1

Nehéz

What additional protective equipment will you use when brazing systems containing HC refrigerants?


Latex gloves
Ear defenders
A high-visibility vest
A flammable gas detector

2

Nehéz

Why can’t a sealed high-pressure switch be replaced with a standard mechanical one in a system containing a flammable refrigerant?


There is a risk of refrigerant leakage
The pressure switch setting will not be correct
It is a potential source of ignition
Dust and moisture may enter

3

Nehéz

What is the minimum (recommended) distance from a work area with HC refrigerants within which there must be no sources of ignition?


3 m
0.5 m
1 m
2 m

4

Nehéz

What is the maximum safe R32 fill of a recovery cylinder approved for flammable gas that holds 20 kg of R410A (the liquid density of R32 is about 8-10% lower)?


20 kg
33 kg
9 kg
18 kg

5

Nehéz

What is the maximum charge of an A3 refrigerant for a hermetic display cabinet with an integral condenser located in the ground-floor sales area of a supermarket?


10 kg
1.0 kg
2.5 kg
0,494 kg

6

Nehéz

How can a vacuum pump be used safely to evacuate a system containing a flammable refrigerant?


Place the pump directly on the floor, as low as possible
Such systems need not be evacuated before charging
Ignition-source-free pump, good ventilation, exhaust to a safe place
Position the pump at least 3 m above floor level

7

Nehéz

What safety measure must you carry in your vehicle when transporting flammable refrigerant cylinders?


A fire blanket
A fire extinguisher
Thick gloves
Tinted safety goggles

8

Nehéz

How would you prepare a 10 kg R32 water chiller located outdoors for debrazing its joints?


Vent the R32 outdoors and purge the system
Vent the R32 outdoors, then fill and vent the system with nitrogen three times
Recover the R32 to a vacuum, then fill the system with nitrogen to a slight positive pressure (approx. 0.1 bar g)
Recover the R32 to a vacuum and start desoldering immediately

9

Nehéz

Which of the following leak detection methods should NOT be used to locate an HC refrigerant leak?


Leak detection foam
Soapy water solution
Electronic HFC leak detector
Electronic leak detector for flammable refrigerants

10

Nehéz

What is the most important difference between a flammable refrigerant recovery unit and a standard one?


Different low-pressure switch setting
A different colour for the station
Different connection sizes
A flammable refrigerant recovery unit has no ignition sources

11

Nehéz

Which of the following is a source of ignition?


A sealed NTC temperature sensor
An 'n'-type (non-sparking) thermostat
A contactor (sparking contacts)
An Ex-certified fan motor

12

Nehéz

What particularly hazardous substance is formed when R32 burns?


Hydrogen chloride (HCl)
Hydrogen fluoride (HF)
Phosgene
Sulphur dioxide (SO₂)

13

Nehéz

What type of refrigerant is R1234ze(E)?


CFC (chlorofluorocarbon)
HFO (hydrofluoroolefin)
HC (hydrocarbon)
HCFC (hydrochlorofluorocarbon)

14

Nehéz

What hazards does a safety group A3 refrigerant pose?


Lower toxicity, higher flammability
Lower toxicity, moderate flammability
Higher toxicity, moderate flammability
Higher toxicity, higher flammability

15

Nehéz

According to EN 378, what is the maximum R290 charge in a cold room measuring 5 m × 3 m × 2.5 m (LFL of R290 = 0.038 kg/m³, access category a, location class I, no additional measures))?


1.5 kg
0.285 kg
4.93 kg
1.0 kg

16

Nehéz

What is the approximate ratio of the volumetric cooling capacity of R32 to that of R410A (same compressor and conditions)?


approx. 0.75
approx. 1.3
approx. 1.05–1.1
approx. 0.6

17

Nehéz

Why are Ex-certified evaporator fan motors used in some systems with flammable refrigerants?


Because they are more reliable
To avoid a source of ignition in the event of a flammable refrigerant leak
Because they are more energy-efficient
Because they must be kept running continuously to disperse the leaking refrigerant

18

Nehéz

Why is the density difference between HC and HFC refrigerants important?


An HC charge in kg is roughly half that of an HFC
Because it determines the system's energy efficiency
Because HCs must be charged much more slowly than HFCs
Because HCs operate at much higher pressures

19

Nehéz

What is the GWP of R290 according to Annex VI to Regulation (EU) 2024/573?


150
7
675
0.02

20

Nehéz

Which of the following is NOT a source of ignition?


An Ex-certified fan motor
An electrical switch
An unsealed mechanical pressure switch
A light switch

21

Nehéz

What is R290?


