1

Ťažká

What additional protective equipment will you use when brazing systems containing HC refrigerants?


A high-visibility vest
Ear defenders
A flammable gas detector
Latex gloves

2

Ťažká

Why can’t a sealed high-pressure switch be replaced with a standard mechanical one in a system containing a flammable refrigerant?


Dust and moisture may enter
There is a risk of refrigerant leakage
The pressure switch setting will not be correct
It is a potential source of ignition

3

Ťažká

What is the minimum (recommended) distance from a work area with HC refrigerants within which there must be no sources of ignition?


1 m
0.5 m
2 m
3 m

4

Ťažká

What is the maximum safe R32 fill of a recovery cylinder approved for flammable gas that holds 20 kg of R410A (the liquid density of R32 is about 8-10% lower)?


33 kg
9 kg
18 kg
20 kg

5

Ťažká

What is the maximum charge of an A3 refrigerant for a hermetic display cabinet with an integral condenser located in the ground-floor sales area of a supermarket?


1.0 kg
10 kg
2.5 kg
0,494 kg

6

Ťažká

How can a vacuum pump be used safely to evacuate a system containing a flammable refrigerant?


Such systems need not be evacuated before charging
Place the pump directly on the floor, as low as possible
Ignition-source-free pump, good ventilation, exhaust to a safe place
Position the pump at least 3 m above floor level

7

Ťažká

What safety measure must you carry in your vehicle when transporting flammable refrigerant cylinders?


A fire blanket
Tinted safety goggles
A fire extinguisher
Thick gloves

8

Ťažká

How would you prepare a 10 kg R32 water chiller located outdoors for debrazing its joints?


Recover the R32 to a vacuum, then fill the system with nitrogen to a slight positive pressure (approx. 0.1 bar g)
Recover the R32 to a vacuum and start desoldering immediately
Vent the R32 outdoors, then fill and vent the system with nitrogen three times
Vent the R32 outdoors and purge the system

9

Ťažká

Which of the following leak detection methods should NOT be used to locate an HC refrigerant leak?


Soapy water solution
Electronic leak detector for flammable refrigerants
Leak detection foam
Electronic HFC leak detector

10

Ťažká

What is the most important difference between a flammable refrigerant recovery unit and a standard one?


Different low-pressure switch setting
A flammable refrigerant recovery unit has no ignition sources
Different connection sizes
A different colour for the station

11

Ťažká

Which of the following is a source of ignition?


An 'n'-type (non-sparking) thermostat
A contactor (sparking contacts)
A sealed NTC temperature sensor
An Ex-certified fan motor

12

Ťažká

What particularly hazardous substance is formed when R32 burns?


Phosgene
Hydrogen chloride (HCl)
Hydrogen fluoride (HF)
Sulphur dioxide (SO₂)

13

Ťažká

What type of refrigerant is R1234ze(E)?


HCFC (hydrochlorofluorocarbon)
HC (hydrocarbon)
HFO (hydrofluoroolefin)
CFC (chlorofluorocarbon)

14

Ťažká

What hazards does a safety group A3 refrigerant pose?


Lower toxicity, higher flammability
Higher toxicity, moderate flammability
Lower toxicity, moderate flammability
Higher toxicity, higher flammability

15

Ťažká

According to EN 378, what is the maximum R290 charge in a cold room measuring 5 m × 3 m × 2.5 m (LFL of R290 = 0.038 kg/m³, access category a, location class I, no additional measures))?


0.285 kg
1.0 kg
4.93 kg
1.5 kg

16

Ťažká

What is the approximate ratio of the volumetric cooling capacity of R32 to that of R410A (same compressor and conditions)?


approx. 1.3
approx. 1.05–1.1
approx. 0.6
approx. 0.75

17

Ťažká

Why are Ex-certified evaporator fan motors used in some systems with flammable refrigerants?


Because they must be kept running continuously to disperse the leaking refrigerant
Because they are more energy-efficient
To avoid a source of ignition in the event of a flammable refrigerant leak
Because they are more reliable

18

Ťažká

Why is the density difference between HC and HFC refrigerants important?


Because it determines the system's energy efficiency
Because HCs operate at much higher pressures
An HC charge in kg is roughly half that of an HFC
Because HCs must be charged much more slowly than HFCs

19

Ťažká

What is the GWP of R290 according to Annex VI to Regulation (EU) 2024/573?


150
7
675
0.02

20

Ťažká

Which of the following is NOT a source of ignition?


An unsealed mechanical pressure switch
An electrical switch
An Ex-certified fan motor
A light switch

21

Ťažká

What is R290?


