F-Gas English Low GWP
Všetky otázky
HFC | Flammable | CO₂ | NH₃
Ľahké otázky |
Stredne ťažké otázky |
Ťažké otázky
1
Stredne ťažká
What process takes place in the condenser of a refrigeration system?
| The refrigerant rejects only the heat generated in the compressor |
| Hot vapour discharged by the compressor is desuperheated, condensed, and the resulting liquid is slightly subcooled |
| The refrigerant absorbs heat from the surroundings and evaporates |
| The secondary fluid (glycol, water) condenses while the refrigerant evaporates |
2
Stredne ťažká
What mainly determines the condensing temperature of an air-cooled condenser?
| The ambient (inlet) air temperature |
| The compressor discharge temperature |
| The evaporating temperature |
| The superheat |
3
Stredne ťažká
Why does heat flow from the condenser to the surroundings?
| Because the compressor pushes heat directly into the surroundings |
| Because the pressure in the condenser is lower than ambient |
| Because the condensing temperature is higher than the ambient temperature, and heat flows spontaneously from a warmer to a colder body (second law of thermodynamics) |
| Because HFC refrigerants attract heat from the surroundings |
4
Stredne ťažká
What should you mainly pay attention to when operating a condenser?
| That the inlet air temperature is lower than the outlet air temperature |
| The colour of the condenser casing |
| Its general condition and the cleanliness of the heat-exchange surfaces |
| That the outlet air temperature is higher than the condensing temperature |
5
Stredne ťažká
What criteria should be considered when selecting a suitable condenser?
| Only own experience and the dimensions |
| Only the size and number of fans |
| Fan noise, connection diameters and colour |
| The required capacity of the condenser and the technical specifications declared by the manufacturer |
6
Stredne ťažká
How do contaminants (dust, particulates, deposits) affect the performance and efficiency of heat exchange surfaces in condensers?
| Contaminants restrict heat transfer (reducing the heat transfer coefficient) and cause an increase in condensing temperature and pressure, which in turn leads to a reduction in the condenser’s efficiency. |
| Contaminants do not significantly affect the efficiency and effectiveness of the heat exchange surfaces in condensers. |
| Contaminants increase the heat transfer area and reduce the condensing pressure. |
| Contaminants restrict heat transfer (reducing the heat transfer coefficient) and cause a reduction in condensing pressure. |
7
Stredne ťažká
How does the capacity of an air-cooled condenser change when it becomes dirty?
| It decreases |
| It remains unchanged |
| It increases |
| It increases because the fan speed rises |
8
Stredne ťažká
What is the main consequence of heavy frost on an air-cooling evaporator?
| An increase in condenser subcooling |
| A rise in the cooled-air temperature with no effect on capacity |
| Reduced heat transfer and airflow, resulting in a drop in cooling capacity and evaporating temperature |
| A rise in evaporating pressure |
9
Stredne ťažká
What happens when the evaporation temperature drops?
| The condenser fan speed increases. |
| The compressor’s cooling capacity increases. |
| The discharge temperature decreases. |
| The compressor’s cooling capacity decreases. |
10
Stredne ťažká
When is natural (off-cycle, air) defrosting possible?
| Only in freezer rooms below −18 °C |
| When the air passing through the cooler is above 0 °C |
| Never – electric heaters must be used in every air cooler |
| Only in coolers fitted with speed-controlled fans |
11
Stredne ťažká
When does frost form on the surface of an air-cooling evaporator?
| Only when the system runs continuously |
| Always, in every air cooler |
| When the evaporator surface temperature is below 0 °C and below the dew point of the air |
| Only when the room air temperature falls below 0 °C |
12
Stredne ťažká
In extensive pipework systems, flash gas (secondary evaporation) in the liquid line can be prevented by…
| …increasing the length of the liquid line |
| …insulating the discharge line between the compressor and the condenser |
| …using smaller-diameter pipes |
| …additional subcooling of the liquid |
13
Stredne ťažká
How does hot gas defrosting of the evaporator work?
| We swap the outlet and inlet sides of the evaporator. |
| Heated vapour (hot gas) from the compressor is directed into the evaporator piping. |
| This involves reversing the direction of rotation of the compressor. |
| We switch on the gas heater directed at the evaporator. |
14
Stredne ťažká
What is the function of the evaporator in a refrigeration system?
| It evaporates the water flowing through the evaporator. |
| It ensures that the refrigerant is superheated over the largest possible heat exchange surface area. |
| It transfers heat from the medium being cooled to the boiling refrigerant. |
| It cools the refrigerant. |
15
Stredne ťažká
What condition must electric heaters for evaporator defrosting meet?
| They must be located beneath the evaporator |
| Heat from the heaters must be carried by the running fans |
| They must have good thermal contact with the heat-exchange surface (e.g. inserted in the fin block) |
| They must be in direct contact with the refrigerant |
16
Stredne ťažká
Refrigerant distributor:
| acts as a buffer for the refrigerant in the event that the pressure upstream of the expansion valve is exceeded. |
| ensures an even distribution of the refrigerant to the individual sections of the evaporator. |
| ensures even distribution of the refrigerant to the individual sections of the condenser. |
| ensures the even distribution of the refrigerant discharged by compressors connected in parallel. |
17
Stredne ťažká
What defrosting methods are used for air coolers?
| Natural only – other methods are ineffective and uneconomic |
| Only by switching off the fans with the compressor running |
| Electric only – other methods are not permitted in refrigeration |
| Electric, hot gas, water spray and natural (at positive temperatures) |
18
Stredne ťažká
The boiling point of a liquid rises when the pressure above the liquid…
| …varies depending on the ambient temperature |
| …rises |
| …remains constant |
| …falls |
19
Stredne ťažká
MOP in thermostatic expansion valves stands for:
| maximum operating pressure. |
| maximum pressure switch protection. |
| self-cleaning of the valve in the event of moisture in the refrigerant freezing. |
| minimum flow opening. |
20
Stredne ťažká
The function of a thermostatic expansion valve (TEV) is:
| to meter refrigerant into the evaporator according to the superheat of the vapour leaving the evaporator |
| to maintain a constant condensing pressure |
| to adjust the evaporating pressure in the condenser |
| to maintain a constant compressor suction pressure |
21
Stredne ťažká
What type of compressor motor can be used with a capillary tube?
| A low-speed motor |
| An electronically commutated motor |
| A low-starting-torque motor (pressures equalise during standstill) |
| A high-starting-torque motor must be used |
22
Stredne ťažká
What does a thermostatic expansion valve control?