Propene (Propylene)
Propane
Isobutane
Butane

22

Nehéz

What is the maximum A2L charge for a hermetic display cabinet with integral condenser in the ground-floor sales area of a supermarket?


2.5 kg
150 g
1.5 kg
1.2 kg

23

Nehéz

Why can’t a standard relay be fitted when retrofitting a compressor’s electrical system for flammable refrigerants?


The method of starting the compressor motor differs from that used with HFCs
It could be a source of ignition
A relay is never required for compressors using flammable refrigerants
Current consumption differs for compressors using flammable refrigerants compared to those using HFCs

24

Nehéz

What is the minimum (recommended) distance from a work area with HC refrigerants within which there must be no ignition sources?


10 m
1 m
5 m
3 m

25

Nehéz

A recovery cylinder holds 10 kg of R404A (filling ratio 0.82 kg/l). What is the maximum R290 charge for this cylinder (propane filling ratio 0.43 kg/l per ADR P200)?


20 kg
approx. 5.2 kg
approx. 8 kg
approx. 17 kg

26

Nehéz

How can a vacuum pump be used safely to evacuate a system containing R290?


Ignition-source-free pump, good ventilation, exhaust to a safe place
R290 systems need not be evacuated before charging
Position the pump at least 3 m above floor level
Place the pump directly on the floor, as low as possible

27

Nehéz

Under ADR, what equipment must you carry in your vehicle when transporting flammable refrigerant cylinders (under the 1.1.3.6 exemption)?


A fire extinguisher (at least 2 kg dry powder)
A fire blanket
Thick gloves
Tinted safety goggles

28

Nehéz

How do you make sure it is safe to light the torch for desoldering joints in a system from which a flammable refrigerant has been removed?


Purge the system with compressed air
Such joints must never be desoldered; they must be cut with a pipe cutter
Ensure good ventilation and check the work area with a flammable gas detector
Working outdoors is sufficient

29

Nehéz

How would you prepare a system containing 100 g of R1270 for debrazing, if local regulations allow controlled venting of small HC quantities?


Vent the R1270 outdoors and start brazing immediately
Vent the R1270 to a safe outdoor location, then purge with OFN three times (pressurise and vent), and braze with OFN flowing
Vent the R1270 into the room and open a window
Recover the R1270 to a vacuum and start brazing immediately without a nitrogen purge

30

Nehéz

Which method should NOT be used to locate an R290 leak?


Fluorescent dye and UV lamp (if approved by the manufacturer)
An electronic detector for flammable refrigerants
An electronic leak detector designed for HFCs
Leak detection foam

31

Nehéz

Why can’t recovery stations designed for HFCs be used with R600a?


They contain ignition sources
The recovery unit cannot withstand the working pressure of R600a
The oil in the recovery unit is not soluble in R600a
The low-pressure switch setting will not be suitable for R600a due to its lower operating pressure

32

Nehéz

According to EN 378, what is the maximum R1234ze(E) charge in a cold room measuring 5 m × 3 m × 2.5 m (LFL = 0.303 kg/m³, access category a, location class I, no additional measures)?


227 kg
6.18 kg
618 kg
2.27 kg

33

Nehéz

What type of refrigerant is R32?


Hydrocarbon
Hydrofluoroolefin
Carbon dioxide
Hydrofluorocarbon

34

Nehéz

What hazards do A2L refrigerants pose?


Lower toxicity, lower flammability (burning velocity ≤ 10 cm/s)
Higher toxicity, lower flammability
Higher toxicity, higher flammability
Lower toxicity, higher flammability

35

Nehéz

What hazard is associated with the combustion of HFO or HFC refrigerants?


Nitrous oxide is formed
Hydrogen fluoride (HF) is formed
Ozone is formed
Phosgene is formed

36

Nehéz

Approximately what compressor displacement is required for R600a compared with R134a for the same cooling capacity?


About twice as large
The same
About half
About seven times as large

37

Nehéz

What is the GWP value for R32 according to Regulation (EU) 2024/573?


3
0
7
675

38

Nehéz

Why is charge accuracy more important in critically charged R290 systems than in HFC systems?


Because R290 is only used in systems below 150 g
Because such systems never have liquid receivers
Because of lower operating pressures
The charge mass is much smaller than in an HFC system, because the liquid density of R290 is much lower

39

Nehéz

Why does the condenser fan run continuously in some systems using R1270?