Isobutane
Propane
Butane
Propene (Propylene)

22

Ťažká

What is the maximum A2L charge for a hermetic display cabinet with integral condenser in the ground-floor sales area of a supermarket?


1.5 kg
1.2 kg
150 g
2.5 kg

23

Ťažká

Why can’t a standard relay be fitted when retrofitting a compressor’s electrical system for flammable refrigerants?


A relay is never required for compressors using flammable refrigerants
It could be a source of ignition
The method of starting the compressor motor differs from that used with HFCs
Current consumption differs for compressors using flammable refrigerants compared to those using HFCs

24

Ťažká

What is the minimum (recommended) distance from a work area with HC refrigerants within which there must be no ignition sources?


10 m
5 m
3 m
1 m

25

Ťažká

A recovery cylinder holds 10 kg of R404A (filling ratio 0.82 kg/l). What is the maximum R290 charge for this cylinder (propane filling ratio 0.43 kg/l per ADR P200)?


approx. 8 kg
approx. 5.2 kg
approx. 17 kg
20 kg

26

Ťažká

How can a vacuum pump be used safely to evacuate a system containing R290?


R290 systems need not be evacuated before charging
Ignition-source-free pump, good ventilation, exhaust to a safe place
Position the pump at least 3 m above floor level
Place the pump directly on the floor, as low as possible

27

Ťažká

Under ADR, what equipment must you carry in your vehicle when transporting flammable refrigerant cylinders (under the 1.1.3.6 exemption)?


Thick gloves
A fire extinguisher (at least 2 kg dry powder)
A fire blanket
Tinted safety goggles

28

Ťažká

How do you make sure it is safe to light the torch for desoldering joints in a system from which a flammable refrigerant has been removed?


Such joints must never be desoldered; they must be cut with a pipe cutter
Purge the system with compressed air
Working outdoors is sufficient
Ensure good ventilation and check the work area with a flammable gas detector

29

Ťažká

How would you prepare a system containing 100 g of R1270 for debrazing, if local regulations allow controlled venting of small HC quantities?


Vent the R1270 to a safe outdoor location, then purge with OFN three times (pressurise and vent), and braze with OFN flowing
Vent the R1270 into the room and open a window
Recover the R1270 to a vacuum and start brazing immediately without a nitrogen purge
Vent the R1270 outdoors and start brazing immediately

30

Ťažká

Which method should NOT be used to locate an R290 leak?


Fluorescent dye and UV lamp (if approved by the manufacturer)
An electronic leak detector designed for HFCs
An electronic detector for flammable refrigerants
Leak detection foam

31

Ťažká

Why can’t recovery stations designed for HFCs be used with R600a?


They contain ignition sources
The oil in the recovery unit is not soluble in R600a
The low-pressure switch setting will not be suitable for R600a due to its lower operating pressure
The recovery unit cannot withstand the working pressure of R600a

32

Ťažká

According to EN 378, what is the maximum R1234ze(E) charge in a cold room measuring 5 m × 3 m × 2.5 m (LFL = 0.303 kg/m³, access category a, location class I, no additional measures)?


2.27 kg
227 kg
618 kg
6.18 kg

33

Ťažká

What type of refrigerant is R32?


Carbon dioxide
Hydrocarbon
Hydrofluorocarbon
Hydrofluoroolefin

34

Ťažká

What hazards do A2L refrigerants pose?


Higher toxicity, lower flammability
Lower toxicity, higher flammability
Lower toxicity, lower flammability (burning velocity ≤ 10 cm/s)
Higher toxicity, higher flammability

35

Ťažká

What hazard is associated with the combustion of HFO or HFC refrigerants?


Ozone is formed
Nitrous oxide is formed
Phosgene is formed
Hydrogen fluoride (HF) is formed

36

Ťažká

Approximately what compressor displacement is required for R600a compared with R134a for the same cooling capacity?


About half
The same
About seven times as large
About twice as large

37

Ťažká

What is the GWP value for R32 according to Regulation (EU) 2024/573?


0
675
3
7

38

Ťažká

Why is charge accuracy more important in critically charged R290 systems than in HFC systems?


Because R290 is only used in systems below 150 g
Because such systems never have liquid receivers
The charge mass is much smaller than in an HFC system, because the liquid density of R290 is much lower
Because of lower operating pressures

39

Ťažká

Why does the condenser fan run continuously in some systems using R1270?


