1

Nehéz

Why do liquid and oil separators in CO₂ systems require particular attention?


Because sight glasses and level indicators must not be used in CO₂ systems
Because of very high pressures – adequate PS and protection devices are required
Because CO₂ needs no lubrication, so oil separators are unnecessary
Because CO₂ is flammable and separators must not be used

2

Nehéz

What is the critical pressure of CO₂ (R744)?


Approx. 74 bar (abs)
Approx. 31 bar
Approx. 10 bar
Approx. 120 bar

3

Nehéz

What characterises the transcritical process in CO₂ systems?


It occurs only at low temperatures
Heat rejection takes place above the critical point – the refrigerant does not condense in the conventional way (gas cooler instead of condenser)
Conventional condensation occurs
It is irrelevant to system operation

4

Nehéz

What characterises the subcritical CO₂ process?


Operation above the critical point
The absence of evaporation
The absence of condensation
The conventional condensation process below the critical point

5

Könnyű

What is the log(p)-h diagram for CO₂ used for?


To detect leaks
To regulate pressure
To measure temperature
For analysing thermodynamic processes in a refrigeration system

6

Könnyű

What can be read from the log(p)-h graph?


Pressure, enthalpy, temperature and state of the refrigerant
Only the temperature
Only the amount of refrigerant
Only the humidity

7

Könnyű

What are CO₂ saturation tables used for?


To measure humidity
To regulate the compressor
To determine the relationship between temperature and pressure at saturation
To determine the oil quantity

8

Könnyű

What does the CO₂ saturation state mean?


A state in which the refrigerant is only a gas
Dry ice state
A state of high pressure
Equilibrium between the liquid and vapour phases

9

Nehéz

When can dry ice (solid CO₂) form?


At high pressure
When the pressure drops suddenly below the triple point (approx. 5.2 bar abs, −56.6 °C), e.g. when venting liquid CO₂ or charging liquid into an evacuated system
At high temperature
During normal operation of the system

10

Nehéz

What risks are associated with dry ice forming in a CO₂ system?


Improved efficiency
Blocked pipes and valves and system damage (and a sharp pressure rise when it thaws)
Pressure reduction
No risk

11

Nehéz

How does CO₂ saturation pressure change as temperature increases?


It remains the same
It decreases
It increases rapidly
It first decreases, then increases

12

Könnyű

Why is understanding the log(p)-h graph particularly important for CO₂?


As CO₂ systems operate in different modes (sub- and transcritical) and require detailed analysis
It is only used for design purposes
It doesn’t matter
It only applies to NH₃

13

Nehéz

What happens to CO₂ above the critical point?


It transitions to a supercritical state (no distinction between liquid and gas)
It ceases to conduct heat
It turns into a liquid
It turns into a solid

14

Könnyű

Why do CO₂ systems require precise pressure control?


Due to significant pressure changes with temperature fluctuations
They do not require control
Due to low pressures
Because there are no valves

15

Nehéz

What is the main characteristic of R744 (CO₂) refrigeration systems?


Very high operating pressures
Low operating pressures
No need for control
Low energy efficiency under all conditions

16

Nehéz

What are the requirements for piping materials in CO₂ systems?


Only plastics
Any material may be used
It doesn't matter
They must withstand high pressures (e.g. stainless steel, high-strength copper-alloy tubes such as K65)

17

Nehéz

How does a booster system work in CO₂ installations?


It reduces evaporator pressure
Low-temperature (LT) compressors discharge into the suction of medium-temperature (MT) compressors – two-stage compression in a single circuit
It reduces the refrigerant quantity
It is used to store refrigerant

18

Könnyű

What is the function of high-pressure control valves in CO₂ systems?


They lower the evaporator temperature
They regulate oil flow
They control the pressure on the high-pressure side and optimise system operation
They are used to store the refrigerant

19

Nehéz

Why is pressure optimisation in CO₂ systems crucial?


It enables the system to achieve maximum energy efficiency in transcritical mode
It doesn’t matter
It reduces the amount of refrigerant
It reduces the ambient temperature

20

Nehéz

What role does parallel compression play in CO₂ systems?


It increases energy consumption
It compresses flash gas from the intermediate receiver directly to high pressure, improving efficiency
It lowers the ambient temperature
It has no significance

21

Nehéz

How does an ejector work in a CO₂ system?


It uses the energy of the higher-pressure refrigerant to raise the pressure of the refrigerant from the lower stage, which improves efficiency
Stores the refrigerant
It increases the amount of refrigerant
It lowers the evaporator temperature

22

Nehéz

What is the function of liquid ejectors in CO₂ systems?


