F-Gas English Low GWP

Všetky otázky
HFC | Flammable | CO₂ | NH₃
Ľahké otázky | Stredne ťažké otázky | Ťažké otázky

1

Ťažká

What additional protective equipment will you use when brazing systems containing HC refrigerants?


A flammable gas detector
Latex gloves
A high-visibility vest
Ear defenders

2

Ťažká

Why can’t a sealed high-pressure switch be replaced with a standard mechanical one in a system containing a flammable refrigerant?


It is a potential source of ignition
There is a risk of refrigerant leakage
The pressure switch setting will not be correct
Dust and moisture may enter

3

Ťažká

What is the minimum (recommended) distance from a work area with HC refrigerants within which there must be no sources of ignition?


0.5 m
1 m
2 m
3 m

4

Ťažká

What is the maximum safe R32 fill of a recovery cylinder approved for flammable gas that holds 20 kg of R410A (the liquid density of R32 is about 8-10% lower)?


20 kg
9 kg
18 kg
33 kg

5

Ťažká

What is the maximum charge of an A3 refrigerant for a hermetic display cabinet with an integral condenser located in the ground-floor sales area of a supermarket?


1.0 kg
0,494 kg
10 kg
2.5 kg

6

Ťažká

How can a vacuum pump be used safely to evacuate a system containing a flammable refrigerant?


Ignition-source-free pump, good ventilation, exhaust to a safe place
Such systems need not be evacuated before charging
Place the pump directly on the floor, as low as possible
Position the pump at least 3 m above floor level

7

Ťažká

What safety measure must you carry in your vehicle when transporting flammable refrigerant cylinders?


A fire extinguisher
Thick gloves
A fire blanket
Tinted safety goggles

8

Ťažká

How would you prepare a 10 kg R32 water chiller located outdoors for debrazing its joints?


Vent the R32 outdoors, then fill and vent the system with nitrogen three times
Recover the R32 to a vacuum and start desoldering immediately
Vent the R32 outdoors and purge the system
Recover the R32 to a vacuum, then fill the system with nitrogen to a slight positive pressure (approx. 0.1 bar g)

9

Ťažká

Which of the following leak detection methods should NOT be used to locate an HC refrigerant leak?


Electronic HFC leak detector
Electronic leak detector for flammable refrigerants
Leak detection foam
Soapy water solution

10

Ťažká

What is the most important difference between a flammable refrigerant recovery unit and a standard one?


Different low-pressure switch setting
A different colour for the station
Different connection sizes
A flammable refrigerant recovery unit has no ignition sources

11

Ťažká

Which of the following is a source of ignition?


A sealed NTC temperature sensor
An Ex-certified fan motor
A contactor (sparking contacts)
An 'n'-type (non-sparking) thermostat

12

Ťažká

What particularly hazardous substance is formed when R32 burns?


Phosgene
Hydrogen chloride (HCl)
Sulphur dioxide (SO₂)
Hydrogen fluoride (HF)

13

Ťažká

What type of refrigerant is R1234ze(E)?


HC (hydrocarbon)
HCFC (hydrochlorofluorocarbon)
CFC (chlorofluorocarbon)
HFO (hydrofluoroolefin)

14

Ťažká

What hazards does a safety group A3 refrigerant pose?


Higher toxicity, moderate flammability
Lower toxicity, moderate flammability
Lower toxicity, higher flammability
Higher toxicity, higher flammability

15

Ťažká

According to EN 378, what is the maximum R290 charge in a cold room measuring 5 m × 3 m × 2.5 m (LFL of R290 = 0.038 kg/m³, access category a, location class I, no additional measures))?


1.0 kg
0.285 kg
1.5 kg
4.93 kg

16

Ťažká

What is the approximate ratio of the volumetric cooling capacity of R32 to that of R410A (same compressor and conditions)?


approx. 0.6
approx. 1.05–1.1
approx. 1.3
approx. 0.75

17

Ťažká

Why are Ex-certified evaporator fan motors used in some systems with flammable refrigerants?


Because they are more energy-efficient
Because they must be kept running continuously to disperse the leaking refrigerant
To avoid a source of ignition in the event of a flammable refrigerant leak
Because they are more reliable

18

Ťažká

Why is the density difference between HC and HFC refrigerants important?


Because HCs must be charged much more slowly than HFCs
Because it determines the system's energy efficiency
An HC charge in kg is roughly half that of an HFC
Because HCs operate at much higher pressures

19

Ťažká

What is the GWP of R290 according to Annex VI to Regulation (EU) 2024/573?