| The discharge temperature |
| The temperature in the cold room |
| The mass flow of refrigerant fed into the evaporator |
| The condensing pressure |
23
Stredne ťažká
What does the manufacturer state as the factory setting of a thermostatic expansion valve?
| the static superheat of the valve. |
| the degree of refrigerant expansion. |
| the superheat value during valve operation. |
| the degree to which the valve is filled with refrigerant liquid. |
24
Stredne ťažká
Where is a new or repaired system with an expansion valve and liquid receiver charged?
| In the liquid phase into the compressor suction, with the compressor running |
| Through the capillary tube outlet during normal system operation |
| In the liquid phase on the high-pressure side, with the compressor stopped |
| Anywhere – the charging point does not matter |
25
Stredne ťažká
What does a thermostatic or electronic expansion valve control?
| Subcooling, by adjusting condensing pressure |
| The evaporating pressure – closing below the set point |
| The compressor speed |
| The amount of refrigerant fed to the evaporator according to superheat |
26
Stredne ťažká
What does the MOP function of thermostatic expansion valves mean?
| The valve maintains a constant condensing pressure |
| The valve limits subcooling |
| The valve limits the maximum evaporating (suction) pressure, protecting the compressor motor from overload, e.g. after defrost |
| The valve prevents motor overheating by injecting liquid into the compressor |
27
Stredne ťažká
The lower the liquid temperature upstream of the expansion valve, (at the same mass flow)…
| …the lower qo and the lower Qo |
| …the lower qo and the lower energy efficiency |
| …the lower qo, with Qo unchanged |
| …the higher the specific refrigerating effect qo [kJ/kg] and the higher the cooling capacity Qo |
28
Stredne ťažká
How should the MOP point of an expansion valve be selected relative to the highest normal evaporating temperature?
| Freely – the MOP value is irrelevant |
| Higher by approx. 20 K |
| A few kelvin higher (approximately 7 K) |
| About 7 K lower than that temperature |
29
Stredne ťažká
What is the function of the suction pressure regulator?
| It maintains the evaporation pressure at a constant level. |
| To maintain the suction pressure at the highest possible level. |
| It limits the suction pressure and protects the compressor from excessively high suction pressure. |
| It prevents a drop in suction pressure and, if necessary, shuts down the refrigeration system. |
30
Stredne ťažká
What is the function of the valve regulating water flow through the condenser?
| To maintain the condensing pressure at the highest possible level. |
| To maintain the condensing pressure at a constant level. |
| To maintain the water temperature at the highest level. |
| To maintain the condensing pressure at the lowest possible level. |
31
Stredne ťažká
The use of a refrigerant distributor requires a thermostatic expansion valve ...
| ... with external pressure equalisation. |
| ... with an adsorption-type sensor filling. |
| ... with internal pressure equalisation. |
| ... with a MOP function. |
32
Stredne ťažká
What properties should good insulation materials have?
| Low thermal conductivity (and low water absorption, vapour tightness) |
| An antistatic coating |
| The ability to absorb large amounts of moisture |
| High thermal conductivity |
33
Stredne ťažká
When is refrigerant vapour superheated?
| When its temperature is higher than the saturation temperature corresponding to its pressure |
| When the pressure on the discharge side is higher than on the suction side |
| When the evaporating temperature is lower than the ambient temperature |
| When the compressor motor temperature rises excessively |
34
Stredne ťažká
How can you check whether the liquid refrigerant is reaching the expansion valve without vapour bubbles?
| We check this using a sight glass. |
| We are unable to check this. |
| We check using a pressure gauge fitted on the discharge side of the compressor. |
| We check using a liquid pressure gauge. |
35
Stredne ťažká
Where does the liquid line run?
| From the condenser (liquid receiver) to the expansion valve |
| Between the evaporator and the compressor |
| Between the evaporator and the suction-line heat exchanger |
| Between the compressor and the condenser |
36
Stredne ťažká
What is the function of the liquid receiver in a refrigeration system?
| To collect liquid refrigerant and excess oil |
| To store refrigerant and compensate for changes in the circulating charge as the heat load varies |
| To further subcool the condensed refrigerant |
| To act as a reserve when the required charge is unknown |
37
Stredne ťažká
What is the purpose of the liquid receiver during service work?
| It allows pump-down and temporary storage of the refrigerant |
| It is a reserve when the installer does not know the required charge |
| It further subcools the refrigerant before the expansion valve |
| It collects excess oil circulating in the system |
38
Stredne ťažká
Where should the liquid receiver be installed?
| It should be installed downstream of the condenser, upstream of the expansion valve. |
| It should be fitted after the evaporator. |
| It should be fitted between the compressor and the condenser. |
| It should be fitted just before the compressor. |
39
Stredne ťažká
What is the function of the suction pressure regulator fitted to the suction pipe when the compressor starts up?
| It opens when the suction pressure upstream of the compressor drops. |
| It regulates the evaporation pressure. |
| It closes when the suction pressure upstream of the compressor drops. |
| It regulates the condensing pressure. |
40
Stredne ťažká
The use of microchannel heat exchangers, compared with conventional heat exchangers made of copper tubes and fins, results in:
| There is no effect whatsoever on either the amount of refrigerant or energy efficiency. |
| A reduction in refrigerant charge and, typically, higher energy efficiency. |
| A reduction in the system’s energy efficiency. |
| An increase in the amount of refrigerant in the system and an increase in condensing pressure. |
41
Stredne ťažká
Which refrigerants belong to the HFC group?
| R11, R12, R502. |
| R134a, R404A, R507A, R410A. |
| R22, R401A. |
| R134a, R32, R22, R507A, R290. |
42
Stredne ťažká
Which refrigerants belong to the HFO group?
| R1234yf, R1234ze(E). |
| R134a, R290. |
| R134a, R404A. |
| R22, R12. |
43
Stredne ťažká
What are the characteristics of R410A refrigerant compared to R407C refrigerant?
| The saturation pressure of R407C refrigerant is much higher than that of R410A. |
| The saturation pressure of R410A refrigerant is higher than that of R407C. |
| The saturation pressure of R407C is 150% higher than that of R410A. |
| The saturation pressure of both refrigerants is roughly the same. |
44
Stredne ťažká
What does the TEWI indicator define?
| The impact of a refrigerant on the ozone layer |
| The ability of the ozone layer to recover |
| Total Equivalent Warming Impact: the sum of direct emissions (leakage and refrigerant losses at disposal) and indirect emissions (CO₂ from generating the energy consumed by the equipment) over its lifetime |
| The global warming potential of a gas relative to CO₂ over a 100-year horizon |
45
Stredne ťažká
What are the characteristics of R452A compared with R404A?