To prevent the build-up of contaminants in the condenser
To ensure that the discharge pressure never becomes excessive
To reduce energy consumption
To dilute the refrigerant in the event of a leak

40

Nehéz

What is the role of a suction liquid separator (also in systems with flammable or toxic refrigerants)?


It separates liquid from oil
It is used only to measure moisture
It heats the refrigerant before the evaporator
It prevents liquid refrigerant from entering the compressor

41

Nehéz

What is the function of an oil separator in systems using flammable or toxic refrigerants?


They are used solely to measure the moisture content of the refrigerant
Heats the refrigerant before it enters the evaporator
Separates oil from the refrigerant and facilitates the return of oil to the compressor
It prevents liquid from entering the compressor

42

Nehéz

Why do liquid and oil separators in CO₂ systems require particular attention?


Because of very high pressures – adequate PS and protection devices are required
Because CO₂ needs no lubrication, so oil separators are unnecessary
Because sight glasses and level indicators must not be used in CO₂ systems
Because CO₂ is flammable and separators must not be used

43

Nehéz

What is the critical pressure of CO₂ (R744)?


Approx. 31 bar
Approx. 120 bar
Approx. 74 bar (abs)
Approx. 10 bar

44

Nehéz

What characterises the transcritical process in CO₂ systems?


Heat rejection takes place above the critical point – the refrigerant does not condense in the conventional way (gas cooler instead of condenser)
Conventional condensation occurs
It is irrelevant to system operation
It occurs only at low temperatures

45

Nehéz

What characterises the subcritical CO₂ process?


The conventional condensation process below the critical point
The absence of condensation
The absence of evaporation
Operation above the critical point

46

Nehéz

When can dry ice (solid CO₂) form?


At high pressure
During normal operation of the system
At high temperature
When the pressure drops suddenly below the triple point (approx. 5.2 bar abs, −56.6 °C), e.g. when venting liquid CO₂ or charging liquid into an evacuated system

47

Nehéz

What risks are associated with dry ice forming in a CO₂ system?


Improved efficiency
No risk
Pressure reduction
Blocked pipes and valves and system damage (and a sharp pressure rise when it thaws)

48

Nehéz

How does CO₂ saturation pressure change as temperature increases?


It decreases
It first decreases, then increases
It increases rapidly
It remains the same

49

Nehéz

What happens to CO₂ above the critical point?


It turns into a liquid
It ceases to conduct heat
It transitions to a supercritical state (no distinction between liquid and gas)
It turns into a solid

50

Nehéz

What is the main difference between a dry-expansion and a flooded evaporator?


A dry-expansion evaporator needs no expansion valve, a flooded one does
In a dry-expansion evaporator the refrigerant completely evaporates and is superheated in the evaporator; in a flooded one part of the refrigerant remains liquid (incomplete evaporation, no superheat)
A dry-expansion evaporator is filled with liquid, a flooded one with vapour
A dry-expansion evaporator always has a lower pressure than a flooded one

51

Nehéz

What is the typical pressure in the evaporator of an R717 deep-freeze system (below −40 °C)?


Positive pressure of 10–20 bar
Atmospheric pressure, approx. 1 bar abs
Below atmospheric (approx. 0.7 bar abs at −40 °C)
Positive pressure of 5–10 bar

52

Nehéz

Why are PFAS formed by the decomposition of certain F-gases (e.g. TFA from HFOs) problematic?


They are very persistent, accumulate in the environment (e.g. water) and may be toxic
They cause rapid cooling of the atmosphere
They are climate- and environment-neutral
They are readily biodegradable

53

Nehéz

How is oil managed in R717 systems?


Oil requires no monitoring
Oil collecting at the lowest points of vessels is regularly checked and drained, because it impairs heat transfer
Oil has no effect on system operation
Oil can be mixed with any refrigerant

54

Nehéz

What should be done with contaminated R717?


Purify it or send it for disposal in accordance with regulations
Continue to use it without restriction
Dilute it with water and reuse it
Release it into the atmosphere

55

Nehéz

What should be done if an NH₃ leak is detected?


Carry on working with the room door open
Carry on working wearing a dust mask
Evacuate people immediately and raise the alarm; stop the leak only if it is safe to do so and with suitable PPE (respiratory protection)
Increase the pressure in the system

56

Nehéz

What role do scrubbers play in NH₃ systems?


They are used to measure temperature
They store the refrigerant
Neutralise ammonia through absorption in a liquid (e.g. water)
They increase the pressure in the system

57

Nehéz

How should the system be prepared before filling with R717?