To reduce energy consumption
To dilute the refrigerant in the event of a leak
To prevent the build-up of contaminants in the condenser
To ensure that the discharge pressure never becomes excessive

40

Ťažká

What is the role of a suction liquid separator (also in systems with flammable or toxic refrigerants)?


It is used only to measure moisture
It heats the refrigerant before the evaporator
It separates liquid from oil
It prevents liquid refrigerant from entering the compressor

41

Ťažká

What is the function of an oil separator in systems using flammable or toxic refrigerants?


It prevents liquid from entering the compressor
They are used solely to measure the moisture content of the refrigerant
Separates oil from the refrigerant and facilitates the return of oil to the compressor
Heats the refrigerant before it enters the evaporator

42

Ťažká

Why do liquid and oil separators in CO₂ systems require particular attention?


Because CO₂ needs no lubrication, so oil separators are unnecessary
Because of very high pressures – adequate PS and protection devices are required
Because CO₂ is flammable and separators must not be used
Because sight glasses and level indicators must not be used in CO₂ systems

43

Ťažká

What is the critical pressure of CO₂ (R744)?


Approx. 120 bar
Approx. 10 bar
Approx. 31 bar
Approx. 74 bar (abs)

44

Ťažká

What characterises the transcritical process in CO₂ systems?


Heat rejection takes place above the critical point – the refrigerant does not condense in the conventional way (gas cooler instead of condenser)
Conventional condensation occurs
It is irrelevant to system operation
It occurs only at low temperatures

45

Ťažká

What characterises the subcritical CO₂ process?


The absence of evaporation
Operation above the critical point
The absence of condensation
The conventional condensation process below the critical point

46

Ťažká

When can dry ice (solid CO₂) form?


When the pressure drops suddenly below the triple point (approx. 5.2 bar abs, −56.6 °C), e.g. when venting liquid CO₂ or charging liquid into an evacuated system
During normal operation of the system
At high temperature
At high pressure

47

Ťažká

What risks are associated with dry ice forming in a CO₂ system?


Improved efficiency
Pressure reduction
Blocked pipes and valves and system damage (and a sharp pressure rise when it thaws)
No risk

48

Ťažká

How does CO₂ saturation pressure change as temperature increases?


It decreases
It remains the same
It first decreases, then increases
It increases rapidly

49

Ťažká

What happens to CO₂ above the critical point?


It turns into a liquid
It transitions to a supercritical state (no distinction between liquid and gas)
It turns into a solid
It ceases to conduct heat

50

Ťažká

What is the main difference between a dry-expansion and a flooded evaporator?


A dry-expansion evaporator always has a lower pressure than a flooded one
A dry-expansion evaporator needs no expansion valve, a flooded one does
In a dry-expansion evaporator the refrigerant completely evaporates and is superheated in the evaporator; in a flooded one part of the refrigerant remains liquid (incomplete evaporation, no superheat)
A dry-expansion evaporator is filled with liquid, a flooded one with vapour

51

Ťažká

What is the typical pressure in the evaporator of an R717 deep-freeze system (below −40 °C)?


Positive pressure of 5–10 bar
Positive pressure of 10–20 bar
Below atmospheric (approx. 0.7 bar abs at −40 °C)
Atmospheric pressure, approx. 1 bar abs

52

Ťažká

Why are PFAS formed by the decomposition of certain F-gases (e.g. TFA from HFOs) problematic?


They cause rapid cooling of the atmosphere
They are very persistent, accumulate in the environment (e.g. water) and may be toxic
They are climate- and environment-neutral
They are readily biodegradable

53

Ťažká

How is oil managed in R717 systems?


Oil can be mixed with any refrigerant
Oil collecting at the lowest points of vessels is regularly checked and drained, because it impairs heat transfer
Oil requires no monitoring
Oil has no effect on system operation

54

Ťažká

What should be done with contaminated R717?


Continue to use it without restriction
Purify it or send it for disposal in accordance with regulations
Release it into the atmosphere
Dilute it with water and reuse it

55

Ťažká

What should be done if an NH₃ leak is detected?


Carry on working with the room door open
Evacuate people immediately and raise the alarm; stop the leak only if it is safe to do so and with suitable PPE (respiratory protection)
Increase the pressure in the system
Carry on working wearing a dust mask

56

Ťažká

What role do scrubbers play in NH₃ systems?


They store the refrigerant
Neutralise ammonia through absorption in a liquid (e.g. water)
They increase the pressure in the system
They are used to measure temperature

57

Ťažká

How should the system be prepared before filling with R717?


