheat of the vapour leaving the evaporator

22

Közepes

What type of compressor motor can be used with a capillary tube?


A low-starting-torque motor (pressures equalise during standstill)
A low-speed motor
A high-starting-torque motor must be used
An electronically commutated motor

23

Közepes

What does a thermostatic expansion valve control?


The temperature in the cold room
The condensing pressure
The mass flow of refrigerant fed into the evaporator
The discharge temperature

24

Könnyű

The refrigerant absorbs heat when…


…it freezes
…it evaporates
…it is subcooled
…it condenses

25

Közepes

What does the manufacturer state as the factory setting of a thermostatic expansion valve?


the degree of refrigerant expansion.
the superheat value during valve operation.
the degree to which the valve is filled with refrigerant liquid.
the static superheat of the valve.

26

Közepes

Where is a new or repaired system with an expansion valve and liquid receiver charged?


Through the capillary tube outlet during normal system operation
Anywhere – the charging point does not matter
In the liquid phase on the high-pressure side, with the compressor stopped
In the liquid phase into the compressor suction, with the compressor running

27

Közepes

What does a thermostatic or electronic expansion valve control?


Subcooling, by adjusting condensing pressure
The amount of refrigerant fed to the evaporator according to superheat
The compressor speed
The evaporating pressure – closing below the set point

28

Közepes

What does the MOP function of thermostatic expansion valves mean?


The valve prevents motor overheating by injecting liquid into the compressor
The valve maintains a constant condensing pressure
The valve limits subcooling
The valve limits the maximum evaporating (suction) pressure, protecting the compressor motor from overload, e.g. after defrost

29

Közepes

The lower the liquid temperature upstream of the expansion valve, (at the same mass flow)…


…the lower qo and the lower Qo
…the higher the specific refrigerating effect qo [kJ/kg] and the higher the cooling capacity Qo
…the lower qo, with Qo unchanged
…the lower qo and the lower energy efficiency

30

Közepes

How should the MOP point of an expansion valve be selected relative to the highest normal evaporating temperature?


About 7 K lower than that temperature
A few kelvin higher (approximately 7 K)
Freely – the MOP value is irrelevant
Higher by approx. 20 K

31

Közepes

What is the function of the suction pressure regulator?


It prevents a drop in suction pressure and, if necessary, shuts down the refrigeration system.
To maintain the suction pressure at the highest possible level.
It limits the suction pressure and protects the compressor from excessively high suction pressure.
It maintains the evaporation pressure at a constant level.

32

Közepes

What is the function of the valve regulating water flow through the condenser?


To maintain the water temperature at the highest level.
To maintain the condensing pressure at a constant level.
To maintain the condensing pressure at the lowest possible level.
To maintain the condensing pressure at the highest possible level.

33

Közepes

The use of a refrigerant distributor requires a thermostatic expansion valve ...


... with external pressure equalisation.
... with internal pressure equalisation.
... with a MOP function.
... with an adsorption-type sensor filling.

34

Közepes

What properties should good insulation materials have?


Low thermal conductivity (and low water absorption, vapour tightness)
An antistatic coating
The ability to absorb large amounts of moisture
High thermal conductivity

35

Közepes

When is refrigerant vapour superheated?


When the compressor motor temperature rises excessively
When the evaporating temperature is lower than the ambient temperature
When the pressure on the discharge side is higher than on the suction side
When its temperature is higher than the saturation temperature corresponding to its pressure

36

Közepes

How can you check whether the liquid refrigerant is reaching the expansion valve without vapour bubbles?


We check using a pressure gauge fitted on the discharge side of the compressor.
We check using a liquid pressure gauge.
We are unable to check this.
We check this using a sight glass.

37

Közepes

Where does the liquid line run?


Between the evaporator and the compressor
Between the evaporator and the suction-line heat exchanger
From the condenser (liquid receiver) to the expansion valve
Between the compressor and the condenser

38

Közepes

What is the function of the liquid receiver in a refrigeration system?


To act as a reserve when the required charge is unknown
To store refrigerant and compensate for changes in the circulating charge as the heat load varies
To collect liquid refrigerant and excess oil
To further subcool the condensed refrigerant

39

Közepes

What is the purpose of the liquid receiver during service work?


It further subcools the refrigerant before the expansion valve
It collects excess oil circulating in the system
It allows pump-down and temporary storage of the refrigerant
It is a reserve when the installer does not know the required charge

40

Közepes

Where should the liquid receiver be installed?


It should be fitted just before the compressor.
It should be installed downstream of the condenser, upstream of the expansion valve.
It should be fitted after the evaporator.
It should be fitted between the compressor and the condenser.

41

Közepes

What is the function of the suction pressure regulator fitted to the suction pipe when the compressor starts up?


It regulates the condensing pressure.
It regulates the evaporation pressure.
It closes when the suction pressure upstream of the compressor drops.
It opens when the suction pressure upstream of the compressor drops.

42

Közepes

The use of microchannel heat exchangers, compared with conventional heat exchangers made of copper tubes and fins, results in:


A reduction in the system’s energy efficiency.
An increase in the amount of refrigerant in the system and an increase in condensing pressure.
A reduction in refrigerant charge and, typically, higher energy efficiency.
There is no effect whatsoever on either the amount of refrigerant or energy efficiency.

43

Közepes

Which refrigerants belong to the HFC group?


R134a, R32, R22, R507A, R290.
R11, R12, R502.
R22, R401A.
R134a, R404A, R507A, R410A.

44

Közepes

Which refrigerants belong to the HFO group?


R1234yf, R1234ze(E).
R22, R12.
R134a, R290.
R134a, R404A.

45

Közepes

What are the characteristics of R410A refrigerant compared to R407C refrigerant?


The saturation pressure of R410A refrigerant is higher than that of R407C.
The saturation pressure of both refrigerants is roughly the same.
The saturation pressure of R407C refrigerant is much higher than that of R410A.
The saturation pressure of R407C is 150% higher than that of R410A.

46

Közepes

What does the TEWI indicator define?


The impact of a refrigerant on the ozone layer
The ability of the ozone layer to recover
The global warming potential of a gas relative to CO₂ over a 100-year horizon
Total Equivalent Warming Impact: the sum of direct emissions (leakage and refrigerant losses at disposal) and indirect emissions (CO₂ from generating the energy consumed by the equipment) over its lifetime

47

Közepes

What are the characteristics of R452A compared with R404A?


It is a non-flammable (A1) HFC/HFO blend with properties similar to R404A and a GWP about 45% lower
The temperature glide of R452A is half that of R404A
Both are azeotropic and have no temperature glide
It is a flammable and toxic single-component HFC

48

Közepes

What distinguishes R1234yf from R134a?


