F-Gas English Low GWP

All questions
HFC | Flammable | CO₂ | NH₃
Easy questions | Medium questions | Difficult questions

1

Easy


2

Easy

What is the base unit of mass in the International System of Units (SI)?


N
kg
t
lb (pound)

3

Easy

The refrigerant absorbs heat when…


…it condenses
…it freezes
…it is subcooled
…it evaporates

4

Easy

What does the GWP indicator mean?


Global Warming Potential: the climate warming impact of 1 kg of a gas compared with 1 kg of CO₂ (GWP = 1) over a defined time horizon, usually 100 years
The annual rise in mean air temperature caused by the emission of 1 kg of the gas
Ozone depletion potential
The ability of a substance to restore the ozone layer

5

Easy

What is the main function of a safety valve?


Prevents the evaporator from freezing
It monitors the moisture content of the refrigerant
It controls the oil level in the compressor
Discharges refrigerant when the set pressure is exceeded

6

Easy

What is the unit of pressure in the International System of Units (SI)?


Pa (pascal)
bar (gauge)
psi (pound per square inch)
atm (standard atmosphere)

7

Easy

What is the log(p)-h diagram for CO₂ used for?


For analysing thermodynamic processes in a refrigeration system
To detect leaks
To regulate pressure
To measure temperature

8

Easy

What can be read from the log(p)-h graph?


Pressure, enthalpy, temperature and state of the refrigerant
Only the temperature
Only the humidity
Only the amount of refrigerant

9

Easy

What are CO₂ saturation tables used for?


To determine the relationship between temperature and pressure at saturation
To determine the oil quantity
To regulate the compressor
To measure humidity

10

Easy

What does the CO₂ saturation state mean?


Equilibrium between the liquid and vapour phases
Dry ice state
A state of high pressure
A state in which the refrigerant is only a gas

11

Easy

Why is understanding the log(p)-h graph particularly important for CO₂?


As CO₂ systems operate in different modes (sub- and transcritical) and require detailed analysis
It doesn’t matter
It only applies to NH₃
It is only used for design purposes

12

Easy

Why do CO₂ systems require precise pressure control?


Because there are no valves
They do not require control
Due to significant pressure changes with temperature fluctuations
Due to low pressures

13

Easy

What is the basic requirement when charging a system with R717 (NH₃)?


Charging must only take place at temperatures below 0°C
Charging can be carried out without personal protective equipment
NH₃ can be charged together with air
Charging should take place in a well-ventilated area using appropriate personal protective equipment

14

Easy

What is the correct procedure for recovering R717 from a system?


The refrigerant must be recovered into suitable, leak-proof tanks designed for NH₃
Recovery is not required
The gas can be released into the atmosphere
The refrigerant can be drained into the sewer system

15

Easy

How should R717 (NH₃) be stored?


In unmarked plastic containers
In any open containers
Near heat sources
In sealed, labelled containers, in a cool and well-ventilated place

16

Easy

What is the main hazard associated with an R717 leak during maintenance work?


Toxic to humans and may cause chemical burns
Increased cooling efficiency
Damage to electrical equipment only
No risk whatsoever

17

Easy

What personal protective equipment is required when working with NH₃?


Workwear only
No requirements
Only a safety helmet
Safety goggles, gloves and respiratory protective equipment

18

Easy

How do system leaks affect compressor energy efficiency?


They affect only safety, not energy use
No effect as long as the system still cools
Refrigerant loss reduces capacity and increases energy use (longer run times, higher superheat)
They improve efficiency because condensing pressure drops

19

Easy

How does a dirty condenser affect the operation of the refrigeration system?


It improves efficiency
It has no effect
It lowers the condensing pressure
Causes an increase in pressure and energy consumption by the compressor

20

Easy

Why is adequate airflow through an air-cooled condenser important?


It ensures effective heat rejection and low condensing pressure
The lower the airflow, the lower the condensing pressure
It affects only noise
It doesn't matter

21

Easy

How does the presence of limescale in a water-cooled condenser affect performance?


Impairs heat exchange and increases energy consumption
It lowers the condensation temperature
It has no effect
It improves heat transfer

22

Easy

How do condenser leaks affect energy efficiency?


They improve efficiency
Causes refrigerant loss and a drop in efficiency
Have no effect
They lower the temperature

23

Easy

How important is the correct positioning of an air-cooled condenser?


It doesn’t matter
It should be installed in a well-ventilated area with unobstructed airflow
It should be housed in a small room
It should be close to heat sources

24

Easy

How does hot air recirculation affect the condenser?


It has no effect
Impairs cooling and increases energy consumption
It improves efficiency
It reduces the pressure

25

Easy

How does evaporator icing affect the system’s operation?


It has no effect
Impairs heat exchange and increases energy consumption
It improves cooling performance
It lowers the condensation temperature

26

Easy

How does dirt on the evaporator surface affect its performance?


It has no effect
It improves efficiency
It reduces the pressure
Impairs heat exchange and increases energy consumption

27

Easy

What maintenance task is crucial for the evaporator?


Regular cleaning and defrosting
Reduced airflow
Lack of maintenance
Increasing the refrigerant charge

28

Easy

How does superheat at the evaporator outlet affect efficiency?


It only causes a temperature drop
It has no effect
It always improves performance
Excessive superheat reduces energy efficiency

29

Easy

How do leaks in the evaporator affect efficiency?


Improves performance
These cause refrigerant loss and a drop in efficiency
Have no effect
Increase capacity

30

Easy

How important is correct expansion valve adjustment?