675
0.02
150
7

20

Ťažká

Which of the following is NOT a source of ignition?


An Ex-certified fan motor
An electrical switch
A light switch
An unsealed mechanical pressure switch

21

Ťažká

What is R290?


Propane
Butane
Propene (Propylene)
Isobutane

22

Ťažká

What is the maximum A2L charge for a hermetic display cabinet with integral condenser in the ground-floor sales area of a supermarket?


1.2 kg
2.5 kg
1.5 kg
150 g

23

Ťažká

Why can’t a standard relay be fitted when retrofitting a compressor’s electrical system for flammable refrigerants?


The method of starting the compressor motor differs from that used with HFCs
It could be a source of ignition
Current consumption differs for compressors using flammable refrigerants compared to those using HFCs
A relay is never required for compressors using flammable refrigerants

24

Ťažká

What is the minimum (recommended) distance from a work area with HC refrigerants within which there must be no ignition sources?


10 m
1 m
3 m
5 m

25

Ťažká

A recovery cylinder holds 10 kg of R404A (filling ratio 0.82 kg/l). What is the maximum R290 charge for this cylinder (propane filling ratio 0.43 kg/l per ADR P200)?


approx. 5.2 kg
approx. 17 kg
approx. 8 kg
20 kg

26

Ťažká

How can a vacuum pump be used safely to evacuate a system containing R290?


Place the pump directly on the floor, as low as possible
Position the pump at least 3 m above floor level
Ignition-source-free pump, good ventilation, exhaust to a safe place
R290 systems need not be evacuated before charging

27

Ťažká

Under ADR, what equipment must you carry in your vehicle when transporting flammable refrigerant cylinders (under the 1.1.3.6 exemption)?


A fire extinguisher (at least 2 kg dry powder)
A fire blanket
Tinted safety goggles
Thick gloves

28

Ťažká

How do you make sure it is safe to light the torch for desoldering joints in a system from which a flammable refrigerant has been removed?


Purge the system with compressed air
Such joints must never be desoldered; they must be cut with a pipe cutter
Working outdoors is sufficient
Ensure good ventilation and check the work area with a flammable gas detector

29

Ťažká

How would you prepare a system containing 100 g of R1270 for debrazing, if local regulations allow controlled venting of small HC quantities?


Vent the R1270 to a safe outdoor location, then purge with OFN three times (pressurise and vent), and braze with OFN flowing
Vent the R1270 into the room and open a window
Recover the R1270 to a vacuum and start brazing immediately without a nitrogen purge
Vent the R1270 outdoors and start brazing immediately

30

Ťažká

Which method should NOT be used to locate an R290 leak?


Fluorescent dye and UV lamp (if approved by the manufacturer)
An electronic detector for flammable refrigerants
An electronic leak detector designed for HFCs
Leak detection foam

31

Ťažká

Why can’t recovery stations designed for HFCs be used with R600a?


The recovery unit cannot withstand the working pressure of R600a
The low-pressure switch setting will not be suitable for R600a due to its lower operating pressure
They contain ignition sources
The oil in the recovery unit is not soluble in R600a

32

Ťažká

According to EN 378, what is the maximum R1234ze(E) charge in a cold room measuring 5 m × 3 m × 2.5 m (LFL = 0.303 kg/m³, access category a, location class I, no additional measures)?


6.18 kg
618 kg
227 kg
2.27 kg

33

Ťažká

What type of refrigerant is R32?


Hydrocarbon
Hydrofluoroolefin
Carbon dioxide
Hydrofluorocarbon

34

Ťažká

What hazards do A2L refrigerants pose?


Lower toxicity, lower flammability (burning velocity ≤ 10 cm/s)
Higher toxicity, higher flammability
Lower toxicity, higher flammability
Higher toxicity, lower flammability

35

Ťažká

What hazard is associated with the combustion of HFO or HFC refrigerants?


Ozone is formed
Phosgene is formed
Nitrous oxide is formed
Hydrogen fluoride (HF) is formed

36

Ťažká

Approximately what compressor displacement is required for R600a compared with R134a for the same cooling capacity?


About twice as large
About seven times as large
The same
About half

37

Ťažká

What is the GWP value for R32 according to Regulation (EU) 2024/573?


0
3
675
7

38

Ťažká

Why is charge accuracy more important in critically charged R290 systems than in HFC systems?


The charge mass is much smaller than in an HFC system, because the liquid density of R290 is much lower
Because R290 is only used in systems below 150 g
Because such systems never have liquid receivers
Because of lower operating pressures

39

Ťažká

Why does the condenser fan run continuously in some systems using R1270?