Check for leaks, remove air and moisture, and create a vacuum
Simply start it up
There is no need to check it
The pressure must be increased above the standard level

58

Nehéz

What are the transport requirements for R717?


Transport is not regulated
It must be carried in suitable, labelled packagings in accordance with ADR (UN 1005, class 2, code 2TC)
It can be carried without labelling
It can be carried in open containers

59

Nehéz

What is the main characteristic of R744 (CO₂) refrigeration systems?


No need for control
Low operating pressures
Very high operating pressures
Low energy efficiency under all conditions

60

Nehéz

What are the requirements for piping materials in CO₂ systems?


Any material may be used
It doesn't matter
Only plastics
They must withstand high pressures (e.g. stainless steel, high-strength copper-alloy tubes such as K65)

61

Nehéz

How does a booster system work in CO₂ installations?


It reduces evaporator pressure
It is used to store refrigerant
Low-temperature (LT) compressors discharge into the suction of medium-temperature (MT) compressors – two-stage compression in a single circuit
It reduces the refrigerant quantity

62

Nehéz

Why is pressure optimisation in CO₂ systems crucial?


It enables the system to achieve maximum energy efficiency in transcritical mode
It doesn’t matter
It reduces the amount of refrigerant
It reduces the ambient temperature

63

Nehéz

What role does parallel compression play in CO₂ systems?


It compresses flash gas from the intermediate receiver directly to high pressure, improving efficiency
It lowers the ambient temperature
It has no significance
It increases energy consumption

64

Nehéz

How does an ejector work in a CO₂ system?


It lowers the evaporator temperature
Stores the refrigerant
It increases the amount of refrigerant
It uses the energy of the higher-pressure refrigerant to raise the pressure of the refrigerant from the lower stage, which improves efficiency

65

Nehéz

What is the function of liquid ejectors in CO₂ systems?


They raise the refrigerant temperature
They return liquid from the separator and allow partially flooded evaporator operation (better evaporator feed)
They reduce atmospheric pressure
They increase the amount of oil

66

Nehéz

What are the characteristics of partially flooded systems in CO₂ systems?


Lack of regulation
The presence of liquid in the evaporator, which improves heat transfer and efficiency
Low operating pressure
The absence of liquid in the evaporator

67

Nehéz

What is the main risk associated with standstill pressure in CO₂ systems?


A decrease in refrigerant quantity
A drop in temperature
A pressure rise as the refrigerant warms up during standstill (possibly exceeding PS and lifting the relief valves)
Increased efficiency

68

Nehéz

How is standstill pressure limited in CO₂ systems?


By increasing the refrigerant charge
By raising the plant-room temperature
By using an auxiliary standstill (stagnation) cooling unit, e.g. cooling the receiver, with back-up power, and by selecting an adequate PS and relief valves
By completely shutting down the system and power supply

69

Nehéz

What does standstill (stagnation) of a CO₂ system mean, and why is it important?


A drop in system temperature
Improved efficiency
A state with no compressor operation or refrigerant flow – pressure rises with ambient temperature and may exceed PS
Normal system operation

70

Nehéz

What must the label of a flammable refrigerant cylinder include?


The refrigerant name, the UN number, the hazard label (e.g. 2.1 – flammable gas) and basic safety information
Only the net weight
Information about the cylinder owner
Only the refrigerant name

71

Nehéz

Why is the absence of a 'flammable refrigerant' label on equipment a serious hazard?


It may lead to the use of tools that are ignition sources
It may lead to the wrong oil being selected
It reduces system efficiency
It has no significant effect on safety

72

Nehéz

Which set of information on the label of a flammable refrigerant cylinder is crucial from a safety perspective?


Cylinder colour and date of manufacture
Name of the substance, hazard label (ADR) / GHS pictogram (CLP), UN number
Gross weight and batch number
Manufacturer’s name and country of origin

73

Nehéz

What is the purpose of gas detectors in a room with a refrigeration system?


Early leak detection and triggering of measures preventing health risks and explosive atmospheres (alarm, ventilation, shut-off)
Monitoring pipe pressure
Controlling compressor capacity
Measuring refrigerant temperature

74

Nehéz

How often should gas detection sensors in a machinery room be checked?


Before every start-up of the unit
Only after a leak has occurred
Once every 5 years
According to the manufacturer's instructions and regulations – at least every 12 months

75

Nehéz

Where should a gas detector be located according to EN 378?


Anywhere in the room
Where the refrigerant would accumulate: low (near the floor) for refrigerants heavier than air, high (near the ceiling) for lighter ones such as NH₃
Near the control panel
Only at the room entrance

76

Nehéz

What safety checks should be carried out when installing a new refrigeration system with a flammable refrigerant?


