F-Gas English Low GWP

Všetky otázky
HFC | Flammable | CO₂ | NH₃
Ľahké otázky | Stredne ťažké otázky | Ťažké otázky

1

Ľahká


2

Ľahká

What is the base unit of mass in the International System of Units (SI)?


t
N
kg
lb (pound)

3

Ľahká

The refrigerant absorbs heat when…


…it evaporates
…it is subcooled
…it freezes
…it condenses

4

Ľahká

What does the GWP indicator mean?


Global Warming Potential: the climate warming impact of 1 kg of a gas compared with 1 kg of CO₂ (GWP = 1) over a defined time horizon, usually 100 years
The ability of a substance to restore the ozone layer
Ozone depletion potential
The annual rise in mean air temperature caused by the emission of 1 kg of the gas

5

Ľahká

What is the main function of a safety valve?


It controls the oil level in the compressor
Prevents the evaporator from freezing
Discharges refrigerant when the set pressure is exceeded
It monitors the moisture content of the refrigerant

6

Ľahká

What is the unit of pressure in the International System of Units (SI)?


Pa (pascal)
bar (gauge)
atm (standard atmosphere)
psi (pound per square inch)

7

Ľahká

What is the log(p)-h diagram for CO₂ used for?


For analysing thermodynamic processes in a refrigeration system
To regulate pressure
To detect leaks
To measure temperature

8

Ľahká

What can be read from the log(p)-h graph?


Only the temperature
Only the amount of refrigerant
Only the humidity
Pressure, enthalpy, temperature and state of the refrigerant

9

Ľahká

What are CO₂ saturation tables used for?


To determine the relationship between temperature and pressure at saturation
To regulate the compressor
To measure humidity
To determine the oil quantity

10

Ľahká

What does the CO₂ saturation state mean?


A state in which the refrigerant is only a gas
A state of high pressure
Dry ice state
Equilibrium between the liquid and vapour phases

11

Ľahká

Why is understanding the log(p)-h graph particularly important for CO₂?


It doesn’t matter
It only applies to NH₃
It is only used for design purposes
As CO₂ systems operate in different modes (sub- and transcritical) and require detailed analysis

12

Ľahká

Why do CO₂ systems require precise pressure control?


Due to low pressures
Due to significant pressure changes with temperature fluctuations
They do not require control
Because there are no valves

13

Ľahká

What is the basic requirement when charging a system with R717 (NH₃)?


Charging should take place in a well-ventilated area using appropriate personal protective equipment
Charging must only take place at temperatures below 0°C
NH₃ can be charged together with air
Charging can be carried out without personal protective equipment

14

Ľahká

What is the correct procedure for recovering R717 from a system?


Recovery is not required
The refrigerant must be recovered into suitable, leak-proof tanks designed for NH₃
The gas can be released into the atmosphere
The refrigerant can be drained into the sewer system

15

Ľahká

How should R717 (NH₃) be stored?


In unmarked plastic containers
In any open containers
In sealed, labelled containers, in a cool and well-ventilated place
Near heat sources

16

Ľahká

What is the main hazard associated with an R717 leak during maintenance work?


No risk whatsoever
Damage to electrical equipment only
Increased cooling efficiency
Toxic to humans and may cause chemical burns

17

Ľahká

What personal protective equipment is required when working with NH₃?


Workwear only
Only a safety helmet
Safety goggles, gloves and respiratory protective equipment
No requirements

18

Ľahká

How do system leaks affect compressor energy efficiency?


They improve efficiency because condensing pressure drops
Refrigerant loss reduces capacity and increases energy use (longer run times, higher superheat)
They affect only safety, not energy use
No effect as long as the system still cools

19

Ľahká

How does a dirty condenser affect the operation of the refrigeration system?


It lowers the condensing pressure
It improves efficiency
Causes an increase in pressure and energy consumption by the compressor
It has no effect

20

Ľahká

Why is adequate airflow through an air-cooled condenser important?


It affects only noise
It ensures effective heat rejection and low condensing pressure
It doesn't matter
The lower the airflow, the lower the condensing pressure

21

Ľahká

How does the presence of limescale in a water-cooled condenser affect performance?


It improves heat transfer
Impairs heat exchange and increases energy consumption
It lowers the condensation temperature
It has no effect

22

Ľahká

How do condenser leaks affect energy efficiency?


They lower the temperature
They improve efficiency
Have no effect
Causes refrigerant loss and a drop in efficiency

23

Ľahká

How important is the correct positioning of an air-cooled condenser?


It should be installed in a well-ventilated area with unobstructed airflow
It should be close to heat sources
It should be housed in a small room
It doesn’t matter

24

Ľahká

How does hot air recirculation affect the condenser?


It improves efficiency
It has no effect
It reduces the pressure
Impairs cooling and increases energy consumption

25

Ľahká

How does evaporator icing affect the system’s operation?


It improves cooling performance
Impairs heat exchange and increases energy consumption
It has no effect
It lowers the condensation temperature

26

Ľahká

How does dirt on the evaporator surface affect its performance?


It reduces the pressure
It has no effect
Impairs heat exchange and increases energy consumption
It improves efficiency

27

Ľahká

What maintenance task is crucial for the evaporator?


Regular cleaning and defrosting
Increasing the refrigerant charge
Lack of maintenance
Reduced airflow

28

Ľahká

How does superheat at the evaporator outlet affect efficiency?


It only causes a temperature drop
It has no effect
Excessive superheat reduces energy efficiency
It always improves performance

29

Ľahká

How do leaks in the evaporator affect efficiency?


Improves performance
Increase capacity
Have no effect
These cause refrigerant loss and a drop in efficiency

30

Ľahká

How important is correct expansion valve adjustment?