A higher normal boiling point
A higher critical temperature
Higher toxicity
It is mildly flammable (class A2L), whereas R134a is non-flammable (A1)

49

Közepes

How does CO₂ (R744) compare with R134a?


Its temperature glide is 7 K greater than that of R134a
Unlike R134a, it is an azeotropic mixture
It has identical properties and is a drop-in replacement for R134a
It has a lower critical temperature, much higher operating pressures and a much higher volumetric cooling capacity (smaller compressors and pipes)

50

Közepes

Which of the following is NOT a fluorinated greenhouse gas?


Perfluorocarbons (PFCs).
Carbon dioxide (CO₂).
Sulphur hexafluoride (SF6).
Hydrofluorocarbons (HFCs).

51

Közepes

What is the greenhouse effect?


Dust in the atmosphere reflects sunlight, lowering the average surface temperature
Chlorine compounds destroy stratospheric ozone, increasing UV radiation at the surface
Greenhouse gases absorb and re-emit the Earth's infrared radiation, warming the lower atmosphere
Clouds reflect ultraviolet radiation, which makes the air near the surface warmer

52

Könnyű

What does the GWP indicator mean?


The annual rise in mean air temperature caused by the emission of 1 kg of the gas
The ability of a substance to restore the ozone layer
Global Warming Potential: the climate warming impact of 1 kg of a gas compared with 1 kg of CO₂ (GWP = 1) over a defined time horizon, usually 100 years
Ozone depletion potential

53

Közepes

How do refrigeration systems contribute to the greenhouse effect?


Indirectly (through energy consumption) and directly (through emissions of refrigerant into the atmosphere)
Only through the heat rejected by the condenser
Through oil emitted into the atmosphere from the condenser and filter
Only through CO₂ given off by the compressor motor

54

Közepes

What is the greenhouse effect?


The trapping of heat in the Earth's atmosphere, which hinders the radiation of heat into space
The filtering of solar radiation by the atmosphere
The formation of a layer that traps only heat from fuel combustion in aircraft
The absorption of solar radiation by the Earth's surface

55

Közepes

Which EU regulation is currently the primary piece of legislation governing the use of fluorinated greenhouse gases (F-gases) in the European Union?


Regulation (EU) 2015/1188
Directive 2009/125/EC
Regulation (EU) 2024/573
Regulation (EU) No 517/2014

56

Közepes

What is the main objective of Regulation (EU) 2024/573?


Prevention of F-gas emissions and the achievement of the EU’s climate targets
To reduce taxes on refrigeration equipment
Standardising metal recycling standards
To facilitate the import of electrical appliances

57

Közepes

What are the ecodesign obligations of manufacturers of refrigerating appliances?


Only using energy labels under Regulation (EU) 2024/573
Only declaring F-gas quantities under Regulation (EU) No 517/2014
Only implementing an ISO 9001 quality management system
Meeting implementing regulations (e.g. 2019/2019, 2015/1095): efficiency, spare parts, reparability

58

Közepes

What is the main objective of EU ecodesign legislation (Directive 2009/125/EC, now Regulation (EU) 2024/1781 – ESPR)?


To increase sales of electrical appliances in the EU
To standardise the appearance of products in the EU
To reduce the negative environmental impact of products by improving energy efficiency, durability and recyclability
To facilitate imports from outside the EU

59

Közepes

What is the function of a ball valve in a refrigeration system?


It measures the moisture content of the refrigerant
It regulates the temperature of the refrigerant
It prevents excessive pressure build-up in the system
Enables the refrigerant flow to be completely shut off

60

Könnyű

What is the main function of a safety valve?


It monitors the moisture content of the refrigerant
Prevents the evaporator from freezing
Discharges refrigerant when the set pressure is exceeded
It controls the oil level in the compressor

61

Közepes

How do certain gases contribute to the greenhouse effect?


They deplete the ozone layer, so more solar radiation reaches the surface
They trap thermal radiation that the Earth would otherwise emit into space
They heat the air through chemical reactions with atmospheric oxygen and nitrogen
They limit UV radiation reaching the Earth's surface, changing the heat balance

62

Közepes

What is the purpose of a sight glass (with moisture indicator)?


Visual assessment of the refrigerant condition in the liquid line (bubbles) and of system moisture
Emergency shut-off of flow
Measuring condenser temperature
Regulating compressor pressure

63

Közepes

What is the function of the temperature regulator in a refrigeration system?


It drains excess refrigerant into the receiver
To maintain a constant pressure in the compressor
Controls the operation of the compressor and valves to maintain the set temperature
It restricts oil flow

64

Nehéz

What is the role of a suction liquid separator (also in systems with flammable or toxic refrigerants)?


It separates liquid from oil
It is used only to measure moisture
It heats the refrigerant before the evaporator
It prevents liquid refrigerant from entering the compressor

65

Nehéz

What is the function of an oil separator in systems using flammable or toxic refrigerants?


They are used solely to measure the moisture content of the refrigerant
Separates oil from the refrigerant and facilitates the return of oil to the compressor
It prevents liquid from entering the compressor
Heats the refrigerant before it enters the evaporator

66

Közepes

What is the purpose of oil level regulators in a refrigeration system?


They control the evaporator temperature
They drain off excess refrigerant
Maintains the correct oil level in the compressor
They control the pressure in the condenser

67

Közepes

What is the function of the liquid receiver in relation to system tightness?


It controls the evaporating temperature by varying the circulating charge
It keeps the whole system at constant pressure regardless of load
It regulates the oil returning to the compressor
It stores refrigerant; checking its liquid level helps detect charge loss

68

Közepes

What is the role of a gauge manifold with thermometers (temperature probes)?


It relieves pressure if it is exceeded
It measures pressures and temperatures to determine superheat and subcooling and thus assess the system charge (indirect leak check)
It controls oil level
It monitors refrigerant moisture content

69

Közepes

What is the role of defrost controls?


They control compressor discharge pressure during defrost
They drain excess oil from the evaporator to the receiver
They protect the evaporator from icing and damage that could lead to leaks
They monitor the moisture content of the refrigerant

70

Könnyű

What is the unit of pressure in the International System of Units (SI)?


atm (standard atmosphere)
bar (gauge)
psi (pound per square inch)
Pa (pascal)

71

Közepes

Where can the lists of fluorinated greenhouse gases be found?


In the Vienna Convention for the Protection of the Ozone Layer
In Annexes I–III to Regulation (EU) 2024/573 of the European Parliament and of the Council
In a regulation of the Minister of Economy on the list of fluorinated greenhouse gases
In the national Act on ozone-depleting substances and certain fluorinated greenhouse gases

72

Közepes

Where can the lists of ozone-depleting substances be found?