The presence of health and safety signage, adequate ventilation and gas detectors
Only that the air filter is new
The colour of pipes and hoses
Only the compressor power

77

Nehéz

What are the requirements for emergency exits from a refrigeration machinery room?


At least two exits are required and signage is optional
In small machinery rooms emergency exits need not be signed
One exit with a sign stating the refrigerant type is sufficient
Outward-opening doors and signed escape routes (number of exits per the standard)

78

Nehéz

Which installation measure for a flammable-refrigerant system improves its energy efficiency?


Omitting the filter-drier
Charging above the nameplate quantity
Restricting room ventilation
A thorough tightness test and evacuation (dehydration) of the system

79

Nehéz

Why is it important to limit the refrigerant charge in HC systems?


It lowers the temperature
It doesn't matter
It limits the possibility of reaching a flammable concentration (≥ LFL) in a leak, increasing safety
It increases capacity

80

Nehéz

Which safety class applies to R744?


A1
B2L
A3
A2.

81

Nehéz

In a simple single-stage R744 system without an intermediate receiver (refrigerant flows from the gas cooler directly to the expansion valve), operating transcritically at 90 bar with a gas-cooler outlet temperature of 35 °C, the refrigerant upstream of the expansion valve is…


…a subcooled liquid
…a two-phase mixture at intermediate pressure
…a supercritical fluid
…saturated vapour at intermediate pressure

82

Nehéz

In R744 transcritical systems, the gas cooler outlet valve controls:


The outlet temperature of the gas cooler
The pressure in the gas cooler
The inlet temperature to the gas cooler
The gas cooler fans

83

Nehéz

Which statement best describes the behaviour of R717 and mineral compressor oil?


R717 does not mix with the oil; the oil, being heavier than liquid NH₃, collects beneath it at the lowest points (mainly on the low-pressure side)
An oil return line cannot be used in R717 systems because the oil is too hot
R717 does not mix with the oil; the oil collects on the high-pressure side above the R717
R717 mixes very well with the oil, which easily returns to the compressor

84

Nehéz

What is the main reason for using K65 copper tubing in some R744 systems?


They have good low-temperature performance
They can withstand higher pressures
They come in a wider range of diameters
They bend easily

85

Nehéz

Which statement about installing Schrader valves is correct?


Hydrocarbons leak through Schrader valves
All Schrader cores are suitable for all refrigerants
When brazing the valve body, the core must be removed, then refitted and tightened to the correct torque
Schrader valves must not be used in R744 systems

86

Nehéz

Which refrigerant can be detected with phenolphthalein paper?


R1234ze(E)
R1270
R717
R744

87

Nehéz

How does an undercharge affect the high-pressure side (without discharge pressure control)?


Discharge pressure higher, subcooling higher
Discharge pressure higher, subcooling lower
Discharge (condensing) pressure and subcooling will both be lower
Discharge pressure lower, subcooling higher

88

Nehéz

What is the benefit of adding helium as a tracer gas to nitrogen in a pressure test?


It reacts with refrigerant residues, producing a visible colour change
It has a distinctive odour that helps locate the leak
Its small atoms pass easily through leaks and are detected
It has a higher pressure than pure nitrogen in the same cylinder

89

Nehéz

Why should an evacuated R744 system initially be charged with refrigerant in the vapour phase?


To charge R744 more slowly and measure it more accurately
To prevent dry ice forming (until approx. 5.2 bar abs is exceeded)
To avoid damaging the compressor with liquid CO₂
To prevent the drain valve on the receiver from opening

90

Nehéz

If moisture remains in an R744 system because it was not properly evacuated (dehydrated), what is the likely consequence?


Formation of hydrogen fluoride and hydrofluoric acid
Reduced cooling capacity
Excessive discharge pressure
Formation of carbonic acid, which damages the system

91

Nehéz

Which system may require manual oil recovery?


R744 cascade system
Secondary system using R744
Supercritical ‘booster’ system using R744
An R717 system

92

Nehéz

The pressure of R744 at a saturation temperature of 20 °C is approx.


25 bar g
14 bar g
56 bar g
90 bar g

93

Nehéz

Which refrigerant is lighter than air?


R1270
R717
R1234ze(E)
R744

94

Nehéz

What hazards are associated with a safety group A3 refrigerant?