Ensures optimal evaporator charge and improves efficiency
Causes leaks
It doesn’t matter
It increases energy consumption

31

Ľahká

How does inadequate insulation of suction (or secondary-coolant) pipes affect evaporator performance?


It has no effect
It lowers the condensing temperature
It causes cooling losses and increased energy use
It improves efficiency

32

Ľahká

How does correct TEV adjustment affect system energy efficiency?


It increases energy use
It ensures optimal superheat and improves efficiency
It has no effect
It causes leaks

33

Ľahká

What happens if the superheat set by the TEV is too high?


The refrigerant charge will increase
It has no effect
Cooling efficiency will improve
Efficiency will drop because the evaporator is not being fully utilised

34

Ľahká

How do contaminants in the system affect the operation of the TEV?


Have no effect
They lower the temperature
They improve its performance
They can cause it to become blocked and reduce efficiency

35

Ľahká

What role does the filter-drier play in terms of system efficiency?


It lowers the temperature
It increases the amount of refrigerant
Removes moisture and contaminants, improving the system’s efficiency
It doesn’t matter

36

Ľahká

How does proper insulation of components (e.g. pipes near the TEV) affect the system?


Prevents unwanted heat gains and improves efficiency
It increases energy consumption
It doesn’t matter
It causes leaks

37

Ľahká

How important is it to check the operation of the condensing pressure control valve in the system?


Ensures operation within the optimum pressure range and reduces energy losses
It causes a significant rise in temperature
It increases energy consumption
It has no effect

38

Ľahká

How does the correct selection of a TEV affect energy efficiency?


It doesn’t matter
It lowers the temperature
It increases the amount of refrigerant
Ensures the system is matched to its capacity and operates optimally

39

Ľahká

What is the function of high-pressure control valves in CO₂ systems?


They are used to store the refrigerant
They regulate oil flow
They control the pressure on the high-pressure side and optimise system operation
They lower the evaporator temperature

40

Ľahká

Why do CO₂ systems require more advanced automation than traditional systems?


They do not require automation
Due to low pressures
Due to the need for precise control of pressure and temperature
Because there are no valves

41

Ľahká

What is the requirement regarding the labelling of an installation containing a flammable substance?


Labelling is required only in technical rooms
Colour-coding of pipes is sufficient
The labelling must indicate the type of substance and the flammability hazard
Labelling is not required for hermetically sealed systems

42

Ľahká

What are the potential consequences of using unsuitable connections in a system containing a flammable substance?


No impact on safety
Merely a reduction in efficiency
Merely installation difficulties
Risk of leakage and the formation of an explosive mixture

43

Ľahká

How should an employee respond when a gas alarm is triggered?


Reduce the pressure in the system
Switch off the system and wait for the alarm to stop
Leave the room immediately and notify their supervisor
Carry on working until they see a leak

44

Ľahká

Gas detectors should be installed in rooms where:


The amount of refrigerant exceeds a specified permissible threshold
Ventilation is natural
Any refrigerant is present, regardless of the quantity
The room is less than 5 m²

45

Ľahká

How do leaks affect systems using flammable refrigerants?


They lower the temperature
They improve efficiency
They cause refrigerant loss, reduced efficiency and a fire hazard
Have no effect

46

Ľahká

Why is the cleanliness of heat exchangers in HC systems important?


Causes leaks
It improves heat transfer and reduces energy consumption
It increases the pressure
It doesn’t matter

47

Ľahká

What maintenance measures improve the efficiency of a system using a flammable refrigerant?


Increasing the refrigerant charge
Regular checks for leaks and operating parameters
Lack of servicing
Disabling safety devices

48

Ľahká

How does the correct selection of components affect a system using a flammable refrigerant?


It ensures safe and optimal operation and minimises energy losses
It doesn’t matter
It increases the amount of refrigerant
It lowers the temperature

49

Ľahká

Why is it important to use the correct service tools in HC systems?


It increases energy consumption
It ensures operational safety and reduces refrigerant losses
Causes leaks
It doesn’t matter

50

Ľahká

How does pipe insulation affect the efficiency of systems containing HC?


Causes leaks
It doesn’t matter
It reduces energy losses and improves efficiency
It increases the pressure

51

Ľahká

What is the base unit of temperature according to the International System of Units (Système International d’Unités)?


°C
°R
K
°F

52

Ľahká

What is the superheat of refrigerant vapour?


The difference between the actual vapour temperature and the saturation temperature corresponding to its pressure (expressed in K)
The amount of heat required to evaporate a liquid
The difference between the condensing temperature and the ambient temperature
The difference between the saturation temperature and the actual liquid temperature in the liquid line

53

Ľahká

What is the compression ratio of a compressor?


The ratio of absolute discharge pressure to absolute suction pressure (pc/po)
The ratio of discharge pressure to the effective capacity of the compressor (p/Vk)
The amount of refrigerant compressed per cycle relative to heat capacity
The ratio of suction pressure to discharge pressure (po/pc)

54

Ľahká

What is the theoretical displacement (swept volume flow) of a compressor?


The volume of vapour drawn in per unit of time, determined by the compressor's geometry and speed (stated by the manufacturer, e.g. in m³/h)
The volume of a single cylinder in cm³
The volume of refrigerant flowing in one piston cycle under actual operating conditions
A value expressed by the coefficient of performance (COP)

55

Ľahká

What is the clearance (dead) volume of a reciprocating compressor?


The space between the underside of the piston and the crankcase cover
The space between the side of the piston and the cylinder
The volume between the valve plate and the piston at bottom dead centre
The volume between the valve plate and the piston crown at top dead centre