F-Gas English Low GWP

All questions
HFC | Flammable | CO₂ | NH₃
Easy questions | Medium questions | Difficult questions

1

Difficult

Why do liquid and oil separators in CO₂ systems require particular attention?


Because CO₂ needs no lubrication, so oil separators are unnecessary
Because sight glasses and level indicators must not be used in CO₂ systems
Because CO₂ is flammable and separators must not be used
Because of very high pressures – adequate PS and protection devices are required

2

Difficult

What is the critical pressure of CO₂ (R744)?


Approx. 31 bar
Approx. 74 bar (abs)
Approx. 120 bar
Approx. 10 bar

3

Difficult

What characterises the transcritical process in CO₂ systems?


Heat rejection takes place above the critical point – the refrigerant does not condense in the conventional way (gas cooler instead of condenser)
It is irrelevant to system operation
Conventional condensation occurs
It occurs only at low temperatures

4

Difficult

What characterises the subcritical CO₂ process?


The conventional condensation process below the critical point
Operation above the critical point
The absence of condensation
The absence of evaporation

5

Difficult

When can dry ice (solid CO₂) form?


At high temperature
During normal operation of the system
At high pressure
When the pressure drops suddenly below the triple point (approx. 5.2 bar abs, −56.6 °C), e.g. when venting liquid CO₂ or charging liquid into an evacuated system

6

Difficult

What risks are associated with dry ice forming in a CO₂ system?


Improved efficiency
No risk
Blocked pipes and valves and system damage (and a sharp pressure rise when it thaws)
Pressure reduction

7

Difficult

How does CO₂ saturation pressure change as temperature increases?


It increases rapidly
It decreases
It first decreases, then increases
It remains the same

8

Difficult

What happens to CO₂ above the critical point?


It transitions to a supercritical state (no distinction between liquid and gas)
It turns into a solid
It turns into a liquid
It ceases to conduct heat

9

Difficult

What is the main characteristic of R744 (CO₂) refrigeration systems?


Low operating pressures
Low energy efficiency under all conditions
Very high operating pressures
No need for control

10

Difficult

What are the requirements for piping materials in CO₂ systems?


It doesn't matter
Only plastics
Any material may be used
They must withstand high pressures (e.g. stainless steel, high-strength copper-alloy tubes such as K65)

11

Difficult

How does a booster system work in CO₂ installations?


It reduces evaporator pressure
It is used to store refrigerant
It reduces the refrigerant quantity
Low-temperature (LT) compressors discharge into the suction of medium-temperature (MT) compressors – two-stage compression in a single circuit

12

Difficult

Why is pressure optimisation in CO₂ systems crucial?


It reduces the ambient temperature
It doesn’t matter
It enables the system to achieve maximum energy efficiency in transcritical mode
It reduces the amount of refrigerant

13

Difficult

What role does parallel compression play in CO₂ systems?


It compresses flash gas from the intermediate receiver directly to high pressure, improving efficiency
It increases energy consumption
It lowers the ambient temperature
It has no significance

14

Difficult

How does an ejector work in a CO₂ system?


It uses the energy of the higher-pressure refrigerant to raise the pressure of the refrigerant from the lower stage, which improves efficiency
Stores the refrigerant
It increases the amount of refrigerant
It lowers the evaporator temperature

15

Difficult

What is the function of liquid ejectors in CO₂ systems?


They return liquid from the separator and allow partially flooded evaporator operation (better evaporator feed)
They increase the amount of oil
They raise the refrigerant temperature
They reduce atmospheric pressure

16

Difficult

What are the characteristics of partially flooded systems in CO₂ systems?


The presence of liquid in the evaporator, which improves heat transfer and efficiency
Low operating pressure
Lack of regulation
The absence of liquid in the evaporator

17

Difficult

What is the main risk associated with standstill pressure in CO₂ systems?


A drop in temperature
Increased efficiency
A pressure rise as the refrigerant warms up during standstill (possibly exceeding PS and lifting the relief valves)
A decrease in refrigerant quantity

18

Difficult

How is standstill pressure limited in CO₂ systems?


By using an auxiliary standstill (stagnation) cooling unit, e.g. cooling the receiver, with back-up power, and by selecting an adequate PS and relief valves
By completely shutting down the system and power supply
By raising the plant-room temperature
By increasing the refrigerant charge

19

Difficult

What does standstill (stagnation) of a CO₂ system mean, and why is it important?


A state with no compressor operation or refrigerant flow – pressure rises with ambient temperature and may exceed PS
Normal system operation
A drop in system temperature
Improved efficiency

20

Difficult

Which safety class applies to R744?


A2.
A3
B2L
A1

21

Difficult

In a simple single-stage R744 system without an intermediate receiver (refrigerant flows from the gas cooler directly to the expansion valve), operating transcritically at 90 bar with a gas-cooler outlet temperature of 35 °C, the refrigerant upstream of the expansion valve is…


…a supercritical fluid
…a subcooled liquid
…a two-phase mixture at intermediate pressure
…saturated vapour at intermediate pressure

22

Difficult

In R744 transcritical systems, the gas cooler outlet valve controls:


The gas cooler fans
The pressure in the gas cooler
The outlet temperature of the gas cooler
The inlet temperature to the gas cooler

23

Difficult

What is the main reason for using K65 copper tubing in some R744 systems?


They can withstand higher pressures
They bend easily
They come in a wider range of diameters
They have good low-temperature performance

24

Difficult

Why should an evacuated R744 system initially be charged with refrigerant in the vapour phase?


To charge R744 more slowly and measure it more accurately
To prevent the drain valve on the receiver from opening
To prevent dry ice forming (until approx. 5.2 bar abs is exceeded)
To avoid damaging the compressor with liquid CO₂

25

Difficult

If moisture remains in an R744 system because it was not properly evacuated (dehydrated), what is the likely consequence?


Formation of hydrogen fluoride and hydrofluoric acid
Excessive discharge pressure
Reduced cooling capacity
Formation of carbonic acid, which damages the system

26

Difficult

The pressure of R744 at a saturation temperature of 20 °C is approx.


56 bar g
90 bar g
14 bar g
25 bar g

27

Difficult

At an ambient temperature of 25 °C, the standstill pressure in the low-pressure stage of an R744 cascade (without standstill cooling) will typically be…


…approx. 27.5 bar g
…the same as the relief valve set pressure
…higher than the maximum allowable pressure (PS) of the low-pressure stage
…the same as the high-pressure switch setting

28

Difficult

What is the correct definition of critical temperature?


The temperature above which there are no distinct liquid and gaseous phases
The temperature at which the vapour pressure of a liquid is equal to the ambient pressure surrounding the liquid
The temperature at which, for certain substances, electrical resistance is zero
The temperature at which a substance changes from a gaseous to a solid state

29

Difficult

In the gas cooler of a transcritical system, the supercritical working fluid…


…rejects heat at constant temperature and pressure
…rejects heat as its temperature falls
…rejects heat as its pressure falls
…rejects heat during a phase change

30

Difficult

Why does the efficiency of transcritical CO₂ systems fall in warm climates, and how is this mitigated?


At high ambient temperatures the system operates transcritically with large throttling losses – parallel compression and ejectors are used, among others
CO₂ freezes in the gas cooler – heaters are used
Efficiency does not depend on climate
Gas cooler pressure drops – extra charge is added