F-Gas English Low GWP

Minden kérdés
HFC | Flammable | CO₂ | NH₃
Könnyű kérdések | Közepes nehézségű kérdések | Nehéz kérdések

1

Nehéz

What is the role of a suction liquid separator (also in systems with flammable or toxic refrigerants)?


It separates liquid from oil
It heats the refrigerant before the evaporator
It prevents liquid refrigerant from entering the compressor
It is used only to measure moisture

2

Nehéz

What is the function of an oil separator in systems using flammable or toxic refrigerants?


Heats the refrigerant before it enters the evaporator
It prevents liquid from entering the compressor
Separates oil from the refrigerant and facilitates the return of oil to the compressor
They are used solely to measure the moisture content of the refrigerant

3

Nehéz

Why are PFAS formed by the decomposition of certain F-gases (e.g. TFA from HFOs) problematic?


They cause rapid cooling of the atmosphere
They are readily biodegradable
They are very persistent, accumulate in the environment (e.g. water) and may be toxic
They are climate- and environment-neutral

4

Nehéz

Which statement about installing Schrader valves is correct?


All Schrader cores are suitable for all refrigerants
Hydrocarbons leak through Schrader valves
When brazing the valve body, the core must be removed, then refitted and tightened to the correct torque
Schrader valves must not be used in R744 systems

5

Nehéz

How does an undercharge affect the high-pressure side (without discharge pressure control)?


Discharge pressure higher, subcooling lower
Discharge pressure higher, subcooling higher
Discharge (condensing) pressure and subcooling will both be lower
Discharge pressure lower, subcooling higher

6

Nehéz

What is the benefit of adding helium as a tracer gas to nitrogen in a pressure test?


It has a higher pressure than pure nitrogen in the same cylinder
Its small atoms pass easily through leaks and are detected
It has a distinctive odour that helps locate the leak
It reacts with refrigerant residues, producing a visible colour change

7

Nehéz

What can be the effect of a relief valve lifting repeatedly?


The valve may not reseat tightly and its set (opening) pressure may decrease
The valve stays fully open permanently
The set pressure increases
The valve no longer opens

8

Nehéz

What is the relationship between the pressure (p) and temperature (T) of nitrogen at the start (1) and end (2) of a tightness test (p absolute, T in kelvin)?


p₂ = T₂/(p₁ × T₁)
p₂ = (p₁ × T₁)/T₂
p₂ = (p₁ × T₂)/T₁
p₂ = T₁/(p₁ × T₂)

9

Nehéz

Which parts of a refrigeration system should be given particular attention during a leak check?


Only compressor connections, because they are the only parts subject to vibration
Compressor and receiver connections, because the pressure is highest there
Joints, valves incl. stems, seals, parts subject to vibration, connections to safety devices
Only condenser connections, because the refrigerant is liquid there

10

Nehéz

Leak checks can be carried out using various methods. Which pair is correct?


Direct and indirect methods
Material quality control methods and electronic methods
Physical and chemical methods
Methods with and without quality control of supplies

11

Nehéz

To whom can leak checks of stationary refrigeration equipment containing F-gases be entrusted?


An employee appointed by the owner of the installation
A person who has carried out such checks before
A natural person holding a certificate covering leak checks (A1, A2 within its charge limit, or E)
Any leak-testing specialist

12

Nehéz

What conditions must be met to use UV dye for leak checking?


It is sufficient that introducing dye into the circuit is technically feasible
It is sufficient to have a UV lamp, dye and safety goggles
A UDT authorisation for pressure testing is required
Manufacturer approval of the method and a certificate covering breaking into the circuit

13

Nehéz

Which leak-checking methods are considered direct methods?


Pressure-change measurement and immersion in water
Nitrogen with tracer gas and pressure measurement
Vacuum test and foam solution
1. gas detection devices (portable or fixed leak detection system), 2. UV detection fluid or dye, 3. bubble/foam solutions

14

Nehéz

What do indirect leak-checking methods involve?


Leak detection with an electronic detector
Leak detection with UV dye
Ultrasonic measurement
A visual and manual check and analysis of parameters: pressure, temperature, compressor current, liquid levels and recharge volume

15

Nehéz

What does a vacuum (decay) test involve?


With the pump running, you watch the vacuum gauge reading
After isolating the pump, you check whether the system pressure rises
The pump runs continuously to hold the required vacuum for the test
The pump is restarted every time the system pressure rises

16

Nehéz

How often should leak tests be carried out on equipment containing 1.5 kg of R404A refrigerant (5.9 tonnes of CO₂ equivalent)?