It increases energy consumption
Causes leaks
It doesn’t matter
Ensures optimal evaporator charge and improves efficiency

31

Easy

How does inadequate insulation of suction (or secondary-coolant) pipes affect evaporator performance?


It has no effect
It lowers the condensing temperature
It improves efficiency
It causes cooling losses and increased energy use

32

Easy

How does correct TEV adjustment affect system energy efficiency?


It causes leaks
It has no effect
It ensures optimal superheat and improves efficiency
It increases energy use

33

Easy

What happens if the superheat set by the TEV is too high?


The refrigerant charge will increase
It has no effect
Cooling efficiency will improve
Efficiency will drop because the evaporator is not being fully utilised

34

Easy

How do contaminants in the system affect the operation of the TEV?


Have no effect
They lower the temperature
They can cause it to become blocked and reduce efficiency
They improve its performance

35

Easy

What role does the filter-drier play in terms of system efficiency?


It doesn’t matter
It increases the amount of refrigerant
It lowers the temperature
Removes moisture and contaminants, improving the system’s efficiency

36

Easy

How does proper insulation of components (e.g. pipes near the TEV) affect the system?


It doesn’t matter
It increases energy consumption
Prevents unwanted heat gains and improves efficiency
It causes leaks

37

Easy

How important is it to check the operation of the condensing pressure control valve in the system?


Ensures operation within the optimum pressure range and reduces energy losses
It causes a significant rise in temperature
It increases energy consumption
It has no effect

38

Easy

How does the correct selection of a TEV affect energy efficiency?


It lowers the temperature
It doesn’t matter
Ensures the system is matched to its capacity and operates optimally
It increases the amount of refrigerant

39

Easy

What is the function of high-pressure control valves in CO₂ systems?


They regulate oil flow
They are used to store the refrigerant
They control the pressure on the high-pressure side and optimise system operation
They lower the evaporator temperature

40

Easy

Why do CO₂ systems require more advanced automation than traditional systems?


They do not require automation
Because there are no valves
Due to low pressures
Due to the need for precise control of pressure and temperature

41

Easy

What is the requirement regarding the labelling of an installation containing a flammable substance?


Labelling is required only in technical rooms
The labelling must indicate the type of substance and the flammability hazard
Labelling is not required for hermetically sealed systems
Colour-coding of pipes is sufficient

42

Easy

What are the potential consequences of using unsuitable connections in a system containing a flammable substance?


No impact on safety
Merely installation difficulties
Merely a reduction in efficiency
Risk of leakage and the formation of an explosive mixture

43

Easy

How should an employee respond when a gas alarm is triggered?


Reduce the pressure in the system
Switch off the system and wait for the alarm to stop
Leave the room immediately and notify their supervisor
Carry on working until they see a leak

44

Easy

Gas detectors should be installed in rooms where:


Ventilation is natural
The amount of refrigerant exceeds a specified permissible threshold
The room is less than 5 m²
Any refrigerant is present, regardless of the quantity

45

Easy

How do leaks affect systems using flammable refrigerants?


They lower the temperature
Have no effect
They cause refrigerant loss, reduced efficiency and a fire hazard
They improve efficiency

46

Easy

Why is the cleanliness of heat exchangers in HC systems important?


It doesn’t matter
It increases the pressure
It improves heat transfer and reduces energy consumption
Causes leaks

47

Easy

What maintenance measures improve the efficiency of a system using a flammable refrigerant?


Lack of servicing
Disabling safety devices
Regular checks for leaks and operating parameters
Increasing the refrigerant charge

48

Easy

How does the correct selection of components affect a system using a flammable refrigerant?


It lowers the temperature
It ensures safe and optimal operation and minimises energy losses
It increases the amount of refrigerant
It doesn’t matter

49

Easy

Why is it important to use the correct service tools in HC systems?


It increases energy consumption
It ensures operational safety and reduces refrigerant losses
Causes leaks
It doesn’t matter

50

Easy

How does pipe insulation affect the efficiency of systems containing HC?


It doesn’t matter
It increases the pressure
Causes leaks
It reduces energy losses and improves efficiency

51

Easy

What is the base unit of temperature according to the International System of Units (Système International d’Unités)?


K
°F
°R
°C

52

Easy

What is the superheat of refrigerant vapour?


The difference between the actual vapour temperature and the saturation temperature corresponding to its pressure (expressed in K)
The difference between the saturation temperature and the actual liquid temperature in the liquid line
The amount of heat required to evaporate a liquid
The difference between the condensing temperature and the ambient temperature

53

Easy

What is the compression ratio of a compressor?


The ratio of absolute discharge pressure to absolute suction pressure (pc/po)
The ratio of discharge pressure to the effective capacity of the compressor (p/Vk)
The ratio of suction pressure to discharge pressure (po/pc)
The amount of refrigerant compressed per cycle relative to heat capacity

54

Easy

What is the theoretical displacement (swept volume flow) of a compressor?


A value expressed by the coefficient of performance (COP)
The volume of a single cylinder in cm³
The volume of refrigerant flowing in one piston cycle under actual operating conditions
The volume of vapour drawn in per unit of time, determined by the compressor's geometry and speed (stated by the manufacturer, e.g. in m³/h)

55

Easy

What is the clearance (dead) volume of a reciprocating compressor?


The space between the underside of the piston and the crankcase cover
The volume between the valve plate and the piston crown at top dead centre
The space between the side of the piston and the cylinder
The volume between the valve plate and the piston at bottom dead centre