They reduce atmospheric pressure
They raise the refrigerant temperature
They return liquid from the separator and allow partially flooded evaporator operation (better evaporator feed)
They increase the amount of oil

23

Nehéz

What are the characteristics of partially flooded systems in CO₂ systems?


The presence of liquid in the evaporator, which improves heat transfer and efficiency
The absence of liquid in the evaporator
Lack of regulation
Low operating pressure

24

Nehéz

What is the main risk associated with standstill pressure in CO₂ systems?


A pressure rise as the refrigerant warms up during standstill (possibly exceeding PS and lifting the relief valves)
Increased efficiency
A decrease in refrigerant quantity
A drop in temperature

25

Nehéz

How is standstill pressure limited in CO₂ systems?


By raising the plant-room temperature
By completely shutting down the system and power supply
By increasing the refrigerant charge
By using an auxiliary standstill (stagnation) cooling unit, e.g. cooling the receiver, with back-up power, and by selecting an adequate PS and relief valves

26

Nehéz

What does standstill (stagnation) of a CO₂ system mean, and why is it important?


A state with no compressor operation or refrigerant flow – pressure rises with ambient temperature and may exceed PS
Improved efficiency
Normal system operation
A drop in system temperature

27

Könnyű

Why do CO₂ systems require more advanced automation than traditional systems?


They do not require automation
Because there are no valves
Due to the need for precise control of pressure and temperature
Due to low pressures

28

Nehéz

Which safety class applies to R744?


B2L
A1
A2.
A3

29

Nehéz

In a simple single-stage R744 system without an intermediate receiver (refrigerant flows from the gas cooler directly to the expansion valve), operating transcritically at 90 bar with a gas-cooler outlet temperature of 35 °C, the refrigerant upstream of the expansion valve is…


…a subcooled liquid
…a supercritical fluid
…saturated vapour at intermediate pressure
…a two-phase mixture at intermediate pressure

30

Nehéz

In R744 transcritical systems, the gas cooler outlet valve controls:


The pressure in the gas cooler
The inlet temperature to the gas cooler
The gas cooler fans
The outlet temperature of the gas cooler

31

Nehéz

What is the main reason for using K65 copper tubing in some R744 systems?


They can withstand higher pressures
They bend easily
They come in a wider range of diameters
They have good low-temperature performance

32

Nehéz

Why should an evacuated R744 system initially be charged with refrigerant in the vapour phase?


To avoid damaging the compressor with liquid CO₂
To prevent dry ice forming (until approx. 5.2 bar abs is exceeded)
To charge R744 more slowly and measure it more accurately
To prevent the drain valve on the receiver from opening

33

Nehéz

If moisture remains in an R744 system because it was not properly evacuated (dehydrated), what is the likely consequence?


Reduced cooling capacity
Excessive discharge pressure
Formation of carbonic acid, which damages the system
Formation of hydrogen fluoride and hydrofluoric acid

34

Nehéz

The pressure of R744 at a saturation temperature of 20 °C is approx.


90 bar g
25 bar g
56 bar g
14 bar g

35

Nehéz

At an ambient temperature of 25 °C, the standstill pressure in the low-pressure stage of an R744 cascade (without standstill cooling) will typically be…


…approx. 27.5 bar g
…higher than the maximum allowable pressure (PS) of the low-pressure stage
…the same as the high-pressure switch setting
…the same as the relief valve set pressure

36

Nehéz

What is the correct definition of critical temperature?


The temperature above which there are no distinct liquid and gaseous phases
The temperature at which the vapour pressure of a liquid is equal to the ambient pressure surrounding the liquid
The temperature at which, for certain substances, electrical resistance is zero
The temperature at which a substance changes from a gaseous to a solid state

37

Nehéz

In the gas cooler of a transcritical system, the supercritical working fluid…


…rejects heat during a phase change
…rejects heat as its pressure falls
…rejects heat as its temperature falls
…rejects heat at constant temperature and pressure

38

Közepes

What hazard does a large CO₂ leak in an enclosed room pose to people?


CO₂ is completely safe
Accumulation near the floor and asphyxiating/toxic effects at high concentrations
Explosion of the mixture with air
Formation of hydrogen fluoride

39

Nehéz

Why does the efficiency of transcritical CO₂ systems fall in warm climates, and how is this mitigated?


CO₂ freezes in the gas cooler – heaters are used
Efficiency does not depend on climate
Gas cooler pressure drops – extra charge is added
At high ambient temperatures the system operates transcritically with large throttling losses – parallel compression and ejectors are used, among others