| It is a non-flammable (A1) HFC/HFO blend with properties similar to R404A and a GWP about 45% lower |
| It is a flammable and toxic single-component HFC |
| Both are azeotropic and have no temperature glide |
| The temperature glide of R452A is half that of R404A |
46
Stredne ťažká
What distinguishes R1234yf from R134a?
| A higher critical temperature |
| It is mildly flammable (class A2L), whereas R134a is non-flammable (A1) |
| A higher normal boiling point |
| Higher toxicity |
47
Stredne ťažká
How does CO₂ (R744) compare with R134a?
| It has identical properties and is a drop-in replacement for R134a |
| Unlike R134a, it is an azeotropic mixture |
| It has a lower critical temperature, much higher operating pressures and a much higher volumetric cooling capacity (smaller compressors and pipes) |
| Its temperature glide is 7 K greater than that of R134a |
48
Stredne ťažká
Which of the following is NOT a fluorinated greenhouse gas?
| Hydrofluorocarbons (HFCs). |
| Perfluorocarbons (PFCs). |
| Carbon dioxide (CO₂). |
| Sulphur hexafluoride (SF6). |
49
Stredne ťažká
What is the greenhouse effect?
| Dust in the atmosphere reflects sunlight, lowering the average surface temperature |
| Clouds reflect ultraviolet radiation, which makes the air near the surface warmer |
| Greenhouse gases absorb and re-emit the Earth's infrared radiation, warming the lower atmosphere |
| Chlorine compounds destroy stratospheric ozone, increasing UV radiation at the surface |
50
Stredne ťažká
What is R1270?
| Isobutane |
| Propane |
| Propene (propylene) |
| n-Butane |
51
Stredne ťažká
How do refrigeration systems contribute to the greenhouse effect?
| Only through the heat rejected by the condenser |
| Indirectly (through energy consumption) and directly (through emissions of refrigerant into the atmosphere) |
| Through oil emitted into the atmosphere from the condenser and filter |
| Only through CO₂ given off by the compressor motor |
52
Stredne ťažká
What is the greenhouse effect?
| The trapping of heat in the Earth's atmosphere, which hinders the radiation of heat into space |
| The absorption of solar radiation by the Earth's surface |
| The filtering of solar radiation by the atmosphere |
| The formation of a layer that traps only heat from fuel combustion in aircraft |
53
Stredne ťažká
Which EU regulation is currently the primary piece of legislation governing the use of fluorinated greenhouse gases (F-gases) in the European Union?
| Regulation (EU) No 517/2014 |
| Regulation (EU) 2015/1188 |
| Regulation (EU) 2024/573 |
| Directive 2009/125/EC |
54
Stredne ťažká
What is the main objective of Regulation (EU) 2024/573?
| To reduce taxes on refrigeration equipment |
| Prevention of F-gas emissions and the achievement of the EU’s climate targets |
| To facilitate the import of electrical appliances |
| Standardising metal recycling standards |
55
Stredne ťažká
What are the ecodesign obligations of manufacturers of refrigerating appliances?
| Meeting implementing regulations (e.g. 2019/2019, 2015/1095): efficiency, spare parts, reparability |
| Only using energy labels under Regulation (EU) 2024/573 |
| Only implementing an ISO 9001 quality management system |
| Only declaring F-gas quantities under Regulation (EU) No 517/2014 |
56
Stredne ťažká
What is the main objective of EU ecodesign legislation (Directive 2009/125/EC, now Regulation (EU) 2024/1781 – ESPR)?
| To increase sales of electrical appliances in the EU |
| To standardise the appearance of products in the EU |
| To facilitate imports from outside the EU |
| To reduce the negative environmental impact of products by improving energy efficiency, durability and recyclability |
57
Stredne ťažká
What is the function of a ball valve in a refrigeration system?
| It prevents excessive pressure build-up in the system |
| It measures the moisture content of the refrigerant |
| It regulates the temperature of the refrigerant |
| Enables the refrigerant flow to be completely shut off |
58
Stredne ťažká
How do certain gases contribute to the greenhouse effect?
| They trap thermal radiation that the Earth would otherwise emit into space |
| They heat the air through chemical reactions with atmospheric oxygen and nitrogen |
| They limit UV radiation reaching the Earth's surface, changing the heat balance |
| They deplete the ozone layer, so more solar radiation reaches the surface |
59
Stredne ťažká
What is the purpose of a sight glass (with moisture indicator)?
| Emergency shut-off of flow |
| Regulating compressor pressure |
| Measuring condenser temperature |
| Visual assessment of the refrigerant condition in the liquid line (bubbles) and of system moisture |
60
Stredne ťažká
What is the function of the temperature regulator in a refrigeration system?
| To maintain a constant pressure in the compressor |
| It drains excess refrigerant into the receiver |
| It restricts oil flow |
| Controls the operation of the compressor and valves to maintain the set temperature |
61
Stredne ťažká
What is the purpose of oil level regulators in a refrigeration system?
| They drain off excess refrigerant |
| They control the pressure in the condenser |
| Maintains the correct oil level in the compressor |
| They control the evaporator temperature |
62
Stredne ťažká
What is the function of the liquid receiver in relation to system tightness?
| It controls the evaporating temperature by varying the circulating charge |
| It stores refrigerant; checking its liquid level helps detect charge loss |
| It regulates the oil returning to the compressor |
| It keeps the whole system at constant pressure regardless of load |
63
Stredne ťažká
What is the role of a gauge manifold with thermometers (temperature probes)?
| It relieves pressure if it is exceeded |
| It measures pressures and temperatures to determine superheat and subcooling and thus assess the system charge (indirect leak check) |
| It monitors refrigerant moisture content |
| It controls oil level |
64
Stredne ťažká
What is the role of defrost controls?
| They protect the evaporator from icing and damage that could lead to leaks |
| They control compressor discharge pressure during defrost |
| They drain excess oil from the evaporator to the receiver |
| They monitor the moisture content of the refrigerant |
65
Stredne ťažká
Where can the lists of fluorinated greenhouse gases be found?
| In a regulation of the Minister of Economy on the list of fluorinated greenhouse gases |
| In the national Act on ozone-depleting substances and certain fluorinated greenhouse gases |
| In the Vienna Convention for the Protection of the Ozone Layer |
| In Annexes I–III to Regulation (EU) 2024/573 of the European Parliament and of the Council |
66
Stredne ťažká
Where can the lists of ozone-depleting substances be found?
