F-Gas English Low GWP

All questions
HFC | Flammable | CO₂ | NH₃
Easy questions | Medium questions | Difficult questions

1

Difficult

What additional protective equipment will you use when brazing systems containing HC refrigerants?


Latex gloves
A high-visibility vest
A flammable gas detector
Ear defenders

2

Difficult

Why can’t a sealed high-pressure switch be replaced with a standard mechanical one in a system containing a flammable refrigerant?


Dust and moisture may enter
The pressure switch setting will not be correct
There is a risk of refrigerant leakage
It is a potential source of ignition

3

Difficult

What is the minimum (recommended) distance from a work area with HC refrigerants within which there must be no sources of ignition?


2 m
3 m
1 m
0.5 m

4

Difficult

What is the maximum safe R32 fill of a recovery cylinder approved for flammable gas that holds 20 kg of R410A (the liquid density of R32 is about 8-10% lower)?


18 kg
9 kg
20 kg
33 kg

5

Difficult

What is the maximum charge of an A3 refrigerant for a hermetic display cabinet with an integral condenser located in the ground-floor sales area of a supermarket?


0,494 kg
10 kg
1.0 kg
2.5 kg

6

Difficult

How can a vacuum pump be used safely to evacuate a system containing a flammable refrigerant?


Place the pump directly on the floor, as low as possible
Such systems need not be evacuated before charging
Position the pump at least 3 m above floor level
Ignition-source-free pump, good ventilation, exhaust to a safe place

7

Difficult

What safety measure must you carry in your vehicle when transporting flammable refrigerant cylinders?


A fire extinguisher
A fire blanket
Tinted safety goggles
Thick gloves

8

Difficult

How would you prepare a 10 kg R32 water chiller located outdoors for debrazing its joints?


Recover the R32 to a vacuum, then fill the system with nitrogen to a slight positive pressure (approx. 0.1 bar g)
Recover the R32 to a vacuum and start desoldering immediately
Vent the R32 outdoors and purge the system
Vent the R32 outdoors, then fill and vent the system with nitrogen three times

9

Difficult

Which of the following leak detection methods should NOT be used to locate an HC refrigerant leak?


Soapy water solution
Leak detection foam
Electronic leak detector for flammable refrigerants
Electronic HFC leak detector

10

Difficult

What is the most important difference between a flammable refrigerant recovery unit and a standard one?


A different colour for the station
Different connection sizes
A flammable refrigerant recovery unit has no ignition sources
Different low-pressure switch setting

11

Difficult

Which of the following is a source of ignition?


An Ex-certified fan motor
A sealed NTC temperature sensor
An 'n'-type (non-sparking) thermostat
A contactor (sparking contacts)

12

Difficult

What particularly hazardous substance is formed when R32 burns?


Hydrogen fluoride (HF)
Sulphur dioxide (SO₂)
Phosgene
Hydrogen chloride (HCl)

13

Difficult

What type of refrigerant is R1234ze(E)?


HC (hydrocarbon)
HCFC (hydrochlorofluorocarbon)
HFO (hydrofluoroolefin)
CFC (chlorofluorocarbon)

14

Difficult

What hazards does a safety group A3 refrigerant pose?


Lower toxicity, higher flammability
Higher toxicity, moderate flammability
Lower toxicity, moderate flammability
Higher toxicity, higher flammability

15

Difficult

According to EN 378, what is the maximum R290 charge in a cold room measuring 5 m × 3 m × 2.5 m (LFL of R290 = 0.038 kg/m³, access category a, location class I, no additional measures))?


1.0 kg
0.285 kg
1.5 kg
4.93 kg

16

Difficult

What is the approximate ratio of the volumetric cooling capacity of R32 to that of R410A (same compressor and conditions)?


approx. 0.75
approx. 0.6
approx. 1.3
approx. 1.05–1.1

17

Difficult

Why are Ex-certified evaporator fan motors used in some systems with flammable refrigerants?


To avoid a source of ignition in the event of a flammable refrigerant leak
Because they must be kept running continuously to disperse the leaking refrigerant
Because they are more energy-efficient
Because they are more reliable

18

Difficult

Why is the density difference between HC and HFC refrigerants important?


Because it determines the system's energy efficiency
Because HCs operate at much higher pressures
An HC charge in kg is roughly half that of an HFC
Because HCs must be charged much more slowly than HFCs

19

Difficult

What is the GWP of R290 according to Annex VI to Regulation (EU) 2024/573?


7
675
0.02
150

20

Difficult

Which of the following is NOT a source of ignition?


