F-Gas English Low GWP

Všetky otázky
HFC | Flammable | CO₂ | NH₃
Ľahké otázky | Stredne ťažké otázky | Ťažké otázky

1

Stredne ťažká

What is R1270?


Propane
Propene (propylene)
n-Butane
Isobutane

2

Stredne ťažká

What is the main design difference in hydrocarbon refrigeration systems?


The need to eliminate ignition sources and limit the charge because of the refrigerant's flammability
Lower energy efficiency
Higher operating pressures
No need for safety measures

3

Stredne ťažká

How do compressors used in hydrocarbon systems differ?


There is no difference
They must be approved by the manufacturer for the specific flammable refrigerant (e.g. electrical components that are not ignition sources, suitable oil)
They must operate at higher pressures than HFC compressors
They need no lubrication

4

Stredne ťažká

What distinguishes class 2L refrigerants from class 2?


Higher toxicity
A maximum burning velocity of no more than 10 cm/s
Heat of combustion above 19 MJ/kg
No lower flammability limit

5

Stredne ťažká

What is the lower flammability limit (LFL) of propane R290?


Approx. 0.038 kg/m³ (approx. 2.1% by volume)
Approx. 0.38 kg/m³
Approx. 0.307 kg/m³
Approx. 1.8 kg/m³

6

Stredne ťažká

Equipment marked 'Ex II 3G' may be used in zone:


20 (dusts)
0
2 (explosive gas atmosphere unlikely and short-lived)
1

7

Stredne ťažká

How is explosion hazard zone 2 defined?


An area where flammable refrigerants are never used
An explosive atmosphere is not likely in normal operation and, if it occurs, persists only for a short period
An explosive atmosphere is present continuously or for long periods
An explosive atmosphere is likely to occur in normal operation

8

Stredne ťažká

Under which UN number is propane (R290) carried under ADR?


UN 3252
UN 3337
UN 1005
UN 1978

9

Stredne ťažká

At what concentration should a portable flammable gas detector used for R290 work raise an alarm at the latest?


No higher than 25% of LFL
At 100% of LFL
At 150% of LFL
At 5% propane by volume

10

Stredne ťažká

How should a recovery cylinder be prepared before filling it with a hydrocarbon refrigerant?


Evacuate it (no air) and label it for the specific flammable refrigerant
Partly fill it with nitrogen to 5 bar
Purge it with compressed air
No preparation is needed

11

Stredne ťažká

What is the correct approach in a risk analysis before work on an HC system?


Having a fire extinguisher is sufficient
First eliminate hazard sources (e.g. ignition sources); where this is not possible, identify them and apply mitigating measures (ventilation, detection, PPE)
First select PPE, then possibly remove ignition sources
The risk analysis is done after the work is finished

12

Stredne ťažká

Why must the charge of small, critically charged R290 systems be weighed to within a few grams during service?


Because extra R290 improves efficiency
Because scales are not needed – charging is done by sight glass
Small charge deviations significantly change superheat/subcooling and efficiency, and overcharge increases the risk in a leak
Because R290 is more expensive than HFCs