Check for leaks, remove air and moisture, and create a vacuum
The pressure must be increased above the standard level
Simply start it up
There is no need to check it

58

Ťažká

What are the transport requirements for R717?


Transport is not regulated
It can be carried without labelling
It can be carried in open containers
It must be carried in suitable, labelled packagings in accordance with ADR (UN 1005, class 2, code 2TC)

59

Ťažká

What is the main characteristic of R744 (CO₂) refrigeration systems?


Low energy efficiency under all conditions
Very high operating pressures
No need for control
Low operating pressures

60

Ťažká

What are the requirements for piping materials in CO₂ systems?


It doesn't matter
Only plastics
They must withstand high pressures (e.g. stainless steel, high-strength copper-alloy tubes such as K65)
Any material may be used

61

Ťažká

How does a booster system work in CO₂ installations?


It reduces the refrigerant quantity
Low-temperature (LT) compressors discharge into the suction of medium-temperature (MT) compressors – two-stage compression in a single circuit
It is used to store refrigerant
It reduces evaporator pressure

62

Ťažká

Why is pressure optimisation in CO₂ systems crucial?


It reduces the ambient temperature
It doesn’t matter
It enables the system to achieve maximum energy efficiency in transcritical mode
It reduces the amount of refrigerant

63

Ťažká

What role does parallel compression play in CO₂ systems?


It compresses flash gas from the intermediate receiver directly to high pressure, improving efficiency
It increases energy consumption
It has no significance
It lowers the ambient temperature

64

Ťažká

How does an ejector work in a CO₂ system?


It increases the amount of refrigerant
It uses the energy of the higher-pressure refrigerant to raise the pressure of the refrigerant from the lower stage, which improves efficiency
It lowers the evaporator temperature
Stores the refrigerant

65

Ťažká

What is the function of liquid ejectors in CO₂ systems?


They raise the refrigerant temperature
They return liquid from the separator and allow partially flooded evaporator operation (better evaporator feed)
They reduce atmospheric pressure
They increase the amount of oil

66

Ťažká

What are the characteristics of partially flooded systems in CO₂ systems?


The absence of liquid in the evaporator
The presence of liquid in the evaporator, which improves heat transfer and efficiency
Low operating pressure
Lack of regulation

67

Ťažká

What is the main risk associated with standstill pressure in CO₂ systems?


A drop in temperature
A decrease in refrigerant quantity
A pressure rise as the refrigerant warms up during standstill (possibly exceeding PS and lifting the relief valves)
Increased efficiency

68

Ťažká

How is standstill pressure limited in CO₂ systems?


By increasing the refrigerant charge
By completely shutting down the system and power supply
By raising the plant-room temperature
By using an auxiliary standstill (stagnation) cooling unit, e.g. cooling the receiver, with back-up power, and by selecting an adequate PS and relief valves

69

Ťažká

What does standstill (stagnation) of a CO₂ system mean, and why is it important?


Improved efficiency
A drop in system temperature
A state with no compressor operation or refrigerant flow – pressure rises with ambient temperature and may exceed PS
Normal system operation

70

Ťažká

What must the label of a flammable refrigerant cylinder include?


The refrigerant name, the UN number, the hazard label (e.g. 2.1 – flammable gas) and basic safety information
Information about the cylinder owner
Only the net weight
Only the refrigerant name

71

Ťažká

Why is the absence of a 'flammable refrigerant' label on equipment a serious hazard?


It may lead to the wrong oil being selected
It has no significant effect on safety
It reduces system efficiency
It may lead to the use of tools that are ignition sources

72

Ťažká

Which set of information on the label of a flammable refrigerant cylinder is crucial from a safety perspective?


Gross weight and batch number
Name of the substance, hazard label (ADR) / GHS pictogram (CLP), UN number
Manufacturer’s name and country of origin
Cylinder colour and date of manufacture

73

Ťažká

What is the purpose of gas detectors in a room with a refrigeration system?


Measuring refrigerant temperature
Monitoring pipe pressure
Early leak detection and triggering of measures preventing health risks and explosive atmospheres (alarm, ventilation, shut-off)
Controlling compressor capacity

74

Ťažká

How often should gas detection sensors in a machinery room be checked?


According to the manufacturer's instructions and regulations – at least every 12 months
Once every 5 years
Only after a leak has occurred
Before every start-up of the unit

75

Ťažká

Where should a gas detector be located according to EN 378?


Near the control panel
Only at the room entrance
Where the refrigerant would accumulate: low (near the floor) for refrigerants heavier than air, high (near the ceiling) for lighter ones such as NH₃
Anywhere in the room

76

Ťažká

What safety checks should be carried out when installing a new refrigeration system with a flammable refrigerant?