In a regulation of the Minister of the Environment on the list of controlled substances
In the Vienna Convention for the Protection of the Ozone Layer
In the national Act on ozone-depleting substances and certain fluorinated greenhouse gases
In Annexes I and II to Regulation (EU) 2024/590 of the European Parliament and of the Council

73

Nehéz

Why are PFAS formed by the decomposition of certain F-gases (e.g. TFA from HFOs) problematic?


They are climate- and environment-neutral
They are very persistent, accumulate in the environment (e.g. water) and may be toxic
They cause rapid cooling of the atmosphere
They are readily biodegradable

74

Közepes

Where and by when must entities obliged under the Polish Act of 15 May 2015 submit annual reports on ODS and F-gases?


By 28 February of the following year, electronically via the Reports Database (BDS) run at the Institute of Industrial Chemistry (ICHP)
By the end of the calendar year, on a form at a regional office of the Office of Technical Inspection (UDT)
By 31 March, electronically to the Ministry of Climate and Environment
By 31 January, in the Central Register of Operators (CRO)

75

Közepes

Which installation measure has a major impact on compressor energy efficiency?


Proper evacuation and dehydration of the system (removing air and moisture)
Installing a suction line smaller than recommended
Charging extra refrigerant 'as a reserve' above the nameplate value
Omitting the filter-drier to reduce flow resistance

76

Közepes

How does regular oil-level monitoring affect compressor operation?


It ensures proper lubrication and limits wear and energy losses
It allows the crankcase heater to be omitted
It increases cooling capacity above nominal
It allows any type of oil to be topped up

77

Könnyű

How do system leaks affect compressor energy efficiency?


They improve efficiency because condensing pressure drops
Refrigerant loss reduces capacity and increases energy use (longer run times, higher superheat)
No effect as long as the system still cools
They affect only safety, not energy use

78

Közepes

Regulation (EU) 2024/590 relates to:


Ozone-depleting substances
Alternative refrigerants replacing fluorinated greenhouse gases
Health and safety during refrigerant recovery
Conditions for F-gas certification of companies recovering and reclaiming refrigerants

79

Közepes

What is the significance of proper suction and discharge pressure control?


Pressures do not affect energy use
The lowest possible suction pressure is best
It keeps the compressor at optimal conditions (suction pressure as high and condensing pressure as low as permissible)
The highest possible condensing pressure is best

80

Közepes

Which maintenance measure reduces compressor energy consumption?


Raising the high-pressure switch setting
Replacing the filter-drier when the pressure drop or moisture indicator shows it is necessary
Topping up refrigerant at every service visit
Permanently disabling the crankcase heater

81

Közepes

How does air (non-condensable gas) in the system affect operation?


It only affects the sight-glass indication
It improves condenser heat transfer
It raises the condensing pressure and reduces efficiency
It lowers the condensing pressure

82

Közepes

What role do controls play in compressor efficiency?


They increase the circulating refrigerant charge
They enable optimised operation and lower energy use (e.g. floating head pressure, capacity matching)
They provide safety only, with no energy effect
They matter only in NH₃ systems

83

Közepes

How does suction superheat at the compressor affect efficiency?


The higher the superheat, the higher the efficiency
Excessive superheat reduces efficiency and raises the discharge temperature
Zero suction superheat is optimal
Superheat has no effect

84

Közepes

How does correct system layout affect efficiency?


It shortens pipe runs and limits pressure drops and energy losses
It affects only appearance
It doesn't matter
Longer pipes improve subcooling and always increase efficiency

85

Közepes

How important is suction pipe insulation?


It has no effect
It limits heat gain and excessive superheat, improving efficiency
It increases energy consumption
It is needed only for appearance

86

Közepes

Which measure most improves condenser energy efficiency?


Regular cleaning of heat-exchange surfaces
Increasing the refrigerant charge
Raising the condensing pressure set point
Reducing fan speed to the minimum

87

Könnyű

How does a dirty condenser affect the operation of the refrigeration system?


It improves efficiency
Causes an increase in pressure and energy consumption by the compressor
It lowers the condensing pressure
It has no effect

88

Könnyű

Why is adequate airflow through an air-cooled condenser important?


It affects only noise
The lower the airflow, the lower the condensing pressure
It doesn't matter
It ensures effective heat rejection and low condensing pressure

89

Közepes

Which refrigerants damage the ozone layer?


All refrigerants containing fluorine and hydrogen in their molecules
All refrigerants containing carbon in their molecules
All natural refrigerants
All refrigerants containing chlorine or bromine in their molecules

90

Könnyű

How does the presence of limescale in a water-cooled condenser affect performance?


It lowers the condensation temperature
It improves heat transfer
Impairs heat exchange and increases energy consumption
It has no effect

91

Közepes

How does correct condensing pressure control affect efficiency?


It keeps the lowest pressure that still ensures proper expansion-valve feed, reducing energy use
It always increases energy use
It is best to keep a constant high condensing pressure all year
It has no effect

92

Könnyű

How do condenser leaks affect energy efficiency?


Causes refrigerant loss and a drop in efficiency
Have no effect
They lower the temperature
They improve efficiency

93

Könnyű

How important is the correct positioning of an air-cooled condenser?


It should be close to heat sources
It should be housed in a small room
It should be installed in a well-ventilated area with unobstructed airflow
It doesn’t matter

94

Könnyű

How does hot air recirculation affect the condenser?


It has no effect
It reduces the pressure
It improves efficiency
Impairs cooling and increases energy consumption

95

Közepes

How does insulation of heating and DHW pipework affect the efficiency of a heat pump system?


It impairs cooling
It doesn't matter
It reduces energy losses and improves overall system efficiency
It increases pressure

96

Közepes

Which measure most improves the energy efficiency of an air-cooling evaporator?


Restricting the airflow through the evaporator
Raising the condensing temperature by a few kelvin
Increasing the refrigerant charge above nominal
Defrosting at the right time and keeping the fins clean

97

Könnyű

How does evaporator icing affect the system’s operation?


It has no effect
It improves cooling performance
It lowers the condensation temperature
Impairs heat exchange and increases energy consumption

98

Könnyű

How does dirt on the evaporator surface affect its performance?


Impairs heat exchange and increases energy consumption
It reduces the pressure
It improves efficiency
It has no effect

99

Könnyű

What maintenance task is crucial for the evaporator?


Regular cleaning and defrosting
Increasing the refrigerant charge
Lack of maintenance
Reduced airflow

100

Közepes

What does a Certificate A2 for natural persons (Implementing Regulation (EU) 2024/2215) authorise?