To prevent the build-up of contaminants in the condenser
To ensure that the discharge pressure never becomes excessive
To reduce energy consumption
To dilute the refrigerant in the event of a leak

40

Ťažká

What must the label of a flammable refrigerant cylinder include?


Only the net weight
Information about the cylinder owner
The refrigerant name, the UN number, the hazard label (e.g. 2.1 – flammable gas) and basic safety information
Only the refrigerant name

41

Ťažká

Why is the absence of a 'flammable refrigerant' label on equipment a serious hazard?


It may lead to the wrong oil being selected
It reduces system efficiency
It has no significant effect on safety
It may lead to the use of tools that are ignition sources

42

Ťažká

Which set of information on the label of a flammable refrigerant cylinder is crucial from a safety perspective?


Name of the substance, hazard label (ADR) / GHS pictogram (CLP), UN number
Manufacturer’s name and country of origin
Cylinder colour and date of manufacture
Gross weight and batch number

43

Ťažká

What is the purpose of gas detectors in a room with a refrigeration system?


Early leak detection and triggering of measures preventing health risks and explosive atmospheres (alarm, ventilation, shut-off)
Controlling compressor capacity
Measuring refrigerant temperature
Monitoring pipe pressure

44

Ťažká

How often should gas detection sensors in a machinery room be checked?


Once every 5 years
According to the manufacturer's instructions and regulations – at least every 12 months
Before every start-up of the unit
Only after a leak has occurred

45

Ťažká

Where should a gas detector be located according to EN 378?


Anywhere in the room
Near the control panel
Only at the room entrance
Where the refrigerant would accumulate: low (near the floor) for refrigerants heavier than air, high (near the ceiling) for lighter ones such as NH₃

46

Ťažká

What safety checks should be carried out when installing a new refrigeration system with a flammable refrigerant?


Only that the air filter is new
The presence of health and safety signage, adequate ventilation and gas detectors
The colour of pipes and hoses
Only the compressor power

47

Ťažká

What are the requirements for emergency exits from a refrigeration machinery room?


One exit with a sign stating the refrigerant type is sufficient
At least two exits are required and signage is optional
In small machinery rooms emergency exits need not be signed
Outward-opening doors and signed escape routes (number of exits per the standard)

48

Ťažká

Which installation measure for a flammable-refrigerant system improves its energy efficiency?


A thorough tightness test and evacuation (dehydration) of the system
Omitting the filter-drier
Restricting room ventilation
Charging above the nameplate quantity

49

Ťažká

Why is it important to limit the refrigerant charge in HC systems?


It increases capacity
It limits the possibility of reaching a flammable concentration (≥ LFL) in a leak, increasing safety
It lowers the temperature
It doesn't matter

50

Ťažká

What hazards are associated with a safety group A3 refrigerant?


Lower flammability, lower toxicity
Lower toxicity, no flame propagation
Higher toxicity, no flame propagation
Higher flammability, lower toxicity

51

Ťažká

What is the GWP of R32 (per AR4, as used in Regulation (EU) 2024/573)?


6
0
3922
675

52

Ťažká

What factors are taken into account when determining the maximum charge for comfort air-conditioning/heating applications?


Lower flammability limit, room volume
Practical limit, height of the indoor unit, floor area
Lower flammability limit, height of the indoor unit, floor area
Practical limit, room volume

53

Ťažká

What compressor displacement is required for R1270 compared with an R404A compressor in the medium-temperature range (cold room)?


Similar
About half
About 6 times larger
About 1.5 times larger

54

Ťažká

What is the maximum R290 charge per circuit of a commercial refrigerating appliance (e.g. a cabinet) according to EN IEC 60335-2-89:2022?


150 g
1.5 kg
1.2 kg
13 × LFL ≈ 494 g

55

Ťažká

Calculate the maximum R32 charge (LFL = 0.307 kg/m³) for a wall-mounted air conditioner (h₀ = 1.8 m) in a 20 m² room using m_max = 2.5 × LFL^1.25 × h₀ × A^0.5.


approx. 4.6 kg
approx. 1.5 kg
approx. 0.46 kg
approx. 13.8 kg

56

Ťažká

What is the maximum quantity of R290 (class 2, group F) that may be carried per transport unit under the ADR 1.1.3.6 exemption?


1000 kg
333 kg
Unlimited
20 kg

57

Ťažká

What is the charge limit m₃ = 130 m³ × LFL for R290 (LFL = 0.038 kg/m³) according to IEC 60335-2-40?


approx. 0.99 kg
approx. 13 kg
approx. 4.94 kg
approx. 0.15 kg