The presence of health and safety signage, adequate ventilation and gas detectors
Only that the air filter is new
The colour of pipes and hoses
Only the compressor power

77

Ťažká

What are the requirements for emergency exits from a refrigeration machinery room?


In small machinery rooms emergency exits need not be signed
One exit with a sign stating the refrigerant type is sufficient
Outward-opening doors and signed escape routes (number of exits per the standard)
At least two exits are required and signage is optional

78

Ťažká

Which installation measure for a flammable-refrigerant system improves its energy efficiency?


Omitting the filter-drier
Charging above the nameplate quantity
Restricting room ventilation
A thorough tightness test and evacuation (dehydration) of the system

79

Ťažká

Why is it important to limit the refrigerant charge in HC systems?


It limits the possibility of reaching a flammable concentration (≥ LFL) in a leak, increasing safety
It doesn't matter
It lowers the temperature
It increases capacity

80

Ťažká

Which safety class applies to R744?


A1
B2L
A3
A2.

81

Ťažká

In a simple single-stage R744 system without an intermediate receiver (refrigerant flows from the gas cooler directly to the expansion valve), operating transcritically at 90 bar with a gas-cooler outlet temperature of 35 °C, the refrigerant upstream of the expansion valve is…


…a supercritical fluid
…a subcooled liquid
…saturated vapour at intermediate pressure
…a two-phase mixture at intermediate pressure

82

Ťažká

In R744 transcritical systems, the gas cooler outlet valve controls:


The pressure in the gas cooler
The gas cooler fans
The outlet temperature of the gas cooler
The inlet temperature to the gas cooler

83

Ťažká

Which statement best describes the behaviour of R717 and mineral compressor oil?


R717 mixes very well with the oil, which easily returns to the compressor
An oil return line cannot be used in R717 systems because the oil is too hot
R717 does not mix with the oil; the oil, being heavier than liquid NH₃, collects beneath it at the lowest points (mainly on the low-pressure side)
R717 does not mix with the oil; the oil collects on the high-pressure side above the R717

84

Ťažká

What is the main reason for using K65 copper tubing in some R744 systems?


They can withstand higher pressures
They come in a wider range of diameters
They bend easily
They have good low-temperature performance

85

Ťažká

Which statement about installing Schrader valves is correct?


All Schrader cores are suitable for all refrigerants
Schrader valves must not be used in R744 systems
When brazing the valve body, the core must be removed, then refitted and tightened to the correct torque
Hydrocarbons leak through Schrader valves

86

Ťažká

Which refrigerant can be detected with phenolphthalein paper?


R1270
R1234ze(E)
R717
R744

87

Ťažká

How does an undercharge affect the high-pressure side (without discharge pressure control)?


Discharge pressure higher, subcooling lower
Discharge (condensing) pressure and subcooling will both be lower
Discharge pressure lower, subcooling higher
Discharge pressure higher, subcooling higher

88

Ťažká

What is the benefit of adding helium as a tracer gas to nitrogen in a pressure test?


It has a higher pressure than pure nitrogen in the same cylinder
It has a distinctive odour that helps locate the leak
Its small atoms pass easily through leaks and are detected
It reacts with refrigerant residues, producing a visible colour change

89

Ťažká

Why should an evacuated R744 system initially be charged with refrigerant in the vapour phase?


To charge R744 more slowly and measure it more accurately
To prevent the drain valve on the receiver from opening
To prevent dry ice forming (until approx. 5.2 bar abs is exceeded)
To avoid damaging the compressor with liquid CO₂

90

Ťažká

If moisture remains in an R744 system because it was not properly evacuated (dehydrated), what is the likely consequence?


Reduced cooling capacity
Formation of hydrogen fluoride and hydrofluoric acid
Formation of carbonic acid, which damages the system
Excessive discharge pressure

91

Ťažká

Which system may require manual oil recovery?


Supercritical ‘booster’ system using R744
R744 cascade system
Secondary system using R744
An R717 system

92

Ťažká

The pressure of R744 at a saturation temperature of 20 °C is approx.


90 bar g
56 bar g
25 bar g
14 bar g

93

Ťažká

Which refrigerant is lighter than air?


R1270
R717
R744
R1234ze(E)

94

Ťažká

What hazards are associated with a safety group A3 refrigerant?