| In the national Act on ozone-depleting substances and certain fluorinated greenhouse gases |
| In a regulation of the Minister of the Environment on the list of controlled substances |
| In Annexes I and II to Regulation (EU) 2024/590 of the European Parliament and of the Council |
| In the Vienna Convention for the Protection of the Ozone Layer |
67
Stredne ťažká
Why is ammonia (R717) classed as a toxic refrigerant?
| It severely irritates the respiratory tract, eyes and skin, and is poisonous when inhaled at higher concentrations |
| Because it is colourless and odourless and therefore hard to detect |
| Because it is heavier than air and displaces oxygen |
| Because it does not react with water, making neutralisation difficult |
68
Stredne ťažká
Where and by when must entities obliged under the Polish Act of 15 May 2015 submit annual reports on ODS and F-gases?
| By 31 January, in the Central Register of Operators (CRO) |
| By the end of the calendar year, on a form at a regional office of the Office of Technical Inspection (UDT) |
| By 28 February of the following year, electronically via the Reports Database (BDS) run at the Institute of Industrial Chemistry (ICHP) |
| By 31 March, electronically to the Ministry of Climate and Environment |
69
Stredne ťažká
Which installation measure has a major impact on compressor energy efficiency?
| Charging extra refrigerant 'as a reserve' above the nameplate value |
| Installing a suction line smaller than recommended |
| Proper evacuation and dehydration of the system (removing air and moisture) |
| Omitting the filter-drier to reduce flow resistance |
70
Stredne ťažká
How does regular oil-level monitoring affect compressor operation?
| It allows any type of oil to be topped up |
| It ensures proper lubrication and limits wear and energy losses |
| It increases cooling capacity above nominal |
| It allows the crankcase heater to be omitted |
71
Stredne ťažká
Regulation (EU) 2024/590 relates to:
| Alternative refrigerants replacing fluorinated greenhouse gases |
| Ozone-depleting substances |
| Conditions for F-gas certification of companies recovering and reclaiming refrigerants |
| Health and safety during refrigerant recovery |
72
Stredne ťažká
What is the significance of proper suction and discharge pressure control?
| The lowest possible suction pressure is best |
| It keeps the compressor at optimal conditions (suction pressure as high and condensing pressure as low as permissible) |
| Pressures do not affect energy use |
| The highest possible condensing pressure is best |
73
Stredne ťažká
Which maintenance measure reduces compressor energy consumption?
| Replacing the filter-drier when the pressure drop or moisture indicator shows it is necessary |
| Raising the high-pressure switch setting |
| Topping up refrigerant at every service visit |
| Permanently disabling the crankcase heater |
74
Stredne ťažká
How does air (non-condensable gas) in the system affect operation?
| It only affects the sight-glass indication |
| It lowers the condensing pressure |
| It improves condenser heat transfer |
| It raises the condensing pressure and reduces efficiency |
75
Stredne ťažká
What role do controls play in compressor efficiency?
| They enable optimised operation and lower energy use (e.g. floating head pressure, capacity matching) |
| They matter only in NH₃ systems |
| They provide safety only, with no energy effect |
| They increase the circulating refrigerant charge |
76
Stredne ťažká
How does suction superheat at the compressor affect efficiency?
| Zero suction superheat is optimal |
| Superheat has no effect |
| Excessive superheat reduces efficiency and raises the discharge temperature |
| The higher the superheat, the higher the efficiency |
77
Stredne ťažká
How does correct system layout affect efficiency?
| It doesn't matter |
| It affects only appearance |
| It shortens pipe runs and limits pressure drops and energy losses |
| Longer pipes improve subcooling and always increase efficiency |
78
Stredne ťažká
How important is suction pipe insulation?
| It is needed only for appearance |
| It limits heat gain and excessive superheat, improving efficiency |
| It increases energy consumption |
| It has no effect |
79
Stredne ťažká
Which measure most improves condenser energy efficiency?
| Regular cleaning of heat-exchange surfaces |
| Raising the condensing pressure set point |
| Reducing fan speed to the minimum |
| Increasing the refrigerant charge |
80
Stredne ťažká
Which refrigerants damage the ozone layer?
| All refrigerants containing chlorine or bromine in their molecules |
| All refrigerants containing carbon in their molecules |
| All refrigerants containing fluorine and hydrogen in their molecules |
| All natural refrigerants |
81
Stredne ťažká
How does correct condensing pressure control affect efficiency?
| It is best to keep a constant high condensing pressure all year |
| It keeps the lowest pressure that still ensures proper expansion-valve feed, reducing energy use |
| It always increases energy use |
| It has no effect |
82
Stredne ťažká
How does insulation of heating and DHW pipework affect the efficiency of a heat pump system?
| It increases pressure |
| It reduces energy losses and improves overall system efficiency |
| It impairs cooling |
| It doesn't matter |
83
Stredne ťažká
Which measure most improves the energy efficiency of an air-cooling evaporator?
| Restricting the airflow through the evaporator |
| Increasing the refrigerant charge above nominal |
| Raising the condensing temperature by a few kelvin |
| Defrosting at the right time and keeping the fins clean |
84
Stredne ťažká
What does a Certificate A2 for natural persons (Implementing Regulation (EU) 2024/2215) authorise?
| Only recovery of F-gases from equipment containing less than 3 kg (or 6 kg in hermetically sealed systems) |
| All activities (leak checks, installation, repair, maintenance, servicing, decommissioning, recovery) involving F-gases and hydrocarbons in equipment containing less than 3 kg, or less than 6 kg in labelled hermetically sealed systems |
| All activities involving equipment using CO₂ (R744) |
| Only leak checks that do not entail breaking into the refrigerant circuit |
85
Stredne ťažká
How does too low superheat setting on the TEV affect performance?
| It increases operational safety |
| It reduces refrigerant flow |
| It has no effect |
| It may lead to improved efficiency, but it increases the risk of the compressor becoming flooded with liquid |
86
Stredne ťažká
What is the scope of Regulation (EU) 2024/573?
| Health and safety requirements for brazing and welding on refrigeration installations |
| Limiting emissions, use and marketing of F-gases, HFC phase-down, certification and reporting |
| Design requirements and conformity assessment for pressure equipment |
| Only requirements for periodic leak checks of refrigeration equipment |
87
Stredne ťažká
What is the main design difference in hydrocarbon refrigeration systems?
| Lower energy efficiency |
| The need to eliminate ignition sources and limit the charge because of the refrigerant's flammability |
| No need for safety measures |
| Higher operating pressures |
88
Stredne ťažká
How do compressors used in hydrocarbon systems differ?