Lower toxicity, no flame propagation
Higher flammability, lower toxicity
Lower flammability, lower toxicity
Higher toxicity, no flame propagation

95

Nehéz

What is the GWP of R32 (per AR4, as used in Regulation (EU) 2024/573)?


6
3922
0
675

96

Nehéz

What factors are taken into account when determining the maximum charge for comfort air-conditioning/heating applications?


Practical limit, room volume
Lower flammability limit, room volume
Practical limit, height of the indoor unit, floor area
Lower flammability limit, height of the indoor unit, floor area

97

Nehéz

What compressor displacement is required for R1270 compared with an R404A compressor in the medium-temperature range (cold room)?


About half
About 1.5 times larger
Similar
About 6 times larger

98

Nehéz

At an ambient temperature of 25 °C, the standstill pressure in the low-pressure stage of an R744 cascade (without standstill cooling) will typically be…


…approx. 27.5 bar g
…the same as the relief valve set pressure
…the same as the high-pressure switch setting
…higher than the maximum allowable pressure (PS) of the low-pressure stage

99

Nehéz

What is the correct definition of critical temperature?


The temperature at which, for certain substances, electrical resistance is zero
The temperature at which a substance changes from a gaseous to a solid state
The temperature at which the vapour pressure of a liquid is equal to the ambient pressure surrounding the liquid
The temperature above which there are no distinct liquid and gaseous phases

100

Nehéz

In the gas cooler of a transcritical system, the supercritical working fluid…


…rejects heat as its temperature falls
…rejects heat at constant temperature and pressure
…rejects heat as its pressure falls
…rejects heat during a phase change

101

Nehéz

R717 is highly corrosive to:


copper (and its alloys)
titanium
aluminium
stainless steel

102

Nehéz

What can be the effect of a relief valve lifting repeatedly?


The set pressure increases
The valve may not reseat tightly and its set (opening) pressure may decrease
The valve stays fully open permanently
The valve no longer opens

103

Nehéz

What is the relationship between the pressure (p) and temperature (T) of nitrogen at the start (1) and end (2) of a tightness test (p absolute, T in kelvin)?


p₂ = (p₁ × T₂)/T₁
p₂ = (p₁ × T₁)/T₂
p₂ = T₂/(p₁ × T₁)
p₂ = T₁/(p₁ × T₂)

104

Nehéz

What is the recommended pre-alarm level for fixed leak detection systems for R717?


500,000 ppm
50,000 ppm
500 ppm
5,000 ppm

105

Nehéz

Why are compressors with a separate motor (open type) mostly used in R717 systems?


Because NH₃ attacks copper motor windings, so hermetic compressors with conventional windings are not used
To increase the refrigerant charge
Because they are cheaper
To lower the condensing pressure

106

Nehéz

Which type of compressor is most commonly used in large ammonia systems?


Rotary vane compressor
A reciprocating or screw compressor
Hermetic scroll
Diaphragm compressor

107

Nehéz

How is the capacity of a piston compressor regulated in NH₃ systems?


By unloading the cylinders or changing the rotational speed
By increasing the condensing pressure
By reducing the refrigerant charge
Solely by adjusting the oil volume

108

Nehéz

How is the capacity of a screw compressor most commonly controlled?


By changing the type of oil
By using a slide valve
By closing the suction valve
By adjusting the oil level

109

Nehéz

When is two-stage compression used in NH₃ systems?


Only in small systems
Only with water-cooled condensers
At small temperature differences
At low evaporating temperatures (pressures) and high pressure ratios

110

Nehéz

What is the advantage of two-stage compression over single-stage compression?


Lower efficiency
No need for a separator
Higher efficiency and lower discharge temperature
Higher energy consumption

111

Nehéz

How does an evaporative condenser used in NH₃ systems work?


It transfers heat only to the air
Operates without a fan
It utilises the evaporation of water to increase cooling efficiency
It does not require a water supply

112

Nehéz

What is the function of the liquid separator in an NH₃ system?


It separates oil from the refrigerant
It prevents liquid from entering the compressor
Increases the discharge temperature
Regulates the condensing pressure

113

Nehéz

What is the purpose of monitoring the liquid level in the separator?


To increase the oil volume
To control the condenser fan
To maintain the correct refrigerant level and prevent the compressor from flooding
To reduce the condensing temperature

114

Nehéz

What is the role of the float switch in NH₃ systems?


It is used to detect leaks
It controls the fan’s operation
It monitors the liquid level in the tank or separator
It regulates the condensation temperature

115

Nehéz

What is a thermosyphon in NH₃ systems?