All activities involving equipment using CO₂ (R744)
Only leak checks that do not entail breaking into the refrigerant circuit
Only recovery of F-gases from equipment containing less than 3 kg (or 6 kg in hermetically sealed systems)
All activities (leak checks, installation, repair, maintenance, servicing, decommissioning, recovery) involving F-gases and hydrocarbons in equipment containing less than 3 kg, or less than 6 kg in labelled hermetically sealed systems

101

Könnyű

How does superheat at the evaporator outlet affect efficiency?


It always improves performance
It has no effect
It only causes a temperature drop
Excessive superheat reduces energy efficiency

102

Könnyű

How do leaks in the evaporator affect efficiency?


Improves performance
These cause refrigerant loss and a drop in efficiency
Increase capacity
Have no effect

103

Könnyű

How important is correct expansion valve adjustment?


It increases energy consumption
Ensures optimal evaporator charge and improves efficiency
It doesn’t matter
Causes leaks

104

Könnyű

How does inadequate insulation of suction (or secondary-coolant) pipes affect evaporator performance?


It lowers the condensing temperature
It has no effect
It improves efficiency
It causes cooling losses and increased energy use

105

Könnyű

How does correct TEV adjustment affect system energy efficiency?


It has no effect
It causes leaks
It increases energy use
It ensures optimal superheat and improves efficiency

106

Könnyű

What happens if the superheat set by the TEV is too high?


The refrigerant charge will increase
It has no effect
Cooling efficiency will improve
Efficiency will drop because the evaporator is not being fully utilised

107

Közepes

How does too low superheat setting on the TEV affect performance?


It increases operational safety
It reduces refrigerant flow
It has no effect
It may lead to improved efficiency, but it increases the risk of the compressor becoming flooded with liquid

108

Könnyű

How do contaminants in the system affect the operation of the TEV?


Have no effect
They can cause it to become blocked and reduce efficiency
They improve its performance
They lower the temperature

109

Könnyű

What role does the filter-drier play in terms of system efficiency?


It lowers the temperature
It doesn’t matter
It increases the amount of refrigerant
Removes moisture and contaminants, improving the system’s efficiency

110

Könnyű

How does proper insulation of components (e.g. pipes near the TEV) affect the system?


It increases energy consumption
It doesn’t matter
It causes leaks
Prevents unwanted heat gains and improves efficiency

111

Közepes

What is the scope of Regulation (EU) 2024/573?


Design requirements and conformity assessment for pressure equipment
Only requirements for periodic leak checks of refrigeration equipment
Health and safety requirements for brazing and welding on refrigeration installations
Limiting emissions, use and marketing of F-gases, HFC phase-down, certification and reporting

112

Könnyű

How important is it to check the operation of the condensing pressure control valve in the system?


It causes a significant rise in temperature
It increases energy consumption
It has no effect
Ensures operation within the optimum pressure range and reduces energy losses

113

Könnyű

How does the correct selection of a TEV affect energy efficiency?


It lowers the temperature
It increases the amount of refrigerant
Ensures the system is matched to its capacity and operates optimally
It doesn’t matter

114

Közepes

How can you tell that the system has been overcharged with refrigerant?


Even under a very small heat load, frost forms on the suction line
Under normal operating conditions the condensing pressure and subcooling rise markedly because excess liquid floods the condenser and reduces its active surface
It cannot be checked, because the sight glass is not intended for this
The compressor runs at a lower load and the suction pressure drops

115

Közepes

Before charging the unit with refrigerant, it is essential to…


…fill in the unit's data sheet
…check the compressor suction and discharge connections
…carry out a trial start-up
…carry out a tightness test (and evacuate the system)

116

Közepes

What information must appear on the label of equipment containing F-gases?


Only the trade name of the refrigerant and the unit's serial number
The manufacturer's logo, the unit weight and year of manufacture from the rating plate
The weight and capacity of the pipework and the colour code of the casing paint
That it contains an F-gas, its designation, quantity in kg and t CO₂ eq, and GWP

117

Könnyű

What is the base unit of temperature according to the International System of Units (Système International d’Unités)?


°R
°F
°C
K

118

Közepes

Which set of information best reflects the content of the equipment records required by Regulation (EU) 2024/573?


The owner, installer and service technician of the unit
The make and model of the unit
Operator details, equipment details, type and quantity of refrigerant, and information on servicing and repairs
Only the date of installation and the installer's name

119

Nehéz

Which statement about installing Schrader valves is correct?


Hydrocarbons leak through Schrader valves
All Schrader cores are suitable for all refrigerants
Schrader valves must not be used in R744 systems
When brazing the valve body, the core must be removed, then refitted and tightened to the correct torque

120

Nehéz

How does an undercharge affect the high-pressure side (without discharge pressure control)?


Discharge pressure higher, subcooling higher
Discharge pressure higher, subcooling lower
Discharge (condensing) pressure and subcooling will both be lower
Discharge pressure lower, subcooling higher

121

Nehéz

What is the benefit of adding helium as a tracer gas to nitrogen in a pressure test?


It reacts with refrigerant residues, producing a visible colour change
It has a distinctive odour that helps locate the leak
It has a higher pressure than pure nitrogen in the same cylinder
Its small atoms pass easily through leaks and are detected

122

Közepes

Who is responsible for keeping the equipment records?


The person responsible for risk assessment.
The operator of the unit or system.
There is no such obligation.
The equipment maintenance technician.

123

Nehéz

What can be the effect of a relief valve lifting repeatedly?


The set pressure increases
The valve may not reseat tightly and its set (opening) pressure may decrease
The valve no longer opens
The valve stays fully open permanently

124

Közepes

Where are oil traps installed on the suction line?


Immediately before the compressor suction connection
At the bottom of vertical suction risers with upward flow
Before the safety valve on the suction side
At the inlet to every component of the refrigeration system

125

Nehéz

What is the relationship between the pressure (p) and temperature (T) of nitrogen at the start (1) and end (2) of a tightness test (p absolute, T in kelvin)?


p₂ = T₁/(p₁ × T₂)
p₂ = T₂/(p₁ × T₁)
p₂ = (p₁ × T₂)/T₁
p₂ = (p₁ × T₁)/T₂

126

Közepes

Which symptoms with the compressor running indicate a refrigerant leak (undercharge)?


Rising liquid level in the receiver and increasing subcooling
Rising condensing and suction pressures with no superheat
Low suction pressure, high superheat and negligible subcooling
Sight glass full of liquid and rising oil level in the crankcase

127

Közepes

Which components of a refrigeration system are potential leak points subject to leak checks?