| They must be approved by the manufacturer for the specific flammable refrigerant (e.g. electrical components that are not ignition sources, suitable oil) |
| They need no lubrication |
| They must operate at higher pressures than HFC compressors |
| There is no difference |
89
Stredne ťažká
How can you tell that the system has been overcharged with refrigerant?
| It cannot be checked, because the sight glass is not intended for this |
| Under normal operating conditions the condensing pressure and subcooling rise markedly because excess liquid floods the condenser and reduces its active surface |
| Even under a very small heat load, frost forms on the suction line |
| The compressor runs at a lower load and the suction pressure drops |
90
Stredne ťažká
Before charging the unit with refrigerant, it is essential to…
| …carry out a tightness test (and evacuate the system) |
| …fill in the unit's data sheet |
| …check the compressor suction and discharge connections |
| …carry out a trial start-up |
91
Stredne ťažká
What information must appear on the label of equipment containing F-gases?
| Only the trade name of the refrigerant and the unit's serial number |
| That it contains an F-gas, its designation, quantity in kg and t CO₂ eq, and GWP |
| The manufacturer's logo, the unit weight and year of manufacture from the rating plate |
| The weight and capacity of the pipework and the colour code of the casing paint |
92
Stredne ťažká
Which set of information best reflects the content of the equipment records required by Regulation (EU) 2024/573?
| Operator details, equipment details, type and quantity of refrigerant, and information on servicing and repairs |
| The owner, installer and service technician of the unit |
| Only the date of installation and the installer's name |
| The make and model of the unit |
93
Stredne ťažká
Who is responsible for keeping the equipment records?
| There is no such obligation. |
| The operator of the unit or system. |
| The equipment maintenance technician. |
| The person responsible for risk assessment. |
94
Stredne ťažká
Where are oil traps installed on the suction line?
| Immediately before the compressor suction connection |
| At the inlet to every component of the refrigeration system |
| At the bottom of vertical suction risers with upward flow |
| Before the safety valve on the suction side |
95
Stredne ťažká
Which symptoms with the compressor running indicate a refrigerant leak (undercharge)?
| Rising liquid level in the receiver and increasing subcooling |
| Low suction pressure, high superheat and negligible subcooling |
| Rising condensing and suction pressures with no superheat |
| Sight glass full of liquid and rising oil level in the crankcase |
96
Stredne ťažká
Which components of a refrigeration system are potential leak points subject to leak checks?
| Hermetic compressors, liquid receivers and liquid separators |
| Only suction-side components |
| Only high-pressure-side components |
| Joints, valves (including stems), seals (including those on replaceable filters and driers), parts subject to vibration and connections to safety and measuring devices |
97
Stredne ťažká
What pressure is used for the pressure tightness test of an installation?
| Always 30 bar |
| A pressure chosen by the technician based on experience |
| A pressure equal to the maximum pressure measured during operation |
| The pressure specified in EN 378-2 or by the manufacturer, not exceeding the maximum allowable pressure of the system (PS) |
98
Stredne ťažká
At which points of the unit must the leak check be carried out?
| Only at connections of measuring instruments |
| Only on discharge-side components |
| At all points where there is a potential risk of refrigerant leakage |
| Only on compressor shut-off valves, solenoid valves and filters |
99
Stredne ťažká
When can a unit be considered tight after a pressure test?
| When gas bubbles appear after immersion in water |
| When the pressure drop does not exceed 0.1 bar regardless of the test duration |
| When the pressure remains constant during the test (allowing for temperature-related changes); any unexplained pressure drop requires the leak to be located |
| When it has been checked with a fixed electronic detector |
100
Stredne ťažká
Which legal act currently sets out the obligation to check stationary refrigeration equipment containing F-gases for leaks, and how often this must be done?
| Commission Regulation (EC) No 1516/2007 |
| Implementing Regulation (EU) 2024/2215 |
| Regulation (EU) 2024/573 |
| Regulation (EU) No 517/2014 |
101
Stredne ťažká
How should the pressure be increased during a pressure tightness test?
| As quickly as possible |
| In any way |
| Gradually, in stages, checking for leaks at each level until the test pressure is reached |
| In one step, by fully opening the nitrogen cylinder valve |
102
Stredne ťažká
What electronic equipment should be used for leak checking?
| Only hot-cathode devices |
| Detectors suited to the refrigerant in the system, with appropriate sensitivity, checked periodically |
| Only devices with an 'ion pump' sensor |
| Only detectors with an infrared sensor |
103
Stredne ťažká
What documentation should be checked before starting a leak check?
| The operator's fixed-asset inventory ledger |
| Only the installation invoice and the first start-up report |
| Attendance sheets of the plant-room staff for the year |
| The equipment records – especially recurring problems and previous leaks |
104
Stredne ťažká
What information must be recorded in the leak check report?
| Date, number and location of leaks, how they were repaired, technician details and signature |
| The date, a general note about the leak and the operator's signature |
| The method used, the time spent on site and the cost of repair |
| Only the number of leaks found and the date of the check |
105
Stredne ťažká
What pressure should be used for the pressure tightness test?
| Always 10–12 bar |
| A pressure not exceeding the maximum allowable pressure of the system (PS) |
| Any pressure, at the technician's discretion |
| Always 2–3 bar |
106
Stredne ťažká
What is the temperature glide of a refrigerant?
| The temperature rise of the vapour in the compressor |
| The temperature drop of the refrigerant across the expansion valve |
| A property of single-component refrigerants, for which one saturation temperature corresponds to a given pressure |
| In zeotropic mixtures, the difference between the temperatures at the start and end of a phase change (boiling or condensation) at constant pressure |
107
Stredne ťažká
In which equipment is a leakage detection system required?
| Equipment with 50 t CO₂ eq or more of F-gases, regardless of equipment type |
| Equipment with 30 kg or more of F-gases, regardless of their GWP |
| Equipment with 5 t CO₂ eq or more of F-gases, regardless of equipment type |
| Equipment with ≥ 500 t CO₂ eq of Annex I F-gases (or ≥ 100 kg of Annex II Section 1 gases) |
108
Stredne ťažká
What should you check before using a portable electronic leak detector?
| That it suits the refrigerant and has been checked as the manufacturer requires |
| That it has an infrared sensor, as only this type is permitted |
| That it holds a valid UDT inspection certificate |
| That it has been zeroed close to the suspected leak point |
109
Stredne ťažká
Which certificate types (A1, A2, B, C, D, E) authorise leak checks of equipment containing F-gases?
| Only A1 and A2 |
| All except D |
| Only E |
| A1, A2 and E |
110
Stredne ťažká
Why is it advisable to subcool the liquid refrigerant?