An electrical switch
An unsealed mechanical pressure switch
An Ex-certified fan motor
A light switch

21

Difficult

What is R290?


Propane
Butane
Propene (Propylene)
Isobutane

22

Difficult

What is the maximum A2L charge for a hermetic display cabinet with integral condenser in the ground-floor sales area of a supermarket?


1.2 kg
150 g
1.5 kg
2.5 kg

23

Difficult

Why can’t a standard relay be fitted when retrofitting a compressor’s electrical system for flammable refrigerants?


The method of starting the compressor motor differs from that used with HFCs
Current consumption differs for compressors using flammable refrigerants compared to those using HFCs
It could be a source of ignition
A relay is never required for compressors using flammable refrigerants

24

Difficult

What is the minimum (recommended) distance from a work area with HC refrigerants within which there must be no ignition sources?


3 m
5 m
10 m
1 m

25

Difficult

A recovery cylinder holds 10 kg of R404A (filling ratio 0.82 kg/l). What is the maximum R290 charge for this cylinder (propane filling ratio 0.43 kg/l per ADR P200)?


approx. 8 kg
approx. 17 kg
20 kg
approx. 5.2 kg

26

Difficult

How can a vacuum pump be used safely to evacuate a system containing R290?


Ignition-source-free pump, good ventilation, exhaust to a safe place
Position the pump at least 3 m above floor level
R290 systems need not be evacuated before charging
Place the pump directly on the floor, as low as possible

27

Difficult

Under ADR, what equipment must you carry in your vehicle when transporting flammable refrigerant cylinders (under the 1.1.3.6 exemption)?


A fire extinguisher (at least 2 kg dry powder)
A fire blanket
Thick gloves
Tinted safety goggles

28

Difficult

How do you make sure it is safe to light the torch for desoldering joints in a system from which a flammable refrigerant has been removed?


Such joints must never be desoldered; they must be cut with a pipe cutter
Ensure good ventilation and check the work area with a flammable gas detector
Purge the system with compressed air
Working outdoors is sufficient

29

Difficult

How would you prepare a system containing 100 g of R1270 for debrazing, if local regulations allow controlled venting of small HC quantities?


Vent the R1270 to a safe outdoor location, then purge with OFN three times (pressurise and vent), and braze with OFN flowing
Recover the R1270 to a vacuum and start brazing immediately without a nitrogen purge
Vent the R1270 into the room and open a window
Vent the R1270 outdoors and start brazing immediately

30

Difficult

Which method should NOT be used to locate an R290 leak?


Leak detection foam
Fluorescent dye and UV lamp (if approved by the manufacturer)
An electronic detector for flammable refrigerants
An electronic leak detector designed for HFCs

31

Difficult

Why can’t recovery stations designed for HFCs be used with R600a?


The oil in the recovery unit is not soluble in R600a
They contain ignition sources
The recovery unit cannot withstand the working pressure of R600a
The low-pressure switch setting will not be suitable for R600a due to its lower operating pressure

32

Difficult

According to EN 378, what is the maximum R1234ze(E) charge in a cold room measuring 5 m × 3 m × 2.5 m (LFL = 0.303 kg/m³, access category a, location class I, no additional measures)?


2.27 kg
6.18 kg
227 kg
618 kg

33

Difficult

What type of refrigerant is R32?


Carbon dioxide
Hydrocarbon
Hydrofluorocarbon
Hydrofluoroolefin

34

Difficult

What hazards do A2L refrigerants pose?


Lower toxicity, lower flammability (burning velocity ≤ 10 cm/s)
Higher toxicity, higher flammability
Lower toxicity, higher flammability
Higher toxicity, lower flammability

35

Difficult

What hazard is associated with the combustion of HFO or HFC refrigerants?


Hydrogen fluoride (HF) is formed
Phosgene is formed
Ozone is formed
Nitrous oxide is formed

36

Difficult

Approximately what compressor displacement is required for R600a compared with R134a for the same cooling capacity?


The same
About seven times as large
About half
About twice as large

37

Difficult

What is the GWP value for R32 according to Regulation (EU) 2024/573?


675
7
0
3

38

Difficult

Why is charge accuracy more important in critically charged R290 systems than in HFC systems?


Because of lower operating pressures
Because such systems never have liquid receivers
The charge mass is much smaller than in an HFC system, because the liquid density of R290 is much lower
Because R290 is only used in systems below 150 g

39

Difficult

Why does the condenser fan run continuously in some systems using R1270?