An oil circulation pump
A type of safety valve
A system with gravity-driven (natural) circulation of liquid refrigerant caused by density differences, used e.g. for screw compressor oil cooling
A defrosting device

116

Nehéz

Why are oils that are immiscible with the refrigerant used in NH₃ systems?


Because the oil mixes only with water
Because NH₃ does not mix with most compressor oils
To reduce the pressure
To increase the amount of refrigerant

117

Nehéz

What is the main function of an oil separator in NH₃ systems?


To separate the oil from the refrigerant and return the oil to the compressor
Removing moisture from the system
To lower the condensation temperature
To increase fan efficiency

118

Nehéz

In which NH₃ system does the refrigerant evaporate completely with superheat in the evaporator, fed by an expansion valve?


A direct-expansion (DX) system
A pumped liquid-recirculation system
An indirect system
A glycol system

119

Nehéz

What is the characteristic feature of a flooded evaporator system?


No level control is required
The evaporator contains a large amount of liquid, which improves heat transfer
The evaporator is filled exclusively with vapour
No separator is used

120

Nehéz

What is the main difference between a direct and an indirect system?


In an indirect system, NH₃ flows directly into the space being cooled
In an indirect system, no compressor is used
In a direct system, there is no evaporator
In an indirect system, NH₃ cools an intermediate medium (e.g. glycol), which in turn cools the load

121

Nehéz

Which parts of a refrigeration system should be given particular attention during a leak check?


Joints, valves incl. stems, seals, parts subject to vibration, connections to safety devices
Only compressor connections, because they are the only parts subject to vibration
Compressor and receiver connections, because the pressure is highest there
Only condenser connections, because the refrigerant is liquid there

122

Nehéz

Leak checks can be carried out using various methods. Which pair is correct?


Methods with and without quality control of supplies
Physical and chemical methods
Direct and indirect methods
Material quality control methods and electronic methods

123

Nehéz

To whom can leak checks of stationary refrigeration equipment containing F-gases be entrusted?


A person who has carried out such checks before
A natural person holding a certificate covering leak checks (A1, A2 within its charge limit, or E)
Any leak-testing specialist
An employee appointed by the owner of the installation

124

Nehéz

What conditions must be met to use UV dye for leak checking?


It is sufficient to have a UV lamp, dye and safety goggles
A UDT authorisation for pressure testing is required
Manufacturer approval of the method and a certificate covering breaking into the circuit
It is sufficient that introducing dye into the circuit is technically feasible

125

Nehéz

Which leak-checking methods are considered direct methods?


Nitrogen with tracer gas and pressure measurement
1. gas detection devices (portable or fixed leak detection system), 2. UV detection fluid or dye, 3. bubble/foam solutions
Vacuum test and foam solution
Pressure-change measurement and immersion in water

126

Nehéz

What do indirect leak-checking methods involve?


Ultrasonic measurement
Leak detection with UV dye
A visual and manual check and analysis of parameters: pressure, temperature, compressor current, liquid levels and recharge volume
Leak detection with an electronic detector

127

Nehéz

What does a vacuum (decay) test involve?


After isolating the pump, you check whether the system pressure rises
The pump is restarted every time the system pressure rises
The pump runs continuously to hold the required vacuum for the test
With the pump running, you watch the vacuum gauge reading

128

Nehéz

How often should leak tests be carried out on equipment containing 1.5 kg of R404A refrigerant (5.9 tonnes of CO₂ equivalent)?


Once every six months.
At least once every 12 months.
On initial commissioning.
Only when servicing the unit.

129

Nehéz

How often should leak tests be carried out on equipment containing 7 kg of R404A refrigerant (27.45 tonnes of CO₂ equivalent)?


At least once every 12 months.
On initial commissioning.
Once every six months.
Only when servicing the unit.

130

Nehéz

Under Regulation (EU) 2024/573, a leakage detection system is mandatory when:


the equipment operates in an enclosed space
the charge is 100 kg or more of ozone-depleting substances
the equipment contains a flammable refrigerant in any quantity
the F-gas charge of the refrigeration equipment is 500 t CO₂ eq or more

131

Nehéz

Which leak-checking method may NOT be used by a holder of a Category E certificate?


Visual inspection
Checking with a foaming solution
Leak checking with a fluorescent dye introduced into the circuit
Measurement with a handheld electronic detector

132

Nehéz

Within what timeframe must a leak test be carried out on a stationary refrigeration system after a leak has been repaired, in accordance with EU Regulation 2024/573 on F-gases?


Immediately after the repair.
At the next periodic inspection.
At any time.
Between 24 hours and 1 month after the repair.