| To allow a smaller expansion valve to be used |
| To allow a condenser with a smaller heat-exchange surface to be used |
| To lower the evaporating temperature in the evaporator |
| To ensure that liquid free of vapour bubbles enters the expansion valve |
111
Stredne ťažká
What must be done after repairing a leak in the refrigeration unit of a refrigerated trailer?
| Charge an alternative refrigerant, start up and measure the parameters |
| Update the equipment records and carry out a leak check (it may be done directly after repair) |
| Issue the invoice and leave the leak check to the next periodic service |
| Visually inspect only the bolted and brazed joints near the repair |
112
Stredne ťažká
Recovery of fluorinated greenhouse gases means:
| The reprocessing of fluorinated greenhouse gases to achieve their specified standard properties. |
| The collection and storage of fluorinated greenhouse gases from containers, products and equipment during maintenance or servicing or prior to their disposal. |
| The reuse of fluorinated greenhouse gases following a basic purification process. |
| The final decommissioning and withdrawal from service or use of a product or piece of equipment containing fluorinated greenhouse gases. |
113
Stredne ťažká
Who is authorised to recover refrigerant from stationary refrigeration equipment containing F-gases?
| The operator |
| The owner of the installation |
| The administrator of the operator's account in the register |
| A natural person holding a certificate of the relevant type (A1; A2. or D within their charge limit) |
114
Stredne ťažká
How must recovered refrigerants be stored?
| In any pressure vessel that has some form of approval |
| In a disposable (non-refillable) cylinder that held the same refrigerant |
| In any used refrigerant cylinder, provided it is leak-tight |
| In a labelled recovery cylinder with a dual valve and a valid inspection |
115
Stredne ťažká
When should the recovery of fluorinated greenhouse gases be carried out:
| Only prior to the final disposal of equipment. |
| Before each leak test of the equipment. |
| Before the final disposal of equipment and, where applicable, during its servicing and maintenance. |
| Always during servicing and maintenance of equipment. |
116
Stredne ťažká
What should be done if recovered refrigerant is contaminated (e.g. with acid, air or moisture)?
| Pass it through a particle filter and reuse it |
| Clean the mixture yourself using a filter-drier |
| Add a special contaminant neutraliser |
| Hand it over to a specialised, authorised company for reclamation or destruction |
117
Stredne ťažká
What should be done if different refrigerants have been mixed in a storage cylinder?
| Hand the mixture over to an authorised company – as a rule for destruction |
| Add a special refrigerant to the mixture |
| Separate the mixture into its components yourself |
| Pass it through a filter-drier and reuse it |
118
Stredne ťažká
How does push-pull refrigerant recovery work?
| Refrigerant is drawn alternately from the suction and discharge sides of the compressor |
| The recovery unit draws vapour from the recovery cylinder and pushes it into the system; the pressure difference forces liquid refrigerant out of the system into the cylinder |
| Nitrogen is injected into the system, pushing the refrigerant into the atmosphere |
| The recovery unit draws vapour from the system and condenses it in the cylinder |
119
Stredne ťažká
What are the options for managing waste refrigerant?
| Recovery, disposal |
| Reclamation, recovery |
| Disposal, storage |
| Recycling, reclamation, destruction |
120
Stredne ťažká
Which management option restores recovered refrigerant to a quality equivalent to virgin product, so that it can be used by any undertaking?
| Destruction |
| Storage |
| Reclamation |
| Recycling |
121
Stredne ťažká
The lower the evaporating temperature, …
| …the lower the density of the suction vapour and the lower the refrigerant mass flow rate |
| …the greater the density of the suction vapour and the greater the refrigerant mass flow rate |
| …the greater the density of the suction vapour and the lower the refrigerant mass flow rate |
| …the lower the density of the suction vapour and the greater the cooling capacity of the compressor |
122
Stredne ťažká
How must transportable pressure vessels (e.g. refrigerant cylinders) be marked?
| With the manufacturer's logo and date of manufacture |
| The marking is optional |
| Among other things: the number of the design and testing standard, marks of the approving country and the inspection body, the date of the initial inspection, and the manufacturer's and operational marks |
| Only with weight and capacity marks |
123
Stredne ťažká
The recovery of refrigerants does not require the use of:
| A refrigerant recovery station. |
| Hoses with shut-off valves. |
| Scales with a measurement range suitable for the size of the cylinder being filled. |
| An electronic leak detector. |
124
Stredne ťažká
What functions does the compressor perform in a refrigeration system?
| The compressor draws in refrigerant vapour from the evaporator, compresses it, and then forces it into the condenser, raising the pressure to the required condensing pressure. |
| The compressor condenses the refrigerant. |
| The compressor creates a vacuum on the suction side of the system |
| The compressor compresses ambient air and increases the pressure of the refrigerant. |
125
Stredne ťažká
What is compressor flooding (liquid slugging)?
| Excess oil in the condenser |
| A large amount of liquid refrigerant in a flooded evaporator, which is a normal operating condition |
| Liquid refrigerant or oil entering the compression chamber |
| Flooding of the compressor by rainwater |
126
Stredne ťažká
Within what range is the compressor motor speed typically controlled using a frequency inverter?
| Approximately 30 to 75 Hz, corresponding to about 60–150% of nominal capacity (depending on the compressor manufacturer) |
| Speed control does not change the cooling capacity |
| By a maximum of 10% |
| From approximately 10% to 90% of nominal capacity |
127
Stredne ťažká
Why is it essential to observe the correct phase sequence for scroll compressors and screw compressors?
| Because the motor speed would decrease, and consequently the compressor’s capacity. |
| Because these types of compressors are sensitive to voltage drops. |
| Because changing the phase sequence would reverse the direction of rotation of the compressor rotors, which could result in damage to the compressors. |
| Because this type of compressor has difficulty starting up if the phase sequence is changed. |
128
Stredne ťažká
What compression ratio should each stage of a two-stage vapour-compression system have (rule of thumb)?
| Greater than 18 |
| Equal to 1 |
| Less than approximately 8 |
| Greater than 10 |
129
Stredne ťažká
Why is a shaft seal necessary in open-type compressors?
| Only to prevent oil leakage |
| To prevent air from entering and refrigerant from leaking out of the compressor |
| To ensure the bearing remains lubricated |
| To protect the crankshaft bearing |
130
Stredne ťažká
How can you check whether the liquid refrigerant is sufficiently subcooled?
| Compare the liquid-line temperature with the saturation temperature at the measured condensing pressure |
| Check whether the whole evaporator surface is covered with an even layer of frost |
| Check whether the liquid distributor upstream of the evaporator feels warm |
| Check by touch whether the condenser outlet is noticeably colder than ambient |
131
Stredne ťažká
Why is the compressor crankcase heated?