Once every six months.
On initial commissioning.
At least once every 12 months.
Only when servicing the unit.

17

Nehéz

How often should leak tests be carried out on equipment containing 7 kg of R404A refrigerant (27.45 tonnes of CO₂ equivalent)?


Once every six months.
At least once every 12 months.
On initial commissioning.
Only when servicing the unit.

18

Nehéz

Under Regulation (EU) 2024/573, a leakage detection system is mandatory when:


the charge is 100 kg or more of ozone-depleting substances
the equipment contains a flammable refrigerant in any quantity
the F-gas charge of the refrigeration equipment is 500 t CO₂ eq or more
the equipment operates in an enclosed space

19

Nehéz

Which leak-checking method may NOT be used by a holder of a Category E certificate?


Checking with a foaming solution
Visual inspection
Measurement with a handheld electronic detector
Leak checking with a fluorescent dye introduced into the circuit

20

Nehéz

Within what timeframe must a leak test be carried out on a stationary refrigeration system after a leak has been repaired, in accordance with EU Regulation 2024/573 on F-gases?


Between 24 hours and 1 month after the repair.
Immediately after the repair.
At any time.
At the next periodic inspection.

21

Nehéz

How often must refrigeration equipment containing ≥500 t CO₂ eq of F-gases be checked if (contrary to Article 6) no leakage detection system is installed?


Every 3 months
Every 6 months
Every 12 months
Every month

22

Nehéz

What is the basis of the GWP values in Regulation (EU) 2024/573?


Each Member State sets its own GWP values
AR4 for all substances
For HFCs (Annex I) – mainly the IPCC Fourth Assessment Report (AR4); for HFOs and non-fluorinated substances (Annexes II and VI) – the Sixth Assessment Report (AR6)
AR6 for all substances

23

Nehéz

An air conditioner (not hermetically sealed) contains 2.5 kg of R410A (GWP 2088). How often must it be checked for leaks?


No checks required (below 3 kg)
Every 3 months
At least every 12 months (5.22 t CO₂ eq)
Every 6 months

24

Nehéz

When is labelled hermetically sealed equipment containing HFCs (Annex I) exempt from leak checks?


Always, regardless of charge
When it contains less than 5 t CO₂ eq
Never – hermetically sealed equipment is always checked
When it contains less than 10 t CO₂ eq, and in residential buildings also when it contains less than 3 kg of F-gases

25

Nehéz

Is a chiller containing 50 kg of R1234ze(E) subject to leak checks under Regulation (EU) 2024/573?


Yes – every 12 months, because its GWP is low
No – the threshold is 5 t CO₂ eq and 50 kg of R1234ze is below 1 t CO₂ eq
No – HFOs are not subject to leak checks
Yes – at least every 6 months (every 12 months with a leakage detection system)

26

Nehéz

In 2026, may an existing refrigeration installation using R404A (GWP 3922) be topped up with virgin refrigerant?


Yes, if the equipment has a leakage detection system
Yes – bans apply only to new equipment
No – only reclaimed or recycled R404A is allowed (until 1 January 2030)
Yes – the ban applies only to equipment ≥40 t CO₂ eq

27

Nehéz

After 1 January 2026, may an R410A (GWP 2088) air conditioner be serviced using virgin R410A?


Yes – the servicing ban for air conditioners and heat pumps covers F-gases with GWP ≥ 2500
No – the ban covers all HFCs
No – the ban covers all refrigerants with GWP ≥ 750
Only with reclaimed refrigerant

28

Nehéz

Since 1 January 2025, may a new single-split air conditioner containing 1.5 kg of R410A be placed on the market?


No – single splits <3 kg with F-gases of GWP ≥ 750 are banned
Yes – the ban applies only to units >12 kW
Yes – the ban applies from 2029
Yes, if the unit is hermetically sealed

29

Nehéz

From when is it prohibited to place on the market split air-to-air systems up to 12 kW containing F-gases with GWP ≥150 (unless required for safety)?


From 1 January 2035
From 1 January 2027
From 1 January 2029
From 1 January 2025

30

Nehéz

Which persistent atmospheric degradation product of R1234yf is classed as a PFAS?


Carbon dioxide
Carbonic acid
Ozone
Trifluoroacetic acid (TFA)