133

Nehéz

How often must refrigeration equipment containing ≥500 t CO₂ eq of F-gases be checked if (contrary to Article 6) no leakage detection system is installed?


Every 3 months
Every month
Every 6 months
Every 12 months

134

Nehéz

What is the basis of the GWP values in Regulation (EU) 2024/573?


AR6 for all substances
For HFCs (Annex I) – mainly the IPCC Fourth Assessment Report (AR4); for HFOs and non-fluorinated substances (Annexes II and VI) – the Sixth Assessment Report (AR6)
Each Member State sets its own GWP values
AR4 for all substances

135

Nehéz

An air conditioner (not hermetically sealed) contains 2.5 kg of R410A (GWP 2088). How often must it be checked for leaks?


No checks required (below 3 kg)
At least every 12 months (5.22 t CO₂ eq)
Every 6 months
Every 3 months

136

Nehéz

When is labelled hermetically sealed equipment containing HFCs (Annex I) exempt from leak checks?


Always, regardless of charge
When it contains less than 5 t CO₂ eq
When it contains less than 10 t CO₂ eq, and in residential buildings also when it contains less than 3 kg of F-gases
Never – hermetically sealed equipment is always checked

137

Nehéz

Is a chiller containing 50 kg of R1234ze(E) subject to leak checks under Regulation (EU) 2024/573?


No – the threshold is 5 t CO₂ eq and 50 kg of R1234ze is below 1 t CO₂ eq
Yes – every 12 months, because its GWP is low
No – HFOs are not subject to leak checks
Yes – at least every 6 months (every 12 months with a leakage detection system)

138

Nehéz

In 2026, may an existing refrigeration installation using R404A (GWP 3922) be topped up with virgin refrigerant?


No – only reclaimed or recycled R404A is allowed (until 1 January 2030)
Yes, if the equipment has a leakage detection system
Yes – the ban applies only to equipment ≥40 t CO₂ eq
Yes – bans apply only to new equipment

139

Nehéz

After 1 January 2026, may an R410A (GWP 2088) air conditioner be serviced using virgin R410A?


Yes – the servicing ban for air conditioners and heat pumps covers F-gases with GWP ≥ 2500
Only with reclaimed refrigerant
No – the ban covers all refrigerants with GWP ≥ 750
No – the ban covers all HFCs

140

Nehéz

Since 1 January 2025, may a new single-split air conditioner containing 1.5 kg of R410A be placed on the market?


No – single splits <3 kg with F-gases of GWP ≥ 750 are banned
Yes – the ban applies from 2029
Yes, if the unit is hermetically sealed
Yes – the ban applies only to units >12 kW

141

Nehéz

From when is it prohibited to place on the market split air-to-air systems up to 12 kW containing F-gases with GWP ≥150 (unless required for safety)?


From 1 January 2027
From 1 January 2029
From 1 January 2025
From 1 January 2035

142

Nehéz

Which persistent atmospheric degradation product of R1234yf is classed as a PFAS?


Ozone
Carbonic acid
Trifluoroacetic acid (TFA)
Carbon dioxide

143

Nehéz

What is the maximum R290 charge per circuit of a commercial refrigerating appliance (e.g. a cabinet) according to EN IEC 60335-2-89:2022?


150 g
1.5 kg
1.2 kg
13 × LFL ≈ 494 g

144

Nehéz

Calculate the maximum R32 charge (LFL = 0.307 kg/m³) for a wall-mounted air conditioner (h₀ = 1.8 m) in a 20 m² room using m_max = 2.5 × LFL^1.25 × h₀ × A^0.5.


approx. 13.8 kg
approx. 4.6 kg
approx. 0.46 kg
approx. 1.5 kg

145

Nehéz

What is the maximum quantity of R290 (class 2, group F) that may be carried per transport unit under the ADR 1.1.3.6 exemption?


333 kg
Unlimited
20 kg
1000 kg

146

Nehéz

What is the charge limit m₃ = 130 m³ × LFL for R290 (LFL = 0.038 kg/m³) according to IEC 60335-2-40?


approx. 4.94 kg
approx. 0.99 kg
approx. 0.15 kg
approx. 13 kg

147

Nehéz

Why does the efficiency of transcritical CO₂ systems fall in warm climates, and how is this mitigated?


Efficiency does not depend on climate
Gas cooler pressure drops – extra charge is added
At high ambient temperatures the system operates transcritically with large throttling losses – parallel compression and ejectors are used, among others
CO₂ freezes in the gas cooler – heaters are used