Joints, valves (including stems), seals (including those on replaceable filters and driers), parts subject to vibration and connections to safety and measuring devices
Only high-pressure-side components
Only suction-side components
Hermetic compressors, liquid receivers and liquid separators

128

Közepes

What pressure is used for the pressure tightness test of an installation?


A pressure equal to the maximum pressure measured during operation
The pressure specified in EN 378-2 or by the manufacturer, not exceeding the maximum allowable pressure of the system (PS)
A pressure chosen by the technician based on experience
Always 30 bar

129

Közepes

At which points of the unit must the leak check be carried out?


At all points where there is a potential risk of refrigerant leakage
Only at connections of measuring instruments
Only on discharge-side components
Only on compressor shut-off valves, solenoid valves and filters

130

Közepes

When can a unit be considered tight after a pressure test?


When it has been checked with a fixed electronic detector
When gas bubbles appear after immersion in water
When the pressure remains constant during the test (allowing for temperature-related changes); any unexplained pressure drop requires the leak to be located
When the pressure drop does not exceed 0.1 bar regardless of the test duration

131

Közepes

Which legal act currently sets out the obligation to check stationary refrigeration equipment containing F-gases for leaks, and how often this must be done?


Commission Regulation (EC) No 1516/2007
Implementing Regulation (EU) 2024/2215
Regulation (EU) No 517/2014
Regulation (EU) 2024/573

132

Nehéz

Which parts of a refrigeration system should be given particular attention during a leak check?


Only condenser connections, because the refrigerant is liquid there
Joints, valves incl. stems, seals, parts subject to vibration, connections to safety devices
Compressor and receiver connections, because the pressure is highest there
Only compressor connections, because they are the only parts subject to vibration

133

Könnyű

What is the superheat of refrigerant vapour?


The amount of heat required to evaporate a liquid
The difference between the actual vapour temperature and the saturation temperature corresponding to its pressure (expressed in K)
The difference between the condensing temperature and the ambient temperature
The difference between the saturation temperature and the actual liquid temperature in the liquid line

134

Nehéz

Leak checks can be carried out using various methods. Which pair is correct?


Physical and chemical methods
Direct and indirect methods
Material quality control methods and electronic methods
Methods with and without quality control of supplies

135

Nehéz

To whom can leak checks of stationary refrigeration equipment containing F-gases be entrusted?


An employee appointed by the owner of the installation
A person who has carried out such checks before
Any leak-testing specialist
A natural person holding a certificate covering leak checks (A1, A2 within its charge limit, or E)

136

Nehéz

What conditions must be met to use UV dye for leak checking?


A UDT authorisation for pressure testing is required
It is sufficient to have a UV lamp, dye and safety goggles
Manufacturer approval of the method and a certificate covering breaking into the circuit
It is sufficient that introducing dye into the circuit is technically feasible

137

Nehéz

Which leak-checking methods are considered direct methods?


1. gas detection devices (portable or fixed leak detection system), 2. UV detection fluid or dye, 3. bubble/foam solutions
Nitrogen with tracer gas and pressure measurement
Vacuum test and foam solution
Pressure-change measurement and immersion in water

138

Nehéz

What do indirect leak-checking methods involve?


A visual and manual check and analysis of parameters: pressure, temperature, compressor current, liquid levels and recharge volume
Ultrasonic measurement
Leak detection with UV dye
Leak detection with an electronic detector

139

Közepes

How should the pressure be increased during a pressure tightness test?


Gradually, in stages, checking for leaks at each level until the test pressure is reached
As quickly as possible
In one step, by fully opening the nitrogen cylinder valve
In any way

140

Közepes

What electronic equipment should be used for leak checking?


Only detectors with an infrared sensor
Only hot-cathode devices
Only devices with an 'ion pump' sensor
Detectors suited to the refrigerant in the system, with appropriate sensitivity, checked periodically

141

Közepes

What documentation should be checked before starting a leak check?


Attendance sheets of the plant-room staff for the year
Only the installation invoice and the first start-up report
The equipment records – especially recurring problems and previous leaks
The operator's fixed-asset inventory ledger

142

Közepes

What information must be recorded in the leak check report?


The date, a general note about the leak and the operator's signature
Date, number and location of leaks, how they were repaired, technician details and signature
Only the number of leaks found and the date of the check
The method used, the time spent on site and the cost of repair

143

Közepes

What pressure should be used for the pressure tightness test?


Any pressure, at the technician's discretion
Always 2–3 bar
A pressure not exceeding the maximum allowable pressure of the system (PS)
Always 10–12 bar

144

Közepes

What is the temperature glide of a refrigerant?


The temperature drop of the refrigerant across the expansion valve
In zeotropic mixtures, the difference between the temperatures at the start and end of a phase change (boiling or condensation) at constant pressure
The temperature rise of the vapour in the compressor
A property of single-component refrigerants, for which one saturation temperature corresponds to a given pressure

145

Nehéz

What does a vacuum (decay) test involve?


After isolating the pump, you check whether the system pressure rises
The pump runs continuously to hold the required vacuum for the test
The pump is restarted every time the system pressure rises
With the pump running, you watch the vacuum gauge reading

146

Nehéz

How often should leak tests be carried out on equipment containing 1.5 kg of R404A refrigerant (5.9 tonnes of CO₂ equivalent)?


On initial commissioning.
Only when servicing the unit.
At least once every 12 months.
Once every six months.

147

Nehéz

How often should leak tests be carried out on equipment containing 7 kg of R404A refrigerant (27.45 tonnes of CO₂ equivalent)?


Once every six months.
On initial commissioning.
Only when servicing the unit.
At least once every 12 months.

148

Közepes

In which equipment is a leakage detection system required?


Equipment with 50 t CO₂ eq or more of F-gases, regardless of equipment type
Equipment with 5 t CO₂ eq or more of F-gases, regardless of equipment type
Equipment with ≥ 500 t CO₂ eq of Annex I F-gases (or ≥ 100 kg of Annex II Section 1 gases)
Equipment with 30 kg or more of F-gases, regardless of their GWP

149

Nehéz

Under Regulation (EU) 2024/573, a leakage detection system is mandatory when:


the F-gas charge of the refrigeration equipment is 500 t CO₂ eq or more
the equipment contains a flammable refrigerant in any quantity
the charge is 100 kg or more of ozone-depleting substances
the equipment operates in an enclosed space

150

Nehéz

Which leak-checking method may NOT be used by a holder of a Category E certificate?


Checking with a foaming solution
Measurement with a handheld electronic detector
Leak checking with a fluorescent dye introduced into the circuit
Visual inspection

151

Közepes

What should you check before using a portable electronic leak detector?


