F-Gas English Low GWP

All questions
HFC | Flammable | CO₂ | NH₃
Easy questions | Medium questions | Difficult questions

1

Difficult

What is the main difference between a dry-expansion and a flooded evaporator?


A dry-expansion evaporator needs no expansion valve, a flooded one does
In a dry-expansion evaporator the refrigerant completely evaporates and is superheated in the evaporator; in a flooded one part of the refrigerant remains liquid (incomplete evaporation, no superheat)
A dry-expansion evaporator is filled with liquid, a flooded one with vapour
A dry-expansion evaporator always has a lower pressure than a flooded one

2

Difficult

What is the typical pressure in the evaporator of an R717 deep-freeze system (below −40 °C)?


Positive pressure of 5–10 bar
Below atmospheric (approx. 0.7 bar abs at −40 °C)
Atmospheric pressure, approx. 1 bar abs
Positive pressure of 10–20 bar

3

Difficult

How is oil managed in R717 systems?


Oil requires no monitoring
Oil collecting at the lowest points of vessels is regularly checked and drained, because it impairs heat transfer
Oil can be mixed with any refrigerant
Oil has no effect on system operation

4

Difficult

What should be done with contaminated R717?


Continue to use it without restriction
Release it into the atmosphere
Purify it or send it for disposal in accordance with regulations
Dilute it with water and reuse it

5

Difficult

What should be done if an NH₃ leak is detected?


Carry on working wearing a dust mask
Evacuate people immediately and raise the alarm; stop the leak only if it is safe to do so and with suitable PPE (respiratory protection)
Increase the pressure in the system
Carry on working with the room door open

6

Difficult

What role do scrubbers play in NH₃ systems?


They increase the pressure in the system
They store the refrigerant
Neutralise ammonia through absorption in a liquid (e.g. water)
They are used to measure temperature

7

Difficult

How should the system be prepared before filling with R717?


Check for leaks, remove air and moisture, and create a vacuum
The pressure must be increased above the standard level
Simply start it up
There is no need to check it

8

Difficult

What are the transport requirements for R717?


Transport is not regulated
It must be carried in suitable, labelled packagings in accordance with ADR (UN 1005, class 2, code 2TC)
It can be carried in open containers
It can be carried without labelling

9

Difficult

Which statement best describes the behaviour of R717 and mineral compressor oil?


R717 does not mix with the oil; the oil collects on the high-pressure side above the R717
R717 does not mix with the oil; the oil, being heavier than liquid NH₃, collects beneath it at the lowest points (mainly on the low-pressure side)
R717 mixes very well with the oil, which easily returns to the compressor
An oil return line cannot be used in R717 systems because the oil is too hot

10

Difficult

Which refrigerant can be detected with phenolphthalein paper?


R744
R1270
R717
R1234ze(E)

11

Difficult

Which system may require manual oil recovery?


Secondary system using R744
R744 cascade system
Supercritical ‘booster’ system using R744
An R717 system

12

Difficult

Which refrigerant is lighter than air?


R1234ze(E)
R1270
R744
R717

13

Difficult

R717 is highly corrosive to:


stainless steel
copper (and its alloys)
aluminium
titanium

14

Difficult

What is the recommended pre-alarm level for fixed leak detection systems for R717?


500,000 ppm
5,000 ppm
50,000 ppm
500 ppm

15

Difficult

Why are compressors with a separate motor (open type) mostly used in R717 systems?


To increase the refrigerant charge
Because NH₃ attacks copper motor windings, so hermetic compressors with conventional windings are not used
Because they are cheaper
To lower the condensing pressure

16

Difficult

Which type of compressor is most commonly used in large ammonia systems?


Hermetic scroll
Diaphragm compressor
Rotary vane compressor
A reciprocating or screw compressor

17

Difficult

How is the capacity of a piston compressor regulated in NH₃ systems?


Solely by adjusting the oil volume
By reducing the refrigerant charge
By unloading the cylinders or changing the rotational speed
By increasing the condensing pressure

18

Difficult

How is the capacity of a screw compressor most commonly controlled?


By adjusting the oil level
By using a slide valve
By closing the suction valve
By changing the type of oil

19

Difficult

When is two-stage compression used in NH₃ systems?


Only with water-cooled condensers
Only in small systems
At low evaporating temperatures (pressures) and high pressure ratios
At small temperature differences

20

Difficult

What is the advantage of two-stage compression over single-stage compression?


Higher efficiency and lower discharge temperature
Higher energy consumption
No need for a separator
Lower efficiency

21

Difficult

How does an evaporative condenser used in NH₃ systems work?


It transfers heat only to the air
Operates without a fan
It utilises the evaporation of water to increase cooling efficiency
It does not require a water supply

22

Difficult

What is the function of the liquid separator in an NH₃ system?


It prevents liquid from entering the compressor
Regulates the condensing pressure
It separates oil from the refrigerant
Increases the discharge temperature

23

Difficult

What is the purpose of monitoring the liquid level in the separator?


To control the condenser fan
To maintain the correct refrigerant level and prevent the compressor from flooding
To increase the oil volume
To reduce the condensing temperature

24

Difficult

What is the role of the float switch in NH₃ systems?


It controls the fan’s operation
It monitors the liquid level in the tank or separator
It is used to detect leaks
It regulates the condensation temperature

25

Difficult

What is a thermosyphon in NH₃ systems?


A defrosting device
A system with gravity-driven (natural) circulation of liquid refrigerant caused by density differences, used e.g. for screw compressor oil cooling
An oil circulation pump
A type of safety valve

26

Difficult

Why are oils that are immiscible with the refrigerant used in NH₃ systems?


Because NH₃ does not mix with most compressor oils
To increase the amount of refrigerant
Because the oil mixes only with water
To reduce the pressure

27

Difficult

What is the main function of an oil separator in NH₃ systems?


To separate the oil from the refrigerant and return the oil to the compressor
To increase fan efficiency
To lower the condensation temperature
Removing moisture from the system

28

Difficult

In which NH₃ system does the refrigerant evaporate completely with superheat in the evaporator, fed by an expansion valve?


A pumped liquid-recirculation system
A direct-expansion (DX) system
A glycol system
An indirect system

29

Difficult

What is the characteristic feature of a flooded evaporator system?


No level control is required
The evaporator contains a large amount of liquid, which improves heat transfer
The evaporator is filled exclusively with vapour
No separator is used

30

Difficult

What is the main difference between a direct and an indirect system?


In an indirect system, NH₃ flows directly into the space being cooled
In an indirect system, no compressor is used
In an indirect system, NH₃ cools an intermediate medium (e.g. glycol), which in turn cools the load
In a direct system, there is no evaporator