Higher toxicity, no flame propagation
Higher flammability, lower toxicity
Lower toxicity, no flame propagation
Lower flammability, lower toxicity

95

Ťažká

What is the GWP of R32 (per AR4, as used in Regulation (EU) 2024/573)?


0
6
3922
675

96

Ťažká

What factors are taken into account when determining the maximum charge for comfort air-conditioning/heating applications?


Lower flammability limit, height of the indoor unit, floor area
Practical limit, room volume
Practical limit, height of the indoor unit, floor area
Lower flammability limit, room volume

97

Ťažká

What compressor displacement is required for R1270 compared with an R404A compressor in the medium-temperature range (cold room)?


About 1.5 times larger
Similar
About half
About 6 times larger

98

Ťažká

At an ambient temperature of 25 °C, the standstill pressure in the low-pressure stage of an R744 cascade (without standstill cooling) will typically be…


…approx. 27.5 bar g
…higher than the maximum allowable pressure (PS) of the low-pressure stage
…the same as the relief valve set pressure
…the same as the high-pressure switch setting

99

Ťažká

What is the correct definition of critical temperature?


The temperature above which there are no distinct liquid and gaseous phases
The temperature at which the vapour pressure of a liquid is equal to the ambient pressure surrounding the liquid
The temperature at which, for certain substances, electrical resistance is zero
The temperature at which a substance changes from a gaseous to a solid state

100

Ťažká

In the gas cooler of a transcritical system, the supercritical working fluid…


…rejects heat as its pressure falls
…rejects heat at constant temperature and pressure
…rejects heat during a phase change
…rejects heat as its temperature falls

101

Ťažká

R717 is highly corrosive to:


stainless steel
copper (and its alloys)
titanium
aluminium

102

Ťažká

What can be the effect of a relief valve lifting repeatedly?


The valve stays fully open permanently
The valve no longer opens
The set pressure increases
The valve may not reseat tightly and its set (opening) pressure may decrease

103

Ťažká

What is the relationship between the pressure (p) and temperature (T) of nitrogen at the start (1) and end (2) of a tightness test (p absolute, T in kelvin)?


p₂ = (p₁ × T₁)/T₂
p₂ = (p₁ × T₂)/T₁
p₂ = T₂/(p₁ × T₁)
p₂ = T₁/(p₁ × T₂)

104

Ťažká

What is the recommended pre-alarm level for fixed leak detection systems for R717?


500 ppm
500,000 ppm
50,000 ppm
5,000 ppm

105

Ťažká

Why are compressors with a separate motor (open type) mostly used in R717 systems?


Because they are cheaper
Because NH₃ attacks copper motor windings, so hermetic compressors with conventional windings are not used
To increase the refrigerant charge
To lower the condensing pressure

106

Ťažká

Which type of compressor is most commonly used in large ammonia systems?


A reciprocating or screw compressor
Hermetic scroll
Rotary vane compressor
Diaphragm compressor

107

Ťažká

How is the capacity of a piston compressor regulated in NH₃ systems?


By reducing the refrigerant charge
By increasing the condensing pressure
Solely by adjusting the oil volume
By unloading the cylinders or changing the rotational speed

108

Ťažká

How is the capacity of a screw compressor most commonly controlled?


By using a slide valve
By changing the type of oil
By adjusting the oil level
By closing the suction valve

109

Ťažká

When is two-stage compression used in NH₃ systems?


At low evaporating temperatures (pressures) and high pressure ratios
At small temperature differences
Only in small systems
Only with water-cooled condensers

110

Ťažká

What is the advantage of two-stage compression over single-stage compression?


Higher efficiency and lower discharge temperature
No need for a separator
Higher energy consumption
Lower efficiency

111

Ťažká

How does an evaporative condenser used in NH₃ systems work?


It transfers heat only to the air
It utilises the evaporation of water to increase cooling efficiency
It does not require a water supply
Operates without a fan

112

Ťažká

What is the function of the liquid separator in an NH₃ system?


Regulates the condensing pressure
It separates oil from the refrigerant
It prevents liquid from entering the compressor
Increases the discharge temperature

113

Ťažká

What is the purpose of monitoring the liquid level in the separator?


To control the condenser fan
To maintain the correct refrigerant level and prevent the compressor from flooding
To increase the oil volume
To reduce the condensing temperature

114

Ťažká

What is the role of the float switch in NH₃ systems?


It regulates the condensation temperature
It is used to detect leaks
It monitors the liquid level in the tank or separator
It controls the fan’s operation

115

Ťažká

What is a thermosyphon in NH₃ systems?