| To keep the lubricating oil liquid |
| To dehydrate the oil |
| To increase dissolution of refrigerant in the oil and improve its viscosity |
| To limit refrigerant migration into, and dissolution in, the oil during standstill |
132
Stredne ťažká
What are compressor packs (racks)?
| Several air-cooled condensers |
| Units with two-stage compressors |
| Sets of compressors connected in any configuration |
| Several compressors connected in parallel on a common frame with common suction and discharge headers |
133
Stredne ťažká
What is the main advantage of multi-compressor packs?
| No need for compressor controls and safety devices |
| Stepwise capacity matching to demand, plus redundancy |
| A smaller refrigerant charge than a single-compressor system |
| Low purchase cost and easy installation without special controls |
134
Stredne ťažká
What is meant by the operating envelope (application range) of a compressor?
| The capacity, refrigerant type and dimensions of the compressor |
| The permissible range of evaporating and condensing temperatures (to, tk), or the corresponding pressures, within which the compressor may operate |
| A range determined by the evaporating temperature at a given ambient temperature |
| A range determined only by the evaporating temperature |
135
Stredne ťažká
What are the basic functions of oil in a compressor?
| Absorbing moisture from the refrigerant |
| Lubricating bearings and sliding surfaces, removing heat, and sealing clearances (e.g. between piston and cylinder, or rotors) |
| Increasing the cooling capacity of the refrigerant |
| Sealing leaks that develop in the installation |
136
Stredne ťažká
What are the most effective ways of controlling compressor cooling capacity?
| An expansion valve |
| Pressure control valves |
| Partially covering the evaporator |
| Changing the displacement: varying the rotational speed or unloading cylinders |
137
Stredne ťažká
What does hot-gas bypass capacity control involve?
| High-pressure liquid is injected into the suction to increase capacity |
| The compressor speed is varied |
| Part of the hot discharge gas is passed through a bypass valve to the suction side (or evaporator inlet), reducing the effective capacity |
| Bypass is not used for capacity control |
138
Stredne ťažká
What is the fundamental difference between hermetic and semi-hermetic compressors?
| Semi-hermetic compressors run more quietly as a complete unit |
| Both can be dismantled; they differ only in cooling capacity |
| The semi-hermetic casing is bolted (can be opened); the hermetic one is welded |
| The semi-hermetic compressor has no motor inside the casing |
139
Stredne ťažká
How does a scroll compressor work?
| It is a positive-displacement compressor in which compression results from the interaction of a fixed and an orbiting scroll. |
| A scroll compressor is also known as a turbo compressor. |
| It uses two screws to compress the refrigerant. |
| It is a type of piston-type device. |
140
Stredne ťažká
What physical process takes place in the evaporator?
| The refrigerant is subcooled as a liquid |
| The liquid refrigerant evaporates, absorbing heat, and the vapour is slightly superheated at the outlet |
| The refrigerant condenses |
| The secondary fluid (glycol, water) evaporates while the refrigerant condenses |
141
Stredne ťažká
What is the purpose of compressor capacity control?
| To match the cooling capacity to the current demand |
| To ensure compressor lubrication |
| To match capacity to the condensing temperature |
| To increase the condensing pressure |
142
Stredne ťažká
Why is inverter speed control advantageous for refrigeration compressors?
| It enables continuous, smooth control of cooling capacity |
| It increases compressor capacity above nominal at any frequency |
| Reducing the speed improves oil return to the compressor |
| It can be used with any compressor to ensure lubrication |
143
Stredne ťažká
Does the suction gas temperature affect the cooling capacity of the compressor?
| Yes, but only if the suction gas is deeply cooled |
| Yes, but only in reciprocating compressors, not scroll |
| Yes – higher temperature lowers vapour density, mass flow and capacity |
| No – capacity depends only on the compressor displacement |
144
Stredne ťažká
In the case of compressor units fitted with an oil level control system, is it necessary to install the compressors at the same height?
| Yes. |
| Only scroll compressors. |
| Only screw compressors. |
| No. |
145
Stredne ťažká
What functions does a compressor powered by the vehicle’s engine perform in a transport refrigeration system?
| This compressor creates a vacuum on the suction side of the system whilst the vehicle’s engine is switched off. |
| The compressor compresses ambient air and increases the pressure of the refrigerant. |
| This compressor condenses the refrigerant whilst the vehicle is in motion. |
| This compressor draws in refrigerant vapour from the evaporator, compresses it and then forces it into the condenser whilst the vehicle’s engine is running. |
146
Stredne ťažká
Which media most commonly absorb heat from the refrigerant in the condenser?
| Ammonia |
| Air and CO₂ |
| Only a water–glycol mixture |
| Air or water |
147
Stredne ťažká
What is the function of the condenser in refrigeration systems?
| Releasing only the heat from the compressor into the surroundings |
| Releasing to the environment the heat absorbed in the evaporator and the heat added during compression |
| Releasing only the heat absorbed in the evaporator into the surroundings |
| Absorption of heat rejected in the regenerative heat exchanger |
148
Stredne ťažká
If the refrigerant temperature on the high-pressure side is above its critical temperature, condensation…
| …always occurs regardless of temperature |
| …occurs provided a special condenser is used |
| …does not occur |
| …does not depend on temperature |
149
Stredne ťažká
How is liquid subcooling usually achieved in a refrigeration system?
| With an additional heat exchanger using liquid nitrogen |
| In the final section of the condenser (or in an additional subcooler) |
| With hot high-pressure vapour |
| By dissolving the refrigerant in oil |
150
Stredne ťažká
What is the purpose of condenser fan speed control?
| To disperse refrigerant in the event of a leak |
| To reduce energy efficiency |
| Only to protect against exceeding the maximum condensing pressure |
| To keep the condensing pressure at the correct level |
151
Stredne ťažká
Which international agreement introduced the global phase-down of HFC production and consumption?
| The Kyoto Protocol |
| The Vienna Convention for the Protection of the Ozone Layer |
| The Paris Agreement |
| The Kigali Amendment to the Montreal Protocol |
152
Stredne ťažká
Which international treaty governs the phase-out of ozone-depleting substances (CFCs, HCFCs)?
| The Montreal Protocol |
| The Paris Agreement |
| The Stockholm Convention |
| The UN Framework Convention on Climate Change (UNFCCC) |
153
Stredne ťažká
Can HFC refrigerant recovered during a repair be put straight back into the same equipment without any cleaning (filtering/drying)?