That it holds a valid UDT inspection certificate
That it suits the refrigerant and has been checked as the manufacturer requires
That it has been zeroed close to the suspected leak point
That it has an infrared sensor, as only this type is permitted

152

Közepes

Which certificate types (A1, A2, B, C, D, E) authorise leak checks of equipment containing F-gases?


Only A1 and A2
A1, A2 and E
All except D
Only E

153

Nehéz

Within what timeframe must a leak test be carried out on a stationary refrigeration system after a leak has been repaired, in accordance with EU Regulation 2024/573 on F-gases?


At the next periodic inspection.
Between 24 hours and 1 month after the repair.
At any time.
Immediately after the repair.

154

Nehéz

How often must refrigeration equipment containing ≥500 t CO₂ eq of F-gases be checked if (contrary to Article 6) no leakage detection system is installed?


Every 3 months
Every 12 months
Every month
Every 6 months

155

Közepes

Why is it advisable to subcool the liquid refrigerant?


To lower the evaporating temperature in the evaporator
To allow a smaller expansion valve to be used
To allow a condenser with a smaller heat-exchange surface to be used
To ensure that liquid free of vapour bubbles enters the expansion valve

156

Közepes

What must be done after repairing a leak in the refrigeration unit of a refrigerated trailer?


Issue the invoice and leave the leak check to the next periodic service
Update the equipment records and carry out a leak check (it may be done directly after repair)
Charge an alternative refrigerant, start up and measure the parameters
Visually inspect only the bolted and brazed joints near the repair

157

Közepes

Recovery of fluorinated greenhouse gases means:


The collection and storage of fluorinated greenhouse gases from containers, products and equipment during maintenance or servicing or prior to their disposal.
The reprocessing of fluorinated greenhouse gases to achieve their specified standard properties.
The final decommissioning and withdrawal from service or use of a product or piece of equipment containing fluorinated greenhouse gases.
The reuse of fluorinated greenhouse gases following a basic purification process.

158

Közepes

Who is authorised to recover refrigerant from stationary refrigeration equipment containing F-gases?


The operator
A natural person holding a certificate of the relevant type (A1; A2. or D within their charge limit)
The administrator of the operator's account in the register
The owner of the installation

159

Közepes

How must recovered refrigerants be stored?


In any pressure vessel that has some form of approval
In a disposable (non-refillable) cylinder that held the same refrigerant
In any used refrigerant cylinder, provided it is leak-tight
In a labelled recovery cylinder with a dual valve and a valid inspection

160

Közepes

When should the recovery of fluorinated greenhouse gases be carried out:


Only prior to the final disposal of equipment.
Always during servicing and maintenance of equipment.
Before each leak test of the equipment.
Before the final disposal of equipment and, where applicable, during its servicing and maintenance.

161

Közepes

What should be done if recovered refrigerant is contaminated (e.g. with acid, air or moisture)?


Add a special contaminant neutraliser
Hand it over to a specialised, authorised company for reclamation or destruction
Clean the mixture yourself using a filter-drier
Pass it through a particle filter and reuse it

162

Közepes

What should be done if different refrigerants have been mixed in a storage cylinder?


Pass it through a filter-drier and reuse it
Add a special refrigerant to the mixture
Hand the mixture over to an authorised company – as a rule for destruction
Separate the mixture into its components yourself

163

Közepes

How does push-pull refrigerant recovery work?


Nitrogen is injected into the system, pushing the refrigerant into the atmosphere
The recovery unit draws vapour from the recovery cylinder and pushes it into the system; the pressure difference forces liquid refrigerant out of the system into the cylinder
The recovery unit draws vapour from the system and condenses it in the cylinder
Refrigerant is drawn alternately from the suction and discharge sides of the compressor

164

Közepes

What are the options for managing waste refrigerant?


Disposal, storage
Reclamation, recovery
Recovery, disposal
Recycling, reclamation, destruction

165

Közepes

Which management option restores recovered refrigerant to a quality equivalent to virgin product, so that it can be used by any undertaking?


Storage
Destruction
Reclamation
Recycling

166

Közepes

The lower the evaporating temperature, …


…the greater the density of the suction vapour and the lower the refrigerant mass flow rate
…the lower the density of the suction vapour and the lower the refrigerant mass flow rate
…the greater the density of the suction vapour and the greater the refrigerant mass flow rate
…the lower the density of the suction vapour and the greater the cooling capacity of the compressor

167

Közepes

How must transportable pressure vessels (e.g. refrigerant cylinders) be marked?


With the manufacturer's logo and date of manufacture
Among other things: the number of the design and testing standard, marks of the approving country and the inspection body, the date of the initial inspection, and the manufacturer's and operational marks
The marking is optional
Only with weight and capacity marks

168

Közepes

The recovery of refrigerants does not require the use of:


Scales with a measurement range suitable for the size of the cylinder being filled.
An electronic leak detector.
Hoses with shut-off valves.
A refrigerant recovery station.

169

Közepes

What functions does the compressor perform in a refrigeration system?


The compressor compresses ambient air and increases the pressure of the refrigerant.
The compressor creates a vacuum on the suction side of the system
The compressor condenses the refrigerant.
The compressor draws in refrigerant vapour from the evaporator, compresses it, and then forces it into the condenser, raising the pressure to the required condensing pressure.

170

Könnyű

What is the compression ratio of a compressor?


The amount of refrigerant compressed per cycle relative to heat capacity
The ratio of discharge pressure to the effective capacity of the compressor (p/Vk)
The ratio of suction pressure to discharge pressure (po/pc)
The ratio of absolute discharge pressure to absolute suction pressure (pc/po)

171

Közepes

What is compressor flooding (liquid slugging)?


Excess oil in the condenser
Liquid refrigerant or oil entering the compression chamber
Flooding of the compressor by rainwater
A large amount of liquid refrigerant in a flooded evaporator, which is a normal operating condition

172

Közepes

Within what range is the compressor motor speed typically controlled using a frequency inverter?


Speed control does not change the cooling capacity
Approximately 30 to 75 Hz, corresponding to about 60–150% of nominal capacity (depending on the compressor manufacturer)
By a maximum of 10%
From approximately 10% to 90% of nominal capacity

173

Könnyű

What is the theoretical displacement (swept volume flow) of a compressor?


A value expressed by the coefficient of performance (COP)
The volume of a single cylinder in cm³
The volume of refrigerant flowing in one piston cycle under actual operating conditions
The volume of vapour drawn in per unit of time, determined by the compressor's geometry and speed (stated by the manufacturer, e.g. in m³/h)

174

Közepes

Why is it essential to observe the correct phase sequence for scroll compressors and screw compressors?