To prevent the build-up of contaminants in the condenser
To ensure that the discharge pressure never becomes excessive
To dilute the refrigerant in the event of a leak
To reduce energy consumption

40

Difficult

What must the label of a flammable refrigerant cylinder include?


Only the refrigerant name
Information about the cylinder owner
Only the net weight
The refrigerant name, the UN number, the hazard label (e.g. 2.1 – flammable gas) and basic safety information

41

Difficult

Why is the absence of a 'flammable refrigerant' label on equipment a serious hazard?


It may lead to the use of tools that are ignition sources
It has no significant effect on safety
It may lead to the wrong oil being selected
It reduces system efficiency

42

Difficult

Which set of information on the label of a flammable refrigerant cylinder is crucial from a safety perspective?


Manufacturer’s name and country of origin
Cylinder colour and date of manufacture
Name of the substance, hazard label (ADR) / GHS pictogram (CLP), UN number
Gross weight and batch number

43

Difficult

What is the purpose of gas detectors in a room with a refrigeration system?


Measuring refrigerant temperature
Monitoring pipe pressure
Early leak detection and triggering of measures preventing health risks and explosive atmospheres (alarm, ventilation, shut-off)
Controlling compressor capacity

44

Difficult

How often should gas detection sensors in a machinery room be checked?


According to the manufacturer's instructions and regulations – at least every 12 months
Before every start-up of the unit
Once every 5 years
Only after a leak has occurred

45

Difficult

Where should a gas detector be located according to EN 378?


Near the control panel
Where the refrigerant would accumulate: low (near the floor) for refrigerants heavier than air, high (near the ceiling) for lighter ones such as NH₃
Only at the room entrance
Anywhere in the room

46

Difficult

What safety checks should be carried out when installing a new refrigeration system with a flammable refrigerant?


Only that the air filter is new
Only the compressor power
The presence of health and safety signage, adequate ventilation and gas detectors
The colour of pipes and hoses

47

Difficult

What are the requirements for emergency exits from a refrigeration machinery room?


Outward-opening doors and signed escape routes (number of exits per the standard)
In small machinery rooms emergency exits need not be signed
At least two exits are required and signage is optional
One exit with a sign stating the refrigerant type is sufficient

48

Difficult

Which installation measure for a flammable-refrigerant system improves its energy efficiency?


A thorough tightness test and evacuation (dehydration) of the system
Charging above the nameplate quantity
Omitting the filter-drier
Restricting room ventilation

49

Difficult

Why is it important to limit the refrigerant charge in HC systems?


It increases capacity
It doesn't matter
It limits the possibility of reaching a flammable concentration (≥ LFL) in a leak, increasing safety
It lowers the temperature

50

Difficult

What hazards are associated with a safety group A3 refrigerant?


Lower toxicity, no flame propagation
Higher toxicity, no flame propagation
Lower flammability, lower toxicity
Higher flammability, lower toxicity

51

Difficult

What is the GWP of R32 (per AR4, as used in Regulation (EU) 2024/573)?


675
6
0
3922

52

Difficult

What factors are taken into account when determining the maximum charge for comfort air-conditioning/heating applications?


Practical limit, room volume
Lower flammability limit, room volume
Lower flammability limit, height of the indoor unit, floor area
Practical limit, height of the indoor unit, floor area

53

Difficult

What compressor displacement is required for R1270 compared with an R404A compressor in the medium-temperature range (cold room)?


About half
Similar
About 6 times larger
About 1.5 times larger

54

Difficult

What is the maximum R290 charge per circuit of a commercial refrigerating appliance (e.g. a cabinet) according to EN IEC 60335-2-89:2022?


150 g
1.5 kg
1.2 kg
13 × LFL ≈ 494 g

55

Difficult

Calculate the maximum R32 charge (LFL = 0.307 kg/m³) for a wall-mounted air conditioner (h₀ = 1.8 m) in a 20 m² room using m_max = 2.5 × LFL^1.25 × h₀ × A^0.5.


approx. 4.6 kg
approx. 13.8 kg
approx. 0.46 kg
approx. 1.5 kg

56

Difficult

What is the maximum quantity of R290 (class 2, group F) that may be carried per transport unit under the ADR 1.1.3.6 exemption?


20 kg
1000 kg
Unlimited
333 kg

57

Difficult

What is the charge limit m₃ = 130 m³ × LFL for R290 (LFL = 0.038 kg/m³) according to IEC 60335-2-40?


approx. 13 kg
approx. 0.99 kg
approx. 4.94 kg
approx. 0.15 kg