| No – recovered F-gas may be used for filling only after it has been recycled or reclaimed |
| Yes, if the operator agrees |
| Yes, if less than 24 hours have passed |
| Yes, always |
154
Stredne ťažká
Who may purchase HFCs for servicing refrigeration equipment?
| Any business |
| Any adult |
| Only the equipment operator |
| Only a person holding the relevant certificate or an undertaking employing such persons |
155
Stredne ťažká
Under what condition may non-hermetically sealed split air conditioning charged with F-gas be sold to an end user?
| Unconditionally |
| When the user signs a statement that they will install it themselves |
| When evidence is provided that installation will be carried out by a certified undertaking |
| Only if the unit contains less than 3 kg of refrigerant |
156
Stredne ťažká
By when must the holder of an F-gas certificate issued under Regulation (EU) No 517/2014 first complete refresher training or an evaluation process?
| By 12 March 2025 |
| By 12 March 2029 (and then at least every 7 years) |
| By 31 December 2030 |
| Never – the certificate is valid indefinitely |
157
Stredne ťažká
What must the holder of a Category I certificate (Regulation 2015/2067) do to continue using it?
| Update their knowledge to the level of Certificate E |
| Apply for an extension without training |
| Nothing – Category I automatically becomes A1 |
| Update their knowledge and skills to the level of Certificate A1 (Annex I to Regulation 2024/2215) |
158
Stredne ťažká
What does Certificate C under Implementing Regulation (EU) 2024/2215 authorise?
| Recovery of F-gases from equipment <3 kg |
| All activities in Article 2(1) in relation to ammonia (NH₃) |
| All activities in relation to CO₂ |
| Leak checks without breaking into the circuit |
159
Stredne ťažká
May a person enrolled in a certification training course carry out certified activities?
| No, never |
| Yes – independently, for 6 months |
| Yes – under the supervision of a certified person, for no more than 24 months in total |
| Yes – with no time limit, if employed by a certified company |
160
Stredne ťažká
How long must the operator keep the records of equipment subject to leak checks, if they are not kept in a national database?
| At least 2 years |
| At least 5 years |
| Until the equipment is decommissioned |
| At least 1 year |
161
Stredne ťažká
What distinguishes class 2L refrigerants from class 2?
| Heat of combustion above 19 MJ/kg |
| No lower flammability limit |
| Higher toxicity |
| A maximum burning velocity of no more than 10 cm/s |
162
Stredne ťažká
What is the lower flammability limit (LFL) of propane R290?
| Approx. 0.307 kg/m³ |
| Approx. 0.038 kg/m³ (approx. 2.1% by volume) |
| Approx. 1.8 kg/m³ |
| Approx. 0.38 kg/m³ |
163
Stredne ťažká
Equipment marked 'Ex II 3G' may be used in zone:
| 20 (dusts) |
| 1 |
| 0 |
| 2 (explosive gas atmosphere unlikely and short-lived) |
164
Stredne ťažká
How is explosion hazard zone 2 defined?
| An explosive atmosphere is likely to occur in normal operation |
| An area where flammable refrigerants are never used |
| An explosive atmosphere is present continuously or for long periods |
| An explosive atmosphere is not likely in normal operation and, if it occurs, persists only for a short period |
165
Stredne ťažká
Under which UN number is propane (R290) carried under ADR?
| UN 3252 |
| UN 1978 |
| UN 3337 |
| UN 1005 |
166
Stredne ťažká
At what concentration should a portable flammable gas detector used for R290 work raise an alarm at the latest?
| At 150% of LFL |
| At 100% of LFL |
| At 5% propane by volume |
| No higher than 25% of LFL |
167
Stredne ťažká
How should a recovery cylinder be prepared before filling it with a hydrocarbon refrigerant?
| Purge it with compressed air |
| Evacuate it (no air) and label it for the specific flammable refrigerant |
| Partly fill it with nitrogen to 5 bar |
| No preparation is needed |
168
Stredne ťažká
What is the correct approach in a risk analysis before work on an HC system?
| First select PPE, then possibly remove ignition sources |
| First eliminate hazard sources (e.g. ignition sources); where this is not possible, identify them and apply mitigating measures (ventilation, detection, PPE) |
| The risk analysis is done after the work is finished |
| Having a fire extinguisher is sufficient |
169
Stredne ťažká
Which property of ammonia helps people detect a leak early?
| It is denser than air |
| It is odourless |
| A very low odour threshold (a few ppm) |
| It is yellow in air |
170
Stredne ťažká
What hazard does a large CO₂ leak in an enclosed room pose to people?
| Accumulation near the floor and asphyxiating/toxic effects at high concentrations |
| CO₂ is completely safe |
| Explosion of the mixture with air |
| Formation of hydrogen fluoride |
171
Stredne ťažká
What is floating head pressure and what does it achieve?
| It lets the condensing pressure fall with ambient temperature, reducing compressor work and raising COP (requires an expansion valve that works at a small pressure difference) |
| It increases subcooling by flooding the condenser |
| It keeps a constant high condensing pressure all year |
| It means switching condenser fans off periodically |
172
Stredne ťažká
How do SEER/SCOP differ from EER/COP?
| SEER/SCOP apply only to natural-refrigerant equipment |
| SEER/SCOP are seasonal indicators accounting for part load and climate (EN 14825); EER/COP refer to a single operating point (EN 14511) |
| There is no difference – they are synonyms |
| EER/COP are always higher than SEER/SCOP |
173
Stredne ťažká
Which design approach can significantly reduce the F-gas charge of a large refrigeration installation?
| Larger liquid-line diameters |
| Adding a second liquid receiver |
| An indirect (secondary-coolant) system or a cascade with a natural refrigerant in the low stage, plus heat exchangers with small internal volume |
| Omitting pipe insulation |
174
Stredne ťažká
Why must the charge of small, critically charged R290 systems be weighed to within a few grams during service?
| Because extra R290 improves efficiency |
| Because scales are not needed – charging is done by sight glass |
| Because R290 is more expensive than HFCs |
| Small charge deviations significantly change superheat/subcooling and efficiency, and overcharge increases the risk in a leak |
175
Stredne ťažká
Which information must be entered in the equipment records after a leak check?
| The date and result of the check and the identity of the undertaking and person who performed it (with certificate number) |
| Only the operator's signature |
| Only the date of the check |
| Only the equipment's energy consumption |
176
Stredne ťažká
What must be done when an indirect method (e.g. parameter analysis) indicates a possible leak?
| Record it and check at the next periodic inspection |
| Nothing – indirect methods are sufficient |
| Top up the refrigerant and end the check |
| Carry out a direct-method examination to locate the leak |