Because these types of compressors are sensitive to voltage drops.
Because changing the phase sequence would reverse the direction of rotation of the compressor rotors, which could result in damage to the compressors.
Because this type of compressor has difficulty starting up if the phase sequence is changed.
Because the motor speed would decrease, and consequently the compressor’s capacity.

175

Közepes

What compression ratio should each stage of a two-stage vapour-compression system have (rule of thumb)?


Greater than 10
Greater than 18
Less than approximately 8
Equal to 1

176

Közepes

Why is a shaft seal necessary in open-type compressors?


To ensure the bearing remains lubricated
To prevent air from entering and refrigerant from leaking out of the compressor
Only to prevent oil leakage
To protect the crankshaft bearing

177

Közepes

How can you check whether the liquid refrigerant is sufficiently subcooled?


Check whether the liquid distributor upstream of the evaporator feels warm
Check by touch whether the condenser outlet is noticeably colder than ambient
Check whether the whole evaporator surface is covered with an even layer of frost
Compare the liquid-line temperature with the saturation temperature at the measured condensing pressure

178

Közepes

Why is the compressor crankcase heated?


To increase dissolution of refrigerant in the oil and improve its viscosity
To dehydrate the oil
To limit refrigerant migration into, and dissolution in, the oil during standstill
To keep the lubricating oil liquid

179

Könnyű

What is the clearance (dead) volume of a reciprocating compressor?


The space between the side of the piston and the cylinder
The space between the underside of the piston and the crankcase cover
The volume between the valve plate and the piston at bottom dead centre
The volume between the valve plate and the piston crown at top dead centre

180

Közepes

What are compressor packs (racks)?


Sets of compressors connected in any configuration
Units with two-stage compressors
Several compressors connected in parallel on a common frame with common suction and discharge headers
Several air-cooled condensers

181

Közepes

What is the main advantage of multi-compressor packs?


No need for compressor controls and safety devices
Stepwise capacity matching to demand, plus redundancy
Low purchase cost and easy installation without special controls
A smaller refrigerant charge than a single-compressor system

182

Közepes

What is meant by the operating envelope (application range) of a compressor?


The capacity, refrigerant type and dimensions of the compressor
A range determined only by the evaporating temperature
A range determined by the evaporating temperature at a given ambient temperature
The permissible range of evaporating and condensing temperatures (to, tk), or the corresponding pressures, within which the compressor may operate

183

Közepes

What are the basic functions of oil in a compressor?


Absorbing moisture from the refrigerant
Increasing the cooling capacity of the refrigerant
Sealing leaks that develop in the installation
Lubricating bearings and sliding surfaces, removing heat, and sealing clearances (e.g. between piston and cylinder, or rotors)

184

Közepes

What are the most effective ways of controlling compressor cooling capacity?


Changing the displacement: varying the rotational speed or unloading cylinders
Pressure control valves
An expansion valve
Partially covering the evaporator

185

Közepes

What does hot-gas bypass capacity control involve?


The compressor speed is varied
Bypass is not used for capacity control
High-pressure liquid is injected into the suction to increase capacity
Part of the hot discharge gas is passed through a bypass valve to the suction side (or evaporator inlet), reducing the effective capacity

186

Közepes

What is the fundamental difference between hermetic and semi-hermetic compressors?


Both can be dismantled; they differ only in cooling capacity
The semi-hermetic casing is bolted (can be opened); the hermetic one is welded
Semi-hermetic compressors run more quietly as a complete unit
The semi-hermetic compressor has no motor inside the casing

187

Közepes

How does a scroll compressor work?


It uses two screws to compress the refrigerant.
A scroll compressor is also known as a turbo compressor.
It is a type of piston-type device.
It is a positive-displacement compressor in which compression results from the interaction of a fixed and an orbiting scroll.

188

Közepes

What physical process takes place in the evaporator?


The refrigerant condenses
The secondary fluid (glycol, water) evaporates while the refrigerant condenses
The liquid refrigerant evaporates, absorbing heat, and the vapour is slightly superheated at the outlet
The refrigerant is subcooled as a liquid

189

Közepes

What is the purpose of compressor capacity control?


To increase the condensing pressure
To match the cooling capacity to the current demand
To ensure compressor lubrication
To match capacity to the condensing temperature

190

Közepes

Why is inverter speed control advantageous for refrigeration compressors?


It enables continuous, smooth control of cooling capacity
It can be used with any compressor to ensure lubrication
It increases compressor capacity above nominal at any frequency
Reducing the speed improves oil return to the compressor

191

Közepes

Does the suction gas temperature affect the cooling capacity of the compressor?


Yes, but only in reciprocating compressors, not scroll
No – capacity depends only on the compressor displacement
Yes, but only if the suction gas is deeply cooled
Yes – higher temperature lowers vapour density, mass flow and capacity

192

Közepes

In the case of compressor units fitted with an oil level control system, is it necessary to install the compressors at the same height?


Only scroll compressors.
No.
Yes.
Only screw compressors.

193

Közepes

What functions does a compressor powered by the vehicle’s engine perform in a transport refrigeration system?


This compressor creates a vacuum on the suction side of the system whilst the vehicle’s engine is switched off.
This compressor condenses the refrigerant whilst the vehicle is in motion.
This compressor draws in refrigerant vapour from the evaporator, compresses it and then forces it into the condenser whilst the vehicle’s engine is running.
The compressor compresses ambient air and increases the pressure of the refrigerant.

194

Közepes

Which media most commonly absorb heat from the refrigerant in the condenser?


Only a water–glycol mixture
Air and CO₂
Air or water
Ammonia

195

Közepes

What is the function of the condenser in refrigeration systems?


Absorption of heat rejected in the regenerative heat exchanger
Releasing only the heat from the compressor into the surroundings
Releasing to the environment the heat absorbed in the evaporator and the heat added during compression
Releasing only the heat absorbed in the evaporator into the surroundings

196

Közepes

If the refrigerant temperature on the high-pressure side is above its critical temperature, condensation…


…occurs provided a special condenser is used
…does not occur
…does not depend on temperature
…always occurs regardless of temperature

197

Közepes

How is liquid subcooling usually achieved in a refrigeration system?


With an additional heat exchanger using liquid nitrogen
By dissolving the refrigerant in oil
With hot high-pressure vapour
In the final section of the condenser (or in an additional subcooler)

198

Közepes

What is the purpose of condenser fan speed control?


To reduce energy efficiency
Only to protect against exceeding the maximum condensing pressure
To disperse refrigerant in the event of a leak
To keep the condensing pressure at the correct level

199

Közepes

Which international agreement introduced the global phase-down of HFC production and consumption?