An oil circulation pump
A system with gravity-driven (natural) circulation of liquid refrigerant caused by density differences, used e.g. for screw compressor oil cooling
A type of safety valve
A defrosting device

116

Ťažká

Why are oils that are immiscible with the refrigerant used in NH₃ systems?


To reduce the pressure
Because the oil mixes only with water
To increase the amount of refrigerant
Because NH₃ does not mix with most compressor oils

117

Ťažká

What is the main function of an oil separator in NH₃ systems?


To increase fan efficiency
Removing moisture from the system
To separate the oil from the refrigerant and return the oil to the compressor
To lower the condensation temperature

118

Ťažká

In which NH₃ system does the refrigerant evaporate completely with superheat in the evaporator, fed by an expansion valve?


An indirect system
A direct-expansion (DX) system
A pumped liquid-recirculation system
A glycol system

119

Ťažká

What is the characteristic feature of a flooded evaporator system?


No level control is required
The evaporator is filled exclusively with vapour
The evaporator contains a large amount of liquid, which improves heat transfer
No separator is used

120

Ťažká

What is the main difference between a direct and an indirect system?


In an indirect system, NH₃ cools an intermediate medium (e.g. glycol), which in turn cools the load
In an indirect system, no compressor is used
In a direct system, there is no evaporator
In an indirect system, NH₃ flows directly into the space being cooled

121

Ťažká

Which parts of a refrigeration system should be given particular attention during a leak check?


Compressor and receiver connections, because the pressure is highest there
Joints, valves incl. stems, seals, parts subject to vibration, connections to safety devices
Only compressor connections, because they are the only parts subject to vibration
Only condenser connections, because the refrigerant is liquid there

122

Ťažká

Leak checks can be carried out using various methods. Which pair is correct?


Physical and chemical methods
Material quality control methods and electronic methods
Methods with and without quality control of supplies
Direct and indirect methods

123

Ťažká

To whom can leak checks of stationary refrigeration equipment containing F-gases be entrusted?


A natural person holding a certificate covering leak checks (A1, A2 within its charge limit, or E)
Any leak-testing specialist
An employee appointed by the owner of the installation
A person who has carried out such checks before

124

Ťažká

What conditions must be met to use UV dye for leak checking?


It is sufficient to have a UV lamp, dye and safety goggles
Manufacturer approval of the method and a certificate covering breaking into the circuit
A UDT authorisation for pressure testing is required
It is sufficient that introducing dye into the circuit is technically feasible

125

Ťažká

Which leak-checking methods are considered direct methods?


Pressure-change measurement and immersion in water
1. gas detection devices (portable or fixed leak detection system), 2. UV detection fluid or dye, 3. bubble/foam solutions
Nitrogen with tracer gas and pressure measurement
Vacuum test and foam solution

126

Ťažká

What do indirect leak-checking methods involve?


A visual and manual check and analysis of parameters: pressure, temperature, compressor current, liquid levels and recharge volume
Leak detection with UV dye
Leak detection with an electronic detector
Ultrasonic measurement

127

Ťažká

What does a vacuum (decay) test involve?


After isolating the pump, you check whether the system pressure rises
The pump is restarted every time the system pressure rises
With the pump running, you watch the vacuum gauge reading
The pump runs continuously to hold the required vacuum for the test

128

Ťažká

How often should leak tests be carried out on equipment containing 1.5 kg of R404A refrigerant (5.9 tonnes of CO₂ equivalent)?


Only when servicing the unit.
Once every six months.
At least once every 12 months.
On initial commissioning.

129

Ťažká

How often should leak tests be carried out on equipment containing 7 kg of R404A refrigerant (27.45 tonnes of CO₂ equivalent)?


At least once every 12 months.
On initial commissioning.
Once every six months.
Only when servicing the unit.

130

Ťažká

Under Regulation (EU) 2024/573, a leakage detection system is mandatory when:


the equipment contains a flammable refrigerant in any quantity
the charge is 100 kg or more of ozone-depleting substances
the equipment operates in an enclosed space
the F-gas charge of the refrigeration equipment is 500 t CO₂ eq or more

131

Ťažká

Which leak-checking method may NOT be used by a holder of a Category E certificate?


Visual inspection
Checking with a foaming solution
Leak checking with a fluorescent dye introduced into the circuit
Measurement with a handheld electronic detector

132

Ťažká

Within what timeframe must a leak test be carried out on a stationary refrigeration system after a leak has been repaired, in accordance with EU Regulation 2024/573 on F-gases?


At the next periodic inspection.
Immediately after the repair.
Between 24 hours and 1 month after the repair.
At any time.