The Kigali Amendment to the Montreal Protocol
The Kyoto Protocol
The Paris Agreement
The Vienna Convention for the Protection of the Ozone Layer

200

Közepes

Which international treaty governs the phase-out of ozone-depleting substances (CFCs, HCFCs)?


The Stockholm Convention
The UN Framework Convention on Climate Change (UNFCCC)
The Montreal Protocol
The Paris Agreement

201

Nehéz

What is the basis of the GWP values in Regulation (EU) 2024/573?


Each Member State sets its own GWP values
For HFCs (Annex I) – mainly the IPCC Fourth Assessment Report (AR4); for HFOs and non-fluorinated substances (Annexes II and VI) – the Sixth Assessment Report (AR6)
AR4 for all substances
AR6 for all substances

202

Nehéz

An air conditioner (not hermetically sealed) contains 2.5 kg of R410A (GWP 2088). How often must it be checked for leaks?


Every 3 months
At least every 12 months (5.22 t CO₂ eq)
No checks required (below 3 kg)
Every 6 months

203

Nehéz

When is labelled hermetically sealed equipment containing HFCs (Annex I) exempt from leak checks?


Never – hermetically sealed equipment is always checked
Always, regardless of charge
When it contains less than 10 t CO₂ eq, and in residential buildings also when it contains less than 3 kg of F-gases
When it contains less than 5 t CO₂ eq

204

Nehéz

Is a chiller containing 50 kg of R1234ze(E) subject to leak checks under Regulation (EU) 2024/573?


Yes – every 12 months, because its GWP is low
No – the threshold is 5 t CO₂ eq and 50 kg of R1234ze is below 1 t CO₂ eq
Yes – at least every 6 months (every 12 months with a leakage detection system)
No – HFOs are not subject to leak checks

205

Nehéz

In 2026, may an existing refrigeration installation using R404A (GWP 3922) be topped up with virgin refrigerant?


Yes – the ban applies only to equipment ≥40 t CO₂ eq
Yes – bans apply only to new equipment
No – only reclaimed or recycled R404A is allowed (until 1 January 2030)
Yes, if the equipment has a leakage detection system

206

Nehéz

After 1 January 2026, may an R410A (GWP 2088) air conditioner be serviced using virgin R410A?


No – the ban covers all refrigerants with GWP ≥ 750
Only with reclaimed refrigerant
Yes – the servicing ban for air conditioners and heat pumps covers F-gases with GWP ≥ 2500
No – the ban covers all HFCs

207

Közepes

Can HFC refrigerant recovered during a repair be put straight back into the same equipment without any cleaning (filtering/drying)?


Yes, if less than 24 hours have passed
Yes, always
No – recovered F-gas may be used for filling only after it has been recycled or reclaimed
Yes, if the operator agrees

208

Közepes

Who may purchase HFCs for servicing refrigeration equipment?


Any adult
Only a person holding the relevant certificate or an undertaking employing such persons
Only the equipment operator
Any business

209

Közepes

Under what condition may non-hermetically sealed split air conditioning charged with F-gas be sold to an end user?


Unconditionally
When the user signs a statement that they will install it themselves
When evidence is provided that installation will be carried out by a certified undertaking
Only if the unit contains less than 3 kg of refrigerant

210

Közepes

By when must the holder of an F-gas certificate issued under Regulation (EU) No 517/2014 first complete refresher training or an evaluation process?


Never – the certificate is valid indefinitely
By 12 March 2029 (and then at least every 7 years)
By 31 December 2030
By 12 March 2025

211

Közepes

What must the holder of a Category I certificate (Regulation 2015/2067) do to continue using it?


Apply for an extension without training
Nothing – Category I automatically becomes A1
Update their knowledge to the level of Certificate E
Update their knowledge and skills to the level of Certificate A1 (Annex I to Regulation 2024/2215)

212

Közepes

What does Certificate C under Implementing Regulation (EU) 2024/2215 authorise?


Recovery of F-gases from equipment <3 kg
All activities in Article 2(1) in relation to ammonia (NH₃)
Leak checks without breaking into the circuit
All activities in relation to CO₂

213

Közepes

May a person enrolled in a certification training course carry out certified activities?


Yes – under the supervision of a certified person, for no more than 24 months in total
Yes – independently, for 6 months
Yes – with no time limit, if employed by a certified company
No, never

214

Közepes

How long must the operator keep the records of equipment subject to leak checks, if they are not kept in a national database?


Until the equipment is decommissioned
At least 2 years
At least 1 year
At least 5 years

215

Nehéz

Since 1 January 2025, may a new single-split air conditioner containing 1.5 kg of R410A be placed on the market?


Yes – the ban applies only to units >12 kW
No – single splits <3 kg with F-gases of GWP ≥ 750 are banned
Yes – the ban applies from 2029
Yes, if the unit is hermetically sealed

216

Nehéz

From when is it prohibited to place on the market split air-to-air systems up to 12 kW containing F-gases with GWP ≥150 (unless required for safety)?


From 1 January 2035
From 1 January 2029
From 1 January 2027
From 1 January 2025

217

Nehéz

Which persistent atmospheric degradation product of R1234yf is classed as a PFAS?


Carbon dioxide
Carbonic acid
Ozone
Trifluoroacetic acid (TFA)

218

Közepes

What is floating head pressure and what does it achieve?


It lets the condensing pressure fall with ambient temperature, reducing compressor work and raising COP (requires an expansion valve that works at a small pressure difference)
It means switching condenser fans off periodically
It increases subcooling by flooding the condenser
It keeps a constant high condensing pressure all year

219

Közepes

How do SEER/SCOP differ from EER/COP?


EER/COP are always higher than SEER/SCOP
SEER/SCOP apply only to natural-refrigerant equipment
There is no difference – they are synonyms
SEER/SCOP are seasonal indicators accounting for part load and climate (EN 14825); EER/COP refer to a single operating point (EN 14511)

220

Közepes

Which design approach can significantly reduce the F-gas charge of a large refrigeration installation?


Larger liquid-line diameters
Adding a second liquid receiver
Omitting pipe insulation
An indirect (secondary-coolant) system or a cascade with a natural refrigerant in the low stage, plus heat exchangers with small internal volume

221

Közepes

Which information must be entered in the equipment records after a leak check?


The date and result of the check and the identity of the undertaking and person who performed it (with certificate number)
Only the date of the check
Only the operator's signature
Only the equipment's energy consumption

222

Közepes

What must be done when an indirect method (e.g. parameter analysis) indicates a possible leak?


Record it and check at the next periodic inspection
Carry out a direct-method examination to locate the leak
Nothing – indirect methods are sufficient
Top up the refrigerant and end the check