133

Ťažká

How often must refrigeration equipment containing ≥500 t CO₂ eq of F-gases be checked if (contrary to Article 6) no leakage detection system is installed?


Every 3 months
Every 12 months
Every month
Every 6 months

134

Ťažká

What is the basis of the GWP values in Regulation (EU) 2024/573?


Each Member State sets its own GWP values
For HFCs (Annex I) – mainly the IPCC Fourth Assessment Report (AR4); for HFOs and non-fluorinated substances (Annexes II and VI) – the Sixth Assessment Report (AR6)
AR4 for all substances
AR6 for all substances

135

Ťažká

An air conditioner (not hermetically sealed) contains 2.5 kg of R410A (GWP 2088). How often must it be checked for leaks?


At least every 12 months (5.22 t CO₂ eq)
Every 6 months
No checks required (below 3 kg)
Every 3 months

136

Ťažká

When is labelled hermetically sealed equipment containing HFCs (Annex I) exempt from leak checks?


When it contains less than 5 t CO₂ eq
Always, regardless of charge
Never – hermetically sealed equipment is always checked
When it contains less than 10 t CO₂ eq, and in residential buildings also when it contains less than 3 kg of F-gases

137

Ťažká

Is a chiller containing 50 kg of R1234ze(E) subject to leak checks under Regulation (EU) 2024/573?


No – HFOs are not subject to leak checks
Yes – at least every 6 months (every 12 months with a leakage detection system)
No – the threshold is 5 t CO₂ eq and 50 kg of R1234ze is below 1 t CO₂ eq
Yes – every 12 months, because its GWP is low

138

Ťažká

In 2026, may an existing refrigeration installation using R404A (GWP 3922) be topped up with virgin refrigerant?


No – only reclaimed or recycled R404A is allowed (until 1 January 2030)
Yes – the ban applies only to equipment ≥40 t CO₂ eq
Yes – bans apply only to new equipment
Yes, if the equipment has a leakage detection system

139

Ťažká

After 1 January 2026, may an R410A (GWP 2088) air conditioner be serviced using virgin R410A?


No – the ban covers all HFCs
No – the ban covers all refrigerants with GWP ≥ 750
Only with reclaimed refrigerant
Yes – the servicing ban for air conditioners and heat pumps covers F-gases with GWP ≥ 2500

140

Ťažká

Since 1 January 2025, may a new single-split air conditioner containing 1.5 kg of R410A be placed on the market?


No – single splits <3 kg with F-gases of GWP ≥ 750 are banned
Yes – the ban applies from 2029
Yes, if the unit is hermetically sealed
Yes – the ban applies only to units >12 kW

141

Ťažká

From when is it prohibited to place on the market split air-to-air systems up to 12 kW containing F-gases with GWP ≥150 (unless required for safety)?


From 1 January 2035
From 1 January 2025
From 1 January 2027
From 1 January 2029

142

Ťažká

Which persistent atmospheric degradation product of R1234yf is classed as a PFAS?


Carbon dioxide
Trifluoroacetic acid (TFA)
Ozone
Carbonic acid

143

Ťažká

What is the maximum R290 charge per circuit of a commercial refrigerating appliance (e.g. a cabinet) according to EN IEC 60335-2-89:2022?


1.5 kg
13 × LFL ≈ 494 g
150 g
1.2 kg

144

Ťažká

Calculate the maximum R32 charge (LFL = 0.307 kg/m³) for a wall-mounted air conditioner (h₀ = 1.8 m) in a 20 m² room using m_max = 2.5 × LFL^1.25 × h₀ × A^0.5.


approx. 1.5 kg
approx. 0.46 kg
approx. 13.8 kg
approx. 4.6 kg

145

Ťažká

What is the maximum quantity of R290 (class 2, group F) that may be carried per transport unit under the ADR 1.1.3.6 exemption?


Unlimited
20 kg
1000 kg
333 kg

146

Ťažká

What is the charge limit m₃ = 130 m³ × LFL for R290 (LFL = 0.038 kg/m³) according to IEC 60335-2-40?


approx. 4.94 kg
approx. 13 kg
approx. 0.15 kg
approx. 0.99 kg

147

Ťažká

Why does the efficiency of transcritical CO₂ systems fall in warm climates, and how is this mitigated?


CO₂ freezes in the gas cooler – heaters are used
Efficiency does not depend on climate
Gas cooler pressure drops – extra charge is added
At high ambient temperatures the system operates transcritically with large throttling losses – parallel compression and ejectors are used, among others